Why is my off peak not working after smart meter installed?

  • August 22, 2025
  • 42 replies
  • 2288 views

I had a smart meter installed. Chose economy 7 tariff as have storage heaters and water heated by thermostat on off peak. Since meter installed off peak does not work. Ovo sent an engineer who changed the meter. Still no off peak. Ovo then said they’d fix the problem remotely. They said it was successful but still no off peak. Now they are saying it must be to do with my wiring or configuration and they can’t do anything more. Now what am I supposed to do? No heating or hot water since July 28th.

Best answer by Firedog

Updated on 09/12/25 by Ben_OVO

You’re not the first to face this difficulty with a new meter. Happily, the remedy is often quite simple.

For a multi-rate system to work properly, three quite separate aspects of it have to be set:

  1. The correct tariff has to be applied to your account. You can with any luck see it on your Plan page, and it will usually show the offpeak timings.
  2. The tariff switching times have to be sent to the meter. It will normally start recording offpeak usage on register 2 at the start of each offpeak period and revert to register 1 at the end of it.
  3. The calendar for the Auxiliary Load Control Switch (ALCS) has to be sent to the meter. This is what decides when to switch power on to the circuit feeding the heating equipment, and in most cases the times will be the same as those in the tariff switching table. 

You should be able to see whether the tariff switching table has been properly set up, because the IHD may have been set up to tell you when the tariff changes. It may not be so easy to spot when the ALCS operates unless you have a neon indicating when power is switched to, say, the immersion heater. It is usually possible to spot it on the meter display itself if you know what to look for. We’d need to see a clear photo of the meter to be able to help with that. ‘Clear’ means a close-up so all the markings are legible, and it usually helps to tough a button before taking the picture to light up the display screen. A wider view showing everything on the meter backboard would help, too, so we can see all the cables to and from the meter. 

If you find out that the tariff is changing at the right times, but the ALCS isn’t playing its part, Support should be able to arrange for the ECAUL request to be sent to update the ALCS. Let’s make sure that this is the right approach first.

If you need to speak our Support Team to arrange an ECAUL request to be sent, our contact details can be found here:

 

 

You can find useful pages about smart meters and IHDs in our Forum Library section here.

42 replies

MilaAuthor
Rank 2
September 12, 2025

Hi again.

Ive been I touch with the Facebook group energy support and advice UK ad I am not getting anywhere on this.

They advised me that the fifth terminal on the smart meter may need activating/reactivating . Can anyone advise how this can be done.

Thank you 

 

Ben_OVO
Community Manager
Community Manager
September 12, 2025

Hi ​@Mila,

 

As our Complaints team has advised that you’ll need an electrician to fix it, then I’m afraid you’ll need to get an electrician to visit and fix it. On the off-chance that an electrician comes and advises that it’s an issue that an OVO metering engineer needs to resolve please send the electrician’s report to our Complaints team, who’ll look into refunding you the money.

Powered by the Sun
Newcomer
October 2, 2025

So basically long and short is I was happily with OVO for 4 years moved to British Gas as coming in cheaper but they messed my switch up and i reverted back to OVO

During the switch they have messed up my 2 rate Alcara 5 stem meter. My off peak circuit is constantly live 24 hours a day causing my storage heaters and water heater to kick and consume peak rate electricity.

I know this is something to do with the Auxiliary Load Control Switch (ACLS) not being set up properly. 

My meter is showing this icon below with LC2 showing when it should have the 2nd contactor icon show open during peak and closed position when switch on during off peak.

 

Switch ı should be always closed (o¯o); it controls the power to the stem/tail labelled 4, for everything not on the offpeak circuit. Switch ıı is the one for heating, closed only during offpeak hours. This is the Auxiliary Load Control Switch (ALCS), governing power to stem/tail 5. 

 

 This is how it shows on my neighbours meter in our block of flats.

 

Surely it something needs to be programmed here correctly. I have an engineer booked out for a site visit Monday.  I was wondering in the mean time you can shed some light on this. I have seen similar post on here and it seems ​@Tim_OVO  is very knowledgeable and helped with a similar issue.

 

At present I manually have to switch off my Off Peak Switch to stop my storage heaters and water heater to be constantly on and wait until 1am to switch the Off Peak circuit back on, and then turn off in morning.

Thanks in advance!

Blastoise186
Super User
Super User
October 2, 2025

Howdy ​@Sukey2K !

I’m afraid Tim has moved on from the Forum.

However, the command to reconfigure ECAUL/ALCS should do the trick - let OVO know and they can arrange it for you.

 

Securing energy by zapping security bugs... For that is The Blastoise Way! Remember, I'm just like you - AI Powered Evil Geniuses aren't Staff!
Firedog
Super User
Super User
October 2, 2025

Yes, something’s wrong! The Load Control 2 switch LC2 is a little 2A contactor designed to control a bigger (often 100A) external contactor for heavy loads like storage heaters and immersion heaters. This is connected separately from the fifth meter tail, using only a low-power cable. Your pictures don’t tell us much about how the meter is wired up, but if there’s constant power to the storage heaters, either they’re wired to the constant circuit along with everything else (appliances, sockets and lights) or there’s a large contactor somewhere that’s constantly energized - something it’s most probably not designed to be.

It’s possible, I suppose, that the LC2 icon is showing when the big (100A) internal LC contactor is energized. This shouldn’t be possible, but who knows - especially if BG’s techs have been messing with the meter*. In any event, the visiting engineer should be able to get you well on the way. Once the wiring’s been sorted out, the engineer should ask his contacts at HQ to send the ECAUL request to configure the ALCS properly.

 


We did have a case not long ago where BG had been trying to configure a smart meter in Scotland. They managed to screw up the meter’s software so badly that the whole meter had to be replaced after OVO had taken it over

Noel | I have no official status; I'm just a volunteer who comes here to help other customers. My gear: Aclara SGM 1416-B Electricity-only E7 meter; Chameleon IHD3-PPMID-AAA | It may look as if I know what I’m talking about, but don’t let that fool you. |
Newcomer
October 2, 2025

Thank you, as mentioned previously BG haven't done nothing physically, this only occurred once we switched to British Gas. I was trying to get sorted it out with them and their customers service was awful. Maybe there is something physically wrong with the meter but prior to the switch I was with OVO for 4 years and it work perfectly!

Blastoise186
Super User
Super User
October 2, 2025

Sounds like BG messed with the configs in ways they’re not supposed to.

OVO can probably fix that. There’s ways to fix this!

Securing energy by zapping security bugs... For that is The Blastoise Way! Remember, I'm just like you - AI Powered Evil Geniuses aren't Staff!
Newcomer
October 6, 2025

So OVO booked the engineer to visit today but no one from MDS turned up! This is getting well frustrating now.  Called OVO again and no arranged another engineer to visit next week. I explained everything about the ALCS/ ECAUL if anything can be done remotely but no, seems to be done on the  meter itself. Now have a engineer booked by Field Force

Ben_OVO
Community Manager
Community Manager
October 7, 2025

Sorry to hear about the missed appointment ​@Sukey2K, very frustrating. If you didn’t get at least 24 hours’ notice for the cancellation then you may be owed back a Guaranteed Standards of Performance compensation payment.

 

You can also find more info on this in this Forum topic:

 

 

Let us know how the appointment with our in-house engineers goes; hopefully no issues with the next one.

Powered by the Sun
MilaAuthor
Rank 2
January 14, 2026

Hi it’s been a long time but I’ve only just got this sorted. After three visits from Ovo meter engineers, nothing changed. I took the matter to the ombudsman who found in my favour another Ovo  meter engineer came after this But could only reiterate that everything was fine. I got to my own electrician in who discovered within five minutes of being in my property that when the smart meter was installed, no neutral cable had been attached, meaning that although electricity was available and the cable from the outside world showed as live,  it was not forming a circuit for the off peak. Please forgive me if the terminology is not technical I am not in electrician, but I hope that people who are electricians will understand what the problem was. He also was critical of the standard of work done by Ovo engineers and tidied up everything neatly that they had left in a mess. The next morning I finally had full heating for my storage heaters.

I am glad to say that Ovo have agreed to pay the cost of my electrician. I had to communicate again with the ombudsman and take time to send photographs of before and after together with my electrician’s report in order for this to happen. Without the work I had to put in and the time and effort of contacting the ombudsman, nothing  would’ve happened as Ovo Engineers consistently told me the System should be working, but they could not explain why it was not. I was very fortunate in having the money to pay the electrician upfront;other people might not be so fortunate.

A day or so ago I heard from Ovo that they would like to send some engineers round to look at my set up so it can be used as training for them. I have agreed to this because I think it’s really important that no one else is put in the position that I have been put in.