Protecting an EV and Charge Point with an Surge Protection Device (SPD)
Outside your house you have an EV and a Charge Point connected to the mains. These items have a considerable value but are subject to mains voltage spikes from time to time. Most of the time the voltage spikes can be handled by the equipment as they have their own limited protection but, just occasionally, you will get the odd damaging spike caused by lightning or a power supply event (outage/restoration).
In order to protect your EV/CP and also other equipment in your house you can fit a Surge Protection Device with a current capability of 40kA (40,000A). For most of the time it doesn’t do anything but it is capable of significantly reducing anomalous power spikes that occur from time to time. There would be a cost to having one of these fitted but consider it as an insurance policy. You might not ever need it but it could prevent a lot of damage to expensive equipment if you did get a large voltage spike for some reason.

This shows a typical arrangement of an SPD within a consumer unit (not mine). The incoming mains isolation switch is on the right followed by an MCB (1) and then the SPD (2). There is some discussion about whether you need to fit an MCB before the SPD but the consensus is that if your incoming DNO fuse is 80 or 100A then an MCB is required. If you are on a looped supply, or otherwise, and your fuse is 60A then not fitting an MCB is considered to be OK.
You might think the MCB would ‘pop’ (go open circuit) when a surge is clamped but it doesn’t as the event happens so quickly it doesn’t have enough time to react. However, if the SPD clamps a surge bigger than it is capable of surviving, and it goes short circuit as a result, then the MCB will open the circuit quicker than an 80/100A fuse would blow. However, it’s considered that a 60A fuse would blow quicker than the MCB would react so the MCB is not needed for that size of fuse. I have a 60A fuse so my SPD doesn’t have the MCB protection which is why I’ve not shown it. If the SPD has clamped more spikes beyond its rating then the green window on the device turns to red and it needs to be replaced. It’s also showing that it’s doing its job.
For EICR checks you can’t have an SPD in circuit and it would have to be temporarily disconnected for the insulation check.
A Youtube video from eFixx