Here's some photos of below the meter and consumer unit, ...
That’s great, thanks. I’d really like to know where these two little red cables end up - somewhere in your flat, perhaps? They are supposed to carry a little signal to turn on the switched circuit (the one powering the heating equipment). There are lots of heaters, so I’d expect to see a 100A contactor somewhere at the end of those cables. It will probably make a noise when it switches, so listen out.
… Found a setting on the meter to test ALCS, upon doing this the heaters and water heater on the economy 7 system do indeed fire p. So hoping it's just a configuration issue with EDF!
Well spotted! If you’d like to learn more about that intricated bit of kit that is your smart meter, there’s a technical user manual here:
https://www.smartme.co.uk/docs/D000058620%20E470%20Series3%20SMETS2%20User%20Manual%20and%20Functional%20Description%20ISSUE%201_2.pdf
When you get on to EDF support, tell them that the heating’s not working, so they probably have to send the ECAUL request to the meter to configure its ALCS, with timings to match the timings your tariff promises and (with any luck) the meter’s registers are following. The registers (1 for peak and 2 for offpeak) should switch a few minutes after the advertised times, and so should the ALCS (this is to prevent a situation where every storage heater in town suddenly fires up at the same instant, which would probably blow up the National Grid).
Don’t forget to mention that you didn’t get an IHD, so could you please have one and whatever extra kit needed to make it work. See if you can pin them down to a date when this will all be fixed; they mustn’t leave you with no heating for more than another day or two.
Good luck!