My smart meter was fitted on 31/05/2024.  I never had a problem with my electricity before then.

My off peak storage heaters were off for the summer.  My immersion heater was still in use. It is on Off Peak tariff & has a Horstman Timer (it comes on between (3 am & 6 am). It is still in use & never been a problem. The immersion heater night rate KW hours are showing on meter readings on my account.

In early October, I put on the storage heating.  

When the off peak for the storage heaters came on at about 12.10 B.S.T. - It tripped all the lights, appliances, TV etc. in the house.

The consumer box could not be reset to turn Lights, appliances etc., until the storage heaters were switched off at the switches in each room.

My electrician has tested my electric system fully over days & weeks and still there is a problem.  His belief is there is a problem with the meter either a switch  or wiring in the meter.

I keep getting fobbed off by customer services & they have asked me to get a plumber to look at the Immersion heater.

 

 

 

Could you please post some photos:

(a)  A close-up of the meter. Touch a button to light up the display so we can clearly read it, and make a note of the time you take it;

(b)  A view of the meter box/cupboard/backboard showing all the cables to and from the meter and any other equipment close to it;

(c)  Close-ups of the consumer unit(s), clear enough for us to be able to read what each breaker is for if possible.

 

I don’t suppose your electrician was there after midnight to see what happened when the switched circuit went live at 00:10 (probably 23:10 now that summertime has ended?). You can probably turn the circuit on during the day for testing purposes if you can find the meter’s boost function, but we’d have to know what sort of meter you have to be sure.

Last - where are you? The first part of your postcode is enough to pin down who your DNO is and what your Economy 7 times should be.


Hi Firedog, 

My DCN is SP Energy (G46). As requested I attach the photos requested plus 3 the electrician told me to take @ 8.48am. on Monday. He put a trace between the CU & the heaters.

There is a scorch on the CU. It has been there for years & the electrian knows about it.

 


Thank you. I hope one or other of our resident electricians ( @BPLightlog ?) will come along with comments.

Meanwhile, you mentioned that ominous scorch mark on the CU and you sound happy that it was dealt with satisfactorily. You didn’t mention the less obvious patch by the bottom seal on the meter itself. The module that’s sealed is the terminal cover, and it looks suspiciously as though something in there (the LCS relay, perhaps, that switches power to the ‘offpeak’ circuit) has overheated and may have caused a fault. Because it’s inside the seal, only a meter engineer can deal with it. 

If it were my stuff, I’d turn the red and blue breakers off along with the 45A one next to them and call OVO for emergency help - I’d be fearing a major hazard.

At the weekend, you can usually get swiftish service from OVO’s social media support:
  

Social Media channels over the weekend:

Whatsapp - 0330 175 9695
https://www.facebook.com/ovoenergy/
https://x.com/ovoenergy?lang=en
https://www.instagram.com/ovoenergy/?hl=en

Opening hours:

Mon-Fri 8am to 8pm
Sat-Sun 8am to 5pm

 

oI’ve had good results with X; post a brief description of the emergency, followed by a DM giving your name, address, postcode and account no. and a detailed explanation. Mention that your own electrician suspected a fault inside the meter; you can also include one of the photos showing the scorch mark on the meter itself.]

 


The circuit with the scorch mark is worrying (to my mind) as it’s next to a 100A breaker 

Unless the breaker was changed after the event, it could have suffered some residual damage. 
Also the main breaker has RCCD protection but only at 30mA 

For any set of circuits with the currents indicated on the trips, I would expect at least a 100mA main RCBO possibly with lower current devices as part of the rest of the circuits. 
In fact the 30mA device might be the cause of your circuit tripping as a smart meter can add a milliamp or so of residual current. These devices detect current flowing to earth but need to be rated at an appropriate level for the circuitry which it connects. Especially when storage heaters are used.


Thanks, @BPLightlog. I noticed that the ‘offpeak’ circuit (three NSH probably drawing ~3kW each) seems to be fed from the main board via the 45A breaker. If that is the case, then the RCCB is protecting the entire installation.

I took Giffy’s remark:“… a scorch on the CU. It has been there for years & the electrian knows about it” to mean that it had been properly dealt with.

You didn’t mention the scorch mark on the meter’s terminal cover. I wouldn’t expect to see anything like that on a shiny new piece of equipment, and it sounds as if the electrician didn’t either. I wouldn’t be happy having the offpeak circuit live if something’s sparking under there until a meter engineer’s had the cover off to check.


Firedog  &  BPLightlog

I tried to call my supplier's (EDF) emergency number, but they are all changed  to weekdays. In the end I called 105 and they came out and checked everything in their remit. The scorch mark was a shadow (thankfully). They took a picture to put on here for information. 

Thank you for letting me know about the RCCB being OK.

My electrician is on holiday and I am keen to get my heating on. Thanks for your help. 


Hey @Giffy

 

I can see that @Firedog and @BPLightlog have already stopped by to help with advice. You’re in great hands and please keep us updated on your progress 😊


I have just looking over old posts. Do you thinkI should ask for a Reconfigure of ECAUL/ALCS via SMETS COMMANDS?  

Thanks

 


I have just looking over old posts. Do you thinkI should ask for a Reconfigure of ECAUL/ALCS via SMETS COMMANDS?  

Thanks

 

If the switch over is happening at the correct time than a reissue of the command wouldn’t help. 
You could try switching off one of the storage heater circuits to see if that allows everything to work without tripping. 
Bear in mind that after a while of little or no usage, the storage heaters will be more leaky, electrically, than normal so that 30mA device might easily detect that. 
 

The point about the main switch being rated at 30mA (for residual current detection) is that it is likely to be too low to properly protect the entire system. I would expect to see a minimum of 100mA for that type of breaker. 
Further circuits could individually have 30mA RCCD protection to prevent a complete system switch off in the event of a trip


I  sure the electrician put on one a night. It still tripped. I think he also had one on & the others totally disconnected. I will put one on again to night & let you know tomorrow 

Also, I enclosed photos from last week where the electrician took a wire from the consumer unit to connect the storage radiator & all 3 came on at 8.48sm.


Just to be sure: each storage heater has two feeds. One of them is switched. i.e. only live during offpeak times. The other is always live, on the constant circuit, to power the heater controls and the fans that push warm air out, and a boost if the heater runs out of steam. It would be worth checking the constant feeds too, by leaving them off before the switched circuit powers up. There could be some crossover in one of the heaters.

 


@BPLightlog  & @Firedog 

As requested, ar 11.10pm the Off peak came on and tripped the daily electricity i.e lamps etc.. I put the 3 radiators on at the switched sockets I attached photos. I had to switch off the off-peak radiator to get normal lights etc.

Also, I put one radiator on at the switched socket & it tripped the daily electricity.

Thanks


@Firedog @BPLightlog @Chris_OVO 

Do you think  a dumb meter  installation would be an option for me. ?  I do not mind reading the meter. 

Thanks


​​​Do you think  a dumb meter  installation would be an option for me. ? 
 

No! For a start, there’s no such animal these days. No-one makes non-smart domestic meters, and suppliers don’t have any. Second, you have a fault somewhere in your electricity installation. It might be as BP suggests just an undersized breaker*, but it might be something else, and you have to find out what it is. 

When your electrician returns, see if you can work out between you how to access the Boost function on the meter. It’s described in the meter manual, but the menu option (§13.7) doesn’t seem to be shown in the graphic provided (§13.1). Once he’s found it, he can use it to activate the switched load, so he can trace the fault when it happens. Be sure to tell him what the DNO engineer found - that there was nothing obviously wrong with the meter once he’d removed its terminal cover. Any fault (e.g. overcurrent) occurring in the meter itself would trigger an alert sent back to OVO’s monitoring team, and that clearly hasn’t happened.

 

*  Your electrician might have a 100mA RCBO in his van that he could perhaps quite easily swap for the 30mA RCCB just to rule that out.


Hey @Giffy

 

I’ll just echo @Firedog in saying that all meters are currently made with smart functionality built in. I’ll tag @Lukepeniket_OVO who can hopefully take a look at this from an engineers perspective and give us some advice. 


@Firedog ​@Chris_OVO 

Thank you - I will pass this on & let you know what happens. 

 


Hey all did we get this one sorted?

 

Storage heaters are new so likelihood is we can discount any of them going faulty.

 

There is an imbalance across the rcd causing it to trip.

 

Is there any other heritage installs in that Meyer cupboard you could send a photo to us of? 

 

Cheers


It looks like there’s also some more… Immediate… Problems here…

Like the exposed yellow wire? Or the invisible anti-tamper cover on a meter?


@Lukepeniket_OVO 

It still is not sorted.

I enclose a phot from the cupboard for a shower fitted 5 years ago.

 


@Blastoise186 

The photo was taken by the DNO when the cover was off to get a clearer picture.

Thanks


@Giffy in your meter cupboard is there any more properties with an arrangement similar to what you had?


Perhaps one. It has a different meter from the one I had. My meter was very small and showed daytime, nighttime & total of both. Everyone has been changing to single tariff.

Thanks


All similar set ups that I’ve seen have had a 100mA RCCD/RCBO as a main feed with if needed, 30mA units on individual circuits - I would still suggest that 30mA is too low for use for the whole installation. 
Note that these storage heaters have been off during summer and so could have additional leakage until heated. 


It looks like on the photo of the brown and blue blocks that both left hand blocks only have 1 cable in them?

 

It does look like the Engineer hasn't wired it up correctly if I'm honest. There should be multiple cables in the neutral block for both 24hour and off peak supplies, I'm unsure if the neutral has been wired to the 5th terminal block (far right). If we've had no luck with supplier I believe it's now time, if not done already, to open a complaint with them.


@Lukepeniket_OVO ​@BPLightlog 

Its now about 5 weeks since I first contacted them. I have raised a complaint, but have to wait 8 weeks for ofgem.

Could you tell me how to proceed? 