New smart meter causing borehole to use more than double the amount of energy as before

  • April 8, 2025
  • 19 replies
  • 307 views

Hello! I’d really appreciate any input anyone can give. My late mums house had water supplied from a borehole. The three phase supply that is used to pump that water to Mums house (and 3 others) was linked to my mums domestic account. In order to see the house I had to have a separate meter put in, to move it from the house. 
The three phase used to used about 1200 kWh per 6mths. The new meter is now reading usage of 2800 per month! 
It seems like the meter is constantly supplying electric rather than just when water is being demanded.

I’m trying to get my electrician back but it’s taking time.

Any one got any ideas please? I just can’t fathom

how the usage can be so high and it’s really worrying bearing in mind in currently having to pay it.

 

thanks! 

19 replies

BPLightlog
Super User
Super User
April 9, 2025

Hi ​@Sassiem , can you show a picture of the meter for context? Also you mention about other properties, could these be requesting water more often or is there perhaps a leak somewhere?

One other thing to check .. are you seeing the high usage directly from meter readings or if online, could they be estimated readings? Have you had the pump checked recently because if there is a fault, that could also draw more power

Bring me Sunshine ~ E&E {Solar PV, Battery Storage, Hybrid EV, ASHP and Home Assistant automation}
Emmanuelle_OVO
Retired Moderator
Retired Moderator
April 9, 2025

Hey ​@Sassiem 

Sorry for the issues you’re having. These topics may be helpful:
 

 

Renewable Energy? Big Fan.
SassiemAuthor
Rank 2
April 9, 2025

Hello- a not very good picture of meter attached. 

Hello- I can take better pictures but a couple attached.

No I don’t think the neighbours can be drawing much more water, there are only three elderly people in 2 of the houses.  If anything it should be using less. No leaks reported anywhere either. The smart meter only sends readings monthly- I’m checking the screen and it’s just racing around- about 1100 kWh in the last 10 days. 
no not checked the pump- it’s 35 m in the ground so not sure how it gets checked but the engineer would

know. 
 

thank you both for your replies. It’s so stressful for someone who doesn’t understand how these things work!

kind rgds

Nukecad
Super User
Super User
April 10, 2025

 

 I’m checking the screen and it’s just racing around- about 1100 kWh in the last 10 days.

1100 / 10 / 24 = 4.583 kWh.

Around 5kW isn’t unusual for a larger sized borehole pump, and the borehole pumps with such a rating do tend to be 3-phase.
(Not important, but do you know what make/model of pump it is?)

However to give the numbers you say then the pump would have to be running constantly.

You said it yourself in your opening post:

It seems like the meter is constantly supplying electric rather than just when water is being demanded.

 

It could well be just that - something has gone wrong with the control system/sensors and the pump is running constantly.

If that is the case then it’s either just recirculating water round and round in the bore, or pumping it out of an overflow to somewhere.

If you go to the top of the borehole you may be able to hear, or feel vibration from, a pump that is running.
 

I said, Hey - Watts going on.
Emmanuelle_OVO
Retired Moderator
Retired Moderator
April 10, 2025

Just tagging ​@BPLightlog so they see this 🙂

Renewable Energy? Big Fan.
SassiemAuthor
Rank 2
April 11, 2025

Thank you all again. I can’t hear anything at the borehole but what I can hear is the water treatment plant-  it’s big enough for 4 houses and had 2 secoh 100 blowers replaced  couple of months ago- they hadn’t been working for who know how long before. 
How much electricity would they draw and could this explain the sudden hike? That said I’m leaning toward the pump having a fault—- I’ll have the make and model of the pump and will send it later. It was only replaced 3 or 4 years ago. 
Have a great day and thanks for the time all.

 

SassiemAuthor
Rank 2
April 11, 2025

Hi- it was a Lowara L4C motor that was replaced with the pump, if that means anything to anyone! 

Nukecad
Super User
Super User
April 11, 2025

Thank you all again. I can’t hear anything at the borehole but what I can hear is the water treatment plant-  it’s big enough for 4 houses and had 2 secoh 100 blowers replaced  couple of months ago- they hadn’t been working for who know how long before. 
How much electricity would they draw and could this explain the sudden hike?
That said I’m leaning toward the pump having a fault—- I’ll have the make and model of the pump and will send it later. It was only replaced 3 or 4 years ago. 
Have a great day and thanks for the time all.

 

Not really, the specification sheet says those are 75W, so even a pair of them isn’t anywhere near 4.5kW.

https://cdn.shopify.com/s/files/1/0269/2035/3881/files/JDK-S-100_120.pdf?v=1647344540

However that is interesting information in itself - Someone was doing work in there at about the time that this problem started?
If so then you have to suspect that the cause lies there.

If it is the pump running constantly then it’s unlikely that the pump itself is faulty and more likely to be a sensor.
As you have obviously been having work done in there then it may even be as simple as a wire having been knocked off a connection. (or taken off and not put back).

 

I said, Hey - Watts going on.
Nukecad
Super User
Super User
April 11, 2025

Hi- it was a Lowara L4C motor that was replaced with the pump, if that means anything to anyone! 

One of these? https://www.pumpsukltd.com/lowara-2gs05m-l4c.html

According to that those are only 550W (and single phase), so wouldn’t account for the amount of usage that you say is happening.

The three phase used to used about 1200 kWh per 6mths.

That’s around 0.28 kWh, so could possibly have been one of those L4C’s running constantly at half it’s capacity?

So if the setup does have the pump running constantly then we need to know what the new pump is so we can find what kWh it is.
You may (should) have the paperwork for it somewehere, or at least an invoice with the make/model number stated.

I said, Hey - Watts going on.
BPLightlog
Super User
Super User
April 11, 2025

There is the possibility that any replacement parts have not been configured as they were originally intended.

With any sort of pump, it can be set up to operate on demand (as was previously) or continuously (might be now?)

I would get it all checked again, motor, sensors and configuration.

Bring me Sunshine ~ E&E {Solar PV, Battery Storage, Hybrid EV, ASHP and Home Assistant automation}