Has anyone successfully moved to Economy 10 with OVO and was your experience?

A few weeks ago I received an email from OVO about the removal of the RTS signal and suggesting I book an appointment to replace my meter. I was a THTC customer so I chose Economy 10 and booked the appointment.

Six days ago the new meter was installed with an In House Display (IHD). The IHD is operating in accordance with the Economy 10 tariff but the meter is supplying power according to Economy 7 times, i.e. power comes to my storage heaters between 01.00 and 07.00 but I am being charged the lower rate at Economy 10 time periods. That means I am being paying the higher rate to charge my storage heaters overnight (and it is getting cold in highland Scotland)

OVO customer support first of all offered to re-program the meter in 6 weeks; they delay because they needed to wait until communication with the meter was established (?). I managed to negotiate them down to making an appointment for a site visit in 2 weeks time.

Tens of thousands of these THTC meters need to be replaced before next June. This is a huge undertaking and my experience indicates the need for a separate help line for follow up support. It has taken me a week and a lot of investigation to get to this stage. My contacts with OVO support via on-line chat have been like wading through treacle. I think OVO need to get on top of this asap because there are very many vulnerable people using the THTC tariff with storage heaters.

An additional complication is that storage heater users have been encouraged to replace old heaters with Dimplex Quantum heaters. The preferred installation uses two power sources - one a 24 hour supply for the heating controls and the other so supply the bricks from off peak. There is a different internal cable setup for a single supply. THTC provides these supplies through two meters. In my ignorance I thought moving to one meter would mean one supply. Apparently the wrongly installed Economy 7 meter provides two supplies. 

Does anyone know if Economy 10 is one supply being billed at the different rates depending on time od day. The IHD would tend to support the later as it is happily billing me as per the Economy 10 tariff.

I hope this lengthy post wiil help me and the wider community with your responses.

You’re not alone. Please see my lengthy reply here:

 

Since this major operation (replacing hundreds of thousands of old RTS meters with smart ones) has only been underway a few weeks, we don’t have much experience of how it’s going. We really only hear in this forum about the ones that go wrong, and not all of those who come here for advice come back to tell us when it all comes right.

Anyway, your situation seems to be very similar to that of the customer I responded to yesterday. In the absence of any information to the contrary, I’m afraid I can’t make any other suggestion. As always, photos would help.

I shouldn’t worry about the power supply to the night storage heaters (NSH). There are indeed two separate supplies, one that is always live (constant) and the other that is only live in offpeak periods (switched). The engineer should have made sure that each NSH is connected to the right circuits. You say your NSH are charging overnight; are their controls active during the day, so you can select ‘comfort’ times and so on? 

Photos, please!


Many thanks, Firedog. At least I am not alone!

As you will be aware, there are two supplies coming from the meter - a 24 hour ‘domestic’ which is feeding the NHS controls and thankfully a boost service to my immersion (otherwise I would have no hot water) and an OP supply for the NHS bricks and water. The NHS 24 hour controls supply is OK and, according to my IHD, is using the Economy 10 tariff.

I have verified that the OP supply is only live between 1.00 and 8.00 (almost opposite of Economy 10 times). It took a night shift and observing the NHS heaters in action to verify that theory.

I don’t think photos would help. The meter itself and the comms device seem standard.

My first problem is that I do not get an OP supply during the Economy 10 OP times.

My other problem is that OVO support do not seem to understand the situation. I am trying to shout loudly and clearly that OVO need to setup a Help Desk for meter replacement problems. You are right about the size of this project and it has started at full pace. Many of the customers they inherited with storage heaters, with our without THTC, are vulnerable and it is not a simple change.

I have had a private message from an OVO employee asking me to verify my identity and account number. We will see where that goes.

I have a suspicion about all of this. Can you confirm if anyone has successfully moved to OVO Economy 10?

Regards


P.S. I should have said I have an Aclara SGM1416-B meter with an EDMI ZigBee comms unit.


That’s the meter that I think OVO is installing exclusively for RTS refugees. I have one, too, but I was never on RTS.

The solution is almost certainly the one I gave: OVO’s smart team have to send the ECAUL request to your meter to configure the ALCS to the times in your plan. 
  


There’s a contradiction in what you write: 

a 24 hour ‘domestic’ which is feeding the NHS controls and thankfully a boost service to my immersion (otherwise I would have no hot water)

and

an OP supply for the NHS bricks and water.”

If the offpeak (switched) circuit is powering your water heater, why would you have no hot water without the 24-hour (constant) boost? 

A common arrangement has two heating elements in the hot water tank: one at the bottom, fed from the switched circuit to heat up the whole tank at offpeak rates, and another near the top, fed from the constant circuit and used to heat up the top quarter or third of the tank at peak rates if you run out of hot water. You shouldn’t ever be left without any hot water if the bottom element is switched on at the same time as the storage heaters. 


Firedog writes:

OVO’s smart team have to send the ECAUL request to your meter to configure the ALCS to the times in your plan.

That nugget of information may be very important for people moving to Economy 10. It might explain why OVO customer support have told me that the meter cannot be configured for Economy 10 until up to 6 weeks after installation. It begs the question, ‘why was I not told that beforehand?’

I also don’t understand why, if the meter can be pre-configured for Economy 7 times, it cannot be pre-configured for Economy 10.

Firedog raises a ‘contradiction’.

This is a red herring sorry, my fault. A little background is needed.

THTC provided off peak power to storage heaters and tank emersions. It also provided 24 hour power to panel heaters and a boost function for water heating (called 24 hr heating). These were separate feeds and, crucially, both were charged at the off peak rates. There was a third feed for normal household i.e. points, cooker, etc. which was charged at the standard rate.

That’s three supplies - off peak (storage and emersion), 24 hour heating (panel heaters and emersion boost) and other normal household.

During my meter replacement, the household and 24 hour heating circuits (including the boost function) were combined and are supplied by the 24 hour side of the meter. That’s why I can use the boost for water heating. I also have only one (long) emersion element.

For full disclosure - I also have solar panels. The energy generated is, after other household demands are met, directed to my immersion and any other excess is pushed out to the grid. To achieve this, the diverter uses the boost function circuit meaning I have full support for water heating.

I hope is makes sense, even if I am no further forward. I have not come across the ECAUL and ALCS stuff before so I will look that up but it sounds as if I may need to wait another few weeks to get my full service.

The panel heaters only heat bedrooms and provided a little back ground warmth in living areas. If it gets colder, I will just switch on my storage heaters and swallow the extra expense for overnight charging. I am sure that OVO will be willing to compensate me when it all pans out ???!!!???. 

I will up date in due course when all is revealed.

 


I’m sure that Firedog will update you but the ECAUL command is only required to be requested/sent if the meter set up isn’t as it’s supposed to be. Meters can be preprogrammed for various tariff setups but there are occasional adjustments required. 


Firedog writes:

OVO’s smart team have to send the ECAUL request to your meter to configure the ALCS to the times in your plan.

  • … OVO customer support have told me that the meter cannot be configured for Economy 10 until up to 6 weeks after installation.
     

That sounds, I’m afraid, like nonsense. There may be some other pitfalls with E10 settings that I’m ignorant of, but I was speaking from experience. When my (E7) SMETS2 meter was installed last year, I noticed straight away that the switched circuit wasn’t working as intended, or indeed at all for that matter. I contacted OVO to say so, and that I was aware of other customers in similar situations whose solution involved (re-) configuring the ALCS remotely. The storage heaters started charging that night.  

hAside: I understood that this failure to configure the ALCS was at the time a common fault caused by an error in the app used by meter engineers. It returned a success message even though the configuration wasn’t actually correct. I rather thought that that particular bug in the app had been squashed, but perhaps not ...]

  

  • That’s three supplies - off peak (storage and emersion), 24 hour heating (panel heaters and emersion boost) and other normal household.
     

I’m still confused: with the old system, your immersion sic] heater was wired both to the constant (household) circuit and to the 24-hour cheap-rate heating circuit. How was that achieved? And for that matter, why doesn’t this arrangement still work? I.e. the immersion heater works during E10 offpeak hours by virtue of being on the same circuit as the storage heaters, but can also be activated when necessary during peak hours by switching the booster on. That will have involved some nifty wiring which the meter engineer won’t have messed with. 

  

  • … I will just switch on my storage heaters and swallow the extra expense for overnight charging.
     

Sorry, what extra expense? They are already wired for offpeak charging, supposed to be three hours at night and seven hours in two daytime slots. Do you mean that this isn’t enough to charge them up (or won’t be when the ALCS is fixed)? 

 


Firedog writes regarding the 6 week wait for the meter to be configured:

That sounds, I’m afraid, like nonsense.

When I ordered Economy 10 I considered trying Economy 7. I was advised by the OVO rep that if I chose 7 a site-visit would be needed to move to 10 later. I pointed this out during my on-line chat and despite their misgivings the support person has arranged a site visit for a week on Friday. Their retained position was that the meter was working OK but could not be configured until it established communication with their systems.

(Did I say that my first on-line chat last Friday resulted in an emergency call-out for ‘exposed copper wiring’? Naturally the engineer could not do anything on a Friday evening to solve my problem but he did suggest I had an Economy 7 meter.)

Firedog asks about my emersion setup. 

When THTC was installed it came with a switch connected to the water heater and fed by two supplies - from the off peak side of the fuse box and from the 24 hour heating side. This switch controls the water heating and has a 1hour timer for boosting. When the off peak supply is available it uses that for the emersion, when a boost is needed at other times it takes power from the 24 hour supply. Two inputs from the fuse box, one output to the emersion.

The energy diverter is another switch which feeds the wiring previously used for boosting. It takes power from the 24hr heating side of the meter previously used for the boost and the solar panels. It diverts power from the solar or from the 24hr supply as it is available and if the water needs it. Another switch with 2 supplies and one output going to water heater via the old boost circuit. Just say if this is incomprehensible and I will try to draw it when all this is sorted.

Firedog asks about extra expense for storage heaters.

I was referring to the extra expense I will incur if I use them before the meter is fixed. The heaters will only charge during Economy 7 hours (01.00 - 08.00) but I am being charged Economy 10 tariff if my IHD is correct. Economy 10 cheap rate ends 01.30 and starts 08.30. In addition because the off peak appliances are not charging I am using backup panel heaters and heating water during peak times. For now, I am going with the IHD because that’s all I have.

BPLightlog and ECAUL

Thanks for that.

 


OVO response to my problem moving to Economy 10 from THTC.

I raised a complaint with OVO this morning and received an impressively quick response which is copied below.

 

I'm Adam, an account management agent here at OVO, I've just received your email regarding the issues since your meter install, I tried calling today around 1.50 P.M but unfortunately there was no answer, Don't worry, everything I was going to discuss with you I have contained within this email.

I am sorry for the inconvenience and for the experience that you have had after a new meter was installed on 1st October. I am sorry that you where not made aware that nothing can be configured for Economy 10 until the data from the smart meter starts coming through to OVO which can take up to 6 weeks. You should have been made aware of this and I am sorry. I do understand that this knowledge would have saved you hours problem determination and influenced your decision to move to Economy 10.

I have raised a case of feedback on your account that will be passed on to my manager and senior members of the team to be reviewed as unfortunately the delay in the configuration of the smart meter is not something that OVO have control over as it is an industry standard time frame of 6 weeks for the meter to connect to us. in this case I have stated The customer has had the meter changed to a smart meter on the 1st of October and feels as no where in the information supplied about moving to Economy 10 does it mention a 6 week delay. OVO's representatives provided the customer with conflicting information about how meters are configured for Economy 10. Overall the customer was not happy with the service received. The case reference number for this should you need to refer to it at any point is 25498383. I hope this is helpful for you.

So, there we have it. It takes up to six weeks for an Economy 10 meter to be configured and they are sorry for not having told me beforehand. 

Should I cancel the site-visit for next Friday (I don’t expect they will be efficient enough to do it themselves) or should I just make sure I am out for the day so that they can share in my ‘inconvenience’?

Interestingly my telephone rung just before 2 p.m. and I answered fairly quickly. The line went dead but the calling number registered in my phone was OVO’s. Maybe Adam thought speaking to me directly might not be a good idea.

Another wee anecdote: When the engineer had finished physically installing my new meter he went back to his van for a cigarette while the meter was going through its paces. When he came back he popped his head through the door and muttered something about the meter being faulty and my heating supply. After a short time he came back and said he had replaced the meter, using one from a different batch just to make sure the fault did not recur. It was only after he left I realised he had done that without switching off the power. No wonder I can’t believe anything someone from OVO tells me.

 

If anyone is really interested in my setup, and I have not described it well enough, please say so and I will try to put some drawings together later. It is the least I can do in return for your help.

 

 

 


It may have been a Comms Hub Hot Swap - those don’t require the power to be turned off.


I’m so sorry if I’ve misled you. I had assumed - obviously wrongly - that the meter was working as intended and was communicating with OVO. It now appears that that isn’t the case. Remote configuration can hardly take place if there’s no communications channel for the commands to be sent over. This is usually how the initial on-site configuration is done by the meter engineer.

New smart meter installations are usually bedded in within hours, sometimes a couple of days. However, if there’s a problem with communication over the smart Wide Area Network (WAN), it can take longer. Six weeks is the arbitrary waiting period before being able to state categorically that communications can’t be established, at which point (I think) the supplier can (or perhaps must) inform the DCC, the body responsible for the smart meter network, whose headache it becomes.

I wish you’d told us on Sunday that the meter wasn’t communicating with OVO. You may have, but I was perhaps led astray by your references to billing. Billing depends on meter readings, and meter readings depend on communications between the meter and OVO. You’d have saved at least one red face …

There are two LED indicators on the communications hub on top of your meter, labelled WAN and HAN (Home Area Network, the Zigbee connection to your In-Home Display). This page tells you what they mean.    


Firedog, I would have told you on Sunday the meter was not communicating with OVO if I had known at that time. I had assumed that everything was connected properly because the meter was successfully providing an Economy 7 type service. I guess it is controlled differently for Economy 10.

No need for any apologies. We were both working from limited information.

For my part, this could all have been avoided if someone had told me, or documented, that activation of Economy 10 could be delayed, and until then the service would default to Economy 7. That way I would have known why I was not getting an off peak service during the day. 

Some method of identifying the start of the Economy 10 service would also be useful. Meanwhile I will just keep an eye on my storage heater input to see when the light comes on the power point. (It is difficult to read the tiny WAN indicator, especially during daylight.)


All good, thanks.

I don’t think anyone could have told you beforehand that there would be a delay in activating full-fat Economy 10. The engineer should have known whether were likely to be problems with communication.

The WAN LED only tells you the state of communications with the network. When everything is working properly, it should flash every five seconds. On the meter itself, press button A to turn on the lights. There are little symbols in the bottom right-hand corner of the screen which tells you whether the constant (ı) and switched (ıı) circuits are live or not:
  

  
The upper one (ı) should always be closed, the lower one (ıı) only during offpeak periods. The heaters will only have power when the lower switch indicator is closed.

In its current state , the second contactor will be following Economy 7 hours. In due course - when the ALCS calendar has been re-configured - it will follow Economy 10 hours. 

 


I also live in the Highlands, we had our smart meter installed yesterday on E10, the IHD is still not working some 24hrs later (Waiting on communication data or something is mentioned on the screen.) I phoned OVO this morning as the engineer said it should be up and running within 2hrs. Only to be now told it can take upto 6wks.

There was never any mention of this long wait when we went through the sign up proceadure, and seems very underhand. 

What concerns me now, is what are we paying, are we on E!0, or are we being charged full rate?? Not very impressed so far. And as others have stated the elderly wont have a clue about any of this, and very unfair!


… the IHD is still not working some 24hrs later
 

What are the two little LEDs on the communications hub on top of the meter doing? If they’re flashing, how long between flashes - five seconds, two seconds or less?
What does the flashing rate mean?

   

What concerns me now, is what are we paying, 
 

We can’t really say. If you’re signed up for Economy 10, then you’ll be paying the peak and offpeak rates you were quoted. However, if you have space and/or water heaters on their own circuit, their off/on times may not be the Economy 10 ones. You’ll just have to watch and see when they heat up, or check the symbols on the meter display as I explained above.

 


Hi @Firedog 

 

Thanks for your reply, we have 2 green lights flashing about every 5 seconds. Sorry for the bit of a rant, but just annoyed as to how this has been handled. I’ll look into the water heater issue, as the engineer stated that it was not able to be put on the lower rate? again we were not advised of this on sign up for the smart meter and economy 10.

He also said OVO were aware of this, and were looking at doing something to the tariff to account for it. But don’t expect it until at least next summer. 

I am disabled, and costs are bad enough as it is,after yet another tariff increase on the 1st Oct the last thing i now need is more cost for a basic need in the coldest area of the UK.


Crag writes: is what are we paying, are we on E!0

Yes! We don’t know if we will be charged the E7 tariff or E10. I am keeping a note of the running total on my IHD because it is set to E10. I will compare that with my when eventually I see one. 

(It was such a relief to hear from someone who sees things as do. I have been ‘ranting’ for more than a week. Consider putting in a complaint as I did. It is the only way OVO will sort out their communication.)


Thank you. The two lamps flashing at five second intervals is a good sign - communications have been established with both the Home Area Network (HAN) and the smart meter network (Wide Area Network, WAN). The former is the one your IHD connects to, the latter connects your meter to OVO. 

I can’t say why your IHD is waiting so long for data. It could be that its commissioning didn’t work while the meter engineer was there. If you can see the little wi-fi symbol on the IHD’s display, it’s in contact with the meter. If you can’t, try moving the IHD a bit closer to where the meter is.

As regards the water heater, it would normally be wired to the switched circuit that’s only live during offpeak hours. I can’t say why the meter engineer couldn’t do this.

We’d have a much better chance of being able to help you if you could post some photos: one close-up of the meter itself so we can read its display and see its markings, another of the meter in situ showing all the cabling to and from it, and one of the water heater showing whatever controls and switches are associated with it. It might also help to see the consumer units (fuse boxes) close up, so we can see which breakers belong to which circuit. Last, a photo of the IHD with its error message. If you can’t manage this yourself, perhaps you could get a granddaughter or neighbour to help (teenage girls are wizards with smart phone cameras!).  

 


Just a quick note that the IHD is not used for billing - that is always from the meter itself. Also the IHD might have 2 ‘connection’ symbols .. one is for connection with the meter communication hub and the other for your WiFi if that’s been connected 


Crag: Were you previously on THTC?


Firedog: My WAN and HAN lights are flashing green every 5 seconds. They are very faint and difficult to see.

Sometime, maybe Monday or Tuesday, two messages appeared on my IHD, both the same - ‘elec meter initialised’. Any idea what that means? I cannot find anything on-line in the IHD documentation.


Firedog: My IHD is now showing an MPAN and OVO as the supplier. I am guessing that means the meter is communicating with OVO. The Economy 10 off peak supply is due to come on at 14.30 and I will post then if everything is OK.


Yes @Keast 


As requested @Firedog 

Please find attatched the following pics.

 

Hot water heater, one always on?

 


In my THTC setup there were two supplies for hot water coming going through a switch. One was taken from the off peak supply, the other was a boost taken from the 24 hour heating supply (both these supplies were charged at the off peak rate). If Crag has a boost switch somewhere it may heat his water because when my new meter was installed the 24 hour heating supply was combined with the 24 hour domestic supply. The boost can therefore be used until the Economy 10 off peak is initiated.

I can’t see from the photo’s if Crag’s setup is the same as mine. 