Flow Temperature settings of my Mitsubishi Ecodan heat pump set correctly?

  • May 29, 2023
  • 37 replies
  • 12840 views

Can anyone tell me what these particular settings mean please see photo 1 of FTC6 controller (I am still on the ASHP learning curve) - I am trying to grapple with whether the Flow Temperature settings are too high/too low/just right. At the moment the outside temperature during the day has been about 18 degrees, at night we have been having near freezing temperatures. See photo 2 from Melcloud. My system is set to run 24/7 which I believe is the most economical way - low and slow. I have been having the room control set to 17 in the day and I have put it up to 18 in the evening during my off peak hours. if I move it up or down it’s only by half a degree.  My problem is that I previously had old storage heaters and this thing is using a fraction of the electricity that they were using, so all the angst about 2.5kwh usage on this forum seems irrelevant to my situation. With my storage heaters I was using 40kwh a day on May 1st, if which 7kwh was all the other stuff including oven. The Ecodan was fitted on 2nd, and now my usage (total) is currently between 8 and 10kwh a day. Happy days! But I am trying to find out as much as I can about the way the current settings are working, preparatory to the Winter when we frequently have as many as 20 days a month with below zero temperatures.  Snow lying many times between November and April. The Melcloud app is quite un-user friendly. I will go into the settings myself before winter to adjust if need be. I have already changed the legionella settings following Heat Geek video, once every 15 days to 60 degrees time 1 hour during off peak, holding for 5 minutes; that should save some money. What I want to do before winter is set up the weather compensation mode. At the moment though I am wondering what the Flow temperature settings on the right of the control panel mean. And if the flow temperature is low enough, too high, or too low - see photo three where something exciting seemed to be happening at around 2.30pm even though I didn’t change anything….!Presumably the water heating up as it had dropped below 40.

(as per advice on heat geek site for hotter weather).

 

Best answer by M.isterW

The first thing to tell you is how the melcloud app works. It doesn't change the settings on the FTC. It overrides them with messages from a cloud server. So my recommendation is to make changes on the FTC and only use melcloud for monitoring.

 

Are you using weather compensation mode or auto adapt, with a Mitsubishi internal temp sensor?

Are your rooms getting to the correct temperature and staying there?

37 replies

Jenp
Newcomer
Newcomer
January 29, 2024

The controller is in a hallway, large one. If wc is set at 35/-5 im not sure why when i changed heating mode to room stat the flow temp jumped to 48 degrees?!  I thought it used the wf settings in background somehow? 

Respectfully,
juliamc
Rank 20
Rank 20
January 29, 2024

You’re so right, although it seems counterintuitive that keeping a hp running all the time is cheaper than having it on a schedule.

Wouldn’t that also depend on usage pattern and energy tariff as well?

 

 

 

I’m experimenting at the moment with a setback of just 1 degree from 9pm to 6am. The heat loss continues day and night of course, and usually the temp difference is greater at night so more heat loss then, and that’s when I get the cheaper electricity.

Usage pattern isn’t really relevant, the effect of people being in the house will add heat, opening doors will move heat around or lose it if an external door, but the hp will just tick over more efficiently if it’s left at a steady target temp.

juliamc
Rank 20
Rank 20
January 29, 2024

The controller is in a hallway, large one. If wc is set at 35/-5 im not sure why when i changed heating mode to room stat the flow temp jumped to 48 degrees?!  I thought it used the wf settings in background somehow? 

Oooh, that does sound wrong, sorry out of my depth now as mine’s a Daikin. Can you post a pic of the controller screen and a Ecodan owner may help here…

amanda1Author
Rank 2
January 29, 2024

@Jenp just lost an entire reply so here goes again: 

  1. Get a wireless remote thermostat see photo.
  2. Do not demand instant water heating via the melcloud app or the thermosat - this relies on the immersion heater. If you have it set to auto adapt (ie Room Temperature control) then it will heat the water when the water temp drops below a certain minimum. In my case it heats the water every 15 hours or so. 
  3. Use auto adapt and get used to the idea of the pump running when it chooses, not when you choose it to.
  4. Do not use timed settings. It is not a gas boiler. 
  5. I have stopped using any degree of set back at the moment and the house is warmer as a result and the usage is about 20kwh a day for the whole house, not just the pump but the oven, tv etc etc as well. My Wireless Remote Controller is set to 19. Temps here in the Cairngorms lie between -18C and 5C or so in Dec through to February. We have had a couple of weeks of -10C or less and max total electricity consumption was 38Kwh. 
  6. Expect the pump to cycle on and off every two hours or so on the coldest days.
  7. Make sure your system has glycol in it and turn off the Freeze Stat function. 
  8. Don’t demand tropical temperatures from it when it is minus C outside. These pumps struggle most around the 0 degrees C mark, and the hotter you want your house the more it’s going to cost you.

My ASHP is on auto adapt, my room temperature setting is 19C, my DHW is 50C with a max drop of 10 degrees before re-heating, my Dec to Jan bill was £200 with a standard variable Economy 10 tariff from OVO, but my bills in Dec-Jan before getting the Pump (ie with storage heaters) were £350 a month. The ASHP has nearly halved my annual electricity costs.

I also came across some stats from a research project in Norway, where they use ASHPs a lot, that suggested that having the DHW desired temperature at 35 or 40 meant that the COP of the pump increased in colder weather.

The more I read in these forums and on FB from local folks who have Heat Pumps, the more I suspect that people are trying to use their ASHPs as if they were gas boilers. I also think that installers don’t explain that if you want to “advance” the heating of the water, then it will be the immersion heater that does the heating, and this costs ££££. If you have your water on timed settings, and it drops low in temp during the off period, the ASHP prioritizes DHW heating and it will spend an hour or more getting the water back up to temp before it starts to heat your house. If your heating is also on timed settings, then your house will maybe take more than an hour after that, to get up to temperature. If you want it to be 23C in there, then it will definitely cost you!

Get a wireless thermostat, use Auto Adapt / Room Temperature Control, and let the pump do its own thing. Keep the wireless thermostat in a room that is reasonably central, and not drafty. 

 

Emmanuelle_OVO
Retired Moderator
Retired Moderator
January 29, 2024

Hey @Jenp,

 

Unfortunately, I’m not an expert in this area.

 

However, I wonder if any of the following Community Members might be able to offer advice: @Ecodanwarrior @James_N   @bgreenwood2000 @Cwriggers @Mimi @OrphM62 @Nicllb @amanda1 @Speps @zzzzz @New ASHP  

 

There might be some insights in the following topics:

 

 

Renewable Energy? Big Fan.
juliamc
Rank 20
Rank 20
January 29, 2024

It may be that the flow temp was 48deg because it was heating the hot water. Where did you see that value ? Do you have underfloor heating or radiators ? What was the temp in the house when you saw the 48deg flow ?

Jenp
Newcomer
Newcomer
January 29, 2024

Thank you for your reply, i used to work in the gas heating industry so understand more than most i guess, i know this runs low and slow, so ve been running in comp curve at 42/-2… so generally runs 24/7 at about 35/36 degrees unless its freezing. Im happy with the running temp etc but wanted to investigate this Aa mode of running. I have solar so dont run anything on a timer as solar heats a tank during the day. Can you advise why i need the wireless stat.,does Aa only run with one of these and it wont work using main controller? Ive lookef at the settings and its set up for ‘main controller’?  I dont understand why putting my main controller on room stat mode it shot up to use 48 flow temp… isnt this linked to the weather comp? What is the benefit of another room stat controller please? This has confused me somewhat!.. many thanks, thought id sussed this ashp just using comp curve… im on comp curve 24/7 with no timer settings. I believe timer settings for hesting only work with aa/room stat mode and not beneficial for ashp that needs running 24/7 or it just goes on and off all the time?

Respectfully,
Jenp
Newcomer
Newcomer
January 29, 2024

Flow temp of 48 is in melcloud reports and on the controller initital settings, you can see the flow and return. Rads were red hot it was not the dhw as this is permanently off as i have solar.

Respectfully,
Jeffus
Rank 20
Rank 20
January 29, 2024

Thank you for your reply, i used to work in the gas heating industry so understand more than most i guess, i know this runs low and slow, so ve been running in comp curve at 42/-2… so generally runs 24/7 at about 35/36 degrees unless its freezing. Im happy with the running temp etc but wanted to investigate this Aa mode of running. I have solar so dont run anything on a timer as solar heats a tank during the day. Can you advise why i need the wireless stat.,does Aa only run with one of these and it wont work using main controller? Ive lookef at the settings and its set up for ‘main controller’?  I dont understand why putting my main controller on room stat mode it shot up to use 48 flow temp… isnt this linked to the weather comp? What is the benefit of another room stat controller please? This has confused me somewhat!.. many thanks, thought id sussed this ashp just using comp curve… im on comp curve 24/7 with no timer settings. I believe timer settings for hesting only work with aa/room stat mode and not beneficial for ashp that needs running 24/7 or it just goes on and off all the time?

Auto Adaption doesn't use the weather compensation curve you have been adjusting in the weather compensation feature.

Auto adaption will boost the flow temperature to get to the room temperature you have set. 

The flow temperature will adjust to as low as possible to maintain the room temperature over time. 

You would need to run the heat pump for a reasonable amount of time under both Auto adaption and weather compensation to see what works best for you in terms of comfort and cost.

For example you'll find Auto adaption reacts quicker when heating a home from cold.

Jenp
Newcomer
Newcomer
January 29, 2024

Ah! Thats why flow temp shot up to 48…. Nothing to do with comp curve settings… interesting. 🤨 so thats really confused me as to how other ppl have told me to set the curve but use aa mode so flow temp is low.. one guy said set room temp to 28.. they must have individual room stats or something?! Thank you for taking time to reply, much appreciated 

Respectfully,