What's an isolation switch?


An isolation switch (also known as a 'double-pole isolator') is a piece of equipment which can be installed on a metering supply that will allow the supply to be de-energised post-meter. The isolation switch should be fitted after the meter but before the consumer unit.

 


What's the purpose of an isolation switch?


An isolation switch is designed to act as a circuit breaker on the mains electrical supply, so that any electrical work that needs to take place within a property can be completed safely by a private electrician. It also negates the need for a supplier to send an engineer to the property to de-energise the cut out (and re-energise afterwards) so that any internal electrical work can take place.

 


What does an isolation switch look like?

 

 

The isolation switch is located on the right of this photo. When the switch is turned off,  there would be no power after the isolation switch, which in turn would allow a private electrician to complete any maintenance work or repairs on the member's internal electrical set up.

 

Who's responsible for installing an isolation switch?


An isolation switch needs to be installed by your supplier. This is because the supply would need to be de-energised via the cut out and private electricians are not permitted to work on the cut out. Therefore, the supplier would need to arrange for an engineer to go to the property to install one. For more on who’s responsible for what parts of the equipment, check out the Library topic below:

 

 

 

How can I arrange an isolation switch install?

 

Reach out to our Support Team in order to schedule in an engineer visit. As a non-essential maintenance job there is a charge for this, check this guide to see the current cost.

46 replies

Markrussell78
Newcomer
You usually have to arrange this with your local electricity distributer. You can find that online with the right searching. It's NEDL where I live. As a sparky myself we 'used' to pull the service fuse to enable a board change and most new installs have an a isolator fitted between the meter and the board. He obviously isn't happy to pull the service fuse which is right enough. Not sure what they'll charge you for fitting the isolator though.

  • Author
  • Rank 1
  • March 27, 2018
Thanks, that's really helpful. As you say, he wasn't happy to pull the service fuse which is fair enough. We'll see what the financial damage will be !

Cheers
Stu

  • Author
  • Rank 1
  • March 27, 2018
Turns out that OVO will do this for considerably less than my local distributor, as in £125 less !

Markrussell78
Newcomer
Bonus! Glad you found a solution.

Transparent
Rank 20
Forum|alt.badge.img+2
  • Rank 20
  • March 28, 2018
That's interesting @Themoid.

The DNO in my area (Western Power) have never charged my sparkys when they attend on-site to re-establish the anti-tamper seals on Main-Fuse or meter. The Sparky just phones them when he starts work and they agree a time (a couple of hours hence) when they'll send an engineer to check the new connections and make the seals.

Here's my separate isolator:



Nor have I been charged when I've asked Western Power to shield overhead cables running close to my scaffolding. They even refitted the bracket completely free.

So I'm guessing that either policy changes with different DNOs or perhaps it's something to do with the rapport with the Sparky. :)

Western Power's strategy seems to concentrate on safe-practice. If they arrive on site to find something has been done without notifying them, then they start charging. This obviously favours the "good guys" and ensures that everything is done properly.

  • Newcomer
  • February 14, 2019
I've been told I need an isolation switch. Can anyone advise how much these cost - currently an OVO electricity only customer...Appreciate any help with this. Thanks

Tim_OVO
OVO Staff
  • OVO Forum Legend
  • Solved
  • February 22, 2019

Updated on 08/05/26 by Chris_OVO

 

What's an isolation switch?


An isolation switch (also known as a 'double-pole isolator') is a piece of equipment which can be installed on a metering supply that will allow the supply to be de-energised post-meter. The isolation switch should be fitted after the meter but before the consumer unit.

 


What's the purpose of an isolation switch?


An isolation switch is designed to act as a circuit breaker on the mains electrical supply, so that any electrical work that needs to take place within a property can be completed safely by a private electrician. It also negates the need for a supplier to send an engineer to the property to de-energise the cut out (and re-energise afterwards) so that any internal electrical work can take place.

 


What does an isolation switch look like?

 

 

The isolation switch is located on the right of this photo. When the switch is turned off,  there would be no power after the isolation switch, which in turn would allow a private electrician to complete any maintenance work or repairs on the member's internal electrical set up.

 

Who's responsible for installing an isolation switch?


An isolation switch needs to be installed by your supplier. This is because the supply would need to be de-energised via the cut out and private electricians are not permitted to work on the cut out. Therefore, the supplier would need to arrange for an engineer to go to the property to install one. For more on who’s responsible for what parts of the equipment, check out the Library topic below:

 

 

 

How can I arrange an isolation switch install?

 

Reach out to our Support Team in order to schedule in an engineer visit. As a non-essential maintenance job there is a charge for this, check this guide to see the current cost.


  • Rank 2
  • July 24, 2020

I've been told I need an isolation switch. Can anyone advise how much these cost - currently an OVO electricity only customer...

 

Good question, @Nells

Fitting this without any other work being done costs £158.25, or £325 if you have a 3-phase supply.

Call us for more info and to book this in for a Monday-Friday appointment at least 17 working days in advance. You can call the team on: 0330 303 5063. Our opening hours are 8am-6pm Monday to Friday.

Appointment slots are:

8am-12pm
10am-2pm
12pm-4pm
2pm-6pm

 

Tim, if i have an isolation switch installed at the same time as having a smart meter installed, what would the cost be?


Ed_OVO
Retired Moderator
  • Retired Moderator
  • July 24, 2020

@Andrewhr - It’d still be the same cost as they’d need to be booked separately.

 

We can’t guarantee that the installer who installs your smart meter is trained to install isolation switches, and vice versa, so we’d need to book each one individually.


Transparent
Rank 20
Forum|alt.badge.img+2
  • Rank 20
  • July 24, 2020

If I was adding my isolation switch now, I might buy a bigger (wider) enclosure and place a pair of lightning / anti-surge devices next to it. That could be a better position than having them within a consumer unit.

It rather depends on the physical layout of the Distribution Grid in your area.

If there’s a large number of overhead cables, then an incoming surge is probably more likely.

On the other hand, if you have a workshop with machine-tools (or a welder!) then you need to also protect against spikes created within your home. So in that case place the surge-protection devices within the Consumer Unit and make sure you have a separate feed to that workshop!

 

Even if you don’t want anti-surge protection at this stage, just leave room to add a pair of modules later on.


  • Rank 2
  • July 24, 2020

@Andrewhr - It’d still be the same cost as they’d need to be booked separately.

 

We can’t guarantee that the installer who installs your smart meter is trained to install isolation switches, and vice versa, so we’d need to book each one individually.

On thx. Tbh if the installer isn't competent to install an isolation switch i wouldnt want them anywhere near the rest of the installation.


Transparent
Rank 20
Forum|alt.badge.img+2
  • Rank 20
  • July 24, 2020

On thx. Tbh if the installer isn't competent to install an isolation switch i wouldnt want them anywhere near the rest of the installation.

:joy:

I agree. I can’t stand it when they leave open ends and the electrons spill out all over the floor!


  • Rank 2
  • July 24, 2020

If I was adding my isolation switch now, I’d might buy a bigger (wider) enclosure and place a pair of lightning / anti-surge devices next to it. That could be a better position than having them within a consumer unit.

It rather depends on the physical layout of the Distribution Grid in your area.

If there’s a large number of overhead cables, then an incoming surge is probably more likely.

On the other hand, if you have a workshop with machine-tools (or a welder!) then you need to also protect against spikes created within your home. So in that case place the surge-protection devices within the Consumer Unit and make sure you have a separate feed to that workshop!

 

Even if you don’t want anti-surge protection at this stage, just leave room to add a pair of modules later on.

I'll be uprating to an 18th ed. CU with SPD and RCBOs but thanks for the suggestion. 


Transparent
Rank 20
Forum|alt.badge.img+2
  • Rank 20
  • July 24, 2020

Glad to hear that @Andrewhr.

For the sake of others who come across this discussion over the ensuing months, may I just translate your TLAs into English? :wink:

CU = Consumer unit (which contains the fuses or trips)

SPD = Surge Protection Device

RCBO = Residual-current Circuit Breaker with Overcurrent protection. That means it will trip either if the current (Amps) is exceeded, or if there is electricity leaking from the circuit (residual current), which is a safety protection. All eight of my power-circuit trips in the photo above are RCBOs.

18th Ed. = 18th edition of the Wiring Regulations, which qualified electricians must comply with. In this case the most obvious requirement, which it’s likely that Andrew has in mind, is the need for the Consumer Unit to be made of non-flammable material (ie metal).

The fact that Andrew is using these terms shows that he’s competent in understanding what’s required.

He may indeed being selecting these items himself and then employing the qualified electrician to install them and provide the test certification. That’s what I do.

If others reading this would like further clarification, then please post here and ask. That’s one of the major benefits of this being an open-discussion Forum.


  • Rank 2
  • July 24, 2020

Just to add

 

TLA= Three Letter Acronym :grinning:

To be fully compliant we need to seal all cable entry points with intumescent grommets/sealant. 


Ed_OVO
Retired Moderator
  • Retired Moderator
  • July 29, 2020

On thx. Tbh if the installer isn't competent to install an isolation switch i wouldnt want them anywhere near the rest of the installation.

 

@Andrewhr - I can completely understand your thoughts on engineers being able to do one or the other. It’s simply the way they train them, some are trained in one field, others in another. We do have engineers trained in both, however, we just can’t guarantee they’ll be the ones turning up to do the job!

 

You sound really knowledgeable on the technical side of things, how would you fancy doing a topic or 2 on the installation of the isolation switch and the smart meter, just so others can see the process?

 

@Transparent - Thanks for the explanation of the technical terms, really helpful (even for me!)


Forum|alt.badge.img
  • Rank 2
  • October 30, 2022

Hello,

 

Really hoping to get somewhere on this forum. Recently got an electric car and have been trying every fortnight by phone and what’s app to arrange to get a switch fitted in order to have a charging unit installed. Started trying 4 months before we received the car. We just aren’t getting anywhere. We are fobbed off at every turn, transferred again and again on the phone,  and promised a call back which we never receive. We are rural Scotland and my husband has to go and drive 15 mins to then sit at a charging point for hours. The other day he had to work in the car while it was charging. It really is becoming an inconvenience not having a charger at home.

 

Has anyone had any success in getting an isolator switch fitted recently and how have you managed it?? I would really love to know the secret!

 

Thank you. 


M.isterW
Rank 6
Forum|alt.badge.img+2
  • Rank 6
  • October 30, 2022

One was fitted at the same time as my smart meter. I'm surprised that customer services haven't been able to book in a request to fit one.

 

Why do you need one to get a car charger installed? Do you not have space in your consumer unit for the charger circuit? Or do you need an additional consumer unit to be fitted for the charger?


Forum|alt.badge.img
  • Rank 2
  • October 31, 2022

Thanks for your reply. Customer services have been useless. I thought it would be a case of requesting the job, paying for it and getting it done but no.

The EV company told us we needed one before installing the charger. My husband dealt with them.

I was just hoping there might be a magic number or way of getting this done! It’s really inconvenient. 
 

Thank you.


M.isterW
Rank 6
Forum|alt.badge.img+2
  • Rank 6
  • October 31, 2022

Let's see if we can get confirmation that you should be able to request this via customer service. @Emmanuelle_OVO  can you help, please?


Jeffus
Rank 20
Forum|alt.badge.img+5
  • Rank 20
  • October 31, 2022

@Jenrendo 

Certainly should be able to

 

Am not saying it will work any better during these busy times. 

You can send OVO a private message via their twitter or facebook accounts.

These are official ovo support channels and the ovo staff their have access to your account.

You need to include the account holder details in the private message. Name, address, account number, date of birth. Together with your request. They have always got back to me within 24hrs in the past. It is useful as you then have a permanent date and time stamp of any conversation, including the names of people in ovo. I don't know if they will need to speak to you. Might be worth a try. 

 


Tim_OVO
OVO Staff
  • OVO Forum Legend
  • October 31, 2022

Yep I agree with the advice above, @Jenrendo - the job should be booked in with Support for a time and date that works for you, as long as it’s more than 14 days in the future. That’s how it should work. Perhaps it’s more complicated due to your location in Scotland. I can ask our Forum_Support team to reach out to you privately and they can check the account notes.


Forum|alt.badge.img
  • Rank 2
  • October 31, 2022

Thanks, I have had a PM from someone 👍🏻


  • Newcomer
  • December 5, 2022

Hi,

 

Is it possible to book an isolator switch to be fitted at the same time as having a smart meter fitted, if so what is the cost and how do I arrange it ?

 

Cheers


Blastoise186
Super User
Forum|alt.badge.img+9
  • Super User
  • December 5, 2022

Hey @Paul l !