Skip to main content
Solved

Is this connection of Yemen flats electric meters safe?

  • December 19, 2025
  • 12 replies
  • 210 views

Is this connection for several falts correct or wrong?

Best answer by Blastoise186

Ok, FINALLY managed to figure out the cable spaghetti… Man this was complicated…

Just trying to translate the Ministry of Electricity resources into English was a headache not least because Iraq uses Right-To-Left text, unlike the Left-To-Right text here in the UK.

Anyway… I did manage to figure it out enough to get you an answer. But I will admit that it’s pushing my understanding pretty hard as we’re not used to foreign setups like this one.

To give you a straight answer: No, this setup is not safe. In fact, by UK safety standards (which is what we specialise in on this forum), this would be considered a "Category A" immediate hazard.

To answer your question about what you are looking at:

  • The "Bird's Nest": This is a chaotic junction of "Live" and "Neutral" feeds. It appears to be a mix of official state power and potentially private generator lines all spliced together using IPCs (Insulation Piercing Connectors). The state supply from the Ministry of Electricity (MoE) is  cheap, but also known to be unstable and only run for limited hours - the private generators are expensive but cover the remaining hours (and they literally are on street corners run by private individuals). Some of the wires are from the state supply, others from the private generators - but they all converge at the same point, hence the bird’s nest.

  • The Hazard: Because these wires are bunched together without "cleating" (proper supports), the weight of the cables is pulling on the connections. This leads to arcing—where electricity jumps through the air—creating temperatures hotter than the sun. This is a massive fire risk to the building.

  • Exposed Live Parts: In your close-up photos, there are exposed metal bolts that are likely carrying 230V. Touching these, or even getting a metal ladder/tool near them, could result in a fatal electric shock or an "Arc Flash" explosion. Even touching the wall they’re on could shock you if it’s damp/wet for any reason.

  • The Meters: You have a mix of standard "Post-Paid" (Red label) and "Pre-Paid" (Yellow label) electronic meters. Because they are all tied into that same messy "bird's nest," a fault in one neighbour's wire could potentially travel through the cluster and blow the electronics in your meter or cause a fire in your flat.

Technical Note: The Wiring "Topology"

I also wanted to highlight a specific technical concern regarding how those meters are physically connected. In a standard UK installation, each meter has its own dedicated, isolated feed. Looking at your photos, that is not the case here:

  • Shared/Common Neutral: It appears that all these meters are sharing a "Common Neutral" line within that cluster. In electrical terms, if that one main neutral wire becomes loose or fails (due to the weight of the "bird's nest"), it can cause a "floating neutral." This can suddenly send 400V through a standard 230V appliance, frying every electronic device in your home instantly.

  • Daisy-Chaining (Serial Routing): It looks like the "Mains" power enters the first meter and is then "jumped" or daisy-chained to the next one. This means the first set of terminals is carrying the electrical load for multiple households. Those terminals aren't designed for that much current; they will eventually overheat, melt the plastic casing, and potentially start a fire on the external wall.

  • Zero Isolation: Because the "routing" is so tangled, there is no way to isolated one meter without potentially disturbing the live wires of another. This is why you must never attempt a DIY repair—moving one wire could cause a short-circuit in the wire next to it.

The Blastoise186 Verdict: As this is a UK-based forum, we deal with a very different grid (SMETS2 meters and strict DNO regulations). We cannot advise you on how to fix this because the logic of that "nest" doesn't follow standard engineering rules.

Please do not touch any part of this setup. You need a local professional who has a full Arc Flash Suit and insulated tools. In the UK, we would call the emergency line (105) immediately for this; please find the equivalent emergency contact for the Ministry of Electricity in your area.

Stay safe

12 replies

Blastoise186
Super User
Forum|alt.badge.img+9
  • Super User
  • December 19, 2025

Hi ​@Ahmed Al Kuhlani ,

That’s not good… Try calling 105 for that.


Nukecad
Super User
Forum|alt.badge.img+5
  • Super User
  • December 20, 2025

I have no idea what we are looking at in that image, other than a bunch of wires and a few clamping blocks.

We would need to see much more, ie. what they connect to, if we are to have any clue about what they are for.

The blocks appear to clamp pairs of single wires, but the wires don’t appear to be joined, the tapes appear to be covering single wire ends and not joints.

I count 12 wires in the loose twist, (one appears to have no insulation), going into 6 clamps, and then being terminated with tape.

To me it looks like something that is no longer is use but hasn’t been removed.
(A bit like the old telephone wires you can often still see on the outside of old office buildings or blocks of flats).


These groups of pair cables supply power from cable source to several electric meters (not shomn in picture) , and another pair wires connected from the meters to individual flats.

My question is this arrangement shown in the picture is correct or not. Does it affects the efficiency of the meters.


Nukecad
Super User
Forum|alt.badge.img+5
  • Super User
  • December 20, 2025

 

We would need to see much more, ie. what they connect to,

 Nobody can give you an answer unless you provide more.

All we can see there is a bunch of wires that may or may may not be connected to anything at all.


This is the full picture, my question, the way of connecting the meters from the source cable, correct or wrong?


Forum|alt.badge.img+2
  • Rank 12
  • December 21, 2025

Where is this? Are they inside or outside? Please give a close up of the “meters”.


Blastoise186
Super User
Forum|alt.badge.img+9
  • Super User
  • December 21, 2025

Just a heads up…

Looks like these meters are located outside the UK (possibly Iraq?). As the OVO Forum is UK based, we’re a bit limited on what we can advise as we don’t specialise in setups elsewhere.

We’ll still be happy to try and offer some advice, but please also consider using local resources in your own country too - you’ll need to double check to be sure!

I will do some research in the background, but please be aware that given your location, resources may be limited.


Blastoise186
Super User
Forum|alt.badge.img+9
  • Super User
  • Solved
  • December 21, 2025

Ok, FINALLY managed to figure out the cable spaghetti… Man this was complicated…

Just trying to translate the Ministry of Electricity resources into English was a headache not least because Iraq uses Right-To-Left text, unlike the Left-To-Right text here in the UK.

Anyway… I did manage to figure it out enough to get you an answer. But I will admit that it’s pushing my understanding pretty hard as we’re not used to foreign setups like this one.

To give you a straight answer: No, this setup is not safe. In fact, by UK safety standards (which is what we specialise in on this forum), this would be considered a "Category A" immediate hazard.

To answer your question about what you are looking at:

  • The "Bird's Nest": This is a chaotic junction of "Live" and "Neutral" feeds. It appears to be a mix of official state power and potentially private generator lines all spliced together using IPCs (Insulation Piercing Connectors). The state supply from the Ministry of Electricity (MoE) is  cheap, but also known to be unstable and only run for limited hours - the private generators are expensive but cover the remaining hours (and they literally are on street corners run by private individuals). Some of the wires are from the state supply, others from the private generators - but they all converge at the same point, hence the bird’s nest.

  • The Hazard: Because these wires are bunched together without "cleating" (proper supports), the weight of the cables is pulling on the connections. This leads to arcing—where electricity jumps through the air—creating temperatures hotter than the sun. This is a massive fire risk to the building.

  • Exposed Live Parts: In your close-up photos, there are exposed metal bolts that are likely carrying 230V. Touching these, or even getting a metal ladder/tool near them, could result in a fatal electric shock or an "Arc Flash" explosion. Even touching the wall they’re on could shock you if it’s damp/wet for any reason.

  • The Meters: You have a mix of standard "Post-Paid" (Red label) and "Pre-Paid" (Yellow label) electronic meters. Because they are all tied into that same messy "bird's nest," a fault in one neighbour's wire could potentially travel through the cluster and blow the electronics in your meter or cause a fire in your flat.

Technical Note: The Wiring "Topology"

I also wanted to highlight a specific technical concern regarding how those meters are physically connected. In a standard UK installation, each meter has its own dedicated, isolated feed. Looking at your photos, that is not the case here:

  • Shared/Common Neutral: It appears that all these meters are sharing a "Common Neutral" line within that cluster. In electrical terms, if that one main neutral wire becomes loose or fails (due to the weight of the "bird's nest"), it can cause a "floating neutral." This can suddenly send 400V through a standard 230V appliance, frying every electronic device in your home instantly.

  • Daisy-Chaining (Serial Routing): It looks like the "Mains" power enters the first meter and is then "jumped" or daisy-chained to the next one. This means the first set of terminals is carrying the electrical load for multiple households. Those terminals aren't designed for that much current; they will eventually overheat, melt the plastic casing, and potentially start a fire on the external wall.

  • Zero Isolation: Because the "routing" is so tangled, there is no way to isolated one meter without potentially disturbing the live wires of another. This is why you must never attempt a DIY repair—moving one wire could cause a short-circuit in the wire next to it.

The Blastoise186 Verdict: As this is a UK-based forum, we deal with a very different grid (SMETS2 meters and strict DNO regulations). We cannot advise you on how to fix this because the logic of that "nest" doesn't follow standard engineering rules.

Please do not touch any part of this setup. You need a local professional who has a full Arc Flash Suit and insulated tools. In the UK, we would call the emergency line (105) immediately for this; please find the equivalent emergency contact for the Ministry of Electricity in your area.

Stay safe


juliamc
Rank 20
Forum|alt.badge.img+11
  • Rank 20
  • December 21, 2025

Wow ​@Blastoise186 this may be your best yet !!


Blastoise186
Super User
Forum|alt.badge.img+9
  • Super User
  • December 21, 2025

I have magic tricks for this :)


The picture is from Yemen, where everything is in very low category.


Blastoise186
Super User
Forum|alt.badge.img+9
  • Super User
  • December 21, 2025

Ah yeah, that makes sense. Just like in Iraq, the official grid supply in Yemen is equally weak and in some areas, non-existent. Over 80% of the supply likely comes from a local “Generator Boss” who runs a private operation and charge a premium for it.

But my advice remains the same - please stay away from that monster of equipment if you can.