Hello! We have recently installed a 12kw Zubadan air heat pump in nov2024. I am not happy with the usage as we used thermostats and it consumed too much - but this is another topic. The issue now is that in january the consumed hot water energy is bigger than the delivered hot water energy: consumed DHW - 186 delivered DHW - 141. How is this possible? I don’t know how the settings are done for hot water, but this not seems physically possible.
We have the model with the 200l hydrotank inside.
Solved
Zubadan shows consumed hot water energy bigger than delivered hot water energy
Best answer by juliamc
I think what you’re seeing with the flow and return temperatures is the heat pump cycling.
This graph shows an example of cycling on an Ecodan of a similar size to yours, its from a government trial which I was on.
The red and green lines show the flow and return temperatures. Cycling results in a poor COP and is a symptom of an oversized heat pump.

Your thermistor reading for TH1A is 26 deg, which I believe is the current room temperature, so I’m not sure why the heating is running at all when you took your previous photos. I need
Reply