@Firedog I’m sorry what I wrote was not clear, in my mind in made sense... I’m not as savvy with the correct terminology.
From your very comprehensive explanation below, I will hopefully be able to get this resolved soon.
At the risk of talking gibberish again, here is my understanding of what is going on.
I believe that my discrepancy was/is the tariff given as per my plan (1) & ‘Tariff Switching Table’ (2) were both programmed @ Region Specific/LMA tariff times - this is where the off peak rate kicks in (visible on the IHD). Therefore this does not align with the ALCS calendar (3), which was set @ E10 times following the ECAUL/ALCS reset.
Saying that, I have actually just managed to speak to a very helpful advisor, who has amended my plan from the Region Specific/LMA tariff to E10. So at least on paper the ‘tariff on the plan’ now aligns with the ‘ALCS calendar’.
I suspect I may still need a reset on the ‘Tariff Switching Table’, which still appears to be on the original ‘Region Specific LMA’ time settings. But I guess this may need a moment to reconfigure? At least I’m 2/3 of the way there now and I know what action I need to ask for next, should all three not line up with the E10 timings in in the next 24/48 hours.
Thanks for your assistance and sharing your knowledge.
... I have been switched to E10 until such time they have a solution ...
… my off peak rate (02) comes on at the times advised as per my Region Specific tariff, which do not align with the E10, ...
I’m beginning to sound a bit like a broken record. ‘… offpeak rate comes on at the times advised ...’. There are three schedules that should match up in a complex metering arrangement like this:
- The tariff as given on your Plan page or as laid out in an offer or confirmation email or letter should specify the times at which the rate changes from peak to offpeak and vice versa;
- The ‘Tariff Switching Table’ in the meter should mimic the timings at (1) to govern when the peak and offpeak registers are active;
- The meter’s ‘ALCS Calendar’ should also mimic the same timings to turn power on and off to the switched circuit for heating equipment..
So which of these three are you referring to when you write ‘I have been switched to E10’? Similarly, which of the three does ‘my off peak rate (02) comes on’ refer to?
You can clearly see when the ALCS energizes the switched circuit when the LED on the contactor enclosure (the L470 type 5451 box on the RHS of the meter) turns from blue to green. There may also be signs within the house - the IHD will show signs of high power draw (>1 kW) and perhaps an orange or red traffic light, and indicators may light up on near heating equipment. It’s not so easy to see which meter register - peak or offpeak - is active. Repeated presses of button ‘A’ may eventually reveal the Actv [=Active] Tariff Price, which should indicate whether the current rate is peak or offpeak. If the heating equipment is charging up, checking which TOU register 01 or 02 is increasing. We can never be certain that this is how the meter has been configured, but 01 ought to be peak and 02 offpeak to avoid DCC’s displeasure. I can’t work out which button sequence to press to get to the different register readings, but a bit of trial and error should sort it out.
Once it’s clear which timetable is right - matching the E10 timings* - and which not, you know which adjustments Support have to ask to be made, either to the Tariff Switching Table or the ALCS calendar - or possibly both.
* Current offpeak times (during BST): 05:30 - 08:30, 14:30 - 17:30, 21:30 - 01:30