What's the best Home Energy Storage option for retaining domestic stored solar power in preparation for power cuts?
Due to inept official planning and misguided political priorities there seems to be a consensus that power cuts are more likely than usual this coming winter. In fact. preparation for power cuts was a strong motivation to me for installing extra storage batteries to keep systems operating during outages.
However, I am looking for some help in how best to achieve this.
I live in Cheshire in the NW and have 28 JASolar PVMono 345 south-facing panels, nominal output 9.5kW.
Pre-solar my domestic load averaged around 10 kWh per 24 hours and is still similar.
I don’t fully understand the relationship or the interface between the AC grid and my installation as it was all put in by a professional team.
The main inverter is Solis 5G Single Phase.
Batteries are controlled by Growatt SPA3000TL BL (AC Coupled inverter)
(BTW, does anyone really know what SPA means in this context? There are vague possibilities among the over 200 meanings listed in “thefreedictionary.com”: Switching Power Amplifier, or Serial Port Adaptor, or Solar Panel Assembly, and several more.)
On any reasonably bright day between April and September and especially with some sunshine my batteries become fully charged, the HW cistern is heated and the grid receives all my excess. The smart meter doesn’t move from one day to the next and I’m basically using solar for everything, which is gratifying.
As the community will be aware, October to March can be rather different. Much less solar input so that a lot of my power is drawn from the grid and the batteries are down to less than 10% capacity each morning.
They do sometimes fill right up after a few hours of winter sunshine, but are used up quickly once the day darkens.
I would like to explore 2 possibilities in preparation for if power cuts start happening:
Some way to manually isolate the batteries once they are filled so as to preserve the stored energy to be available when the lights go out.
When there is very little daylight and not much chance of charging the batteries from the panels, some way to manually charge them from the grid while it is live and then reconnect then during the next power cut.
Does anyone have experience of this, or do you think it could be done?
Thanks, David 101
Page 4 / 4
So it’s a big thumbs up for Yaming Electric and the excellent customer service of Chinese business
and a wake-up call for me, because I got wires crossed, which is always a bad sign when we’re discussing electrical safety
Let’s have an initial look at the Solis SOL-5K-RHI-48ES-DC inverter which you’re considering @dnshorto. I have a few points which will need investigation.
The Solis inverter you are considering only has the briefest overview of its features on the Segen website. You must go to the website of the Chinese manufacturer to obtain the detailed specification and installation manual.
Even so, the feature overview raises a couple of issues:
You might think that the battery compatibility isn’t a problem for you because your four existing batteries are Pylontech. However, it might constrain your choices if you decide in future to operate both on-grid and off-grid storage simultaneously.
You would also want to enquire if a purchase of an existing unit would allow future upgrade to a wider range of batteries. After all, it may be that the design does support further batteries, but that the way in which this is achieved has not met the standards required for regulatory approval in the UK. The question needs to be asked.
Secondly, you might think that the matter of having more than one Solis inverter isn’t a problem either. After all, you intend only one of these to be grid-connected, and the new one to be used as a hybrid.
But the crunch issue is the emphasis on the word hybrid in the warning which Segen have published.
Might it still be a problem to have two Solis inverters connected to the grid, even if only one of the two is designated as a hybrid?
Furthermore, this Solis inverter model does not operate within the normally-accepted definition of a hybrid unit. It is actually capable of exporting back to the grid in addition to export in-house using its “AC backup” connector.
Under the rules agreed with the Electricity Networks Association (ENA), you would therefore have two grid-connected Solis inverters, both with grid-export capability. This applies even if you have the mechanism (and intention) to only operate one at a time.
Your G99 site approval will need to be updated to reflect this.
You might also find that the Solis hybrid inverters are not on the list of approved devices for grid-connection for this very reason.
So you have some further investigation to do even before we turn to look at the manual and installation instructions in greater detail.
Thanks @Transparent . The 6 pole isolator is on order, £23 with tax. Delivery early January:
The plan is to install it in its own enclosure just where the 6 leads emerge along with lightning protection, then take the leads on to a separate string combiner enclosure. This is because of space restrictions in my particular layout. However, I still don’t know why it seems to have twice as many terminals as it needs!
So I would welcome your input on putting the surge compression modules, plus fuses?, on order from FEEO . There is such a bewildering array of choices.
On the inverter questions, Pylontech 48v battery is exactly what it would be linked to, and it would be the only HYBRID Solis inverter on the site, so there didn’t seem to be a problem. I downloaded the data sheet for the range (3kW to 6 kW) from the Chinese manufacturers, Ginlong Solis, but could do with some help in checking its suitability. The model number I first quoted (SOL-5K-RHI-48ES-DC) was specifically off-grid, but there didn’t seem to be an exact match from the data sheets list and the models below are clearly grid-connectable.
Datasheet
Model Name RHI-3K-48ES-5G RHI-3.6K-48ES-5G RHI-4.6K-48ES-5G RHI-5K-48ES-5G RHI-6K-48ES-5G
Grid connection standard G98 or G99, VDE-AR-N 4105 / VDE V 0124, EN 50549-1, VDE 0126 / UTE C 15 / VFR:2019, RD 1699 / RD 244 / UNE 206006 /
UNE 206007-1, CEI 0-21, C10/11, NRS 097-2-1, TOR, EIFS 2018.2, IEC 62116, IEC 61727, IEC 60068, IEC 61683, EN 50530, MEA, PEA
Safety/EMC standard IEC/EN 62109-1/-2, EN 61000-6-2/-3
Features
DC connection MC4 connector
AC connection Quick connection plug
Display 7.0"LCD color screen display
Communication RS485, Optional: Wi-Fi, GPRS
---------------------------------
I have emailed the UK importers in Bootle to see if they can help.
@dnshorto
Why is this so complicated ? I thought I wanted battery storage etc too, until reading this.
I agree @juliamc . Battery storage is straightforward and I would highly recommend it for stored solar power when the sun isn’t shining. The complications arise when trying to prepare for future power cuts, when our grid-connected solar systems are designed to shut down, leaving us in the dark and cold. It is building an OFF-Grid facility for back-up which introduces the complications. Without the wisdom accessible on this Forum I doubt if most of us would contemplate even considering the challenge!
@dnshorto
Apologies @Transparent. I didn’t even see the second half of your reply, listing the further reasons why 2 Solis inverters might cause problems. Trying to do too many things at once.
So maybe I need to find a different inverter without grid-export capability.
One comment of yours which I can respond to is <<However, it might constrain your choices if you decide in future to operate both on-grid and off-grid storage simultaneously.». Who knows how needs and ideas might develop in future, but my plan if you remember is to use the off-grid facility seasonally; basically in the winter, and to revert to my original system when the sun shines, when power cuts are less likely and when the need for central heating is not critical.
@dnshorto
@juliamc - having a straightforward off-grid storage system is simple.
There are two issues with @dnshorto ‘s site which have made it sufficiently complex that I’ve felt the need to write about the details in this topic.
a: We’re modifying an existing grid-connected installation, which is already complicated by the installer’s use of two separate inverters.
b: We’re trying to use the same set of batteries for either on-grid or off-grid.
Dave, the main/obvious reason that Solis state you can only use one hybrid inverter on site is that their design doesn’t allow parallel operation in order to handle greater capacity.
Almost all off-grid inverters do have parallel operability, which is why it’s important for Solis to state this limitation for their product.
However… if the software doesn’t allow for parallel operation on the DC side, then is it OK to assume that two Solis inverters may be installed in parallel on the AC (grid) side?
It’s the absence of such information which I’m flagging up!
@juliamc - having a straightforward off-grid storage system is simple.
There are two issues with @dnshorto ‘s site which have made it sufficiently complex that I’ve felt the need to write about the details in this topic.
a: We’re modifying an existing grid-connected installation, which is already complicated by the installer’s use of two separate inverters.
b: We’re trying to use the same set of batteries for either on-grid or off-grid.
I see, but it sounds highly likely that buying an ‘off the shelf’ PV + battery system would result in the same problem. I’m glad I didn’t go with the Solar Together option recently quoted for via Surrey County Council as that wasn’t designed for off-grid, at least I don’t think so.
For @juliamc and others whose life will forever be simpler than @dnshorto’s, let me present a more typical off-grid installation using a hybrid solar inverter:
Note the arrows. The hybrid inverter can import electricity from the Distribution Grid during winter when there is insufficient solar energy to support the house.
However, the inverter does notexport back to the grid and therefore doesn’t require a G98 grid-connection certificate.
The only reason that the hybrid inverter is required to create 240v 50Hz ‘mains’ is in order to operate appliances which can only be used with AC power. Typically these would contain synchronous motors, such as water pumps.
There is no point in running WiFi routers, DECT landline phones and LED lighting from this off-grid mains supply because they simply use a ‘switch-mode’ transformer to convert it back to DC again!
At some point I need to create a new topic on running DC devices and home lighting directly from a Storage Battery. They will use various voltages, but there are cheaper, safer and more efficient ways to overcome this using DC-DC Converters. You do not need to go all the way up to 240v AC and back down again!
Running household devices off-grid has tended to be the domain of enthusiastic amateurs. They freely help each other using YouTube videos and online forums, and have built up a wealth of shared expertise.
When most people say that they’re ‘having solar installed’, it is generally assumed that this is grid-connected and will create an income stream when it exports.
But this shouldn’t be the case any longer.
The need to combat GlobalWarming and the present high price of gas should persuade more people to consider running as much as possible off-grid.
This Forum is ideally suited to such discussions.
We can be sure that the Moderators would encourage such topics despite them working for an Energy Supplier. After all, we’re not advocating customers to sever their Grid connection. But we do want to make best use of the precious energy resources available in the UK.
@dnshorto - I’m re-posting inverter specifications similar to that which you published above so that I can comment on a few points. I’m actually getting this from here on the Ginlong website which has “off-grid” inverters without the 5G suffix.
Hopefully this will put you (and others) in a better position when trying to track down a hybrid off-grid inverter which does what you want.
DC / PV input spec
Apart from the fact that your total array size is slightly larger than their recommended figure, everything else seems a reasonable match for your arrays using the 340w panels if we consider the string of 10 panels
However, this inverter could not support the two strings of 9+9 panels in parallel. The resulting peak output voltage of 19.6A is far more than the 11A max rating of the MPPT input.
Battery storage:
The specified maximum battery capacity of 2000Ah gives us 9.6kW at the nominal 48v of your Pylontech batteries. So this inverter cannot handle the 14kWh capacity of your present batteries.
I’m unsure how it ‘knows’ this. Perhaps it’s advisory, based on the low charge-rate of just 3kW… just one-third of what your PV panels can deliver.
AC output:
The AC output side is ok to operate a gas-boiler heating system, but you couldn’t simultaneously boil a kettle.
It’s also too little to operate a Heat pump, in case anyone else is interested in that!
The switch-over time suggests that this inverter normally drives the AC-output directly from its mains-input. When this fails it draws on the battery instead; similar operation to a UPS for a computer. The 0.02secs lag is equivalent to one mains-cycle at 50Hz.
Thanks @Transparent. I hugely appreciate all your helpful input over many exchanges of information, and trust that others who may read through what we have discussed will benefit; if only by avoiding the mistakes I have made!
I hope to return to the task of setting up an off-grid element to my solar installation but have had to shelve it for now. As you know, my primary motivation all along has been to prepare for power cuts and I have come to realise, with a great deal help from this forum, that even with my rather OTT solar array and battery capacity converted to off-grid use it would leave my home vulnerable to prolonged outages. I hope they don’t happen, but fear they might.
Therefore I have reverted to Plan A and invested in a 5kVA inverter generator to be quite sure of being able to keep my vulnerable family warm with gas central heating. Not a solution that is likely to appeal to many members but it has a number of advantages, including availability.
I plan to return to protecting my solar system with surge suppression in the new year and would value your help in sourcing the components, maybe on a separate thread.
Many thanks again
@dnshorto
5kVA inverter generator
a diesel generator set?
I’m not complaining about the power-source. It’s a logical approach to an immediate need.
But I’m intrigued how this provides the electricity to run the central heating when there is a power-cut. Have you installed an automatic transfer switch (ATS) on the mains supply to the boiler?
If not, then what prevents the generator from sending power back to the substation?
And I’m just going to make a note to the moderators: @Tim_OVO and @Jess_OVO
I don’t think we should regard this subject as ‘dead’.
In this case it has proved more difficult than @dnshorto expected to utilise his existing grid-tied Storage Batteries installation.
But the desire to have such Batteries able to deliver electricity in a power-cut is a more widespread issue. See the comment above (a fortnight ago) from @juliamc and the diagram I posted as a response.
Let’s remember that she is a participant in the Heat pump Trials and we have also identified a need for off-grid Battery Storage at those sites. They require storage in order to time-shift when they draw mains power, whether or not they have PV Solar Panels.
The technology to achieve this is already available, but there is a dearth of knowledge required to attain it. That’s where the Forum can help.
We should consider a fresh topic where this can be discussed (without the complexities of @dnshorto ‘s existing installation!).
Perhaps I should copy across the earlier diagrams on this thread where I introduced the underlying concepts. That leads directly to this diagram which I created above for JuliaMC:
Those early concept diagrams are here, here and here. They’ll benefit from a bit of simplification and tidying.
Off-grid storage still a big subject so I’ll need to count it as satisfying all of my 2022 New Year Resolutions!
Wise words @Transparent. There is clearly a need for a workable solution to using stored energy in a power cut situation and a new, uncluttered thread would make sense. One inherent weakness in what I was trying to acheive is that power cuts are more likely in winter, when solar input is low, so a dedicated battery kept full in preparation would be more likely to be of practical use. Hence my wish for a seasonal switchover capability.
which is full of fascinating info, if predictably American biased.
You asked how I have connected the generator power to the boiler in such a way that it doesn’t then send power back to the substation. Building on the wisdom gleaned from this forum I inserted a 4 pole changeover switch between the generator, the grid, the boiler and a double “generator only” socket (to run the fridges). The boiler receives power from either the grid or the generator and all seems to work happily. In fact with boiler and 2 fridge freezers drawing power there is still ample capacity to run a 2 kW heater. For “running-in” the engine prefers a half load for the first 20 hours, so 10 hours have already been clocked up in this way.
Also utilising the tips and hints so generously shared here I have now received direct from China a very nicely made 6 pole isolator for the 3 solar strings, made to order with amazing customer service! Surge suppression wisdom sought soon please!
@dnshorto
I agree this is a fantastic thread specifically about using energy storage in the presence of power cuts.
@Transparent this topic you’re suggesting for energy storage and heat pumps sounds fantastic. Feel free to simply create a new thread to get the ball rolling on that. I have a feeling it won’t be the last time that subject is covered, what with the community of heat pumpers we already have!