I live in south of the UK in a rural location and my property has a split (2) phase electricity supply rated at 200A per phase and is currently metered by a Elster A1140 CT meter.  

The meter is modern but operates in single tariff “dumb” mode so requires periodic manual meter readings to be taken.

I am keen to access a wider range of modern electricity tariffs but getting a meter that can facilitate this seems a bit of a challenge.  I have been told that SMETS2 meters (even polyphase ones) seem to only go to 100A per phase so they aren’t an option.  

Most Domestic Electricty supply companies I discuss this with are unable to offer any other options.  Some Business Electricity Suppliers have indicated that our set up is more common on the Commercial side of things and an AMR meeting solution might be appropriate but the Domestic suppliers I speak to seem unable to help with this - even if AMR meters are offered by the Business side of their operations.

*

What meter solutions could Ovo offer in this context?  Can you offer “smart” (not necessarily SMETS2) meters for existing CT metered polyphase supplies rated at 200A per phase that would provide access to wider range of tariffs than single rate variable tariff?

*

Motivation for all of this is since moving in a few year back i have replaced the old oil based heating system with a ground source heat pump, and added a PV solar array too.  Having electrified much of our energy usage I am keen have access to more useful and efficient electricity tariffs and to be able to easily sell excess power from the PV array back to the grid. 

*

Our annual power consumption approx 40,000 kWh per year (largely driven by ground source heat pump system). 

 

Emmanuelle_OVO
Emmanuelle_OVOBest Answer
Retired Moderator

Updated on 13/03/25 by Ben_OVO:

 

Hey,

 

I got an update from one of our smart meter experts: 

There isn't a Smart solution for CT meters.. it doesn't exist... they must have Automatic Meter Read (AMR). There is confusion about what 'types' of AMR, but all AMR meters are configurable to record export.. (they're technically a Half Hourly meter that's programmed to be read Non Half Hourly) - so they can record the 4 quadrants of energy and present them (import, export, import lag and export lag).

 

Do we support that, I highly doubt it, as we don't support AMR itself very well. All suppliers are required to support it for their domestic CT customers, the licence states that very clearly, it's part of the Smart roll out obligation, that any domestic customer with a CT supply must have a AMR capable meter by a set date and report that to Ofgem.

 

But it must be CAPABLE to providing remote readings (AMR means Automated Meter Reading) but it depends on the communications solution in place.. as sometimes it's not possible to get reads remotely.. this is causing confusion with the RCAMR an RCAMY..

 

*NC stands for Non configurable Remotely (of course!!) where as RC stands for Remotely configurable.. can be done by comms signal.. doesn't need a site visit*

 

The RCAMR and RCAMY bit relates to if they can be remotely enabled or not, to provide reads, but NONE of the descriptions means they are communicating, just that they are all capable of doing so, but need to be connected to a communication solution, be that a telephone line or cellular solution whereas Smart should always communicate..

 

AMR meters are only really one way, they send reads, that's it, nothing else that smart does.

Renewable Energy? Big Fan.

36 replies

Tim_OVO
OVO Staff
OVO Forum Legend

Some fact checking here on AMR meters:

 

“We've several hundred AMR meters.. none of them 'talk' to a Domestic Supplier though.. that's not how they work.. they are communicated with by the AMR agent that then provides us the readings.”

 

I’ll share this topic with our secret weapon smart experts that blastoise refers to, and see if they can suggest anything. 

 

@Cumberland Lass @timciren are ground source heat pump forum members. Could you share your meter type to help out, @ruralCTsupply?

Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
Tim_OVO
OVO Staff
OVO Forum Legend

Hi again, @ruralCTsupply.

 

Some detail here from a colleague who is working on the smart platforms team: 

 

The polyphase meters we're starting to install are capped at 100amps per phase, but the amp rating isn't the issue here.. it's that the ONLY option, as they call out, is for them to have an automatic meter reader (AMR) meter installed with working communication (comms). There is no smart solution for CT, polyphase or otherwise. They were explicitly excluded due to the complexity of the way the energy is managed and measured. So suppliers are obliged to install an Advanced (AMR) meter for these sites.

 

It must be noted that the Elster A1140 IS an AMR capable meter already... it can have a comms module connected to it to provide remote readings to a supplier. But that means they cannot get access to any smart products or services. This, or a meter exchange for another AMR meter is the only options OVO could offer. 

 

 

Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
Jeffus
Rank 20
Rank 20

Some detail here from a colleague who is working on the smart platforms team: 

 

The polyphase meters we're starting to install are capped at 100amps per phase, but the amp rating isn't the issue here.. it's that the ONLY option, as they call out, is for them to have an automatic meter reader (AMR) meter installed with working communication (comms). There is no smart solution for CT, polyphase or otherwise. They were explicitly excluded due to the complexity of the way the energy is managed and measured. So suppliers are obliged to install an Advanced (AMR) meter for these sites.

 

It must be noted that the Elster A1140 IS an AMR capable meter already... it can have a comms module connected to it to provide remote readings to a supplier. But that means they cannot get access to any smart products or services. This, or a meter exchange for another AMR meter is the only options OVO could offer. 

 

Sorry for the basic question @Tim_OVO 

So does that mean OVO couldn't even fit a SMETS2 3 phase meter for this property even if they did manage to get the load down to 100a per phase? The amp rating isn't the issue?

I think that is what you are saying? 

 

Rank 2

@ruralCTsupply

Best wait for @Blastoise186 then to see if he discovers any options.

The reality is Octopus Energy have the vast majority of time of use type tariff at the moment so you may be best directing the question at them in case what works for OVO won't work for Octopus, or if they have any solutions. 

Other suggestions are messy. I am not sure they are realistic, and you may already have considered them. For example 

A left field idea is to investigate the use of battery storage so you shift your energy use and dramatically reduce your peak load down to 100a per circuit. Also this could store some but perhaps not all the excess PV. 

Another is possibly have two separate meters if one could be 100a and one 200a and have a ToU tariff on the 100a meter. Again messy and you have the issue of standing charges and it is still not giving you ToU over all your energy. Am not sure this idea is realistic and may not work with your usage anyway 

I am sure you have considered lots of things reading your posts.

The ultimate challenge is that suppliers won't be looking to offer solutions for what will be a very small number of domestic customers i suspect. I fear no supplier will offer a domestic solution so you won't ever be able to access any domestic time of use tariffs without 

1. Getting the peak load down

2. Going to the expense of getting that 3rd phase installed. 

Have you had your actual peak load measured in real-time? I just wonder how high it is as that would help inform possible solutions perhaps? Comparing it to the theoretical maximum that has been calculated might be interesting?

Octopus is my current supplier and it is their Time Of Use tariffs i have been trying to access. Somewhat frustratingly i went through a lengthy discussion with them prior to getting the solar array about whether - if i got a PV array - would be able to access their solar export tariffs.  We discussed the nature of the meter and supply in some detail and they (eventually) confirmed if i was to get a solar array they would be able to provide a suitable meter to access their TOU tariffs.  This was welcome news as exporting via their Solar Tariffs made the project considerably more economically compelling that SEG or no export options.

So i went ahead health with planing permissions and DNO G98 permissions etc and paid for the array installation.  Planing and permission took 6 months (Planing Authorities we slow and DNO was slow), but eventually install happened in Nov last year.  I then went back to Octopus to deal with the meter upgrade and it seems they have now decided they can’t supply the meter they confirmed previously and is looking increasingly like they can’t provide any meter that would allow me access to their TOU or Solar Export tarifs.  This is quite frustrating - particularly from an economic point of view as not being able to sell excess pv power back via their solar tariffs is not small. 

Although I haven’t quite exhausted the conversations with them, as I am having trouble finding people there who can see the whole picture (i.e. the CT 200A supply and meter and tariff options in a Domestic context).  So possibly there might still be a plausible solution.

 

The helpful input on this forum makes me think there might not be an easy solution to the meter issue other than the Reduction in the Peak Load and adding a 3rd phase options.  

 

The other option for improving the economics is increasing self consumption somehow (adding batteries or converting some other steady demand energy source to electricity). Although this requires further upfront cost etc so is not a no-brainer.

The suggestion about actual realtime peak load measurement is also a good one.  I have a monitor installed where i track and store intra day power kWh energy use (down to minute by minute) across the 2 phases, but not for an Amp/current. I will see if i can find a suitable electrician who might be able to help with this, although night need a whole 12 months worth of monitoring to capture realistic profile across all seasons. 

 

Rank 2

Hi again, @ruralCTsupply.

 

Some detail here from a colleague who is working on the smart platforms team: 

 

The polyphase meters we're starting to install are capped at 100amps per phase, but the amp rating isn't the issue here.. it's that the ONLY option, as they call out, is for them to have an automatic meter reader (AMR) meter installed with working communication (comms). There is no smart solution for CT, polyphase or otherwise. They were explicitly excluded due to the complexity of the way the energy is managed and measured. So suppliers are obliged to install an Advanced (AMR) meter for these sites.

 

It must be noted that the Elster A1140 IS an AMR capable meter already... it can have a comms module connected to it to provide remote readings to a supplier. But that means they cannot get access to any smart products or services. This, or a meter exchange for another AMR meter is the only options OVO could offer. 

 

 

Thanks for this.  The A1140 is AMR capable but our one up doesn't have the communications model attached (although I understand that could be added).  the specs indicate it can provide import and export measurements as well as Half Hourly Readings (or more).  The bit i haven’t been able to find out is if Ocotpus (or another supplier) could actually use this data transmission to provide access to Solar tariffs of Time Of Use tariffs.  I have been told by Octopus Business they only offer fixed 12m contracts, so possibly that is the case for all Business suppliers, and if so perhaps no supplier has systems set up to take HH AMR data for their TOU or export tariffs and are only set up to use the SMETS data.

I am not sure if there is an Advanced AMR meter (AAMR?) that suppliers are able to use to offer TOU and/or solar export tariffs that might be suitable, although given the supply size if it is a thing it sounds more like it would be on the Commercial side of things rather than Domestic. 

Octopus have suggested they could do a meter exchange to provide an RCAMR meter that could automatically provide monthly readings instead of a manual requirement but it would offer no other benefits in terms of access to a wider range of tariffs, so this makes little sense.  Also, given historical experience on this matter with Octopus I imagine something will come up if I did pursue this that meant they they couldn’t actually do it.

Tim_OVO
OVO Staff
OVO Forum Legend

Thanks for this extra information, @ruralCTsupply - it’s a shame to hear you were given the impression a smart meter would be possible. @Jeffus that is correct, I’m told there is currently no smart solution for CT, polyphase or otherwise.

 

One thing though, it’s worth checking with your solar installers if you can get an export meter for your solar panels. @M.isterW has shared some great advice on a topic recently that explained that it would have to communicate every 30 minutes. But that would allow export of excess solar generation via the smart export guarantee.

Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
Jeffus
Rank 20
Rank 20

Thanks for this extra information, @ruralCTsupply - it’s a shame to hear you were given the impression a smart meter would be possible. @Jeffus that is correct, I’m told there is currently no smart solution for CT, polyphase or otherwise.

 

One thing though, it’s worth checking with your solar installers if you can get an export meter for your solar panels. @M.isterW has shared some great advice on a topic recently that explained that it would have to communicate every 30 minutes. But that would allow export of excess solar generation via the smart export guarantee.

@Tim_OVO

I am really showing my ignorance now…

What is the difference between "CT, polyphase or otherwise" and a regular 2 or 3 phase supply that can support a SMETS2 3 phase meter? 

Rank 2

One further question for the expertise of this forum is a bit more Out There.

 

Next to our main 200A split phase CT supply (literally 1 metre away) we have a second metered supply that is single phase 100A.  this second supply has separate mpan etc and is normal sized supply for normal small/medium sized residential property.  this supply DOES have a SMETS2 meter that happily transmits usage data to supplier over the SMETS2 WAN (via a connected T2 boosting aerial) and I can get access to all Octopus’s TOU tariffs for it.  The demand from this supply is v small, approx 9kWh per day in the winter and <2kWh per day in the spring/summer/autumn.

 

The Out There question is does anyone here have any idea whether it would be possible to add a diverter or manager some sort after my Solar Edge pv inverters that could send the electricity generated by the PV array to the main supply (as it does at present) when there was demand from the main supply and but when that demand had been satisfied could send any excess generated electricity back to the grid via the SMETS2 meter?

 

It sounds a bit whacky to me but if this was possible I could possibly self consume as much as possible via the Main CT supply and export the PV generated electricity via the SMETS2 meter?

Newcomer

@ruralCTsupply @Tim_OVO We have  GSHP and solar PV. I'm getting a bit lost with the techy chat in relation meters, but if it helps anyone here are photos of our meters.  

Ours isn't a particularly large set up. House is 4 bed semi.

 

Jeffus
Rank 20
Rank 20

One further question for the expertise of this forum is a bit more Out There.

 

Next to our main 200A split phase CT supply (literally 1 metre away) we have a second metered supply that is single phase 100A.  this second supply has separate mpan etc and is normal sized supply for normal small/medium sized residential property.  this supply DOES have a SMETS2 meter that happily transmits usage data to supplier over the SMETS2 WAN (via a connected T2 boosting aerial) and I can get access to all Octopus’s TOU tariffs for it.  The demand from this supply is v small, approx 9kWh per day in the winter and <2kWh per day in the spring/summer/autumn.

 

The Out There question is does anyone here have any idea whether it would be possible to add a diverter or manager some sort after my Solar Edge pv inverters that could send the electricity generated by the PV array to the main supply (as it does at present) when there was demand from the main supply and but when that demand had been satisfied could send any excess generated electricity back to the grid via the SMETS2 meter?

 

It sounds a bit whacky to me but if this was possible I could possibly self consume as much as possible via the Main CT supply and export the PV generated electricity via the SMETS2 meter?

Plenty of people dump excess Solar PV into immersion heaters to heat water, simple convector heaters, LiFePO4 electric batteries and heat batteries like  Sunamp etc.

Again plenty of people export stored energy in their LiFePO4 batteries.

So it is certainly an interesting idea.