Updated on 03/10/24 by Abby_OVO
As your energy supplier, OVO can’t advise what might be causing an issue with your supply beyond the meter (ie a faulty fuse or appliance). We’d recommend contacting an electrician if you don’t feel confident following the advice given by one of our members below.
@Malc98 does the RCD still trip if the kitchen sockets trip is on but with nothing plugged in to the sockets? If so then electrician is the answer; it may just be a faulty RCD or MCB.
If not, then plug in half of the kitchen appliances normally plugged in, lets call that group 1. If the RCD doesn’t trip you know that a fault may lie with one of the appliances in the other half, Group 2.
If it did trip then the fault is in one of the appliances in Group 1
Then either way, split the group that caused the trip into two again and repeat the exercise again and again if necessary until you only have two suspect appliances when repeating the exercise overnight will reveal the culprit. Hope that’s clear enough.
Peter