Skip to main content
Rank 1
May 16, 2020
Solved

Can OVO fit a 3 phase meter which measures solar exports if we switch over?

  • May 16, 2020
  • 21 replies
  • 2156 views

Good morning

 

We currently have a 3 phase supply with a Landys Gyr meter 

 

We added solar a couple of months ago but have realised the meter isn’t billing us correctly for our net usage

 

Instead it bills us for import on any phase, even if we’re exporting on another phase.

 

weve been told by Ofgem tte meter needs to be compatible with “Vector sum metering” which our current model is not. 
 

Our current supplier (Bulb)  cannot supply the correct meter so have advised us to move. 
 

Before we change we’re looking for a supplier that will supply the correct meter. We’re aware smart meters aren’t yet available and we don’t want one anyway. But there are plenty of normal meters which perform this funxtionality

 

Can you let me know if Ovo can fit the correct meter if we move to you?

 

Thanns
 

 

Best answer by Nancy_OVO

Updated on 14/09/23 by Abby_OVO

 

Do OVO offer 3 phase smart meters?

 

3 phase (aka polyphase) installations in domestic properties are few and far between, so it's a minority of meter engineers across the country that have the skills required to complete these installations. There are also some technical challenges in making sure your job is allocated to an engineer with these skills but we are just as keen as you are to have Smart available for these sites ASAP, so if you would like to take part in this beta stage release, please consider the steps below:


From the start of May 2023, if you have a single rate 3 phase meter (i.e. not Economy 7 / 2-rate etc.) we would encourage you to book a smart meter appointment as normal online or over the phone on 0330 303 5063. (Please do not attempt to book sooner than May unless you have been contacted.)


This will then go through to a specialist team who will validate that it is single rate job and that an 3 phase engineer is available in your region. If this is the case, they will re-book your appointment with the right engineer. (So please bear in mind your appointment date/time will likely change, but we'll try to keep it the same where possible.)


Unfortunately, if you have a 2-rate meter or are not in an area covered by our current crop of 3 phase skilled engineers, you will need to continue with your heritage meter. We know this will be frustrating, so we are sorry about that, we are working to expand our coverage and by you flagging your interest to us, you are helping us shape where and when that coverage develops. - thank you!

 

Smart meters are able to measure export, for use in solar and other generation with the smart export guarantee 


If all 3 phases aren’t in use, you may consider downgrading to a single phase supply which is compatible with the current Smart meters we fit. Here's the process:

- Get an electrician to check if downgrading the supply is possible (you've done this already - nice work).
- Arrange a date for (and pay for) a visit from your Distribution Network Operator (DNO), who will rewire your supply to make it a single phase set up.
- Contact our Support Team to make sure we can get an engineer to you on the same day that the DNO visit, to fit your smart meter free of charge.

 

OVO member but not got a smart meter yet? - Book today!

 

Interested but not yet an OVO member? - Check out our plans!

 

21 replies

Transparent
Rank 20
Rank 20
May 16, 2020

Hi @Benseb and welcome to the Forum.

Well that question opens up multiple cans - all of which are full of worms! :face_palm_tone2:

Let me explain first that this is a discussion forum hosted by OVO. Their Customer Services don’t read what’s here and you can’t obtain “official” responses. We are fellow energy customers, like yourself.

 

Let me me just lay out the situation before you as it currently stands:

 

1; All GB Energy Suppliers are constrained in doing on-site work due to the Coronavirus pandemic. They are unable to meet their contractual obligations for the number of Smart Meter installations. OVO will now only undertake installations for Pay-As-You-Go (pre-pay) meters.

 

2; Even as the pandemic restrictions are lifted, the priority will be to fit SMETS2 meters. They have no available manpower capacity for non-Smart on-site work unless the meter is actually faulty, which yours is not.

 

3; OVO’s earlier SMETS1 meters (manufactured by Secure) are scheduled to upgraded to SMETS2 capability and transferred across to the National Smart Meter Network on Sunday 28th June ‘20. This is barely 6 weeks away.

At that point all manner of new faults will manifest themselves. Some properties may even find themselves without gas, electricity or both, and Pre-pay meters in rural locations are particularly vulnerable. They will require site visits to re-boot software and restore power. That takes manpower from experienced engineers.

 

4; There are no 3-phase SMETS2 meters yet approved for connection on the National Smart Meter Network. You can see the list of approved hardware here.

The same situation applies to all Energy Suppliers. So hunting around each one and asking the same question won’t get you very far! It’s better to discuss the options here where there are technically-aware people who can help find some answers.

 

5; You have hit the nail on the head when you write

it bills us for import on any phase, even if we’re exporting on another phase

Precisely! That is how existing 3-phase meters were designed to work. See what I wrote here on another Topic a couple of months ago.

Vector sum metering” on its own doesn’t resolve the problem either. You still need a Supplier who can offer a suitable tariff, and whose Billing Software has the capability to handle the data. I don’t know of any domestic Energy Supplier who is yet in a position to provide this.

 

Now let me tag a Moderator, @Tim_OVO and another couple of Forum Members who are technically astute: @ITGeek123 and @PeterR1947 .

Each of these may have their own view on the situation. That includes disagreeing with what I’ve just written above! But that’s the benefit of using a Forum to chew over problems like this.

Save energy... recycle electrons!
PeterR1947
Newcomer
Newcomer
May 16, 2020

 

Three phase meters should calculate exports thus:

Look at the total amount of energy being consumed on all 3 phases, look at the solar being generated on the single ‘solar’ phase then subtract the consumption from the generation to get the export total.

So if the system in generating say 3.5kW of power, and they are using 1 kW on each of the 3 phases, it is exporting 0.5kW (3.5kW – 3kW) and importing nothing from the grid.

On some meters, the firmware is configured to only count exports on the solar phase so using the same scenario, the system is generating 3.5kW but consuming 1kW therefore we are exporting 2.5kW back to the grid on the solar phase but on the other two phases 1 kW is being imported on each so paying for 2kW in total.  The net result is that the householder is losing out!  Being cynical, which sort of meter would a supplier prefer?

As @Transparent says, “Vector sum metering” isn’t the complete answer but I’m sure a meter such as the first scenario described would solve the problem.  Unfortunately, as far as I’m aware, there isn’t a standard dealing with how three phase meters calculate import/export, the only answer would be to check what sort of meter each supplier uses.

PeterR
Transparent
Rank 20
Rank 20
May 16, 2020

Thanks @PeterR1947 .

That sort of meter configuration would seem to work OK from the householder’s viewpoint…

… but it’s bad news for the Grid. :disappointed_relieved:

Installing 3-phase meters which increase phase-imbalances is a no-no!

It cuts across the RIIO-ED1 strategy which Distributed Network Operators are required to adhere to under their Ofgem licences.

I gave a more full (and illustrated) explanation of phase-imbalance losses here on this other Topic.

To reduce losses and reduce our carbon footprint, we need to reconfigure domestic properties with 3-phase supplies so the current drawn is more evenly spread across all three phases.

One solution is to input PV-panels to a Storage Battery, where its output is connected to whichever phase is drawing the most current from the Grid.

OVO/Kaluza are currently evaluating test sites to trial such a battery, albeit at this stage only on single-phase locations.

 

@Benseb- please say if you’re not able to follow what Peter and I are discussing. We may be introducing all sorts of concepts and terms that you’re unfamiliar with.

Save energy... recycle electrons!
BensebAuthor
Rank 1
May 16, 2020

Hi all

 

our situation is as Peter has explained

 

we have 3 phase supply and 3 phase solar too

 

However the house was only wired to use one phase. We’ve since added some extra loads to different phases (Air Source Heat Pump) however there is still an imbalance between phases.

 

So as an example

 

ph 1: 2kW Gen.  No load, 2kW export

ph2: 2kW Gen. 1kW load, 1kW export

ph3: 2kW Gen.  3kW load. 0kW export  1kW import  

 

Here we are  generating 6kW and using 4kW. Our meter shouldn’t be showing import as we are net exporting. However it seems to measure the import independently on each 3 phases and therefore is billing us for the ph3 import. 
 

From my understanding there’s a legal obligation of the supplier to ensure our electric is metered correctly. Which it isn’t. 
 

we’ve really hit a brick wall with Bulb so are hoping another supplier will understand and offer a meter. But it’s so hard to explain!
 

 

Nancy_OVO
Retired Moderator
Nancy_OVOSolved
Retired Moderator
May 18, 2020

Updated on 14/09/23 by Abby_OVO

 

Do OVO offer 3 phase smart meters?

 

3 phase (aka polyphase) installations in domestic properties are few and far between, so it's a minority of meter engineers across the country that have the skills required to complete these installations. There are also some technical challenges in making sure your job is allocated to an engineer with these skills but we are just as keen as you are to have Smart available for these sites ASAP, so if you would like to take part in this beta stage release, please consider the steps below:


From the start of May 2023, if you have a single rate 3 phase meter (i.e. not Economy 7 / 2-rate etc.) we would encourage you to book a smart meter appointment as normal online or over the phone on 0330 303 5063. (Please do not attempt to book sooner than May unless you have been contacted.)


This will then go through to a specialist team who will validate that it is single rate job and that an 3 phase engineer is available in your region. If this is the case, they will re-book your appointment with the right engineer. (So please bear in mind your appointment date/time will likely change, but we'll try to keep it the same where possible.)


Unfortunately, if you have a 2-rate meter or are not in an area covered by our current crop of 3 phase skilled engineers, you will need to continue with your heritage meter. We know this will be frustrating, so we are sorry about that, we are working to expand our coverage and by you flagging your interest to us, you are helping us shape where and when that coverage develops. - thank you!

 

Smart meters are able to measure export, for use in solar and other generation with the smart export guarantee 


If all 3 phases aren’t in use, you may consider downgrading to a single phase supply which is compatible with the current Smart meters we fit. Here's the process:

- Get an electrician to check if downgrading the supply is possible (you've done this already - nice work).
- Arrange a date for (and pay for) a visit from your Distribution Network Operator (DNO), who will rewire your supply to make it a single phase set up.
- Contact our Support Team to make sure we can get an engineer to you on the same day that the DNO visit, to fit your smart meter free of charge.

 

OVO member but not got a smart meter yet? - Book today!

 

Interested but not yet an OVO member? - Check out our plans!

 

Your guiding light(bulb)
Transparent
Rank 20
Rank 20
May 18, 2020

It’s interesting that @Nancy_OVO has indicated that it’s possible to have a SMETS1 3-phase meter. Which manufacturer?

Is the one used by OVO a “Vector sum” model?

All the SMETS1 meters made by Secure are due to receive a software upgrade and be migrated onto the National Smart Meter Network from Sunday 28th June. I wonder what happens then if it’s a 3-phase installation?  :thinking:

 

@Benseb- I think you should know that there is serious consideration at a national level to require all new houses to be constructed with 3-phase electricity supplies. This would not only slow the increase in technical losses at substations, but it is also required for homes with electric showers and an EV charger of 7kW and above.

That being the case, I can’t believe it will be long before the Data Communications Company (DCC) announce that they have approved a model.

Save energy... recycle electrons!
Nancy_OVO
Retired Moderator
Retired Moderator
May 19, 2020

@Transparent 

Sorry my bad, I was thinking of 5 port meters, not 3 phase ones. I’ve corrected this above.

Your guiding light(bulb)
Transparent
Rank 20
Rank 20
May 19, 2020

Ah… that makes more sense @Nancy_OVO. :slight_smile:

5-port SMETS2 meters are being fitted by other Energy Suppliers. They are most likely required for switching loads when we have Time Of Use tariffs in the future.

However, OVO have the Kaluza Platform which provides a more powerful/flexible way of achieving Load Control. So they are the least likely Supplier to need 5-port electricity meters for their customers!

Save energy... recycle electrons!
Nancy_OVO
Retired Moderator
Retired Moderator
May 19, 2020

@Transparent 

We can offer 5 port with S1, it’s currently being looked into for S2 too :)

Your guiding light(bulb)
Newcomer
April 5, 2022

I am considering switching to Ovo. I have a 3 phase supply with export for my solar panels. Does Ovo offer a 3 phase smart meter with export?