Open LV Trial - Making local substation data available to community groups

  • May 28, 2018
  • 20 replies
  • 2131 views

.OpenLV is a ground-breaking project that’s making local electricity data openly available for the first time ever, to benefit local communities and the wider energy industry. OpenLV is led by project partners Western Power Distribution and EA Technology. It is funded by Ofgem’s Network Innovation Competition. Project partner CSE is leading the community engagement, to support communities to access their local electricity data for local benefit. Regen is leading the evaluation of community groups taking part in OpenLV.

The OpenLV Project is trialling an open software platform in electricity substations that can monitor substation performance and electricity demand. The LV-CAP (TM) platform is designed to integrate with third party products to enable network control and automation, and increased customer participation in network management. The platform will host applications provided by a diverse set of developers, such as community groups, businesses and universities, providing a variety of services to network operators, communities and the wider industry.

As part of the OpenLV project, the software will be installed in 80 Low Voltage (LV) distribution substations located in Western Power Distribution’s (WPD’s)
licence areas – the Midlands, the South West and South Wales.

 

 

 

46a1b19d-7172-4650-ae5e-70e3a084c7ce.jpg


Western Power Distribution covers areas with heavy industrial demand and high population density, such as the Midlands, Avonmouth and areas of South Wales. It also embraces rural regions with sparse populations such as mid-Wales, and others with high proportions of renewable energy, as in Devon and Cornwall. Balancing the grid-loading is becoming increasingly difficult, whilst upgrading the substations is prohibitively expensive.

Great Britain has about 1 Million Low Voltage (LV=230/440v) feeders from 230,000 ground-based substations and a further 320,000 pole-mounted transformers. These have largely been designed and operated on a fit-and-forget basis for the last 100 years, but this cannot continue. The LV networks are expected to see radical change as we, the customers, alter our behavior and requirements stemming from the vehicles we drive, to the generation and storage devices we put onto and into our homes.

 

 

 

 

f9918a88-0af4-46f9-bc0d-2c9d00a35204.jpg


Many rural substations serve a very small number of homes, whilst in built up areas a single substation may serve hundreds. Larger consumers, such as tower-blocks, schools or hospitals, will often have their own substation.

The LV-CAP software could ultimately be deployed across the electricity network. The project will use three approaches to demonstrate the platform’s ability to provide benefits to the network owner, customers, and service providers. The OpenLV project could potentially enable data to be presented on websites and through phone apps which will help people to get to grips with things like:

 

 

 

  • Get to know my substation
  • Reducing costs of community energy
  • Influencing community demand for electricity
  • Electricity generation across a community
  • Demand-side response for managed EV charging
  • Community information alerts

 


The Community Trials commence on 3rd Sept 2018 and will last 9 months, followed by reporting and evaluation stages. Seven Community Trial sites are being coordinated by the Centre for Sustainable Energy (CSE) in Bristol. Of the total eighty substations sites in the Project, ten are designated for the Community Trial.

The OpenLV strategy will open up the usage-data from sub-stations, allowing us to see fluctuations in energy supply. We don't yet know whether grid-loading varies wildly, with large/rapid peaks and troughs, or smoothly, whereby peak-usage gradually increases and falls.

The Intelligent Substation Devices (ISD's) used during the Trials will allow Community Groups to evaluate methods to better utilise the electricity provisions within their sampling areas.

 

 

 

 

4a4376ed-0282-4a5a-988b-ff4d898faf42.jpg


We will be able to evaluate what effect various incentives have in altering consumer behavior. Individual houses will be able to compare the impact of their own electricity usage against the average for their local area. Based on that data they can better decide whether to invest in solar panels, grid-connected battery-storage or an Electric Vehicle (EV).

The Trials will include users being provided with real-time data showing the energy-mix plotted against the throughput on their own substation, allowing them to choose when they switch on appliances.

In future Energy Suppliers may offer tariffs which vary throughout the day depending on demand and local (solar/wind) generation. A substation with an ISD is analogous to it having a Smart Meter, allowing Suppliers to use higher and lower costs per half-hour charging-period to encourage consumers to prevent overloading of the local Grid.

Further information to follow:

 

 

20 replies

Rank 2
October 14, 2021

...

Do all 3 phases ideally need to be in perfect balance so there is no loss?

My questions may be showing my lack of knowledge 😊

I’ll latch onto any chance to fill gaps in my own knowledge(*), to offer/ask @Transparent about a geometric way of thinking of things (this is a question not an answer)…

I picture the three phases as three arrows, ideally the same length, and at 120 degrees to one another, rotating around (at 50 Hz, in the UK).

I recall that phases being balanced is a matter of the resultant (vector addition) being zero.

Do the losses correspond to the length of the resultant (which is in practice never exactly zero?

Or the squared length?

[This is of interest because as something goes to zero, its square goes to zero a lot more quickly.]

If the latter (which would be my gut expectation, half-remembering that in the electrical engineer's use of complex variables, power is something like the product of one complex voltage and a complex conjugate current, says I, bluffing furiously) then so long as the phases are moderately well balanced, then the losses are probably small enough not to worry. @Transparent's comment that the phases weren't very well balanced in the first place may count for a lot here…

 

 

(*) I was a little embarrassed to have to edit “fill gaps in my ignorance” to the intended “fill gaps in my knowledge” :-)

Oh that my ignorance could be complete and with no gaps at all...

Simon
Transparent
Rank 20
Rank 20
October 14, 2021

@Simon1D  wrote:

My knowledge of substation transformers is close to zero, but they are evidently massive (tonnes) and benefit from active cooling.

Not the sort we’re talking about here.

The sub-1000kVA transformers used in substations with an 11kV input are passive cooling.

The core and windings are held in a bath of oil which circulates upwards by convection, and then out to finned cooling pipes on the outside. The exact arrangement varies, but here’s a photo on the left and then a couple of views of my simplified 3D model:

 

On a lightly-loaded ground-mounted transformer you would typically see 30-40°C at the point where the oil leaves the main casing.

There’s a transformer about 5 miles from me which runs too hot to touch. This can lead to premature aging of the internal insulation.

 

@Jeffus  wrote:

Do all 3 phases ideally need to be in perfect balance so there is no loss?

We’ll never reach that ideal situation on a substation supplying domestic customers because 99.999% will be using single-phase devices!

I don’t know what tolerance levels are regarded as ‘satisfactory’ by the DNOs. They’ve just got used to running them ever more out-of-balance over the last 20-years.

The break point in time was when the Government started offering FIT payments to install PV Solar Panels. Since then the losses on the Distribution Grid have doubled.

Now that Heat pumps are being promoted we’ll also be seeing increased losses due to harmonics. The problem there is that harmonic losses get propagated back through the Grid to the much larger 33kV and 132kV transformers.

That annoying hum you can hear when nearby is evidence of harmonic loss. If it was at 50Hz then it would be below the audible threshold.

 

I’ve written more extensively on this subject in the Topic Balancing the Grid.

Save energy... recycle electrons!
Transparent
Rank 20
Rank 20
October 14, 2021

There’s an informative 4.20min video on YouTube which takes you around a Grid Supply Point transformer (330kV input; 132kV output). The transformer gets energized at 3m45s if you’re just interested in hearing the harmonics!

The “tertiary winding” referred to in the video clip is to produce 11kV. This then gets transformed down to 440v 3-phase to operate the pumps and cooling fans.

The way in which these auxiliary devices get powered is extremely important. In the event of a nationwide National Grid collapse, there must be a way to bring the complete system back online again. So you can’t ‘borrow’ 11kV from an adjacent transformer to run the cooling system. The entire transformer mechanism must be capable of self-start when the breakers are closed.

Save energy... recycle electrons!
Tim_OVO
OVO Staff
OVO Forum Legend
October 15, 2021

I’ve enjoyed reading up on this thread today. But also I’ve realised how little I understand this infrastructure. Simon’s analogy of 3 arrows at 120 degrees confused me further. I’ll look to do some reading on this subject over the weekend, and I notice our forum site doesn’t have much to help me with this… yet.

 

There’s an informative 4.20min video on YouTube which takes you around a Grid Supply Point transformer (330kV input; 132kV output). The transformer gets energized at 3m45s if you’re just interested in hearing the harmonics!

 

 

Oh wow, yes at 3m45s it kicks off. A perfect musical 5th interval in fact, a tonic and a 5th above it. I’ve heard ambient musical performances just like this transformer! :joy:

Carbon neutral - we need a community to get there! My green tech: Aclara SGM 1411-B smart meter, Chameleon IHD6
Rank 2
October 15, 2021

There’s an informative 4.20min video on YouTube which takes you around a Grid Supply Point transformer (330kV input; 132kV output). The transformer gets energized at 3m45s if you’re just interested in hearing the harmonics!

The “tertiary winding” referred to in the video clip is to produce 11kV. This then gets transformed down to 440v 3-phase to operate the pumps and cooling fans.

The way in which these auxiliary devices get powered is extremely important. In the event of a nationwide National Grid collapse, there must be a way to bring the entire system back online again. So you can’t ‘borrow’ 11kV from an adjacent transformer to run the cooling system. The entire transformer mechanism must be capable of self-start when the breakers are closed.

Fascinating! Many thanks, @Transparent!

Simon
Transparent
Rank 20
Rank 20
October 15, 2021

I had missed answering this point from @Jeffus 

Is it difficult to switch individual homes or groups of homes from one phase to another, appreciating this isn't a long term fix?

In most cases it’s time-consuming and labour-intensive to change the phase supplying a house.

The majority of our 3-phase 440v feeds are underground. It means digging up the road to access the connection point.

Moreover if the cable run to the house itself is ever renewed or replaced it’s common practice to connect it to whichever conductor was at the top of the bundle when you locate it in the trench.

I live in an area with lots of above-ground feeds. These are now being changed to Aerial Bundled Cabling (ABC). This is 3 separate cables (or 4 if Neutral required) twisted together with connections made in pole-top boxes.

Cable upgrade to ABC by Western Power Distribution

Connections to a house can be made using Insulation Displacement Connectors which are tightened onto the ABC cable with a spanner. This automatically provides a water-tight seal without having to cut the feed-cable or switch off the power.

Connector for overhead ABC cable

There is no map which shows the phase supplying each house and it would be difficult to produce one. The three phases do not have a ‘master set’ anywhere in the country which can be used as a reference. Each transformer through which the electricity supply passes will rotate the phases +30° (Dyn-1) or -30° (Dyn-11).

Dyn-11 identification on substation transformer

In effect, houses have been randomly assigned to a phase. This was fine when each property had roughly equal demand, but that’s no longer the case.

Save energy... recycle electrons!
Jess_OVO
OVO Staff
OVO Staff
October 18, 2021

You’ll be proud to hear I’ve been bringing up phase-imbalances to my friends over the weekend, @Transparent.

 

My engineering friend explained the difference between a single phase and three phase supply using a rope-wave analogy, and I thiiiiink I can visualise things now.

 

 

There is no map which shows the phase supplying each house and it would be difficult to produce one. The three phases do not have a ‘master set’ anywhere in the country which can be used as a reference. Each transformer through which the electricity supply passes will rotate the phases +30° (Dyn-1) or -30° (Dyn-11).

Dyn-11 identification on substation transformer

In effect, houses have been randomly assigned to a phase. This was fine when each property had roughly equal demand, but that’s no longer the case.

 

This is where my understanding gets a bit ropey (excuse the pun), why do the phases need to be rotated or is this a by-product of them being ‘transformed’?

Powered by Re-knowable Energy!
Transparent
Rank 20
Rank 20
October 18, 2021

Excellent question @Jess_OVO - have a gold star :star:

The reason for rotating the phases in a transformer is to make best use of the magnetic flux in the core. You don’t want the flux to decrease to zero and then increase again as the next phase of the incomer rises in voltage.

Think of the magnetic flux as a temporary energy store.

A Local Substation transformer is usually wired in a Delta-Wye format. The primary 11kV windings are the Delta, and the secondary Wye windings have a central connection point which provides the neutral.

 

Higher voltage 3-phase transformers on the Distribution Grid are more likely to be Star/Delta winding format.

Historically the transformer manufacturers have sought to maximise the efficiency in the forwards direction – from primary to secondary.

The consequence of this is that efficiency is lower in the reverse-power direction – when homes are feeding back to the Grid.

The Standard Technique procedures (the “rule book”) state that a transformer may only accept 50% of its rated capacity in reverse-power mode unless it has been manufactured and specified for greater efficiency in the reverse direction.

The most critical parameter is when reverse-power is being applied with the phases imbalanced. Energy losses will be roughly double those associated with the same amount of imbalanced power in the forwards direction.

This characteristic helps to explain why a DNO will normally accept 32A import for Low Carbon Technology single-phase loads such as Heat pumps and EV charge-points, but only 16A (3.68kW) for export from Solar Panels.

Save energy... recycle electrons!
Jess_OVO
OVO Staff
OVO Staff
October 19, 2021

Wow - things did get very technical very quickly there, @Transparent !

 

So from my understanding on things the current transformer set-up is more designed for energy to be imported from the grid rather than exported to the grid from individual homes. Obviously this will become more and more relevant as more homes install devices capable of exporting energy.

 

So in the current situation, how are transformers (or substations) adapted to cater to homes exporting larger amounts of energy, or would it be the case that the DNO would limit the number of applications it grants to exceed the usual export limit depending on the devices already installed - ie. you may be denied an application to export from a larger amount of solar panels if you neighbor or someone also linked to the same substation is already exporting over a certain amount of energy?

 

Not sure if that fully makes sense but trying to keep up! :slight_smile:

Powered by Re-knowable Energy!
Transparent
Rank 20
Rank 20
October 19, 2021

Yes it’s the case that a DNO can reject an application for export from your house due to the existing levels of export from your neighbours. That’s a safety issue and trumps all other points of negotiation.

The issue depends on whether you and the neighbours are on the same phase of course. If the Substation transformer is still well within its overall Reverse-Power capacity, then moving a couple of houses to different phases may actually make things better and reduce losses.

 

You can begin to see why Western Power decided to keep the original OpenLV Project alive for just the Community Groups. They have the ability to coordinate demand and supply between neighbours in ways that Energy Suppliers and DNOs cannot!

 

We must understand that there is difference between

a: trying to ‘balance the grid’ solely on the matter of supply & demand

b: taking a holistic view of the Distribution Grid, such that its enhancement also permits:

  • reduction of losses through phase-imbalance, harmonics etc
  • increasing the proportion of renewables exported to the grid

Option (a) is short-sighted and can make (b) even more difficult to implement.

Save energy... recycle electrons!