I have a traditional ie non smart Economy 10 meter with digital readings. Is Rate 1 peak Rate and Rate 2 of peak?

Firedog
FiredogBest Answer
Super User
January 19, 2024

Updated on 22/09/26 by Chris_OVO

 

Thanks, that’s excellent - the more documentation, the better!

 

This is a complete nightmare, now that you’ve revealed the problem with the meter clock. Modern meters have a backup battery that keeps the clock ticking over - keeping time - even though there’s a power cut. I can’t find any details about your Type S123C03 meter, but it may be that it either doesn’t have a backup battery, or if it does, it’s flat. but this is what I think the situation is:

 

(Numbering your latest images from the top down)

  • No. 4 shows that you took the pictures at 16:07 meter time.
  • No. 5 shows that at that point, the current rate was Rate 2, reading 07085.
  • No. 3 shows that 16:07 is in the second daily offpeak slot, 13:30 - 16:30.
  • Ergo, Rate 2 is offpeak as far as the meter is concerned.
  •  No. 2 shows that Rate 2 readings (in the 07000 series) are (wrongly) applied to your account as if they were peak readings, confirming what you’ve suspected all along. 
  • No. 1 shows that you have been billed at the higher rate for what the account thinks is peak consumption.
  • No. 2 shows that something happened between March and July last year; the registers swapped places in the listing, but the readings were still applied as if they hadn’t. Was this something you instigated - by asking Support to reverse the registers, for example?
     

This is an impossible situation that may not be resolvable, unless you know and can prove exactly when the clock went wrong. Even assuming that it’s been wrong for the past year, it will take a really determined operative and a supercomputer ages to adjust the consumption figures to the correct times, and of course that wouldn’t make sense until the meter clock has been put right or - preferably - the meter exchanged for a modern smart one. You’ve been diddled out of at most about £20 in the past year, which I’m sure OVO would be happy to compensate you for once they’ve acknowledged the fault. 

 

Now, there is little difference between your peak and offpeak usage according to your readings page (80 peak and 75 offpeak in 120 days). I would call this extremely light usage (1.3 kWh/day), so I wonder where else you’re getting energy from. If your storage heaters are being switched on and off automatically at the right times according to your plan, I’d expect the off-peak consumption to be a lot higher during the winter, but it’s impossible to say how much higher. 

 

The first thing is to get the meter sorted out. Do any of your neighbours in that enchanting spot have working smart meters? I’m not saying that that would be the end of your troubles, because getting smart meters to work with Economy 10 hasn’t proved problem-free for some customers. But I’d say it’s a prerequisite for any further action: How to book a smart meter appointment on your online account or OVO app | (ovoenergy.com) 

 

If you’ve got a faulty economy 10 meter then we can replace it free of charge with a smart meter. our Support Team can arrange this for you. You can find our guide for economy 10 here.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |

20 replies

Firedog
Super User
Super User
January 19, 2024

I am being billed for off peak electricity at peak rates, 

 

OK, that’s a real cause for concern. I’d really like to see the evidence for this situation; other cases where we’ve seen E10 customers billed for offpeak usage at peak rates and vice versa have apparently resulted from misconfiguration of their smart meters. That’s clearly not your problem, so the fault seems to lie with billing.

It would help if you could post screenshots of:

  • your Plan page showing the rates and timings;
  • your Readings page;
  • the Electricity in detail page of your latest bill showing the charges and readings on which the bill is based.

(None of that contains any personal information you’d want to keep private.)

It should be fairly obvious from these images where the fault is arising, and it will simplify making your case to Support: if you use webchat, you can copy the images into the chat to get them added to your account notes. 

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
Jack OatAuthor
Rank 2
January 19, 2024

Hello again Firedog, you had better know one or two other facts which complicate matters. Firstly the meter is faulty with regard to the time. I have included two screenshots of images I took where the time of the images being taken does not correspond with the time on the the meter clock- currently it is running approximately 4hrs 42 mins behind GMT. 

SSE, as it was then, sent an engineer to change the meter but he advised me not to go ahead with this because I would lose evidence for the incorrect readings. He agreed that the readings were the wrong way round but also checked the wiring to see if the meter had been installed incorrectly, which it hadn’t. He was supposed to let SSE know his findings. I subsequently contacted them on their complaints page but received no response.

That all said, using the timings on the meters, and having looked at the information you asked for, it is now clear to me that Rate 1 is Peak and rate2 is off peak and therefore I am correct in thinking the readings are the wrong way round on my bills.

Thank you very much for directing me to the information needed for proof of this, however, I would be grateful if you would confirm my conclusions please.

Thanks again!

 

 

 

 

 

 

Firedog
Super User
FiredogSuper UserBest Answer
Super User
January 19, 2024

Updated on 22/09/26 by Chris_OVO

 

Thanks, that’s excellent - the more documentation, the better!

 

This is a complete nightmare, now that you’ve revealed the problem with the meter clock. Modern meters have a backup battery that keeps the clock ticking over - keeping time - even though there’s a power cut. I can’t find any details about your Type S123C03 meter, but it may be that it either doesn’t have a backup battery, or if it does, it’s flat. but this is what I think the situation is:

 

(Numbering your latest images from the top down)

  • No. 4 shows that you took the pictures at 16:07 meter time.
  • No. 5 shows that at that point, the current rate was Rate 2, reading 07085.
  • No. 3 shows that 16:07 is in the second daily offpeak slot, 13:30 - 16:30.
  • Ergo, Rate 2 is offpeak as far as the meter is concerned.
  •  No. 2 shows that Rate 2 readings (in the 07000 series) are (wrongly) applied to your account as if they were peak readings, confirming what you’ve suspected all along. 
  • No. 1 shows that you have been billed at the higher rate for what the account thinks is peak consumption.
  • No. 2 shows that something happened between March and July last year; the registers swapped places in the listing, but the readings were still applied as if they hadn’t. Was this something you instigated - by asking Support to reverse the registers, for example?
     

This is an impossible situation that may not be resolvable, unless you know and can prove exactly when the clock went wrong. Even assuming that it’s been wrong for the past year, it will take a really determined operative and a supercomputer ages to adjust the consumption figures to the correct times, and of course that wouldn’t make sense until the meter clock has been put right or - preferably - the meter exchanged for a modern smart one. You’ve been diddled out of at most about £20 in the past year, which I’m sure OVO would be happy to compensate you for once they’ve acknowledged the fault. 

 

Now, there is little difference between your peak and offpeak usage according to your readings page (80 peak and 75 offpeak in 120 days). I would call this extremely light usage (1.3 kWh/day), so I wonder where else you’re getting energy from. If your storage heaters are being switched on and off automatically at the right times according to your plan, I’d expect the off-peak consumption to be a lot higher during the winter, but it’s impossible to say how much higher. 

 

The first thing is to get the meter sorted out. Do any of your neighbours in that enchanting spot have working smart meters? I’m not saying that that would be the end of your troubles, because getting smart meters to work with Economy 10 hasn’t proved problem-free for some customers. But I’d say it’s a prerequisite for any further action: How to book a smart meter appointment on your online account or OVO app | (ovoenergy.com) 

 

If you’ve got a faulty economy 10 meter then we can replace it free of charge with a smart meter. our Support Team can arrange this for you. You can find our guide for economy 10 here.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
Jack OatAuthor
Rank 2
January 19, 2024

First of all thanks for all the time you have spent on this and for your advice.

Having raised the issue of the faulty clock, I think that it is probably irrelevant anyway as the meter shows what rate it is recording at any one time with NOW on the display, and therefore I think that the readings are correct (albeit the wrong way round) and the meter just switches to a different rate as it should according to the time schedule for Economy 10, but 4hrs 40mins out.

As far as the low usage is concerned, especially recently, this is due to two things. It is a second home and we switch off all circuits on the CU when we are not there, and secondly we have stopped using the storage heaters even in really cold weather as they are so expensive to run especially as we are being charged at peak rate for them. We rely on a woodburner, plenty of jumpers and a thick duvet.

 

You’re absolutely correct, it’s a lovely spot and we’re very lucky to have it.

 

I’ll now write to OVO using the web chat as you suggested and include appropriate evidence.

Have a good weekend, you deserve it!

 

 

 

Emmanuelle_OVO
Retired Moderator
Retired Moderator
January 22, 2024

Hey @Jack Oat,

 

Welcome to the OVO Online Community,

 

Did the support team get this sorted for you? 

 

I can see Firedog has already given some brilliant advice here, just wanted to add, an easy way to check which register is peak or off peak is to see which register clocks during ‘peak’ hours.

 

That’s presuming a customer knows what hours are peak or off peak, usually simple for Economy 7 and more difficult for Economy 10. 

Renewable Energy? Big Fan.
Jack OatAuthor
Rank 2
January 22, 2024

Yes, thank you I now have the evidence I need to ask for my meter readings to be reversed and ask for a refund.

Firedog was excellent, thorough, prompt, knowledgeable and gave good advice.

Newcomer
May 13, 2026

My meter reading this month is lower tha last months 

Peter E
Super User
Super User
May 13, 2026

I'm guessing that this is the meter reading that you gave? I don't think that is possible if the meter is read automatically. i.e. You have a smart meter. If it's a manual reading it's possible you made a mistake with the previous reading. 

 

Perhaps you could give us more details so we can identify any possible issue. Many thanks for reaching out to us.

 

Peter

 

Reducing my yearly fossil fuel usage with an EV (-900 litres petrol saving about £950/year), A2AHP (-8,700 kWh gas, cost neutral) and Timed Immersion heater (-1,500 kWh gas, £20/year more expensive but reducing as the gas price goes up)
Nukecad
Super User
Super User
May 14, 2026

As Peter E says you will need to give us more details for anyone to work out what may have happened.
In particular if you could tell us the following:

  • Where are you seeing these readings? On the meter itself or on your billing/account?
  • What was the reading last month? If on the billing then was it an estimate or one that you sent in?
  • What is the reading this month? If on the billing then Is it an Estimate or one that you sent in?

Without knowing the answers to those questions we are just guessing.

I said, Hey - Watts going on.
Abby_OVO
Community Manager
Community Manager
May 15, 2026

Hey ​@MoiraF 

 

I’m glad to see a couple of our community members have already stopped by with some useful questions so we can try and help further. 

 

It’s tricky to tell from what you’ve said so far what might be wrong, if you could answer some of PeterE and Nukecad’s questions that’d be really helpful and we’ll do our best to help you out.