I finished building my house this year and moved in back in June. I’ve been using my air source heat pump for heating and water and not really thought anything about it until I noticed my electricity bills. I’m spending about £13 a day on electricity and decided I need to learn how to most efficiently run my airsource and heating schedule.
There really isn’t much information online about this. So I’m really hope someone here will be able to help me please.
Thank you
My set up is as follows:
Mitsubishi Electric Ecodan PUHZ-HW140VHA2 14kW air-source heat pump
Mitsubishi Electric EHPT25X-UKHCW 250 litre water tank
Mitsubishi Electric FTC5 Ecodan Controller PAC-IF062B-E
Heatmiser Streamline controllers in each room
House:
New build house. Largely open plan downstairs. Does have some large window walls in the entrance hall which we would lose a bit of heat through.
Floor coverings: upstairs is carpet and low tog underlay. Carpet is thick, but we kept the total tog below the recommended amount (my memory is hazy, possibly 2.5 tog?) Downstairs we have 12mm thick laminate.
Underfloor heating upstairs and down
Current schedules:
Ecodan controller set to run at 18degrees continuously.
3 main living rooms (open plan kitchen, dining and lounge) set to 21 degrees between 5am-8.30am and then 16 degrees, then on again at 4pm for a couple of hours at 21, then back to 16
All other rooms in the house: Heatmiser contollers set to Frost protection mode (set to between 10degrees and 15 degrees)
Hot water is heated from 6-7am and then half an hour in the afternoon 3-3:30pm. Hot water seems to heat to41degrees now – although it used to be higher (could it be the compensation curve? Not sure if that changes DHW temp)
I think my hot water only heats when scheduled to heat on the Ecodan controller – I though it might be using the immersion heater. From what I can work out, i don’t think the underfloor heating results in the water heating at all unless the immersion heater turns on.
Hot water costs:
October 158 kWh £34.74
November 228 kWh £50.13
December (<19th) 164 kWh £36.06
Heating costs:
October 164 kWh £36.06
November 621 kWh £136.54
December (<19th) 491 kWh £107.96
Temperatures
The room temp on the thermometers seems to average around between 15 and 17 degrees. Which I feel is too low. We do have a wood burning stove which we have been using to heat the downstairs rooms to a more reasonable temp (gets up to 21-23 when this is running)
COP values
According to my MSC certificate we should get 3.48 COP. I reckon we’re getting the following:
December 2021 <19th 2.348
November 2021 2.377
October to December 19th 2.179
If anyone can help with any advice that would be very much appreciated. Thank you very much