Why is my off peak not working after smart meter installed?

I had a smart meter installed. Chose economy 7 tariff as have storage heaters and water heated by thermostat on off peak. Since meter installed off peak does not work. Ovo sent an engineer who changed the meter. Still no off peak. Ovo then said they’d fix the problem remotely. They said it was successful but still no off peak. Now they are saying it must be to do with my wiring or configuration and they can’t do anything more. Now what am I supposed to do? No heating or hot water since July 28th.

Firedog
FiredogBest Answer
Super User
Aug 22, 2025 4:22 PM UTC

Updated on 29/10/26 by Ben_OVO

You’re not the first to face this difficulty with a new meter. Happily, the remedy is often quite simple.

 

For a multi-rate system to work properly, three quite separate aspects of it have to be set:

  1. The correct tariff has to be applied to your account. You can with any luck see it on your Plan page, and it will usually show the offpeak timings.
  2. The tariff switching times have to be sent to the meter. It will normally start recording offpeak usage on register 2 at the start of each offpeak period and revert to register 1 at the end of it.
  3. The calendar for the Auxiliary Load Control Switch (ALCS) has to be sent to the meter. This is what decides when to switch power on to the circuit feeding the heating equipment, and in most cases the times will be the same as those in the tariff switching table. 

 

You should be able to see whether the tariff switching table has been properly set up, because the IHD may have been set up to tell you when the tariff changes. It may not be so easy to spot when the ALCS operates unless you have a neon indicating when power is switched to, say, the immersion heater. It is usually possible to spot it on the meter display itself if you know what to look for. We’d need to see a clear photo of the meter to be able to help with that. ‘Clear’ means a close-up so all the markings are legible, and it usually helps to tough a button before taking the picture to light up the display screen. A wider view showing everything on the meter backboard would help, too, so we can see all the cables to and from the meter. 

 

If you find out that the tariff is changing at the right times, but the ALCS isn’t playing its part, Support should be able to arrange for the ECAUL request to be sent to update the ALCS. Let’s make sure that this is the right approach first.

 

If you need to speak our Support Team to arrange an ECAUL request to be sent, our contact details can be found here:

 

 

You can find useful pages about smart meters and IHDs in our Forum Library section here.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |

42 replies

MilaAuthor
Rank 2
Aug 26, 2025 1:55 PM UTC

No I haven’t checked the breakers  I don’t even know what they are.. There appear to be two fuse boxes one the general one and another labelled off peak which seems inaccessible as there is some sort of box in the way with a wire looking like some kind of anti tamper device.? As you will have guessed I am not an electrician so don’t know what I’d be looking for. Totally agree about safety which is why I am very wary of investigating things myself. And also confused as to why ‘engineers’ who fit the meters are not electricians. I would have thought it would be common sense for them to be both. 

Firedog
Super User
Super User
Aug 26, 2025 3:56 PM UTC

… why ‘engineers’ who fit the meters are not electricians. I would have thought it would be common sense for them to be both. 
  

Think of doctors and dentists. They both carry out maintenance on the same sort of system (the human body), but specialize in different bits of it. Electricians in general don’t know much about meters, but meter engineers know lots about them.

  

… there appear to be two fuse boxes one the general one and another labelled off peak which seems inaccessible as there is some sort of box in the way with a wire looking like some kind of anti tamper device.? 
    

If you post photos of your fuse boxes, we can probably shed some light on them for you. You should be able to open the lid on a ‘consumer unit’ to get access to the breakers inside. If you can, please prop it open when you take a photo so we can read any labels on the bits inside.

When you ask the electrician to come and trace your fault, ask him to explain what bits of the electrical installation you can safely access; every householder should know how to reset a tripped circuit breaker or replace a blown fuse once whatever caused it to trip or blow has been identified and rectified.  

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
MilaAuthor
Rank 2
Aug 26, 2025 6:29 PM UTC

This is the off peak bit but it doesn’t look like I can access it

MilaAuthor
Rank 2
Aug 26, 2025 6:31 PM UTC

By the way and untelated (?) my smart meter serms to have stopped sending readings to ovo now as well 

Emmanuelle_OVO
Retired Moderator
Retired Moderator
Aug 27, 2025 10:09 AM UTC

Hey ​@Mila, 

I’m sorry for the issues you’re experiencing, it sounds like a stressful situation to be in. 

With regards to your smart meter’s communication issues, this topic should be helpful:
 


I’m hoping that ​@Lukepeniket_OVO our metering expert can pop by & offer some advice here. There is also the option to raise a complaint, you can find out more about our complaint procedure here:
 


I’ve found this similar topic with the following advice:
 


Our metering engineers are not permitted to alter the wiring configuration of the customer's property as we cannot confirm that the customer's equipment that is currently connected to the off-peak circuit is suitable for a constant load. Some equipment such as storage heaters are not designed to be on 24/7, and doing so may lead to increased bills and potential damage.

In addition to this, altering the timing of the meter's ALCS connection to be permanently closed, would result in the Proteus EHC1 contactor being permanently engaged which would contravene the manufacturer's intended use.  

In a scenario where a customer requests a tariff change from multirate to single rate, OVO would replace the meter and install an isolation switch. The existing off-peak circuit would be left disconnected from the new single rate meter installation, leaving the customer's electrician responsible for reconnecting the previously off-peak circuit to the new permanently energised isolation switch if they deem it suitable.

 

 

Renewable Energy? Big Fan.
Firedog
Super User
Super User
Aug 27, 2025 10:15 AM UTC

Thanks. The first picture is of an unremarkable consumer unit, with all its breakers in the ‘on’ position. If a fault were to develop in any of the circuits listed there, its breaker would trip - drop down to the ‘off’ position. 5 Common Causes of Electrical Trips and How to Fix Them

The second shows an older box of tricks and I’ve no idea what it’s supposed to do. However, the fuse box on the front of it isn’t tamper-sealed, so it should be in order to remove the screw and the cover it’s holding in place. If you don’t know how to check safely for a blown fuse and replace it, you’ll probably want to leave this exercise to the electrician.
  

… my smart meter serms to have stopped sending readings to ovo now as well 
  

Looking at your online account, can you see half-hour usage data here: Your energy use? What about meter readings here: Meter readings history? If they have indeed stopped updating, can you say when the last sets of both were received?

There’s no way of knowing whether your heating problems and this reluctant data flow are related, but I doubt it.

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
MilaAuthor
Rank 2
Aug 27, 2025 11:31 AM UTC

Hi there is no meter reading history available according to what it says.

also emmanuelle re your comments the property has been on off peak for years. I asked for economy seven and was told this is what I’d get so there’s no real change from what it was in before 

Firedog
Super User
Super User
Aug 27, 2025 1:54 PM UTC

… there is no meter reading history available according to what it says.
  

OK. I forgot that this was a brand new meter. It can take a few weeks for everything to settle down, so you should really wait until mid-September before bothering about incomplete details on the account website. If readings and usage data are still absent after 15 September, contact Support to ask why.   

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
Emmanuelle_OVO
Retired Moderator
Retired Moderator
Aug 28, 2025 10:17 AM UTC

… there is no meter reading history available according to what it says.
  

OK. I forgot that this was a brand new meter. It can take a few weeks for everything to settle down, so you should really wait until mid-September before bothering about incomplete details on the account website. If readings and usage data are still absent after 15 September, contact Support to ask why.   



Firedog has given some helpful advice here. I think as OVO has already exchanged the meter & sent an engineer out, & the issue persists. The next steps would either be to raise a complaint. Or if the support team have suggested that you need to get an engineer out to take a look at your wiring at your own expense, if the engineer deems that the problem was caused by OVO & raises this in their job report, there may be the opportunity for OVO to re-imburse you for this.

Please keep us posted with how you get on.
​​​​​

 

Renewable Energy? Big Fan.
MilaAuthor
Rank 2
Aug 28, 2025 6:44 PM UTC

Can anyone tell me what this is and what it does? The wires go in from the smart meter and out to the off peak bit?