What do codes 9-02 and 903 mean on my Daikin heat pump?

 Hello, I have a DAIKIN ERSQ 011AAV1  16KW. I have a BRC21A52 controller and there is a code in the service manual 9-02 that is indicated as Thermo on/off admission with a range -5  till +5. Does anyone what exactly does it do? For example what's the difference between setting it at +5 and -5? There is also another code 9-03 that the step is every 0.2 and it can be set either until +5 or -5 but there isn't any explanation in the manual what is this code about. Any help would be nice. Thank you in advance.

karas21Best Answer
Rank 2
Mar 14, 2026 10:43 AM UTC

Hello. I sent an enquiry to Daikin.co.uk and that was their response.

 

The field settings you're referring to (accessed via the BRC21A52 wired remote controller in service mode) are part of the [9] group for automatic temperature compensation in Daikin Altherma high-temperature systems like your ERSQ016AAV1. These allow fine-tuning of thermistor readings and control logic by applying correction values to compensate for temperature differences or system behavior. The ranges and steps may vary slightly by firmware or regional manual, but based on the service documentation for this series, here's the breakdown:

[9-02]: Thermo ON/OFF Admission

  • Description: This setting defines the temperature compensation or hysteresis (deadband) for the thermostat's ON/OFF control logic. It adjusts the threshold at which the system admits (allows) operation based on measured temperatures (e.g., leaving water or ambient). Essentially, it prevents short-cycling by creating a buffer around the setpoint where the system won't toggle on/off unnecessarily. Positive values make the system less sensitive (higher threshold for activation), while negative values make it more sensitive (lower threshold).
  • Range: -5°C to +5°C
  • Step: Typically 1°C (though some variants allow 0.5°C increments, aligning with your example).
  • Default: 0°C (no compensation; standard logic).
  • Difference between +0.5 and -0.5:
    • +0.5°C: Increases the activation threshold. For example, in heating mode, the system might require the temperature to drop 0.5°C below the setpoint before turning ON, and it turns OFF at or above the setpoint. This delays activation for stability in milder conditions.
    • -0.5°C: Decreases the activation threshold. The system turns ON sooner (e.g., at 0.5°C above the setpoint drop) and may stay ON longer. This is useful for quicker response in colder or more demanding conditions but risks more frequent cycling.

[9-03]: (Likely Domestic Hot Water Tank Compensation Value or Related Offset)

  • Description: This code is not always explicitly detailed in user-facing manuals but appears to be a fine adjustment for temperature compensation, possibly related to the domestic hot water (DHW) tank thermistor or a secondary hysteresis/offset for room or water temperature control. It applies a correction to measured values to align with actual conditions, affecting when the system engages for DHW or space heating.
  • Range: -5°C to +5°C
  • Step: 0.2°C (as per your description; this allows precise tuning).
  • Default: 0°C.
  • Purpose: Similar to [9-02], it compensates for discrepancies (e.g., sensor placement or pipe losses). Positive values raise the effective setpoint, negative lower it. Without explicit manual explanation, it's often left at default unless calibration shows inaccuracies.

[9-04]: (Likely Thermo ON/OFF Admission or Time-Related Delay)

  • Description: This setting is tied to the thermo ON/OFF logic, potentially as an additional hysteresis or a time-based parameter for admission (e.g., minimum runtime or delay before ON/OFF to avoid rapid switching). In some contexts, it's a compensation value like the others, but your step/range suggests it may be a timer (e.g., anti-short-cycle delay in minutes). It ensures stable operation by delaying state changes.
  • Range: Up to 60 (likely minutes if time-based; or -5°C to +5°C if temp-based like the others).
  • Step: 10 (e.g., 10, 20, 30...60).
  • Default: 0 or model-specific.
  • Purpose: If temperature-based, similar to [9-02] for finer control. If time-based (matching your step/until 60), it sets a delay period for thermo transitions, preventing wear from frequent starts/stops.

12 replies

Peter E
Super User
Super User
Mar 17, 2026 9:50 AM UTC

The length of pipe directly affects the ability of any heat generator (HP or boiler) to get hot water to the furthest radiators. Ideally you would have the heat source as close to the middle of the system as possible.

 

With a gas boiler you could use thermostatic radiator valves, TRVs, to limit the flow to the nearest radiators so that the other radiators get more of the flow. You can also use the shield valves at the other end of the radiator as well to get a better balance. 

 

However, heat pumps generally don't like having the flow restricted and the COP can suffer as a result which is why you should consult a heating engineer for the best solution in your case. If your system already has TRVs you could try setting those a bit lower in temperature but you may reduce the efficiency if the system if you restrict the flow too much.

 

I have a gas boiler that is very happy to work with TRVs but when I enquired about an ASHP the heating engineer said TRVs are a bad idea. I stuck with my gas boiler but now have an A2AHP to do most of my heating. 

 

Peter 

 

PS The water leaving the heater / boiler is the Flow and what is coming back is the Return.

 

Reducing my yearly fossil fuel usage with an EV (-900 litres petrol saving about £950/year), A2AHP (-8,700 kWh gas, cost neutral) and Timed Immersion heater (-1,500 kWh gas, £20/year more expensive but reducing as the gas price goes up)
karas21Author
Rank 2
Mar 20, 2026 11:19 PM UTC

Maybe a buffer and two different circulators, one for each one of the two houses, will be better for the circulation of the water to the radiators in the second floor? Or, maybe, a buffer and a circulator just for the second floor house? I don't if this is possible, to use a buffer in parallel connection to the inner unit of the pump and have a circulator just for the second floor apartment. Just thoughts, maybe someone who has done it  know better.