Economy 7 tariff changes on SMETS2 meter but fifth terminal not activating at all!

  • March 18, 2023
  • 39 replies
  • 2177 views

Hi, hoping someone may be able to help with this - I’m having an absolute NIGHTMARE trying to get through to a OVO/SSE department who is able to help progress this.

Not sure if they’re going through a change with call centres or the like but there’s a language barrier happening and the operators, in the several departments I’ve tried to speak to, over several hours, can’t understand the technical aspects and vocabulary such as fifth terminal, secondary contactor, etc, only picking up on words like ‘heating’ ‘not’ ‘working’ until eventually I was put through to a lady in Scotland who is in the home cover insurance department for when your boiler or water heater stops working!

Any help in getting through to the proper support line would be really helpful - I can sympathise with the call centres abroad not understanding the technical aspects, as it’s a totally different language for everyone whatever their first language - but at the moment I have a OSO 210L water heater that’s only half-working (on a very expensive day tariff!) because the fifth terminal which feeds the bottom element isn’t getting any electricity during the night when it should.

Basically, I had an Alcara SGM1416-B smart meter fitted a few days ago, and noticed the bottom element didn’t kick in during the night (more obvious now that I have a smart monitor to help look for the 3kW spikes).  Second night, after reading the Alcara manual to work out what I should look out for, I stayed up until 00:30 to check the status of the secondary contactor, which should show a ‘closed’ switch symbol around this time when the tariff changes from day to night (I can confirm the night-tariff changeover is working fine, on 00:30, off 07:30).  As far as any movement goes on the secondary contactor - not a sausage - no change on the digital display - no click heard like before.

 

Apologies not easy to see but bottom right of digital display shows open switch symbol (o/o) for secondary contactor when it should show closed (o-o).  This taken just after 00:30 tariff change.
Much easier to see on this photo, bottom right of digital display, secondary contactor still open (o/o).  This taken just before tariff changes back to day rate.

Fortunately I had the installer’s mobile number, so called him, and he suggested it’s a faulty meter and needs to be sorted - but I’d need to go through customer service to organise this - which is proving a very difficult problem!!!  I seem only to be left with writing to Smart Customer Services at the Havant address, but this would seem to be a very long way around.

I’ve just messaged the installer to ask if he did an ECAUL and waiting a response - not sure though if he might go silent on me because he has plenty to be getting on with.  I know the tariff change may not exactly correspond to the secondary contactor change (hence the ECAUL query) but in this case it’s not activating at all, at any time throughout the day.

All help and guidance will be gratefully received.  Many thanks in advance.

 

PS You may also notice that the smart monitor is not fully configuring - showing 0.000p standing charge - that would be nice 😶

Best answer by Tim_OVO

Updated on 20/07/26 by Ben_OVO

*update on this @SteveBee :

 

I’m told that with smart meters connected with a 5th port,  the tariff and ALCS schedule are separate objects in the meter, and they both need to be set for the 5th terminal (or any ALCS connection) to work.

 

The team found your meter based on its serial number and they could see that the ALCS calendar wasn't set on that one, they're not quite sure why. It has been set now.

 

As a result, this should now be fixed. Please let us know.

 

39 replies

Tim_OVO
OVO Staff
OVO Forum Legend
March 20, 2023

Thanks for the post, @SteveBee - lots of helpful information and images to work with which is great. 

 

Sorry to hear about your experience when calling in. You’re correct in saying this stuff can get a bit technical, but that’s from the customer perspective. We should be pro’s with this stuff. A few more questions to help us narrow this down:

 

 

  • You’ve just had the meter fitted. So your online account won’t be updated with new details yet I’m assuming? 
  • Was it the installer of the smart meter that you contacted?
  • The heating system connected to the meter’s 5th port: has it never worked since the meter install? From your topic title, I’m going to assume no.
  • Is this the only thing connect to the 5th port?
Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
Tim_OVO
OVO Staff
Tim_OVOSolved
OVO Forum Legend
March 20, 2023

Updated on 20/07/26 by Ben_OVO

*update on this @SteveBee :

 

I’m told that with smart meters connected with a 5th port,  the tariff and ALCS schedule are separate objects in the meter, and they both need to be set for the 5th terminal (or any ALCS connection) to work.

 

The team found your meter based on its serial number and they could see that the ALCS calendar wasn't set on that one, they're not quite sure why. It has been set now.

 

As a result, this should now be fixed. Please let us know.

 

Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
SteveBeeAuthor
Rank 2
March 20, 2023

Thank you Tim, great news.

I'll be back tomorrow so will be able to report on Wednesday morning as to what happens overnight.

SteveBeeAuthor
Rank 2
March 22, 2023

Oh dear, the remote tweak has managed to switch the 2A auxiliary load control relay on at 00:30, but the secondary contactor / fifth port remains inactive (photo below, symbol LC1 is 2A relay).  Good news is though that these changes can seem to be done remotely, so remain hopeful that a fix can be found.

 

 

The smart monitor should be showing over 3kW load at this point were the secondary contactor to be closed and supplying the bottom element of the water heater.  Photo below is general set-up for info, showing dedicated fifth port/terminal feed to right side of consumer unit for the E7 bottom element.

 

 

The installer has not come back to me when I texted him about the ECAUL request.  I remember him saying that he was sure the ALCS request got the green light on his system, so thought it might be a faulty meter?

Some useful info following, extracted from the Smart Meter User Manual (with some highlighting/annotation by me), might help as background.

 

 

 

 

 

SteveBeeAuthor
Rank 2
March 22, 2023

Oops, sorry Tim, meant to include @Tim_OVO so you would be notified.

@cwebster17 also looking to have similar problem post-install.

 

SteveBeeAuthor
Rank 2
March 23, 2023

Fantastic, smart meter timings for secondary contactor / fifth port look to be working correctly now, hope yours is sorted soon @cwebster17.

 

 

Saw (and heard) it switch off this morning at 07:30 so presume it switched on at 00:30.  Smart monitor is showing around 1.5kWh for the 00:00-01:00 window - equating to half hour of 3kW bottom element in cylinder - which makes sense.  Will stay up tonight just to be sure.

@Tim_OVO, are you able to let me know if this was further work on your part (or @Blastoise186) as I did also recently send a letter to Smart Customer Services in Havant to investigate, which they might have also acted on.

Not mentioned here before, but I did also highlight in the letter that the installer seems to have taken the wrong final readings from the old meter, taking the ‘total’ and one of the ‘day’ or ‘night’ readings, rather than the usual ‘day’ and ‘night’ readings - obviously can work out the missing number if you have either of the other two - but did seem a bit odd and not sure if the installer training covers enough of the Economy 7 systems to ensure near-faultless install - might be worth the installation department circulating a memo to highlight recent installation issues?

Also, still puzzled why my smart monitor is not showing the standing charge - still stating 0.000p 😶?  Not a major issue though, it still seems to include the standing charge in the overall totals.

Thanks to all in getting this resolved!

Rank 2
March 23, 2023

That’s great news @SteveBee! Fingers crossed they can fix mine too. I stayed up last night to see if that second circuit closes when on the off peak tarrif and it does not - I have the same as you in your first post.  At least it sounds like it is the same problem as you had so I am hopeful it can be fixed easily! 

 

Tim_OVO
OVO Staff
OVO Forum Legend
March 23, 2023

Thanks for reporting back, @SteveBee.

 

The team have just sent another message to that meter which we're fairly confident should get the correct ALCS triggering. Without going in to too much technical detail, there's a chance what we've sent might not have worked (and we're also working on resolving that issue too), but would you be able to check and let us know if it's worked tomorrow?

 

Please bear in mind that randomised offset is a thing too. What this means is that whilst your switch time might be 00:30, the meter will switch up to 10 minutes after that scheduled time (e.g. times set are 00:30 to 07:30 but meter actually switches at 00:36 to 07:36).

Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
SteveBeeAuthor
Rank 2
March 25, 2023

Thanks @Tim_OVO, all seems to be working ok so far.

Will report back end of next week, to be doubly sure.

SteveBeeAuthor
Rank 2
April 1, 2023

Hi @Tim_OVO, after a week of observation, I can happily confirm that the smart meter is now operating as wished, with the secondary contactor switching on (and off) for 7 hours overnight.

I can also confirm that the dual tariff and the secondary contactor timings have also stayed synchronised since moving to BST, so now switching on at 01:30 at the same time as the change to the night tariff, and switching off at 08:30 when the tariff changes back to the day rate.

Many thanks for all your help, and hope that the main OVO/SSE support channels are now more switched on (pardon the pun) to this install issue on E7 smart meters and ALCS requests so to help others like myself and @cwebster17 get it sorted without such a fuss - I couldn’t believe it when on first raising it with them they told me to first get a written report from an electrician to confirm that it’s nothing to do with my (consumer side) installation - fancy getting an electrician out at one o’clock in the morning?!