@BPLightlog makes a very good point. It is very common to loop houses together. The cable goes into the first house and is looped back out to a neighbouring property. You may be fed from a cable only to your property or in the middle of a loop or the end of a loop. For the latter two the supply will be insufficient for two properties so you will need to get your own supply sorted out.
The only one you can tell for sure is if you are in the middle of a loop. There will be a black cable going in and a black cable going out just before the DNO fuse. If you contact the DNO they will tell you if you have your own cable or if you are looped but they will probably insist on each property having it's own cable.
If you are looped your DNO fuse will be 60A that will have to be shared between two properties which is not a lot. Even if you have your own cable the fuse may still only be 80A.
Peter
Reducing my yearly fossil fuel usage with an EV (-900 litres petrol saving about £950/year), A2AHP (-8,700 kWh gas, cost neutral) and Timed Immersion heater (-1,500 kWh gas, £20/year more expensive but reducing as the gas price goes up)