Heat pump pipe insulation: Energy efficiency starts with the pipes

Heat pump pipe insulation: Energy efficiency starts with the pipes
Userlevel 7

Updated on 11/12/23 by Emmanuelle_OVO:

 

Pipe Insulation for your Air Source Heat Pump (ASHP)

 

In collaboration with our Zero Carbon Homes trialists, we’ve put together a guide to the pipe insulation which should be fitted alongside an Air Source Heat Pump. Getting this pipe insulation right will make sure your new heating system runs as efficiently as possible so it’s really valuable to learn from those who’ve already been through the installation process.

 

Below we’ve combined images and testimonials from members that have made the move away from carbon intensive gas boilers, to help show what to look out for following a visit from your installers.

 

The basics

 

@Transparent writes that: “There are three different categories of pipe insulation to be considered:

 

1: Exterior - must be Class-O, closed-cell, UV-resistant with wall thickness greater than 19mm.

2: In lofts, unheated “plant-rooms”, garage spaces or below a suspended floor. This should also have high wall-thickness and the joins taped. It may be subject to condensation but not exposed to sunlight and rain.

3: Internal - Can be the more common Climaflex type held with clips such as those sold here

 

External ASHP pipe insulation

 

The temperature difference between the water flowing from and returning to the Heat pump will be about 5°C whilst the pump is running. It is therefore important to properly insulate these external pipes in order to prevent heat-loss.

 

Exterior insulation needs to have two main characteristics:

  • it must be of closed-cell construction to prevent rain or condensation filling up the voids within the material. They are what provide the insulating properties.
  • it must be resistant to UV radiation from sunlight.
  •  

Neither the common grey Polyethylene (Climaflex) insulation, nor the black nitrile-rubber (Armaflex) insulation satisfy these criteria.

 

If there is little choice available, Armaflex nitrile-rubber can be used, but should then be over-painted with at least 2 coats of a terpolymer resin paint such as Armafinish 99, or ArmaFinish FR. These are available in black, grey or white.

 

 

The better choice is to use an EPDM-rubber insulation such as Armaflex HT. This is more commonly sold for use on pipework connections to solar-thermal panels - hence the HT designation for High Temperature. However, it is its resistance to UV radiation which makes solar-pipe insulation suitable for Heat pumps.

 

Both Armaflex nitrile rubber and Armaflex HT EPDM pipe insulation are sold in 2m lengths with wall thicknesses of 13, 19 and 25mm.

 

 

When lagging long runs of 15mm or 22mm pipe, rolls of insulation are also available. However as this roll option is only manufactured with wall thicknesses of 13mm or 19mm, it is of little use for exterior Heat pump pipework in the UK’s winter climate. Long pipe runs would require 25mm thickness.

 

Armaflex pipe insulation (unsplit and self-sealing) with tape for joins

 

Insulation should cover not just the external pipework, but also every valve. This requires sections to be made from lengths with a larger internal bore. EPDM-rubber insulation is available with bore sizes in steps from 15mm to 89mm for both 19mm & 25mm wall-thicknesses.

 

Generic “solar” pipe insulation is readily available from BES and BIS (no relation). But avoid buying from Ebay and Amazon sellers unless you really can tell the difference between UV-resistant EPDM and ordinary Nitrile Rubber! You may not be supplied with what you’ve ordered.

 

Both types of black rubber insulation are normally referred to as ‘Class-O’. This is their fire-rating. They are much less combustible than the grey Polyethylene variety and do not give off poisonous fumes when in a fire.

 

To accommodate a valve lever, a round hole is made in the insulation on the opposite side to the lengthways split.

 

 

It can be fitted by temporarily removing the handle on a manually-operated valve. That split is then on the opposite side of the valve body, and must be sealed with exterior-grade Class-O insulation strip.

 

To avoid ingress of rain water, valves in external pipework should not be installed with the lever-handle upwards.

 

Joins between sections of insulation need covering with a UV-resistant tape. This must not be stretched when being applied. It may unstick itself when it later contracts, and it can compress the EPDM, decreasing the wall thickness and hence leave a weak-spot for heat-loss.

 

Armaflex EPDM tape being used to replace degraded duct-tape joins

 

Tape with integrated fabric is best. If you can’t find an EPDM tape then Scotch (3M) do a Tough Duct Tape which is UV resistant.

 

(Duck Tape is also used - mainly by those who’ve only heard an audible description and don’t mind the bill.)

 

Here’s an example of what might be considered good insulation:

@nealmurphy“I’m happy that the insulation has been done well and is neat and tidy and I believe suitable materials have been used. Following the independent audit the only comment mentioned about the external insulation was that the joints where the pipes entered the house could be better taped to ensure that it didn’t come away.”

 

Here’s another example:

@juliamc“My heat pump is a split system. An R32 refrigerant takes energy from the outside unit into the inside unit as a gas under pressure (I believe). The insulation for the pipes is more important inside the building to prevent condensation. Insulation on the outside pipework doesn’t need to be as thick as that for monoblock systems which contain water, but it does have to be UV resistant. However I now have a good thick covering of Armaflex taped onto the pipes.”

 

 Here are some before and after shots on a different location, one installer vs another: 

 

Before:

@hydrosam“External insulation at connections to external heat pump unit showing poor detail with non-UV resistant insulation used to repair corner and cable-ties to hold it on. Valve also not easily operated without damaging insulation.

 

After:

 

Before:

@hydrosam“External insulation to wall run with non-UV resistant insulation used, joints not taped or glued, cable-ties used to secure insulation which squeeze joints and cause them to open. Entry through wall could allow weather to enter building. Poor detailing around anti-frost valve leaving exposed metal leading to unnecessary heat loss.”

 

After:

 

@hydrosam“External insulation at right-angle bend on pipework showing exposed pipe resulting in heat loss and allowing weather to enter and degrade.”

 

@Transparent writes that: “The metal valves should be completely encased with an insulation tube having a larger bore. A round hole is made in the insulation on the opposite side to the lengthways split.

 

It can be fitted by temporarily removing the handle on a manually-operate valve. That split is then on the opposite side of the valve body, and must be sealed with exterior-grade Class-O insulation strip.”

 

 

insulation cut to encapsulate a valve with handle

@Transparent“All joins between sections of insulation, and the split at the back should be taped with Armourflex. Cable ties not only compress the insulation, but also force the joins apart.”

 

From @Primary ProOne of the biggest issues was condensate insulation and external heating pipework insulation.

 

If any joint / valve/ fitting is not sealed correctly, moisture/rain/snow will get in and not only reduce the efficiency of the heat pump/system but also deteriorate the insulation.

 

All Class O, including the HT type, is not fully waterproof and has to be installed to their manufactures instruction. The issue with this is that sealing and painting class O cant be done in humidity higher than 80% or temps lower than 10 ℃. This means most of the time in UK, it cant be fitted correctly. 

 

This is why you will see many installations with Tie Wraps fitted, trying to keep the insulation on however, if there are any gaps or holes, this will effect the efficiency  of the heat pump/system and insulation  as you can see from the photos:

 

 

 

Here’s a great video, found by @nealmurphy (with permission to share here) showing an approach taken by a ASHP pipe installer and insulator:

 

 

Indoor ASHP pipe insulation 

 

@Transparent“Once inside the insulation layer of the property it is more common to use less expensive pipe insulation with a wall thickness around 9-12mm. Internal insulation is commonly fitted without needing to tape or glue the joins.”

 

@juliamc writes: “All the hot pipes in the airing cupboard (image above) are lagged with Climaflex pipe insulation. It’s very easy to cut through using a bread knife, taking care to get the mitre joints to line up. I’ve used Climaflex clips (£3.84 for 50) to ‘stitch’ together the open seam of the pipe insulation, which I found quicker and neater than taping, particularly over the curved pipework where the seam tended to open. It was useful to practice on the airing cupboard pipework before tackling the loft pipes, as any rookie errors and gaps would just allow heat to escape into the airing cupboard, as it does from the brass fittings. Even so the cupboard is noticeably cooler than with my old unlagged pipes.”

 

Here’s another before and after combination. Notice the lack of insulation in the before shot!

 

Before:

 

After:

 

Loft / garage ASHP pipe insulation

 

@Transparent“Loft insulation would normally have a much greater wall thickness because the loft in most houses is unheated (above the insulation level). The same would be true for the unheated area below a suspended floor. This underfloor void should have vents to the outside. The air-flow prevents moisture build-up, which would otherwise result in fungal rotting of timbers.”

 

@juliamc“Photo above show the volumiser as installed with no insulation, and in the image below is my improvement of 25mm foil backed duct wrap”: 

 

 

@Transparent writes: The most common foil insulation over the past decade has been Triso Super-10 from the French company Actis. But there is now a wide range of foils available from UK-based Superfoil.

 

Note that foil insulation predominately offers a defence against thermal radiation. The traditional rockwool and glass fibre products counter losses through conduction and convection. They are different approaches and need evaluation for each situation.

 

In some areas of the UK the Local Planning Authority (LPA) will not allow a house to pass Building Regs if it uses solely foil-based insulation in the attic/roof area. This is a controversial topic, based on the way in which the National Physics Laboratory and BRE specify the tests prior to awarding the required certification.

 

That product accreditation issue should not prevent foil-based products being used to  add insulation to component parts of a Heat pump installation. It can easily be cut to shape and produces minimal wastage.

 

@juliamc“Pipework was roughly insulated with 9mm which I am replacing with 13mm or 20mm Climaflex, however photos show that the insulation tends to shrink ! so I now have a few gaps to deal with”:

Initial pipe insulation when first fitted
Climaflex clips used to minimise gaps formed when insulation shrinks

 

Another example here:

@SandraAA writes: “The half insulated pipe is nothing to do with the ASHP, it’s to the cold water tank. The board at the back is the meter board and that no longer has the main controls. The hot water has a controller in the airing cupboard and the heating (including  thermostat) is a wireless Honeywell unit.”

 

@James_N“Here’s the completed pipe insulation which I added. Now any pipe that gets warm has insulation.”

 

@Amarritt writes:  “The install is tucked into my loft as I had the old gas boiler there. They used the old flue and condense pipe holes to feed the new pipework and swa cable.”  

 

Conclusion

 

There’s many shapes and sizes to a heat pump, and the pipes that connect the system together. No two installs look the same, but there are common principles for effective pipe insulation that are worth getting right. 

 

Just how much of an impact pipe insulation makes for the overall efficiency (and cost effectiveness) of the system might be up for debate, but we hope this guide has helped you to better understand what good insulation looks like. 

 

If you’re unsure about the pipe insulation for your heat pump, post a few picture below and our community members might just be able to help!


41 replies

Userlevel 7

A big thanks to everyone who collaborated on this guide! 

 

If you have any other advice around pipe insulation for someone getting a heat pump, leave a comment below to give them a heads up. Likewise feel free to post more images and info about your set up below. We can easily edit, add to and improve this guide moving forwards. 

 

Great effort ASHP’ers!

Userlevel 7
Badge +2

Q: What if I’ve already got external pipes insulated, but the installers haven’t used UV-resistant EPDM?

A: If you don’t want the cost or disruption of replacing existing external insulation, it’s possible to buy thin sheets and rolls of EPDM from roofing suppliers such as Mammoth. Most are coloured black, except ClassicBond which is a mid-grey.

Sheets can readily be cut into strips to fold around the existing insulation, and the edges then glued together with ordinary impact adhesive.

Rolls of pre-glued EPDM tape are also available because the roofing trade uses this to seal between sheets.

It’s much more expensive than buying the plain flat sheeting, but the convenience may may outweigh the cost for smaller sections of pipe insulation.

 

Userlevel 7

Shout out to @hydrosam for providing the latest before and after shots of his set up. Looking much better Sam! Main article now updated to feature these. 

 

 

Userlevel 7

Thanks again to all our Heat Pump trialists for this really great insight into the vital element of a Heat Pump installation - getting pipe insulation right!

 

In case you haven’t already spotted it our content team have recently written this guide to the overall installation process, which covers what to expect before during and after a Heat Pump installation. Interesting to learn here that you can expect different sized heat pumps depending on the size of your house. Has this got the potential for another collaborative experience sharing thread…?

Thanks! Very useful. Is it possible to overinsulate heat pump pipes in a loft? My partner thought so but I was concerned that we have somewhat thin nitrile insulation and I can feel the heat through the insulation and therefore dissipating into our cold loft space. I’m presuming that adding insulation to this ?8 m long run in the attic could only be a good thing - although not sure what to add?

 

thanks again!

Userlevel 7
Badge +1

Hey @Alex19 !

Thanks for asking this one. While I don’t have a heat pump myself, I'd say the answer is probably no. While you can definitely go wrong by not insulating the pipes enough and allowing all the heat to escape too soon, I don’t see any realistic way to overdo the insulation easily. And even if you do go overboard, you could always just adjust the settings of your system and turn the dials down a bit to compensate. Might even save some cash too on the electric bill.

As it so happens, @hydrosam is one of the heat pump experts that we’ve seen on the forum and he might be able to recommend some insulation strategies.

Thanks 🙂 it seemed unlikely to me that it was possible to overinsulate in this context, but not my field & partner had an idea in their head so any expertise on the topic most welcome! :)

Userlevel 7
Badge +1

No worries. I’m just curious actually… But how did you get your heat pumps? Did you buy the kit yourself, or was it funded via some kind of trial scheme?

Userlevel 7

Great to see another Air Source Heat Pump (ASHP) owner here, @Alex19 - benefitting from the great advice given in our collaborative guide above!

 

As our community volunteer, @Blastoise186 mentions there’s plenty of community members here with experience of living with an ASHP and making sure their pipe insulation is doing the important job of keeping things running as efficiently as possible. Know @juliamc has made some great improvements to setup (which also features pipes running through her attic) - any top tips on how best to reduce heat loss in the attic space, Julia?

 

Our resident home builder @Transparent might also be the best person to advise on whether there’s a risk of over-insulating these pipes -  Is @Blastoise186  right in thinking that wouldn’t be something to worry about? 

Userlevel 7
Badge +2

No particularly top tips, the more the merrier I think, but if there was a leak I’m sure it would be very difficult to find ! 

Userlevel 1
Badge

Anyone got any tips for insulating Daikin Altherma Anti-freeze valve. I guess oversize with holes in it? thanks es

Userlevel 6
Badge +4

@edbond these are the valve on my unit. It was audited on the heat pump trial, external insulation was upgraded and this was the final result. The body of the valve is insulated but the anti-freeze valve is not. It does seem a bit bonkers to have a brass unit exposed but I’m guessing the heat loss through here is minimal compared to the rest of the pipe work. I believe they are meant to be left this this. 
 

 

Userlevel 6
Badge +4

@Alex19 over-insulating is about diminishing returns. Go for it but at some point the cost outweighs the benefit. Without doing sums I’d take a view of if it’s cheap and easy, go for it.

Userlevel 1
Badge

@edbond …….. The body of the valve is insulated but the anti-freeze valve is not. ……

 

 

Thanks - looks sensible and way better than how mine has been done. Regards ed

Userlevel 7

Great to see another ASHP owner here, seeking advice from our knowledge heat pump community, @edbond.

 

Hoping the pipe insulation tips above help you get the best out of your new heating system. How are you finding life with the heat pump so far? Any valuable insight to share over here:

 

 

Userlevel 7

Heads up @edbond @Alex19, you should consider coming along next Tuesday to hear from 3 heat pump guest speakers, sharing their experience and learnings and answering questions:

 

 

It’s on the 2nd of March at 5pm, it’s free, and you can even pre submit a question to be asked on the night here:

 

 

Hope to see you all there!

Userlevel 2
Badge +3

@edbond these are the valve on my unit. It was audited on the heat pump trial, external insulation was upgraded and this was the final result. The body of the valve is insulated but the anti-freeze valve is not. It does seem a bit bonkers to have a brass unit exposed but I’m guessing the heat loss through here is minimal compared to the rest of the pipe work. I believe they are meant to be left this this. 
 

 

 

Badge

We are having an air source heat pump installed, which will sit outside next to the garage wall. The 28mm flow/return pipes will run inside the garage (on top on of an uninsulated concrete floor) to the cylinder at the front of the garage – a run of about 8m.

Currently the garage is a cold space, but in a few weeks we’re having 2/3rds of it converted so this run will be in the “warm” space (albeit in the floor buried in screed). The cylinder will be in the last third of the garage, which will remain unheated.

I’m planning to use 25mm Armaflex HT for the very small parts of the pipe which will be external (where it connects into the pump) but what should I use for the “garage” run? I want to keep costs down so would “standard” nitrile pipe insulation be OK – I don’t need UV protection for this bit - and what thickness can I get away with?

Also, would the nitrile stuff be OK to be buried in a latex screed?

TIA

Userlevel 2
Badge +3

@edbond these are the valve on my unit. It was audited on the heat pump trial, external insulation was upgraded and this was the final result. The body of the valve is insulated but the anti-freeze valve is not. It does seem a bit bonkers to have a brass unit exposed but I’m guessing the heat loss through here is minimal compared to the rest of the pipe work. I believe they are meant to be left this this. 
 

 

 

@edbond these are the valve on my unit. It was audited on the heat pump trial, external insulation was upgraded and this was the final result. The body of the valve is insulated but the anti-freeze valve is not. It does seem a bit bonkers to have a brass unit exposed but I’m guessing the heat loss through here is minimal compared to the rest of the pipe work. I believe they are meant to be left this this. 
 

 

These are Altecnic ones and can't be insulated like this 

 

see a video we made after speaking to them about what is needed 

 https://www.youtube.com/watch?v=A1sncTcQ9oo

 

Intatec Ltd have made some antifreeze valves that they asked us to show how to insulate 

if insulated and seal this will keep the heat in and cold out so extending the time the valves will get down to 3 degrees 


https://www.youtube.com/watch?v=Wt1WfYUK2QU&t=13s

Badge

Hello,

I’m not seeing the performance I would expect from our ASHP and checked the insulation to the external pipework which is poorly done.

 

I’m confused about what pipe insulation to order, not helped by the fact that it does look like a few different pipe sizes have been used, ranging from 22 - 35mm, all cable tied together and with numerous gaps. 😒 

Armaflex HT doesn’t look like it comes with a ‘split’ and so must be applied during installation of the pipes? Is it OK to use the self-sealing stuff, which can be wrapped around existing pipework and then tape up any other joins?

 

 

 

Userlevel 7
Badge +2

@hydrosam has plenty of experience with this…. Cable ties🙄

Userlevel 6
Badge +4

@Primary Pro thanks for sharing the feedback. I had come across your video about a week ago, I think via Heat Geeks on Twitter. 

I will pass this back to the smart homes team who are coordinating the trial I am on. There are other things I’ve picked up on too that aren’t quite right, I’m not sure how far they will go to remedy them all, they’ve already done a lot a remedial work to do at my property, but we’ve got to share all these lessons learnt. 

It does seem counter intuitive to be exposing the valves, losing more valuable heat out of the system, the other valves in your video seem like a better design. Maybe Altecnic will redesign their valve in the future. 
 

@HugosDad the poor insulation will have an impact on poor performance but if it’s really bad it’s more likely to be system design or setup that need solving first. Insulation improvements will improve performance by a few 0.1’s on COP but won’t solve all the problems. 

Userlevel 6
Badge +4

@HugosDad also the split insulation is fine but it does want taping up and also painting with UV protection paint. The primary pro videos are worth a watch. See link above, or https://youtube.com/@primarypro1627

 

Userlevel 2
Badge +3

@Primary Pro thanks for sharing the feedback. I had come across your video about a week ago, I think via Heat Geeks on Twitter. 

I will pass this back to the smart homes team who are coordinating the trial I am on. There are other things I’ve picked up on too that aren’t quite right, I’m not sure how far they will go to remedy them all, they’ve already done a lot a remedial work to do at my property, but we’ve got to share all these lessons learnt. 

It does seem counter intuitive to be exposing the valves, losing more valuable heat out of the system, the other valves in your video seem like a better design. Maybe Altecnic will redesign their valve in the future. 
 

@HugosDad the poor insulation will have an impact on poor performance but if it’s really bad it’s more likely to be system design or setup that need solving first. Insulation improvements will improve performance by a few 0.1’s on COP but won’t solve all the problems. 

100% every part has to be spot on with and heat pump( to be honest also with a gas boiler as well but thats been overlooked due to how cheap gas has been in the past ) you would be amazed at what effect not insulating and sealing correctly  has on the efficiency of the heat pump & System 

 

 

Userlevel 2
Badge +3

 

I hope you don't  mind me adding my experience and finding to this post 

I owned a  large heating company before I sold it 2018. We were fitting over 5000 boilers and just started fitting heat pumps ( around 20 a month )

One of the biggest issues was condensate insulation  and external heating pipework insulation 
we worked on a solution that stopped condensate freezing and had no issues with customers with frozen condensate in 2018 when the  beast from the east hit 
we had an answer but not a Total Solution as out the solution was very time cond=suming and did not last as not UV protected

So after I sold, I spent three years finding the products and  a total solution to help professionals protect their customers 
we launched Condensate pro first and then Primary pro for external heating pipework and fittings 

The comments and photos/videos are all from working with other products when i owned a heating company, and from work, i did and still do my companies Condensate Pro & Primary Pro

if anyone needs any help or info, I am more than willing to help as i have been in the heating industry for over 40 i will always be passionate about raising the standards and helping others 

 Please email to info@condensatepro.co.uk 

Will help and advise where I can, if you can bare with me on spelling  and grammar as i am dyslexic  


if every joint / valve/fitting is not sealed correctly, moisture/rain/snow will get in and not only reduce the efficiency of the heat pump/system but also deteriorate the insulation 
all Class O, including the HT type, is not fully waterproof and has to be installed to their manufactures instruction 
The issue with this is that sealing and painting class O cant be done in humidity higher than 80% or temps lower than 10 ℃. This means most of the time in UK, it cant be fitted correctly. 

this is why you will see many installations with Tie Wraps fitted, trying to keep the insulation on 
however, if there are any gaps or holes, this will effect the efficiency  of the heat pump/system and insulation  as you can see from the photos 

 

 

Reply