Ecodan heat pump FTC 7. When heating is on, our water heats up at the same time non-stop. How do I fix it?

  • April 6, 2026
  • 8 replies
  • 117 views

When heating is on, the water starts to heat up as well, but it is not on the controller - water is shown as OFF. Looks like something is wrong with the settings. Please Help!

Remote controller: Switchee Hot water set 45. NOT legionella mode 

 

Best answer by VicByron

Thanks everybody! I found a solution, in the settings there was an option: use electric heating for water and for heating, just removed the tick. Thanks again.😊

8 replies

Chris_OVO
Community Manager
Community Manager
April 15, 2026

Hey ​@VicByron,

 

Welcome to the community! 

 

I’ll tag a few members who might have some great advice to share! It’s possible that the issue could be related to a control or valve, which an engineer might need to take a look at in person. But let’s see if we can come up with some solutions together first!

 

Could you share a bit more about your setup? Do you have underfloor heating or a hot water tank? Also, are there any settings that might be affecting things, like a hot water priority mode, or is it set up to work at the same time as your heating? Looking forward to your response!

 

@Ecodanwarrior ​@BPLightlog ​@Peter E could any of you offer any advice on the above? 

Renewable energy jokes never get old.
juliamc
Rank 20
Rank 20
April 15, 2026

If the hot water really is 64 deg then unlikely to be a stuck 3 way valve which was my 1st thought. 🤔 

BPLightlog
Super User
Super User
April 15, 2026

I’m not too familiar with Ecodan, Julia has pointed to a key part to consider.

Normally, the motorised three-way valve switches between hot water and heating, so the only way it can normally be heating both is if the valve is stuck part way open. This might also explain the over temperature as there would be no way to switch hot water off.

Bring me Sunshine ~ E&E {Solar PV, Battery Storage, Hybrid EV, ASHP and Home Assistant automation}
Rank 2
April 15, 2026

I haven’t seen this issue before but a test to check the valve would be to put your hand near the pipes going into the water tank, if they are hot then most likely points to a valve being stuck open.

 

Curious to know though if you're running a compensation curve for the heating?  I have found that the temp in the rads don’t usually get above 30-35 degrees, so that heat would not be enough to raise the tank from 45 to 64.  

Peter E
Super User
Super User
April 15, 2026

As above. Sounds like a stuck valve so I would target that first.

 

Peter

 

Reducing my yearly fossil fuel usage with an EV (-900 litres petrol), A2AHP (-8,700 kWh gas) and Timed Immersion heater (-1,500 kWh gas)
VicByronAuthorSolved
Rank 1
April 15, 2026

Thanks everybody! I found a solution, in the settings there was an option: use electric heating for water and for heating, just removed the tick. Thanks again.😊

Peter E
Super User
Super User
April 15, 2026

Thanks for coming back. We do appreciate finding out what the answer was.

Reducing my yearly fossil fuel usage with an EV (-900 litres petrol), A2AHP (-8,700 kWh gas) and Timed Immersion heater (-1,500 kWh gas)
Chris_OVO
Community Manager
Community Manager
April 16, 2026

Hey ​@VicByron,

 

I'm really glad it was a simple fix! As Peter said, we truly appreciate you jumping in to share the resolution with us. 😊

 