My smart meter was fitted on 31/05/2024.  I never had a problem with my electricity before then.

My off peak storage heaters were off for the summer.  My immersion heater was still in use. It is on Off Peak tariff & has a Horstman Timer (it comes on between (3 am & 6 am). It is still in use & never been a problem. The immersion heater night rate KW hours are showing on meter readings on my account.

In early October, I put on the storage heating.  

When the off peak for the storage heaters came on at about 12.10 B.S.T. - It tripped all the lights, appliances, TV etc. in the house.

The consumer box could not be reset to turn Lights, appliances etc., until the storage heaters were switched off at the switches in each room.

My electrician has tested my electric system fully over days & weeks and still there is a problem.  His belief is there is a problem with the meter either a switch  or wiring in the meter.

I keep getting fobbed off by customer services & they have asked me to get a plumber to look at the Immersion heater.

 

 

 

Lukepeniket_OVOBest Answer
OVO Engineer
Nov 17, 2024 12:28 PM UTC

Updated on 23/10/26 by Abby_OVO

 

I am now 99% certain the metering installation is wired wrong, I've zoomed in. 

 

Black cable far right looks like a neutral which is connected to the 5th terminal... I believe that black cable should be in the neutral block and the small red cable for left should be moved to fsr right hand side.

 

Surely some sort of emergency visit due to no heating or hot water needs to happen?

 

Are you on Facebook? I would search for the group 'Facebook group energy support and advice UK' and find the admin. 

 

Basically she's a god, she's unaffiliated with any supplier but has a hotline to most of them to get issues sorted out!! Saves waiting 3 more weeks for supplier and then going to Ofgem, worth a go.

 

You can also go straight to your supplier who will be able to help directly. If you’re with OVO, you can reach out to the Support Team for assistance via the contact details in the following topic:

 

OVO Operations Excellence Manager and Former Field Operations Team Leader

30 replies

Firedog
Super User
Super User
Nov 9, 2024 12:13 AM UTC

Could you please post some photos:

(a)  A close-up of the meter. Touch a button to light up the display so we can clearly read it, and make a note of the time you take it;

(b)  A view of the meter box/cupboard/backboard showing all the cables to and from the meter and any other equipment close to it;

(c)  Close-ups of the consumer unit(s), clear enough for us to be able to read what each breaker is for if possible.

 

I don’t suppose your electrician was there after midnight to see what happened when the switched circuit went live at 00:10 (probably 23:10 now that summertime has ended?). You can probably turn the circuit on during the day for testing purposes if you can find the meter’s boost function, but we’d have to know what sort of meter you have to be sure.

Last - where are you? The first part of your postcode is enough to pin down who your DNO is and what your Economy 7 times should be.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
GiffyAuthor
Rank 2
Nov 9, 2024 1:09 PM UTC

Hi Firedog, 

My DCN is SP Energy (G46). As requested I attach the photos requested plus 3 the electrician told me to take @ 8.48am. on Monday. He put a trace between the CU & the heaters.

There is a scorch on the CU. It has been there for years & the electrian knows about it.

 

Firedog
Super User
Super User
Nov 9, 2024 2:31 PM UTC

Thank you. I hope one or other of our resident electricians ( @BPLightlog ?) will come along with comments.

Meanwhile, you mentioned that ominous scorch mark on the CU and you sound happy that it was dealt with satisfactorily. You didn’t mention the less obvious patch by the bottom seal on the meter itself. The module that’s sealed is the terminal cover, and it looks suspiciously as though something in there (the LCS relay, perhaps, that switches power to the ‘offpeak’ circuit) has overheated and may have caused a fault. Because it’s inside the seal, only a meter engineer can deal with it. 

If it were my stuff, I’d turn the red and blue breakers off along with the 45A one next to them and call OVO for emergency help - I’d be fearing a major hazard.

At the weekend, you can usually get swiftish service from OVO’s social media support:
  

Social Media channels over the weekend:


https://www.facebook.com/ovoenergy/
https://x.com/ovoenergy?lang=en
https://www.instagram.com/ovoenergy/?hl=en

Opening hours:

Mon-Fri 8am to 8pm
Sat-Sun 8am to 5pm

 

[I’ve had good results with X; post a brief description of the emergency, followed by a DM giving your name, address, postcode and account no. and a detailed explanation. Mention that your own electrician suspected a fault inside the meter; you can also include one of the photos showing the scorch mark on the meter itself.]

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
BPLightlog
Super User
Super User
Nov 9, 2024 5:35 PM UTC

The circuit with the scorch mark is worrying (to my mind) as it’s next to a 100A breaker 

Unless the breaker was changed after the event, it could have suffered some residual damage. 
Also the main breaker has RCCD protection but only at 30mA 

For any set of circuits with the currents indicated on the trips, I would expect at least a 100mA main RCBO possibly with lower current devices as part of the rest of the circuits. 
In fact the 30mA device might be the cause of your circuit tripping as a smart meter can add a milliamp or so of residual current. These devices detect current flowing to earth but need to be rated at an appropriate level for the circuitry which it connects. Especially when storage heaters are used.

Bring me Sunshine ~ E&E {Solar PV, Battery Storage, EV, ASHP and Home Assistant automation}
Firedog
Super User
Super User
Nov 9, 2024 7:09 PM UTC

Thanks, @BPLightlog. I noticed that the ‘offpeak’ circuit (three NSH probably drawing ~3kW each) seems to be fed from the main board via the 45A breaker. If that is the case, then the RCCB is protecting the entire installation.

I took Giffy’s remark:“… a scorch on the CU. It has been there for years & the electrian knows about it” to mean that it had been properly dealt with.

You didn’t mention the scorch mark on the meter’s terminal cover. I wouldn’t expect to see anything like that on a shiny new piece of equipment, and it sounds as if the electrician didn’t either. I wouldn’t be happy having the offpeak circuit live if something’s sparking under there until a meter engineer’s had the cover off to check.

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
GiffyAuthor
Rank 2
Nov 9, 2024 7:37 PM UTC

Firedog  &  BPLightlog

I tried to call my supplier's (EDF) emergency number, but they are all changed  to weekdays. In the end I called 105 and they came out and checked everything in their remit. The scorch mark was a shadow (thankfully). They took a picture to put on here for information. 

Thank you for letting me know about the RCCB being OK.

My electrician is on holiday and I am keen to get my heating on. Thanks for your help. 

Chris_OVO
Community Manager
Community Manager
Nov 11, 2024 3:21 PM UTC

Hey @Giffy, 

 

I can see that @Firedog and @BPLightlog have already stopped by to help with advice. You’re in great hands and please keep us updated on your progress 😊

Renewable energy jokes never get old.
GiffyAuthor
Rank 2
Nov 11, 2024 3:31 PM UTC

I have just looking over old posts. Do you thinkI should ask for a Reconfigure of ECAUL/ALCS via SMETS COMMANDS?  

Thanks

 

BPLightlog
Super User
Super User
Nov 11, 2024 3:39 PM UTC

I have just looking over old posts. Do you thinkI should ask for a Reconfigure of ECAUL/ALCS via SMETS COMMANDS?  

Thanks

 

If the switch over is happening at the correct time than a reissue of the command wouldn’t help. 
You could try switching off one of the storage heater circuits to see if that allows everything to work without tripping. 
Bear in mind that after a while of little or no usage, the storage heaters will be more leaky, electrically, than normal so that 30mA device might easily detect that. 
 

The point about the main switch being rated at 30mA (for residual current detection) is that it is likely to be too low to properly protect the entire system. I would expect to see a minimum of 100mA for that type of breaker. 
Further circuits could individually have 30mA RCCD protection to prevent a complete system switch off in the event of a trip

Bring me Sunshine ~ E&E {Solar PV, Battery Storage, EV, ASHP and Home Assistant automation}
GiffyAuthor
Rank 2
Nov 11, 2024 4:42 PM UTC

I  sure the electrician put on one a night. It still tripped. I think he also had one on & the others totally disconnected. I will put one on again to night & let you know tomorrow 

Also, I enclosed photos from last week where the electrician took a wire from the consumer unit to connect the storage radiator & all 3 came on at 8.48sm.