Hi, I have a solis 5kw hybrid inverter paired with 16.1k fogstar eco battery, but know the Inverter will not let the charge deplet from the battery. It worked fine until it reached 100 % at which point in just stays at 100%and draws power from the grid. Thanks for any help as this is driving me crazy.
- Forum
- Green tech & greener living
- Home and heating
- Solis 5kw hybrid inverter paired with 16.1k fogstar battery not depleting it's charge
Solis 5kw hybrid inverter paired with 16.1k fogstar battery not depleting it's charge
- March 19, 2026
- 18 replies
- 172 views
- Rank 2
Hi, I have a solis 5kw hybrid inverter paired with 16.1k fogstar eco battery, but know the Inverter will not let the charge deplet from the battery. It worked fine until it reached 100 % at which point in just stays at 100%and draws power from the grid. Thanks for any help as this is driving me crazy.
Check your inverter for “minimum SOC” or “reserve battery” settings, it’s likely set to 100%, so it won’t discharge. Lower that (e.g. 10–20%) and it should start using the battery.
Hi vertesol, I have tried all the normal settings and no luck unfortunately..
I think it maybe a software update that is required so waiting for Solis to update the firmware on the inverter.
Thanks
18 replies
- Super User
- March 20, 2026
Hi
Ours is a different manufacturer but I have a setting called ‘Charge Priority’ which makes sure the battery is topped up but can also stop power being drawn from the battery.
A few things to check - You might have
- Set Reserve SOC high (e.g. 80–100%) - keeps battery charge high
- Use Feed-in Priority mode - designed to make most use of export
- Or configure TOU with no discharge window - depending on your tariff, can restrict battery discharge at certain times
- Community Manager
- March 20, 2026
Hey
I’m glad to see BPLightlog has already stopped by with some helpful advice here, if you’ve not had a chance to check that out, please do and let us know if that helps.
We have some slightly similar topics on the Forum, I wonder if those could be helpful too, I’ve linked to a couple of those below:
Do let us know how you get on, I hope some of the above is helpful to you.
- Author
- Rank 2
- March 20, 2026
Hi
Ours is a different manufacturer but I have a setting called ‘Charge Priority’ which makes sure the battery is topped up but can also stop power being drawn from the battery.
A few things to check - You might have
- Set Reserve SOC high (e.g. 80–100%) - keeps battery charge high
- Use Feed-in Priority mode - designed to make most use of export
- Or configure TOU with no discharge window - depending on your tariff, can restrict battery discharge at certain times
Hi BP, I thank you for the reply..
The battery came prey charged at 30% it charged to 66 % and depleted to 20% that night so was working as it should
The problem came when it changed to 100 % the next day, after that it never departed it's charge.
I have tried all your suggestions but still no luck unfortunately.. I believe the inverter has a failsafe or something that won't release the charge?
- Author
- Rank 2
- March 20, 2026
Hey
I’m glad to see BPLightlog has already stopped by with some helpful advice here, if you’ve not had a chance to check that out, please do and let us know if that helps.
We have some slightly similar topics on the Forum, I wonder if those could be helpful too, I’ve linked to a couple of those below:
Do let us know how you get on, I hope some of the above is helpful to you.
Hi Abby, thank you for your reply..
Still no luck unfortunately
- Super User
- March 20, 2026
Hi BP, I thank you for the reply..
…
The problem came when it changed to 100 % the next day, after that it never departed it's charge.
I have tried all your suggestions but still no luck unfortunately.. I believe the inverter has a failsafe or something that won't release the charge?
The ‘fail safe’ is generally to prevent the battery going too low or to stop discharge during a power cut (there needs to be extra protection for engineers) rather than when full so I’m not sure what else to suggest if you’ve checked your timings (sometimes used to prevent discharge during the day or at any off-peak times).
There should also be a forced discharge setting which might help if you want to get the battery below 100% although this does export power rather than powering the home.
- Author
- Rank 2
- March 20, 2026
Hi BP, I thank you for the reply..
…
The problem came when it changed to 100 % the next day, after that it never departed it's charge.
I have tried all your suggestions but still no luck unfortunately.. I believe the inverter has a failsafe or something that won't release the charge?
The ‘fail safe’ is generally to prevent the battery going too low or to stop discharge during a power cut (there needs to be extra protection for engineers) rather than when full so I’m not sure what else to suggest if you’ve checked your timings (sometimes used to prevent discharge during the day or at any off-peak times).
There should also be a forced discharge setting which might help if you want to get the battery below 100% although this does export power rather than powering the home.
I contacted Solis and they were rude and unhelpful.. They said the fogstar battery was not compatible with the solis inverters.
Fogstar are telling me the battery is fully functional and it is the inverter at fault so I don't know what to do now
- Super User
- March 20, 2026
…
I contacted Solis and they were rude and unhelpful.. They said the fogstar battery was not compatible with the solis inverters.
Fogstar are telling me the battery is fully functional and it is the inverter at fault so I don't know what to do now
Who did the install ? At this point I would get the installer back to rectify.
Or you could ask Fogstar how to ensure it’s set properly. Some inverters have a setting for which batteries are connected (which adjust levels for voltage, current etc)
- Author
- Rank 2
- March 20, 2026
…
I contacted Solis and they were rude and unhelpful.. They said the fogstar battery was not compatible with the solis inverters.
Fogstar are telling me the battery is fully functional and it is the inverter at fault so I don't know what to do now
Who did the install ? At this point I would get the installer back to rectify.
Or you could ask Fogstar how to ensure it’s set properly. Some inverters have a setting for which batteries are connected (which adjust levels for voltage, current etc)
I am not having any luck with Solis they said the fogstar battery is not compatible and may void the warranty and Fogstar just uses the pylon protocol that doesn't work so I am between a rock and a hard place. Thanks for your help BP.. Much appreciated
- Super User
- March 21, 2026
I’ve found a few more details that might be worth checking:
- The set up must be for a 48v Solis inverter
- You should have the batteries connected via 50mm^2 cables
- You need to use the CAN connection from the inverter CAN port to the battery
- Set the battery protocol to CAN>Pylontech
- The inverter needs the battery type set to Pylontech>Lithium (CAN)
The CAN connection and set up is critical otherwise the inverter cannot read the SOC (state of charge) which might explain why your battery won’t discharge.
If you have multiple batteries, only the master links via CAN, the others via RS485.
Of course, you may have already covered these points - the other thing to check is that firmware is up to date
- Author
- Rank 2
- March 21, 2026
I’ve found a few more details that might be worth checking:
- The set up must be for a 48v Solis inverter
- You should have the batteries connected via 50mm^2 cables
- You need to use the CAN connection from the inverter CAN port to the battery
- Set the battery protocol to CAN>Pylontech
- The inverter needs the battery type set to Pylontech>Lithium (CAN)
The CAN connection and set up is critical otherwise the inverter cannot read the SOC (state of charge) which might explain why your battery won’t discharge.
If you have multiple batteries, only the master links via CAN, the others via RS485.
Of course, you may have already covered these points - the other thing to check is that firmware is up to date
You are a legend BP.. I will give that a go and let you know the out.. Thanks again
- Newcomer
- March 31, 2026
Hi, I have a solis 5kw hybrid inverter paired with 16.1k fogstar eco battery, but know the Inverter will not let the charge deplet from the battery. It worked fine until it reached 100 % at which point in just stays at 100%and draws power from the grid. Thanks for any help as this is driving me crazy.
Check your inverter for “minimum SOC” or “reserve battery” settings, it’s likely set to 100%, so it won’t discharge. Lower that (e.g. 10–20%) and it should start using the battery.
- Community Manager
- April 1, 2026
Thanks for your input here
Let us know if you have solar panels and a battery - if so we’ll update your profile with the relevant badges.
- Author
- Rank 2
- April 1, 2026
Hi, I have a solis 5kw hybrid inverter paired with 16.1k fogstar eco battery, but know the Inverter will not let the charge deplet from the battery. It worked fine until it reached 100 % at which point in just stays at 100%and draws power from the grid. Thanks for any help as this is driving me crazy.
Check your inverter for “minimum SOC” or “reserve battery” settings, it’s likely set to 100%, so it won’t discharge. Lower that (e.g. 10–20%) and it should start using the battery.
Hi vertesol, I have tried all the normal settings and no luck unfortunately..
I think it maybe a software update that is required so waiting for Solis to update the firmware on the inverter.
Thanks
- Community Manager
- April 2, 2026
- Super User
- April 2, 2026
Hi
I've been tracking this issue for a little while and thought that it might have got fixed by now. I'm not familiar with solar or a home battery so my go to ploy when the answer seems intractable is the ask Chat and here is what it has said. My apologies for the length of the response but I don't know what is important or not so I've left it unedited and also for repeated advice given by others. I really hope one of these is your issue and you can get it working.
Peter
---------------------------------- ChatGPT
This isn’t a rare issue with Solis hybrids + third-party batteries. When a system suddenly refuses to discharge after hitting 100%, it’s almost always a control/communication or protection limit—not a hardware failure. Here’s how I’d attack it, in the right order (don’t skip around):
1) Check battery → inverter communication (most likely)
Your Solis inverter relies on BMS data from the Fogstar battery. If comms drop or become invalid at high SOC, the inverter will lock out discharge as a safety default.
What to check:
Is the battery showing “Normal” / “Ready” / “Discharge allowed” on its interface?
Any CAN/RS485 errors in the inverter logs?
Cable seated properly (this causes more issues than people admit)
👉 If comms fail, many Solis units assume “battery full but unavailable” → so they sit at 100% and pull from grid.
2) SOC calibration / top-of-charge lockout
Fogstar (and many LiFePO4 systems) can misreport 100% SOC after a full charge if the BMS hasn’t properly balanced.
That can cause:
BMS says “100%”
But also “do not discharge” due to cell imbalance or protection thresholds
What to do:
Let it sit at 100% for a few hours (allows passive balancing)
Then force a discharge (see section 5)
If possible: check individual cell voltages via BMS app
👉 If one cell is high, the BMS may block discharge to avoid over-voltage swing.
3) Inverter discharge settings (very common misconfig)
Go into the Solis settings and check:
Battery discharge limit / reserve SOC
If set to 100% → it will never discharge
Time-of-use / forced modes
Could be stuck in a “charge-only” window
Self-use mode enabled?
If not, it may prioritise grid
Typical culprits:
“Backup reserve” accidentally set high (e.g. 100%)
“Min SOC” set too high (e.g. 95–100%)
4) Charge/discharge current limits from BMS
If the battery reports:
Charge current = OK
Discharge current = 0
…the inverter will obey.
Check:
Max discharge current reported by BMS
Any protection flags:
Overvoltage
Low temp
Cell imbalance
5) Force a discharge (diagnostic step)
Temporarily override normal operation:
Put inverter in manual/self-use mode
Turn on a large load (kettle, heater, EV charger etc.)
See if battery responds
If it still won’t discharge: 👉 That confirms a BMS restriction, not inverter logic
6) Firmware compatibility
This combination (Solis + third-party battery) can be fragile.
Check:
Inverter firmware version
Battery firmware version
Whether Fogstar officially supports Solis comms protocol
👉 Mismatched protocols often break specifically at high SOC states
7) Grid-charge priority bug / quirk
Some Solis firmware versions behave badly at 100%:
They prioritise grid once “full”
Don’t re-enable discharge until SOC drops slightly
Workaround:
Lower max charge SOC to ~95–98%
This often “unsticks” the system
8) Temperature edge case
If battery temp is:
Too low → discharge blocked
Too high → protection mode
Worth checking, especially if installed in garage/outdoor space.
What I think is most likely (based on your description)
Bluntly:
80% chance it’s either reserve SOC set to 100% or BMS not allowing discharge at full charge due to imbalance/comms
Fastest way to narrow it down
Do this in order:
Check min SOC / reserve SOC setting
Try force discharge with a heavy load
Look for BMS “discharge allowed” flag
Reduce max SOC to 95% and retry
If you want, tell me:
Exact Solis model (there are subtle differences)
How the battery is connected (CAN or RS485)
Current SOC / voltage / any error codes
…and I’ll pinpoint it much more precisely.
- Author
- Rank 2
- April 2, 2026
Hi
I've been tracking this issue for a little while and thought that it might have got fixed by now. I'm not familiar with solar or a home battery so my go to ploy when the answer seems intractable is the ask Chat and here is what it has said. My apologies for the length of the response but I don't know what is important or not so I've left it unedited and also for repeated advice given by others. I really hope one of these is your issue and you can get it working.
Peter
---------------------------------- ChatGPT
This isn’t a rare issue with Solis hybrids + third-party batteries. When a system suddenly refuses to discharge after hitting 100%, it’s almost always a control/communication or protection limit—not a hardware failure. Here’s how I’d attack it, in the right order (don’t skip around):
1) Check battery → inverter communication (most likely)
Your Solis inverter relies on BMS data from the Fogstar battery. If comms drop or become invalid at high SOC, the inverter will lock out discharge as a safety default.
What to check:
Is the battery showing “Normal” / “Ready” / “Discharge allowed” on its interface?
Any CAN/RS485 errors in the inverter logs?
Cable seated properly (this causes more issues than people admit)
👉 If comms fail, many Solis units assume “battery full but unavailable” → so they sit at 100% and pull from grid.
2) SOC calibration / top-of-charge lockout
Fogstar (and many LiFePO4 systems) can misreport 100% SOC after a full charge if the BMS hasn’t properly balanced.
That can cause:
BMS says “100%”
But also “do not discharge” due to cell imbalance or protection thresholds
What to do:
Let it sit at 100% for a few hours (allows passive balancing)
Then force a discharge (see section 5)
If possible: check individual cell voltages via BMS app
👉 If one cell is high, the BMS may block discharge to avoid over-voltage swing.
3) Inverter discharge settings (very common misconfig)
Go into the Solis settings and check:
Battery discharge limit / reserve SOC
If set to 100% → it will never discharge
Time-of-use / forced modes
Could be stuck in a “charge-only” window
Self-use mode enabled?
If not, it may prioritise grid
Typical culprits:
“Backup reserve” accidentally set high (e.g. 100%)
“Min SOC” set too high (e.g. 95–100%)
4) Charge/discharge current limits from BMS
If the battery reports:
Charge current = OK
Discharge current = 0
…the inverter will obey.
Check:
Max discharge current reported by BMS
Any protection flags:
Overvoltage
Low temp
Cell imbalance
5) Force a discharge (diagnostic step)
Temporarily override normal operation:
Put inverter in manual/self-use mode
Turn on a large load (kettle, heater, EV charger etc.)
See if battery responds
If it still won’t discharge: 👉 That confirms a BMS restriction, not inverter logic
6) Firmware compatibility
This combination (Solis + third-party battery) can be fragile.
Check:
Inverter firmware version
Battery firmware version
Whether Fogstar officially supports Solis comms protocol
👉 Mismatched protocols often break specifically at high SOC states
7) Grid-charge priority bug / quirk
Some Solis firmware versions behave badly at 100%:
They prioritise grid once “full”
Don’t re-enable discharge until SOC drops slightly
Workaround:
Lower max charge SOC to ~95–98%
This often “unsticks” the system
8) Temperature edge case
If battery temp is:
Too low → discharge blocked
Too high → protection mode
Worth checking, especially if installed in garage/outdoor space.
What I think is most likely (based on your description)
Bluntly:
80% chance it’s either reserve SOC set to 100% or BMS not allowing discharge at full charge due to imbalance/comms
Fastest way to narrow it down
Do this in order:
Check min SOC / reserve SOC setting
Try force discharge with a heavy load
Look for BMS “discharge allowed” flag
Reduce max SOC to 95% and retry
If you want, tell me:
Exact Solis model (there are subtle differences)
How the battery is connected (CAN or RS485)
Current SOC / voltage / any error codes
…and I’ll pinpoint it much more precisely.
Hi Peter..
I have also tried Chat to help me resolve the issue and have exhausted all the fixes apart from the firmware update.. Waiting on Solis to upgrade remotely for 3 days now and still nothing.
I will drop a message once Solis updates the inverter.
Thanks for your help.. Much appreciated as this is nearly 4 weeks now.
- Super User
- April 2, 2026
Many thanks
Peter
Need advice from other members?
Ask your question to our members - they have the experience you're looking for:
Ask our communityLog in to the OVO Forum
No account yet? Create an account
Enter your E-mail address. We'll send you an e-mail with instructions to reset your password.
Scanning file for viruses.
Sorry, we're still checking this file's contents to make sure it's safe to download. Please try again in a few minutes.
OKThis file cannot be downloaded
Sorry, our virus scanner detected that this file isn't safe to download.
OKContact us
Tips & advice
Resources
For business
OVO Energy Ltd, registered office 1 Rivergate Temple Quay Bristol, BS1 6ED, company no. 06890795 registered in England and Wales.
OVO (S) Gas Limited is registered in England and Wales (Company No. 02716495) at 1 Rivergate, Temple Quay, Bristol, BS1 6ED.
OVO (S) Gas Limited is part of OVO Group Ltd