Skip to main content
Rank 2
Solved

The smart meter shows electricity consumption that was not there. Why?

To install the smart meter, I had normal power consumption. After installing this, the counter suddenly increased. I wasn't able to determine how much electricity consumption had increased. But from April 15 to September 25, 2023, I was not in the apartment. I turned off everything. even the electricity consumption indicator which supposedly consumes 1kWh of electricity per year. I also turned off all the sockets. I also unplugged the refrigerator and washing machine. Unfortunately, after receiving the bills, I saw in black and white that I used over 111 kWh per month when I was not at home. Nobody has a key to my apartment. How is it possible?

Emmanuelle_OVO
Emmanuelle_OVOBest Answer
Retired Moderator

Updated on 01/04/25 by Ben_OVO:

Hey @Dorota Parker,

 

From the screenshots you’ve sent it does seem that your meter is communicating fine, and that usage was consumed. 

 

I think the best advice for you would be to follow these instructions:

 

What’s the best way to locate an energy guzzling appliance?

 

Worried that your electricity usage seems high? By checking the usage of each circuit you might be able to find out the particular appliance which is the culprit. The meter will need to have decimals showing in the reading for this test to be useful:

  1. Leave the main breaker in.
  2. Turn off all individual circuits (on the fuse board, for example).
  3. The electricity meter should stop clocking usage. If not, there could be a short in the fuse/breaker panel box or an appliance connected without fuse/breaker protection. An electrician will be needed to investigate this.
  4. Turn on one individual circuit.
  5. Watch to see if the electric meter starts to clock usage.
  6. Turn off that individual circuit and turn on another one. Again, watch to see if the electric meter is clocking.
  7. Repeat step 6 until all individual circuits have been checked.

You’re looking for a circuit that causes the meter to clock a lot of usage, compared to the other circuits. There could be a problem with an appliance or a connection on that circuit. We’d recommend contacting an electrician to check the appliances on this circuit, particularly if there are any old or potentially faulty appliances plugged in.  Find out the average usage for each appliances on this great guide and some great energy saving advice on the Centre for Sustainable Energy.


How do I perform a Creep Test on my electricity meter?


If you’ve been unable to get to the bottom of an increase in our usage by locating a greedy appliance, the next step would be to carry out an initial check on the accuracy of the meter with a ‘Creep Test’. To carry this out: turn off the power to your fuse box and check if the meter continues to clock. If the meter clocks (more than 1 - 2 units which could be down to residual power in the wires)  then it's either faulty, or clocking someone else’s usage.

 

If your meter is in a communal meter cupboard, sometimes the meter details can get mixed up. Firstly it’s worth checking the meter serial number on the meter matches the serial number registered on your account. You can see this on the ‘Meter readings’ page of your online account.

 

Renewable Energy? Big Fan.

53 replies

Firedog
Super User
Super User

Thanks for posting those figures. 

The table for 23 September shows very clearly that there is something drawing about 150 W running all the time, day and night. That quickly mounts up and it’s costing you more than £30 a month, so you must find out what it is. The tests recommended earlier should help you trace where all this energy is going. You mentioned lights (“Sometime I think that our lights in the building are eat our electricity”) - have you been able to check this?

As for 24 September, you arrived at 9 PM and turned some things on. It looks like heating appliances of some sort drawing about 3 kW; that might have been the oven, the hot water tank and/or electric heaters. None of this would be unusual on a September evening in Cardiff. The big spike at half-past midnight* looks very much like overnight heaters starting up, whether possibly storage heaters or immersion heaters for hot water. 

How is the flat heated? There may be storage heaters (which heat up overnight and then release the heat they contain gradually over the following day), but if there are, the account would normally be set up to buy electricity at a cheaper rate overnight, a so-called Economy 7 tariff. Is this the case? 

If you’re not able to get to the bottom of this now, we would have to see a photo of your meter and the other stuff around it, and a screenshot of your Plan page to tell us what sort of tariff you’re on. 

 

  • It’s very unfortunate that there was at this time a fault in the way the figures were displayed on the Usage page, at least for some customers. It was related to the need to convert times from GMT (used always by the energy industry) to BST (used by ordinary people from March to October). Inexplicably, usage for the last hour of the day was shown as if it occurred during the first hour. The figures you see at the top for 12:00am and 12:30am in fact belong at the bottom, after 11:30pm. This should make more sense: it’s continuing the higher-than-normal usage from earlier on in the evening. 
Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
Rank 2

Thank you very much. I do not have a storage heaters. I am now investigate hot water cylinder. We off all but hot water cylinder we do not off from switch only we off programmer. I think maybe this programmer is not proper fix because it switch is not working- do not off.

I am happy Juliamic find what I do not saw that on 24th I have usage between 12AM and 1.30 AM when nobody must be in, because we came only 8.30-9PM and usage shows that we came that time.

No any item use this electricity, but before we go out in May we gave the key to estate agency and I think somebody was there night time. We made photos before we go and we found something was change and for me was strange to see very dirty sink, specially I left everything very clean.

I like to ask one things please: If usage is from 12AM shows in online account if this electricity was use exactly this time or for ex starts 11.50PM and shows only from 12AM?

juliamc
Rank 20
Rank 20

That’s shocking that your estate agent appears to have allowed someone to use the property! @Firedog must take the credit for directing you to the information which helped you find the anomaly, and he will be able to answer the question about the time slots.

Firedog
Super User
Super User

I like to ask one things please: If usage is from 12AM shows in online account if this electricity was use exactly this time or for ex starts 11.50PM and shows only from 12AM?

 

The timings are exact, to the second. If the energy is used between 11:30 PM and midnight, it will be shown as used in that half-hour slot. 

Please read the footnote in my last post: it explains why you see usage between midnight and 1 AM that shouldn’t be there. That usage in fact took place 24 hours later, like this for the end of 24 September:
  

11:00pm 1.67 kWh
11:30pm 1.35 kWh

 

12:00am 1.87 kWh
12:30am 3.15 kWh

 

The electricity being used until you got there in the evening of 24 September was constant at 140 - 160 W. That’s what you should be worried about; the big figures after you arrived show just how much it costs to heat the flat and/or the hot water.

 

The hot water tank probably has two 3 kW elements, one at the bottom and one near the top. The bottom one makes sure that the whole tank heats up, because the water it heats rises to the top and cold water takes its place ready to be heated. The top one can be used to heat up just enough water for, say, a bath when you don’t need a whole tankful, or when the water has cooled down since it was last heated. It looks like the top one was working before midnight to give you some hot water before the bottom element switched on at 00:30 according to its programme. 

 

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
Rank 2

Thank you very much for your help and support. As I wrote earlier, I do not have any storage heaters. All the lights were off and the fridge and washing machine were unplugged.
I'm not there, so I give instructions to my daughter to find out what the problem is, but now I'm devastated.
1 I thought that someone was using electricity at our expense, but I can't check.
2 I thought the counter was wrong. I read that there are problems with these meters abroad. Disturbances due to the location of the meter and elements near it. I hoped that this was the reason, but it is impossible to check it
3 What I tried to check was I turned off the fuses to see if the counter shows consumption - it shows 0 consumption
4. I turned off the fuses and left only the one responsible for the hot water tank on. If the problem was in this tank, I hoped that within an hour, with all devices turned off, I would have about 0.07 -0.08 kWh in every 30 minutes, as I have for 4 months, but I have almost nothing.
12:00pm 0.01 kWh
12:30pm 0.01 kWh
1:00pm 0 kWh
I know that it is not possible for someone to turn something on immediately after we left and for 4 months for it to consume 0.07 kWh every 30 minutes. If an hour was enough to test this water heater, it would show that it is not a water heater. On the other hand, now we have all devices under power even when they are not turned on. This should also give us the same consumption, but we have 0.01 kWh each, so this is not the reason.
I think there was something with the counter after all. There was a huge metal box with some wires there and it was impossible to remove it to get to our meter, maybe it had an impact on consumption.
To be honest, I have no idea because I don't have any new devices, only the ones I had before I left. Why don't I have the same wear and tear all the time as when I was away? If anything consumed electricity, I should now have at least this amount of consumption - and sometimes I have less. I don't assume much wear and tear during the apartment, because the apartment is on the top floor, the roof is without insulation and there are 3 external walls.
I didn't understand one thing - consumption is shown in real time, but at the same time on September 24 between 12 AM and 1.30 AM it is shown with a "24 hour delay", the time change is in October and not in September?
Do you have any ideas on how I can check where this 4-month consumption is coming from?

Rank 2

the thing is that I am not able to determine which device consumes electricity because everything was turned off. The plugs of all devices were disconnected and the sockets were also turned off. The only thing left energized was the electric water cylinder. - here there was a programmer connected to the electricity, which is turned on manually when hot water is needed. So I don't have to check the devices, and yet I connected the devices one by one with the water heater turned off and the consumption was lower than when we left and turned everything off. Then I turned off all the fuses and left only the cylinder with it connected (with the programmer diode on) and there was zero consumption. Therefore, I am sure that no device in the house caused the electricity consumption that must have already occurred before our departure, but since we used electricity we could not notice the additional consumption. Analyzing the daily consumption since the meter was installed, I noticed that there was a similar situation in the past, when the electricity consumption was the same when we were absent for several days. If it was due to our devices, they would not consume any electricity after completely disconnecting them. In my opinion, the problem is with the meter or someone is drawing electricity for us. It may not happen all the time, but it does happen. Why, if these are devices that produce consumption - why then, when they were not connected to electricity at all, there was consumption, but now, when they are used, there is no such consumption. Especially since it was the same consumption of 0.07-0.08 kWh per hour. The one-time night wear may have been caused by someone using our apartment during the night for 1.5 hours on September 24. I read that there may be interference due to the location of the meter, because a regular meter measures consumption linearly, while a smart meter measures consumption in impulses. Someone wrote somewhere about the voltage that may be different on the meter and in the fuse box? but I didn't understand what this was about. If the devices were connected and the consumption was too high, you can look for the source of this consumption, but how should I look for the electricity consumption when everything was turned off and we were away for almost 5 months at that time and the consumption of 0.07 is already visible in the next 30 minutes after everything is turned off? and leaving the house. So it was also added when we used electricity earlier - but this could not be detected. I don't know if the electrician will detect it? I would think it would be a very professional person with experience, but I don't have one. Even if OVO found that the meter was the cause, they would never admit it to me because they would have to refund the money even for the 4.5 months of our absence. That's why I asked for the meter to be replaced. Now I'm trying to get rid of this apartment because I can't afford to pay for unused electricity. Therefore, I want to confirm again that the wear and tear was not caused by connected devices at home, as everything was turned off. We consume a lot when we are at home due to heating, but I cannot agree to the additional costs of electricity that we did not use. Consumption when you are at home is not constant - it varies by several or several kWh, while consumption when you are away is the same - daily consumption varies by 0.02 kWh, which is not possible when different devices are used at different times each day. Here you can see that there is one reason, I see that it is not in our devices.

Tim_OVO
OVO Staff
OVO Forum Legend

What a puzzle @Dorota Parker - I totally understand you wanting to rule out something off at the meter, or even someone drawing power for their own use. 

 

We’ve made a guide here to help offer some options and things to check:

 

 

Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
juliamc
Rank 20
Rank 20

That link’s already been suggested earlier on Tim 😕

Dorota, you said “There was a huge metal box with some wires there and it was impossible to remove it to get to our meter, maybe it had an impact on consumption.” Can you ask your daughter to send a photo of this please ? It might help.

This question “consumption is shown in real time, but at the same time on September 24 between 12 AM and 1.30 AM it is shown with a "24 hour delay"” relates to an anomaly in the OVO usage page during summer Daylight Saving hours (BST: British Summer Time). Now we’re in GMT (Greenwich Mean Time) the consumption is shown correctly. You can rest easy about anyone using your flat during that time, it’s the chart that’s misleading for that time.

Rank 2

Juliamc all meters are in one place looks like big wardrobe, but our meter is up the floor. Before there was big metalic box with some cable and I do not understand why it was there. Its cover my meter. To see it I must to took this box out with somebody help to get access to our meter. The door to this wardrobe was open because the metalic box do not give a chance to close properly the doors. Now when we came the box was not there and wardrobe door was close. Anyway I will be happy to change this meter to ordinary, but OVO does not wanted to do that for us. I am disabled person and my child has big students loan and we must to pay. I do not tell anything about our big usage when she is living there because of central heating and I do not want my disabled child learn in cold room to get infection. For me is not possible to find the problem. To do the photos I need to go there to Cardiff. I cannot ask my daughter to do anything more. I know that smart meters sometimes gave the problems. Only from my investigation I found that it took extra electricity when she was living there because after we left strait away was 0.07 kWh and was not possible somebody come in to the flat when we left. Only what was in electricity hot water cylinder programmer buy it was off too- only red diode was on. When I investigate and put programmer on the same how we done when we left and off fuse I found that is not any usage. When I off from fuse programmer and put unplug all appliance buy not use there was not usage too.

100% the problem is not with any appliance which was unpluged and there is not hot water cylinder too.

If OVO took out this meter we will solve the problem

 

juliamc
Rank 20
Rank 20

That’s true, OVO won’t refit a non-smart meter, supplies are not available. 
This diode you mention, could your daughter send a photo of that ? I don’t know what a diode is but maybe that’s using power ? Perhaps someone here could advise  ?