Skip to main content
Solved

My switch away was rejected as I have a 'profile class 0' (commercial) supply - how do I get database updated?


I applied to change my Provider through Uswitch at the end of July. I have been informed by my intended new Supplier that the delay is entirely caused by Ovo failing to amend the database. This has dragged on for ten unneccesary weeks, if anyone knows how I can move this along and switch away from Ovo I would be really grateful. This has been dragging on far too long and I was assured that it was a simple process that would probably only take a fortnight.

Best answer by Nancy_OVO

Updated on 10/06/24 by Shads_OVO

 

Welcome to the OVO online community. Great question to ask about why you’re having trouble switching away.

Sorry to hear your switch is being delayed due to the way your supply is listed on the national database. What’s likely is your electricity supply is ‘half-hourly settled’. This means the readings we receive from your smart meter are shared with the industry on a half-hourly basis. This makes sure we’re able to anticipate your energy demand more efficiently and is an important part of de-carbonising the grid on our journey to Plan Zero

This ‘half hourly settlement’ is listed on the national database as a profile class 0, which up until 2017 was only for business listings. This is an industry wide change so all suppliers should be aware that half-hourly settled supplies can now include residential supplies. However there are a lot of suppliers who still haven’t adjusted to this change and therefore may not be able to onboard you as a customer with this profile class.

 

We can change your entry on the national database so that it’s not listed as half hourly settled, in order to avoid confusion from another supplier. Reach out to our Support Team to request this update. Once requested it takes around 2 - 4 weeks for the listing to be updated. Please be aware that as this relies on the actions of a third party, unfortunately we’re unable to speed this process up, however it might be worth contacting your prospective supplier to check whether they are able to request your switch without needing an update to your address listing.

 

Hope this helps get things sorted and your switch back on track!

 

OVO member but not got a smart meter yet? - Book today!

 

Interested but not yet an OVO member? - Check out our plans!

 

View original

56 replies

Nancy_OVO
Retired Moderator
  • Retired Moderator
  • 171 replies
  • Answer
  • October 16, 2018

Updated on 10/06/24 by Shads_OVO

 

Welcome to the OVO online community. Great question to ask about why you’re having trouble switching away.

Sorry to hear your switch is being delayed due to the way your supply is listed on the national database. What’s likely is your electricity supply is ‘half-hourly settled’. This means the readings we receive from your smart meter are shared with the industry on a half-hourly basis. This makes sure we’re able to anticipate your energy demand more efficiently and is an important part of de-carbonising the grid on our journey to Plan Zero

This ‘half hourly settlement’ is listed on the national database as a profile class 0, which up until 2017 was only for business listings. This is an industry wide change so all suppliers should be aware that half-hourly settled supplies can now include residential supplies. However there are a lot of suppliers who still haven’t adjusted to this change and therefore may not be able to onboard you as a customer with this profile class.

 

We can change your entry on the national database so that it’s not listed as half hourly settled, in order to avoid confusion from another supplier. Reach out to our Support Team to request this update. Once requested it takes around 2 - 4 weeks for the listing to be updated. Please be aware that as this relies on the actions of a third party, unfortunately we’re unable to speed this process up, however it might be worth contacting your prospective supplier to check whether they are able to request your switch without needing an update to your address listing.

 

Hope this helps get things sorted and your switch back on track!

 

OVO member but not got a smart meter yet? - Book today!

 

Interested but not yet an OVO member? - Check out our plans!

 


  • Author
  • New Member***
  • 1 reply
  • October 16, 2018
Thank you Nancy_OVO. Who should I contact to update the profile class? I have no idea if this is the reason for the delay just that I am keen to do all I can to move this along.

Nancy_OVO
Retired Moderator
  • Retired Moderator
  • 171 replies
  • October 16, 2018
Hey @ravensclaw - drop the team a message on Facebook or Twitter with your account number, full name and DoB and they can check on the progress of this for you.

Nancy

  • New Member**
  • 1 reply
  • April 28, 2019
As topic title. My account is with OVO, price comparison sites - including a price comparison with OVO - has the meter registered as an card meter but it is not. I pay by DD.

How can I get this updated?

Amy_OVO
Retired Moderator
  • Retired Moderator
  • 115 replies
  • April 30, 2019
Hey @jpig, I've moved your post here, the info above should help.

  • Carbon Cutter**
  • 4 replies
  • May 9, 2019
Hi everyone, my girlfriend has recently come off of prepay with Scottish power and had the prepay meters removed and replaced. There have been a few issues with linking the smart metres and the electric still doesn't submit metre readings, these are all issues to be resolved.

When I come to check prices with Ovo, the website states that this address is currently still showing as a prepayment address. How do I override this as I know this is now incorrect?

And finally, will this issue stop a switch going through to Ovo who I use without any issues. I appreciate it is easy enough to have Ovo replace the metres at her house with Ovo smart ones and be billed for anything used with Scottish power since they changed their metres.

Any advice is gratefully received!

Steven

Amy_OVO
Retired Moderator
  • Retired Moderator
  • 115 replies
  • May 10, 2019
I've moved your post here, @falkirk81, the info above will explain why a switch won't go ahead when leaving us, but I think it is due to the same issue when trying to leave Scottish Power.

Scottish Power will need to ensure the meter is listed correctly on the national database before any supply would be able to take over your girlfriends supply as a credit meter.

Thanks!

  • Carbon Cutter**
  • 4 replies
  • June 13, 2019
@Amy_OVO Thank you for the reply. We have spoken again to SP about this and they are adamant that the national database is correct and that the fault lies elsewhere. Do you have any advice? Can OVO not switch us over regardless of this issue, as both of the prepayment metres have been removed by SP and replaced with post payment metres.

I also don't want to ring up OVO and find I lose the referral money for us both.

steven

Amy_OVO
Retired Moderator
  • Retired Moderator
  • 115 replies
  • June 14, 2019
Hey @falkirk81,

I think it's best to give our team a call, they'll be able to check over the national database. You wouldn't risk losing your refer a friend incentive by calling us.

You can reach our team on: 0330 303 5063 Our opening hours are 8am-6pm Monday to Friday.

Hope this helps!

  • Carbon Cutter**
  • 4 replies
  • June 14, 2019
@Amy_OVO Many thanks, I will do this.

  • Carbon Cutter**
  • 8 replies
  • August 23, 2020

I have the situation whereby I moved into a property over 10 years ago and have had several gas and electricity suppliers and no problem switching between them. However, I applied to switch away from OVO  recently and have been told by the supplier I’ve applied to that, because of the way my electricity details are recorded on the industry database they’re unable to make any changes to the way my details are stored, as my current supplier is responsible for keeping my details up to date. They have advised that my electricity meter is currently showing as non domestic, profile class 0.

Last year I gave up trying to switch for the same reason, but this year I wish to get this issue resolved. Do I need to provide the same information detailed above* bearing in mind this was not an issue in the early years of my owning the property and appears to result from, perhaps, a meter change.

*Specifically: 

a. Your full name and address
b. The date you moved in
c. The name of the previous occupant
and preferably the address they've moved to
d. The gas meter number
and the meter reading for the day you moved in
e. The electricity meter number (which can be used to verify the address)
 


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Carbon Catcher***
  • 982 replies
  • August 23, 2020

Well I’m unsurprised that the new Energy Supplier rejected the switch. Meter Profile Class 00 is a commercial user with peak demand in excess of 100kW :astonished:

Historically this won’t have been a problem, but the National electricity meter database, ECOES, are continually honing the rules in order to clear out just such anomolies.  Energy Suppliers must register with Ofgem according to the types of customer contracts they provide. So a Supplier registered for Profile classes 1 & 2 can’t take over a meter that’s Class 0.

Yes, just email OVO with the suggested proof of identity and ask them to get it changed. hello@ovoenergy.com


  • Carbon Cutter**
  • 8 replies
  • August 23, 2020
Transparent wrote:

Well I’m unsurprised that the new Energy Supplier rejected the switch. Meter Profile Class 00 is a commercial user with peak demand in excess of 100kW :astonished:

Historically this won’t have been a problem, but the National electricity meter database, ECOES continually honing the rules in order to clear out just such anomolies.  Energy Suppliers must register with Ofgem according to the types of customer contracts they provide. So a Supplier registered for Profile classes 1 & 2 can’t take over a meter that’s Class 0.

Yes, just email OVO with the suggested proof of identity and ask them to get it changed. hello@ovoenergy.com

Thank you. Interestingly, they are the second supplier to reject this switch for the reason outlined. Thank you for taking the time to respond.

 


Tim_OVO
Community Manager
  • Community Manager
  • 1878 replies
  • August 23, 2020

HI @HelsTC 

 

I’ve moved your back and forth with @Transparent over to this topic. Please see the ‘best answer’ (at the top) for info on the likely cause of this issue, and how to resolve. 

 

Could you also consider coming back here to update us on what happened and in what time frames? It will be useful for anyone with the same query :)


  • Carbon Cutter**
  • 8 replies
  • August 24, 2020
Tim_OVO wrote:

HI @HelsTC 

 

I’ve moved your back and forth with @Transparent over to this topic. Please see the ‘best answer’ (at the top) for info on the likely cause of this issue, and how to resolve. 

 

Could you also consider coming back here to update us on what happened and in what time frames? It will be useful for anyone with the same query :)

 

Happy to provide updates. I've just requested the amendment via Facebook messenger and provided the information required.


  • Carbon Cutter**
  • 8 replies
  • August 24, 2020

Update: having contacted OVO regarding the need to amend my meter details on the national database they have advised me the amendment should be done in 4 weeks, from tomorrow. Information provided to them: my account no., name and date of birth.


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Carbon Catcher***
  • 982 replies
  • August 24, 2020

That seems quite a long delay, doesn’t it?

I guess it’s not entirely within OVO’s control. They must allow ECOES sufficient time to go through all their checks.

After all, there are probably several commercial users who would be very keen to have their meter re-classed as domestic if it was easy enough to do!


  • Carbon Cutter**
  • 8 replies
  • August 24, 2020

Yes, it does seem like a long time but no doubt there's a reason. It's enough time to estimate any loss of savings resulting from the delay to the switch and to work out who 'sold' me the smart meter. 


Tim_OVO
Community Manager
  • Community Manager
  • 1878 replies
  • August 24, 2020

Yes @HelsTC this time is for the administrators of the database (ECOES) to get round to the update. We might take a day or two to pick up the request and send it over, but then it’s on them. 
 

Check back with the Support team in 3 weeks in case the update’s ahead of schedule :)


  • Carbon Cutter**
  • 8 replies
  • August 27, 2020

Unfortunately that remains unacceptable in light of the fact I flagged this issue 1 year ago in an attempt to switch away and neither OVO or the supplier I wished to switch to had answers other than ‘it’s a commercial meter’ or ‘it’s not a commercial meter but other suppliers don’t understand that’. So 1 year later,  I attempt another switch away and find I am now unable to complete that switch before the OVO announced price increase due to the same issue (the switch should, under normal circumstances, have completed on 26.9.20). Pennies it may be, but that is not the point. OVO will know exactly which suppliers customers go to and which suppliers their new customers come from: that ought to make it easy to resolve this issue in a communication to other suppliers, or do suppliers not communicate for the good of customers?


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Carbon Catcher***
  • 982 replies
  • August 28, 2020

That’s not a good background story @HelsTC. I wish you’d posted here last year and I could’ve advised then how to get this resolved in time.

Whilst I appreciate all the checks that ECOES need to go through, they, like OVO, are still subject to the authority of the Energy Ombudsman. If you don’t have a satisfactory resolution within 8-weeks, you are able to take an issue to them whether or not you have been supplied with the proper Deadlock Notification.

This is the sort of advice that we can help with, here on the Forum.

Actually OVO have an excellent record in resolving matters before there’s any need to approach the Office of the Energy Ombudsman. That’s why they repeatedly score highly in the annual Which? customer survey.

So I’m pretty sure you’ll get the required action from them… but we could’ve done so ten months back.


Tim_OVO
Community Manager
  • Community Manager
  • 1878 replies
  • August 28, 2020

Yep as @Transparent mentioned, a bad background story/experience for you @HelsTC 

 

If we can find some kind of trace to suggest that you flagged this to us earlier then the few weeks ago that you mentioned, I’m sure the agent, or their manager, would be able to consider this in a resolution. Having worked in the ‘Complaints’ team for years, I would suggest (assuming we can confirm evidence of you contacting us about this issue last year) that we could look to cover any difference in prices from the supplier of your choice at the time.  

 

One bit of defense for OVO here: it’s the new supplier that has rejected this switch. It’s their prerogative to reach out. But even if they did, you’d need to restart the switch directly with them. 

 

Hope this gets resolved quickly. Feel free to send the URL of this topic to any agent you speak to on the web chat team


Alice_OVO
OVO Staff
  • OVO Staff
  • 2 replies
  • August 28, 2020

Just been catching up on the situation @HelsTC and it doesn’t sound ideal to hear you mentioned this a year back. 

I’m hoping the process here on is a smooth one, but please keep us posted.


  • Carbon Cutter**
  • 8 replies
  • August 28, 2020

@Transparent. Thank you. Unfortunately I just did not have the time to see it through last year as it was evident to me from the responses of both suppliers last August that neither recognised it was unacceptable to expect me to spend time convincing the other supplier that they were the party in this situation that needed to address the issue. In fact neither recognised a dead end / stale mate had been reached. This was probably not reflective of OVO organisational culture, but clearly this one individual did not recognise the situation I was being put in.

I agree, OVO are a great provider in my experience and I am confident the people with the right problems solving skills now have this on their radar, and would be highly surprised if I found myself in the position in which the Ombudsman was the next step.

 


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Carbon Catcher***
  • 982 replies
  • August 28, 2020

Yes, I don’t think this one will end up with the Energy Ombudsman either.

But for the sake of others who come to read this in future, you don’t actually require a Deadlock Letter in order to take a matter to the Ombudsman. You merely have to demonstrate that you’ve exhausted the (Ofgem approved) complaints process for your Energy Supplier.

And that’s why I always recommend that such communication is done by email. You get to retain a time/date-stamped copy of what you wrote. Simples.

Even if the actual issue rests at the door of ECOES, the route to a resolution starts with the Complaints Procedure of the Supplier.


Reply


Cookie policy

We use cookies to enhance and personalize your experience. If you accept you agree to our full cookie policy. Learn more about our cookies.

 
Cookie settings