Rts switchover

It has been a week now since I've had the rts meter switchover. Since then I've only been able to pop my heating on twice. It just won't come on. On 2 occasion, after my back shift I had to take a cold shower, no hot water. I will be calling them back in the morning. 

My heating has previously been on a timer and since the switchover it hasn't came on once. 

Anyone else experiencing problems? 

18 replies

Ben_OVO
Community Manager
Community Manager

​@Smiller I’m sorry to hear this is happening since the appointment. Please could you post some clear photos of the meter setup, which will help us to gauge what the issue might be.

 

Hopefully this is one that’s easily fixable 🤞. We have seen similar instances to this before, and there’s a few different scenarios that could be the issue here, such as the meter not being configured correctly, something being incorrectly wired, or the contract being incorrect. I’ll link some similar Forum threads below, and I don’t doubt that some of our community would be happy to lend a hand here as well ​@Firedog ​@BPLightlog.

 

If you haven’t already, please raise the issue as a complaint with our Support Team. You can find the complaints process here.

 

 

We look forward to hearing back from you with the photos.

Powered by the Sun
BPLightlog
Super User
Super User

As Ben mentions, photos would help to see what might be happening. A clear look at the wiring around and connected to the meter is important if possible.
Also you mention a timer - is this still connected or was it taken out at the same time as the meter change? The newer meters have their own timing built in.

Bring me Sunshine ~ E&E {Solar PV, Battery Storage, EV, ASHP and Home Assistant automation}
SmillerAuthor
Rank 2

This is what controls my heating. As you can its ignighted on, but no heating. 

I appreciate yous both responding. I'm unsure if the pictures I've uploaded will be of any use. 

SmillerAuthor
Rank 2

This is the smart meter

SmillerAuthor
Rank 2

This has also been added

Firedog
Super User
Super User

Hello ​@Smiller 
If we’re to be able to see what’s going on and perhaps make suggestions about possible remedies, we’ll have to have a lot more information. As well as photos of the meter itself (we’re assuming it’s a new smart meter), we’ll need to know what sort of heating equipment you have. For example, night-storage heaters work quite differently from modern panel heaters and need different sorts of control. The more you can tell us about your heating arrangements (including for water), the more likely it is that we’ll be able to help.

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
BPLightlog
Super User
Super User

A few things here ​@Smiller , your first photo seems to show a room thermostat. It might well be what switches your boiler? on or off. The controller gives 10:13pm as the time, yet your photo shows 21:07 (9:07pm).

The second photo is not the smart meter but what is called the in home display (IHD) - this is designed to give a simple indication of your energy usage.

The third photo is the smart meter. It is difficult to see the wiring but it looks like a 5 terminal device which gives a timed switch for off-peak circuits. Whatever needs to be energised during those off-peak times should be connected to that circuit.

Bring me Sunshine ~ E&E {Solar PV, Battery Storage, EV, ASHP and Home Assistant automation}
Ben_OVO
Community Manager
Community Manager

Thanks for the photos ​@Smiller and for your help ​@Firedog and ​@BPLightlog.

 

​@Smiller have you spoken to OVO about this at all? If so it’d be good to know what you’ve been advised by Customer Services.

 

As Firedog has said, some photos of your heaters would be really helpful here. We’ll help you get to the bottom of this one way or the other!

Powered by the Sun
Firedog
Super User
Super User

The controller gives 10:13pm as the time, yet your photo shows 21:07 (9:07pm).
  ​​​​​

 

Good start!  This might have resulted from having the power off for some time while the RTS stuff was being removed and the new meter installed, probably on top of other earlier power cuts adding up to 10 hours altogether. Funny, since it looks like the unit has battery power …

I found this:

Why is the C-Stat 17-ZW thermostat not displaying the correct time and date?

If the Horstmann C-Stat 17-ZW thermostat is not displaying the correct time and date, you can follow these steps to troubleshoot the issue: 

1. Press the "BACK" button to return to the normal operating mode. 
2. Press the "ENTER" button twice to access the time and date settings. 
3. The hours for the time of day will start flashing on the display. Use the "-" or "+" buttons to adjust the hours, then press "ENTER" to confirm. 
4. The minutes for the time of day will start flashing. Use the "-" or "+" buttons to adjust the minutes, then press "ENTER" to confirm. 
5. The day of the date will now flash on the display. Use the "-" or "+" buttons to adjust the day to match today's date, then press "ENTER" to confirm. 
6. If you need to change between the day, month, and year, press "ENTER" to cycle through the options. 
7. Once the time and date are set correctly, the unit will return to normal operating mode. 

 

It’s not clear how this central heating controller will interact with ​@Smiller’s electricity supply, but we’ll get to that once the time’s set properly.  

The photo of the meter shows an L&G SMETS2 meter with a bolt-on ALCS (the excrescence with the blue light) and an ultra-modern 4G Communications Hub on top, so a typical 5-wire set-up for managing Economy n heating. It’s a bit surprising if there is indeed oil- or gas-fired central heating, but that will hopefully come clear once we see the (electrical) heating equipment. 

The blue light indicates that power was on to the auxiliary (heating) circuit when the photo was taken - Economy 9 or 10, perhaps? 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
SmillerAuthor
Rank 2

I have electric only in property. So radiators. When I called ovo today I was put on hold, then cut off 🤦🏻‍♀️ was at work so will have to try again tomorrow. Will update here once I get through and what I am advised