It is a derating message from the inverter.
What’s causing it, is something you will need to investigate further from the list in the link
You may need to check with Solis if you can’t identify the problem
If you look at one of the condition notes :
•If the internal temperature is between 40°C (104°F) and 60°C (140°F) the inverter will have derated to somewhere between 100% and 77% of maximum output power Above 60°C the inverter will stop producing power until the internal temperature lowers.
you will see that at 84°C internally, the electronics are protecting themselves so unless you can improve the cooling around the inverter it will derate at that level.