Why is my off peak not working after smart meter installed?

I had a smart meter installed. Chose economy 7 tariff as have storage heaters and water heated by thermostat on off peak. Since meter installed off peak does not work. Ovo sent an engineer who changed the meter. Still no off peak. Ovo then said they’d fix the problem remotely. They said it was successful but still no off peak. Now they are saying it must be to do with my wiring or configuration and they can’t do anything more. Now what am I supposed to do? No heating or hot water since July 28th.

Firedog
FiredogBest Answer
Super User
Aug 22, 2025 4:22 PM UTC

Updated on 29/10/26 by Ben_OVO

You’re not the first to face this difficulty with a new meter. Happily, the remedy is often quite simple.

 

For a multi-rate system to work properly, three quite separate aspects of it have to be set:

  1. The correct tariff has to be applied to your account. You can with any luck see it on your Plan page, and it will usually show the offpeak timings.
  2. The tariff switching times have to be sent to the meter. It will normally start recording offpeak usage on register 2 at the start of each offpeak period and revert to register 1 at the end of it.
  3. The calendar for the Auxiliary Load Control Switch (ALCS) has to be sent to the meter. This is what decides when to switch power on to the circuit feeding the heating equipment, and in most cases the times will be the same as those in the tariff switching table. 

 

You should be able to see whether the tariff switching table has been properly set up, because the IHD may have been set up to tell you when the tariff changes. It may not be so easy to spot when the ALCS operates unless you have a neon indicating when power is switched to, say, the immersion heater. It is usually possible to spot it on the meter display itself if you know what to look for. We’d need to see a clear photo of the meter to be able to help with that. ‘Clear’ means a close-up so all the markings are legible, and it usually helps to tough a button before taking the picture to light up the display screen. A wider view showing everything on the meter backboard would help, too, so we can see all the cables to and from the meter. 

 

If you find out that the tariff is changing at the right times, but the ALCS isn’t playing its part, Support should be able to arrange for the ECAUL request to be sent to update the ALCS. Let’s make sure that this is the right approach first.

 

If you need to speak our Support Team to arrange an ECAUL request to be sent, our contact details can be found here:

 

 

You can find useful pages about smart meters and IHDs in our Forum Library section here.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |

42 replies

Firedog
Super User
FiredogSuper UserBest Answer
Super User
Aug 22, 2025 4:22 PM UTC

Updated on 29/10/26 by Ben_OVO

You’re not the first to face this difficulty with a new meter. Happily, the remedy is often quite simple.

 

For a multi-rate system to work properly, three quite separate aspects of it have to be set:

  1. The correct tariff has to be applied to your account. You can with any luck see it on your Plan page, and it will usually show the offpeak timings.
  2. The tariff switching times have to be sent to the meter. It will normally start recording offpeak usage on register 2 at the start of each offpeak period and revert to register 1 at the end of it.
  3. The calendar for the Auxiliary Load Control Switch (ALCS) has to be sent to the meter. This is what decides when to switch power on to the circuit feeding the heating equipment, and in most cases the times will be the same as those in the tariff switching table. 

 

You should be able to see whether the tariff switching table has been properly set up, because the IHD may have been set up to tell you when the tariff changes. It may not be so easy to spot when the ALCS operates unless you have a neon indicating when power is switched to, say, the immersion heater. It is usually possible to spot it on the meter display itself if you know what to look for. We’d need to see a clear photo of the meter to be able to help with that. ‘Clear’ means a close-up so all the markings are legible, and it usually helps to tough a button before taking the picture to light up the display screen. A wider view showing everything on the meter backboard would help, too, so we can see all the cables to and from the meter. 

 

If you find out that the tariff is changing at the right times, but the ALCS isn’t playing its part, Support should be able to arrange for the ECAUL request to be sent to update the ALCS. Let’s make sure that this is the right approach first.

 

If you need to speak our Support Team to arrange an ECAUL request to be sent, our contact details can be found here:

 

 

You can find useful pages about smart meters and IHDs in our Forum Library section here.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
MilaAuthor
Rank 2
Aug 22, 2025 4:46 PM UTC

This is my meter set up 

MilaAuthor
Rank 2
Aug 22, 2025 4:47 PM UTC

Thank you for taking the time to help -  dealing with Ovo is driving me to despair 

Firedog
Super User
Super User
Aug 23, 2025 7:26 AM UTC

Thank you for the photo. It’s a pity you didn’t notice the suggestion that “it usually helps to touch a button before taking the picture to light up the display screen,” because then we’d probably have seen these little fellows much more clearly:
  

 

These show the state of the meter’s internal relays. The upper one, labelled ı, shows that the main 100A relay is closed ( o¯o ) as it always should be unless something bad has happened. The lower one (labelled ıı) shows the state of the ALCS, which governs power to the heating equipment during offpeak hours. It is currently open ( o´o ), but it should change to something else at the start of an offpeak period to show that it’s closed. You may see LC1 like in this illustration from an instruction manual:

  
 … but that’s not certain. What is important is that when the tariff changes to offpeak, the ALCS should close in order to deliver power to the heaters and the lower icon should no longer show as open. In your case, I think your offpeak hours are currently nominally 01:00 - 08:00, so looking at the meter a minute before 08:00 should tell you whether the ALCS relay is closed as it should be. If it is, watch it until it changes again in a few minutes’ time* as the offpeak period ends, and make a note of the exact time when it does.

If the relay is closed at 08:00, well and good - the meter’s working as expected, but there may be a fault further downstream, e.g. a fuse blown, a breaker tripped or a wire come loose. You’ll have to call in your friendly neighbourhood electrician if you can’t spot it yourself.

If the relay is open at 08:00, the ALCS has probably not been properly configured. Call Support and ask them to have the ECAUL request sent to your meter to update the ALCS calendar to what it should be to match your E7 plan. 

  

*   Offpeak periods don’t start and stop at precisely the nominal times. There is a random delay, usually of less than 10 minutes, built in to each meter just to ensure that not every storage heater in town suddenly switches on at the same millisecond, which might blow up the grid if they did. Make a note of your meter’s delay so you know when it’s best to run power-hungry appliances and you don’t switch them on too early.

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
Chris_OVO
Community Manager
Community Manager
Aug 25, 2025 11:12 AM UTC

Hey ​@Mila, 

 

Welcome to the community.

 

I noticed that ​@Firedog has shared some great advice already! If the ALCS isn’t set up just right, don’t hesitate to reach out to our Support Team. They’re helpful and can send a request to the meter to take care of it remotely. Also, make sure to ask them about doing a tariff configuration for you. This'll help get things back on track for you.  

 

You’ll find similar topics below and if you have any further questions we’d be happy to help.

 

Renewable energy jokes never get old.
MilaAuthor
Rank 2
Aug 25, 2025 12:00 PM UTC

Thank you for your reply. What seems most bizarre and mysterious to me is that everything was working until they put the new smart meter in. It seems as if Ovo aren’t bothering to check if everything is working and I just walking away and leaving customers to sort it for themselves. If these issues are a known problem then ovo should be making sure everything is working properly before leaving a customer In the lurch. I’ve checked the switch things that firedog mentioned and it seems they’re doing what he says they should. But I still have no off-peak electricity. So now it appears it’s up to me to go to the expense of getting an electrician to try and sort a problem which didn’t exist until Ovo started messing about with a meter. I’m really unhappy with their customer service. The customer relations assistant has said that his escalated to another level and I have to wait a few more days to see what they say, but I’m not holding my breath

Chris_OVO
Community Manager
Community Manager
Aug 25, 2025 2:11 PM UTC

Hey ​@Mila,

 

Technology can be a bit unpredictable at times. It’s so frustrating when trying to fix one thing leads to another issue cropping up! I totally understand where you’re coming from. While engineers do their best to leave everything in top shape, there are some areas they just can't touch because of training and liability rules. I’ve shared an article below that breaks down who’s responsible for what, which I hope makes things clearer for you.

 

By the way, when you said you checked those switches that ​@Firedog mentioned, did you make sure they are opening and closing at the right times or at least pretty close?

Renewable energy jokes never get old.
Firedog
Super User
Super User
Aug 25, 2025 2:52 PM UTC

It seems as if Ovo aren’t bothering to check if everything is working and I just walking away and leaving customers to sort it for themselves. … ovo should be making sure everything is working properly before leaving a customer In the lurch. 
 

You’ll hopefully realize that one thing the meter  engineer can’t check is whether the auxiliary load control switch is operating at the right times for Economy 7. Although all the checks that can be made before he leaves are made, he can’t reasonably be expected to come back in the wee small hours to see whether things are working as they’re supposed to just then.

Now you’ve told us that the ALCS is doing its job, but power isn’t reaching the heating equipment. You’ve checked the fuses in the fuse box or breakers in the consumer unit and nothing is off there. OVO engineers aren’t supposed to touch anything downstream of equipment OVO have installed, which all seems to be in order. That’s why you’ll have to get an electrician in to see what the problem is. I should point out that meter engineers aren’t (necessarily) electricians.

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
MilaAuthor
Rank 2
Aug 25, 2025 8:59 PM UTC

I understand from what you both replied with that ovo take no responsibility for their actions. I certainly don’t expect anyone to come in the ‘wee small hours’ but I would expect an energy company to take responsibility for their actions and not wash their hands of errors caused by their operatives or by their technology , whichever is at fault here.. If the system was working before why should the fuses or breakers or anything else  suddenly become an issue? 

Firedog
Super User
Super User
Aug 26, 2025 12:26 PM UTC

We have seen customers in a similar situation to yours come here after a few days’ to-and-fro troubleshooting, which culminated in a suggestion to call in an electrician to trace the fault. Sheepishly, but really courageously, they reported that the first thing the electrician did was to check the breakers, found the one that had tripped, reset it and solved the problem in just a minute. Can you confirm that you’ve checked yourself and that all is in order? 

We’ve also seen cases where the engineer has done everything he was supposed to, but whoever wired the consumer unit did a poor job of connecting the cable from the meter to the CU. When the engineer reattached the cable at the meter end, he didn’t notice that it had come adrift at the other end. I don’t expect you to look for faults like this - it’s an electricians job.

In any case, safety is everyone’s priority. Fuses blow, breakers trip, things stop working for all sorts of reasons. When a fault occurs, it’s a good idea to get an expert in to check for possible risks - there are two many reports in the press about fatalities caused by electrical faults.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |