What's the best Home Energy Storage option for retaining domestic stored solar power in preparation for power cuts?

  • 20 October 2021
  • 89 replies
  • 3202 views


Show first post

89 replies

Userlevel 7
Badge +2

The cable which exits the AC rotary switch below the Solis inverter goes to the small metal distribution board we discussed earlier.

 

I’m pretty sure that the 8kW Solis goes to the blue 32A trip, whilst the Growatt is fed via the 20A trip to its left. They’re in parallel.

Thus the 2-pole red disconnector isolates both inverters from the mains.

I can’t yet comment on whether there is or isn’t a hybrid inverter with adequate capability for the 9.5kW of PV Solar Panels on your roof.

I haven’t yet researched this, but I intend doing so because a similar solution would be required by participants in the Zero Carbon Heating Trial if they wish to run their Heat pumps off-grid.

Userlevel 4
Badge +1

Thanks for the very clear pictorial layout drawing @Transparent; that’s very helpful in working out which hardware item does what. There are actually 2 consumer units, DB1 & DB2 one above the other but I guess the mains connection into one inevitably connects both.

Given that the Growatt inverter connects to the grid at the small metal distribution board (let’s call that DB3?), how does it only use solar power to charge the battery? Is there a diode in that circuit to prevent grid power going the other way, or is that incorporated in the inverter itself? Hope that is not too dumb a question.

Another question. I know (now) that if grid power fails the inverter(s?) must disconnect from the mains immediately. Is that built in to the inverters? Will the potential off-grid inverter be a different type, or specification, or simply with adjustable settings to enable it to function without grid input?

Regarding the DIN enclosures; is it possible to be confident that all the needed components fit on to a DIN rail? No extra “non-DIN” space needed for incompatible items?

It’s all highly useful information, thank you

@dnshorto 

Userlevel 7

 

@Jess_OVO- I’m aware that there is a lot of practical content emerging here which others might want to find if they’re reading the general topic on PV Panel Installation.

Let us know if you want things moved, or whether we periodically insert links to direct people here.

 

Great minds, @Transparent! I think there’s a real value in keeping this as a separate discussion but great point about including a link to this thread on our Solar PV guide, I’ll get that added now! :sunny:

Userlevel 7
Badge +2

There’s no diode @dnshorto  - We’re talking about Alternating Current, so a diode would only stop it flowing in one direction.

You’ve got a couple of Current-clamps on the Live-Feed to the house.

 

I’m uncertain where they connect to, but I would guess one for the Growatt and one for the Solic Load Diverter. The current-clamp enables those devices to first take what solar-generation you have available for storage, and only then allow the remainder to be exported.

 

The mains-disconnect system is inbuilt to every export device which is permitted to be connected to the UK Grid. They must be tested and certified to the G98 Standard.

It doesn’t apply to an off-grid inverter because it’s not an export device.

Userlevel 4
Badge +1

Spot on as usual @Transparent . The left hand cable clamp is to the Solic 200, the right hand one I had to reposition early on in the saga as the original (dumb) meter readings were not being reduced by the solar input.

In a previous interchange about a year ago on this forum you pointed out that the clamp was too close to other cables and was thus suffering from interference.

The panels were churning out power and the phone app showed how much I was exporting to the grid but the daily meter readings had hardly changed from pre-solar days, and the bills are based on what the meter records. So, from what you have just written, it wasn’t that the meter was influenced by moving the clamp but that I wasn’t using the incoming PV power optimally for storage nor for domestic load. Makes sense. @dnshorto 

Userlevel 4
Badge +1

Please may I redraw your attention @Transparent  to earlier questions about batteries? I am extremely grateful for all the time and effort you are putting in so am hesitant to make this request, but to me some way of using the existing storage capacity during the winter is an essential part of my original question

I now understand the necessity for an off-grid system to cope with power cuts, but which would also have year-round value for some dedicated AC loads such as gas boiler pump and fridge motor plus DC lighting etc. You have made that very clear, thank you.

I also understand the steps so far taken towards an off-grid inverter, powered by a variable number of panels via a string combiner. No doubt there are more details yet to be revealed but the basics are now clear and it has all been extremely useful info.

Obviously a battery will be needed too.

On your pictorial diagram of my installation you show the battery connected directly to the Growatt inverter and I can confirm that the heavy red and black cables go straight there. I have 4 Pylontech 48volt Li-ion units in parallel. each with a usable capacity of 3200Wh according to the user manual, and a recommended charge/discharge current of 37 Amps, maximum 74 A.

Could a new off-grid inverter be directly connected to the battery instead via a DC changeover switch, so that either inverter could be linked to the battery but not both?

Thanks,

Dave

@dnshorto 

Userlevel 7
Badge +2

Thanks for keeping me on track @dnshorto  :slight_smile:

Yes, in theory your 48v battery pack could be connected either to one supply (existing Growatt) or another (new off-grid inverter).

It would probably need to be achieved with a Contactor (relay) rated at 80A+ because it would be a hefty manual switch to be specified for use at 74A current.

[Aside] You might wonder why you couldn’t have just two of the four PylonTech batteries switched across. In theory this is also possible, thus dividing your storage assets. But it would need checking with Pylontech because re-joining the battery packs would occur with them at different charge levels.

 

One of my present thoughts is that you might as well replace the existing Growatt inverter with a hybrid one which could take input from either the mains or a  Solar array. This would be permanently connected to the same four batteries, but only used for charging (not discharge). There’s then no requirement for any switch.

The existing Growatt then gets repurposed for export only.

 

Depending on the characteristics of the new hybrid inverter, that might leave you with no export capability from the Pylontech batteries, either to the Distribution Grid or back into the home.

Is that a critical issue?

It could later be overcome if you had an EV with a V2G charger.

Userlevel 4
Badge +1

All highly relevant and useful thoughts thank you @Transparent. That’s a very helpful picture-drawing of a possible solution (only the off-grid consumer unit needs to be DB4 as DB1 and DB2 exist already, along with DB3) but I would 100% want to keep the battery in it’s present role for the sunnier half of the year. The capacity is enough to run everything easily through the night if it has had a reasonable charge during the day, so that we use zero grid energy for much of the time. The meter stops for days on end! Plus I am sold on your plan of a string combiner so that i can have flexibility of input from the sun for different priorities and changing seasons.

It’s a different story in winter though, which is why my preferred plan is to have the entire battery switchable between inverters. The storage is little use in the winter for the full domestic load in the evenings and I am concerned that the battery never gets a full charge, whereas it would do much better only powering DB4.

I had wondered about a Contactor for switching the battery between inverters and there are 48v coil versions available, but a manual switch such as this one would cost around £70:

or similar rated at 100 amp for around £80.. Would this suffice?

The new off-grid hybrid inverter would ideally be capable of handling up to 21 of the 28 panels via the string combiner, so 21 x 340 = 7.14kW. If only 14 panels then 14 x 340 = 4.76kW.

Although it is “off grid” I see your drawing shows the inverter connected to DB1 via an isolator and hope that this implies that the off grid inverter could also be used to charge the battery if needed in low solar input times. Is this last paragraph making sense?

 

Once again, huge thanks for the detailed and valuable knowledge you are sharing.

@dnshorto 

 

 

Userlevel 7
Badge +2

Let’s leave aside the battery characteristics and their switching for the moment @dnshorto and have a look at your Growatt grid inverter:

 

Unlike an off-grid inverter, yours has no on-board reference for voltage and frequency. As it can be grid-connected, it isn’t allowed to!

The Growatt senses the mains voltage and frequency, and then adjusts its output accordingly.

So to repurpose it for off-grid use it will require a small off-grid inverter in parallel to provide those two references:

 

I’ve never tried this before! The important points are the small inverter must :

  • provide a full sine-wave output (not a stepped pseudo sine-wave)
  • supply negligible current to the output (that’s the job of the Growatt)
  • not go into oscillation as the Growatt kicks in after a couple of minutes

I’ll bet there’s someone else on the internet who’s done this and uploaded a YouTube video or a blog. See if you can find one.

If I were doing this myself, I’d be very tempted to open up the Growatt’s case and separate out the Grid sensing circuitry. I could then use the small inverter to supply just those two references:

 

But I couldn’t possibly suggest on the Forum that you get out your soldering iron and start cutting and joining 240v connections. So I’ll avoid doing so.

 

Here’s a typical 48v pure sine wave inverter which might do the job. I found this on AliExpress ‘Black Friday deals’ and that price includes shipping!

 

I doubt it would provide the specified 1kW with any appropriate level of stability. But for your purposes it doesn’t even need to supply 1w :kissing:

Userlevel 4
Badge +1

A fascinating thought @Transparent and a very economical and ingeneous way to repurpose the existing Growatt inverter for off-grid use. However, since I want to retain my present grid-connected system, to enjoy the benefits of solar for my whole domestic load and reduce my reliance on the UK’s dwindling mains power I need my Growatt for that.

I can’t go fully off-grid without a sizeable back-up generator but what I have realised that I can do (with the invaluable help of this forum) is to prepare for future power shortages by installing a separate off-grid inverter variably fed through a string combiner and feeding a dedicated distribution board as already discussed.

I had an opportunity to test the makeup of the solar panel strings and it seems you were right @transparent to hesitate, and doubt your initial guess that the 28 panels had been configured 14 -7 -7.

Remembering your warning about high DC voltage I disconnected the 6 terminals at night, and was surprised that there was a small but steady input. The inverter has 6 terminals, number 1 on its own, number 2 as two pairs, so for clarity I refer to them as A for terminal 1, and B and C for the other two.  The A pair showed a night-time average of 4.3v. B and C an average of 3.2v each.

In very weak sunlight the next day A gave 390v, B & C 352v each. Slightly brighter light put A up to 400v, B & C up to 370v each, from which I calculate that terminal A has 10 panels, while B & C have 9 panels each; 28 in total. Would you concur?

Turning back, if you don’t mind, from interesting but possibly illicit tinkering inside the Growatt to the perhaps boring topic of batteries, my preferred plan is to have the entire battery switchable between inverters. The storage is little use in the winter for the full domestic load in the evenings and I am concerned that the battery never gets a full charge, whereas it would do much better only powering DB4 (off-grid appliances) 

I had wondered about a Contactor for switching the battery between inverters and there are 48v coil versions available, but a manual switch such as this one would cost around £70:

or similar rated at 100 amp for around £80.. Would this suffice?

The new off-grid hybrid inverter would ideally be capable of handling up to 19 of the 28 panels via the string combiner, so 19 x 340 = 6.46kW. If only 10 panels then 10 x 340 = 3.4kW. Some off grid hybrid inverters have a TOU function for topping up batteries at cheap rate times which I would need in winter. How about SKU: SOL-5K-RHI-48ES-DC Categories: Hybrid Inverter, Solis,, or there is a 6kW version?

Once again, huge thanks for the detailed and valuable knowledge you are sharing.

@dnshorto 

 

 

Userlevel 7
Badge +2

I want to retain my present grid-connected system, to enjoy the benefits of solar for my whole domestic load and reduce my reliance on the UK’s dwindling mains power I need my Growatt for that.

If you chose the required specification for the new Hybrid inverter, then you can achieve everything you want from that. Simply allow it to feed back to the grid in summer.

The only problem with the existing Growatt is that it has no capability for DC-input from Solar Panels. So I’m suggesting it’s moved to a section of the supply system where that isn’t required.

There are alternative ways to achieve this. But I’m starting from the position that you already have the Growatt.

One other possibility is to sell the Growatt and simply buy a standard 48v off-grid inverter  the required power-rating. 500w is a typical peak-load for a central-heating system with a gas boiler. So the decision rests on precisely what you require to be run from 240v AC (pure sine wave) during winter.

 

Solar panel topolgogy: It seems most likely that the layout is indeed 10-9-9 based on your measurements.

It’s slightly tricky to be certain of this because

(a) you’re measuring open-circuit voltage of those panels (41.36v max.) which will vary more than the specified voltage under operating conditions (MPPT in action).

(b) there’s not a great deal of difference between 9 and 10 panels

If it were me, I’d be taking a further measurement in brighter light to check if the same voltage ratios were consistent.

 

I need a bit more time to check the specs of the Hybrid inverter you suggest. Its MPPT inputs have to match the open-circuit voltage at the moment of switching panels to it.

Userlevel 4
Badge +1

Thanks for the latest ideas @Transparent. I have a few more questions too, if you don’t mind. Hopefully the answers may be useful to other readers in due course

I realise that buying a third inverter may seem wasteful but I still lean towards that solution in my particular situation. The system as installed works well and is under warranty. If I monkey about with the Growatt I might regret it, so I am prepared to splash out on a separate off grid inverter to be ready for power cuts. A big enough generator would cost much more and I’d rather harness the sun as far as possible.. 

My previous post included a photo of a rotary switch to changeover the battery connection between inverters. The photo vanished so here is another.

<<I had wondered about a Contactor for switching the battery between inverters and there are 48v coil versions available, but a manual switch such as this one would cost around £70:

or similar rated at 100 amp for around £80.. Would this suffice? Or would a specifically DC type be better?» 

 I assume that I would only need to divert the positive battery cable, and that the negative could remain connected to both inverters?

The 6 pole rotary isolator which you suggested for the incoming 6 PV leads is proving slightly puzzling. There are several offerings, but the suggested wiring layouts are all somewhat confusing. I picture a simple 6 incoming terminals paired with 6 corresponding outgoing terminals, but the accompanying drawings of wiring diagrams make it all look much more complicated. Any ideas?

Lightning protection. I understand your proposal that the surge protection devices are incorporated in the DIN rail enclosure of the string combiner. Due to lack of adjacent space this item will be several metres away. Would it be better to introduce stand-alone lightning protection right where the 6 cables from the roof arrive; before or after the 6 pole isolator?

Solar PV cabling. Preparing to extend and supplement the existing cabling I need to establish the size. I suspect it is all 4mm as this seems to be the most common, but the OD by micrometer is nearer to 5mm. Does this sound like 4mm to you?

Solar panel topology. Thanks; next time the sun shines I will measure the voltages again to try to be sure the panels are arranged 10 : 9 : 9. The new inverter should be sized to accept input from up to 18 panels, so realistically the present grid-connected set-up would have 10 panels permanently connected, and the off-grid 9, with the 3rd string of 9 switchable between them. Simpler than first proposed.

Off-grid domestic loads. Thanks for the CH boiler peak-load estimate of 500w. When choosing the 3rd inverter I would rather over specify than under. While the boiler is #1 priority as the house has no other form of heating and I have vulnerable occupants to protect in 2 separate households, I would also want to build in the capacity to run the 2 fridge freezers if the battery was up to it. The rating plate on the larger one states 2 amps but I realise there will be higher start-up loads.

As winter advances I am now anxious to get something set up urgently, with bells and whistles added later. Once we have the new inverter, fed by 9 or 18 panels and storing energy in the full battery of nominally 14Ah capacity I can run 230v extension leads to the appliances in an emergency.

Once again, massive thanks for the time and brain-power you are spending on this.

@dnshorto 

 

Userlevel 7
Badge +2

Sorry, there’s a lot to take in from your last message @dnshorto 

May I just pick off one point in an attempt to simplify issues:

In the diagrams I drew, I have placed the Storage Battery assembly between the two inverters in such a way that they do not have to be switched!

Provided that there is no data-transfer required between an inverter and the batteries it is connected to, such a sharing arrangement can work. Each inverter only works out the capacity and State of Charge (SoC) by reading the combined cell-voltage for itself.

So having ‘dumb’ Lithium Ion arrays can be advantageous.

 

That still means we need safety isolators between the battery-stack and the inverters they connect to. But that’s just in order to allow them to be removed for ‘maintenance’ as necessary.

Userlevel 7
Badge +2

Let me pick off another couple from the list:

 

Solar cables from the roof are most likely to have a cross-sectional area of 4mm² with an outer diameter of 5.4mm. It gets abbreviated to 4mm because none of us can be bothered to say ‘square millimeters’ all the time. :hugging:

 

Lightning protection. See the tutorial first because it’s full of pretty graphics. :slight_smile:

There must be nothing between the physical cables from the Solar Panels and the surge suppressors  – no switch and no trip!

The whole point is for the high-current surge to pass through the suppressor and thence to ground. If it has to pass through anything else first then it will vapourise the contacts in that device. That leaves the suppressors no longer physically connected to the Panels which they’re trying to protect! :face_palm_tone1:

We can possibly ‘allow’ a fuse because it has no contacts to arc and there’s little chance of it melting in a few nS. But it must be the correct HRC (High Rupture Capacity) and totally enclosed in its DIN-rail mounted carrier.

 

Userlevel 7
Badge +2

DC rotary isolator switch: This is the 4-pole device I used for my own String Combiner. I bought direct from FEEO via AliExpress. You’ll probably find the same item on ebay or Amazon at a higher price if it’s already in the UK.

 

A red/yellow rotary switch is the normal, accepted ‘standard’ for a safety isolator on renewable-energy installations. Each ‘pole’ is effectively a disc on a central shaft. The more poles you have, the deeper the switch will be.

The switch depth dictates whether it could still be fitted alongside trips in a DIN-rail enclosure. 6-pole switches therefore tend to be in separate boxes.

Take care that the switch really is capable of switching DC at the required current. The DC capability will be less than that specified for AC. If only one current-rating is stated, then the isolator cannot be used for DC because the contacts will degrade and become pitted.

Userlevel 4
Badge +1

Many thanks @Transparent  for your 3 separate nibbles at my stack of questions. Please may I seek further clarity? I’m well aware that certain aspects of the technology are of more interest than others, which I am therefore hesitant to keep asking you about. Despite the arguable advantages of the more adventurous solutions which you would perhaps prefer, as you will have gathered I have decided to retain my present system as installed, but to ADD the off-grid facility and utilise my present battery with it in the appropriate season. I am keen to get the equipment soon because the winter cometh, and my home is not prepared.

On “dumb” LI battery arrays, connected alternatively to my current Growatt on-grid inverter, or else to the proposed off-grid one (OGI for short); you say <<Provided that there is no data-transfer required between an inverter and the batteries it is connected to, such a sharing arrangement can work. Each inverter only works out the capacity and State of Charge (SoC) by reading the combined cell-voltage for itself.>>  The Growatt has data connections for battery management which seem to work efficiently. If instead, the battery is connected to the OGI, without data transfer, are you saying it can still be kept charged by the OGI working solely on the combined voltage; by PV solar when available, or by TUO at cheap rates by timer? Is this correct?

Lightning Protection; thanks for the very helpful tutorial. I understand the desire to protect against strikes, but the cost seems to be prohibitive. My 3 incoming circuits would require 6 surge compressors, and the Phoenix Contact items seem to be around £300 each with VAT. This is a high insurance premium, when my household cover already protects me against lightning strikes. I get what you write about fire hazard, and I know strikes happen even in urban areas; our own son had lightning strike through his TV antenna, but his insurance put it all right and the danger zone is not in our house but in the garage. I’m inclined to take the risk, unless I have misunderstood and there is a more affordable method of protection such as the HRC fuse? The photo you kindly supplied of your own installation shows 4 suppression units. How does that work with the multiple arrays you have?

DC rotary isolator switch. With all those separate arrays, how do you manage with a 4 pole switch? These are relatively inexpensive, but the 6 pole versions are much dearer. The CPC Farnell 6 pole DC rotary isolator switch is £45 and the CEF offering is over £100. Plenty of 3 or 4 pole versions at £15 to £30. Do the incoming negative PV leads need isolating? Would a 3 pole isolator for the 3 positive leads be one solution?

Battery changeover switch. Yes, I still want to follow this method if possible. I understand your point about DC use of an AC rated switch and eventual points pitting, but if the changeover were to be done intelligently, when load was low for instance, this could be reduced. Is this a valid argument?

Solar panel topology. I checked the voltages again in full (winter) sunlight but the sun was so low that next door’s roof partially blocked one row of panels. A = 408v, B = 357v, c = 367v; so still I believe A = 10 panels, with B & C having 9 panels each.

Multiple questions again I fear, but I hope these exchanges will prove useful to other Forum readers.

Thanks again

@dnshorto 

Userlevel 7
Badge +2

@dnshorto  wrote:

I have decided to retain my present system as installed

Ah… that’s the bit I hadn’t understood!

I was attempting to use the existing devices but reconfigured differently rather than “as is”.

I need a bit of thinking time! It’s the data connections between the Pylontech batteries and the Growatt which make this slightly more tricky.

 

Lightning protection. My present arrangement is being used as part of the OVO PowerVault Storage Battery Trial. As this has only two solar MPPT inputs I’ve (temporarily) got the three rooftop arrays strapped together within the String Combiner Box, and therefore sharing just 2 pairs of suppressors.

The enclosure does have space set aside for the third pair, but I just haven’t got around to fitting them yet.

 

Costs: Yes, Phoenix Contact units are the top-end of the market. They get more thorough testing and intensive product design than their rivals. But my house is positioned on top of a hill in full view of the prevailing SW winds off the Atlantic!

You can purchase much cheaper units made by manufacturers in the Far East, including FEEO, who make the DC rotary isolator. Buying a ‘named brand’ is better because they won’t want to risk adverse publicity if the product should fail to provide protection.

You should feel free to message these Chinese Manufacturers with any questions. Many can reply in English, and others use the inbuilt AliExpress auto-translator which is pretty good! They are extremely polite and their culture puts a high value on customer service.

(We have so much to learn from them!). :slight_smile:

 

4-pole & 6-pole DC rotary isolator switches: It is usual practice to keep each pair of Solar Panel drop-leads separate and not try to combine the -ve between arrays. Thus each array is treated as ‘floating’.

Remember, you do not know how the MPPT inputs are wired within the inverter. There is no ‘standard configuration’ which suggests that the -ve wires are connected internally. It is permissable for the inverter manufacturer to keep each MPPT input channel isolated and floating, with no common reference point.

The prices you are quoting for rotary isolators are high because you’ve only considered the usual UK electrical suppliers. If you think ‘Chinese’ then the prospects are far more encouraging. Here’s a 6-pole unit I found in less a minute:

These Chinese suppliers will put together whatever combination of contacts and switch handle you require. They even say so in their product descriptions:

 

These rotary isolators are often called ‘cam switches’. Just go to AliExpress and type “isolator cam switch” into the search box at the top of any page. It really is that easy. :blush:

Userlevel 4
Badge +1

Thanks for that very useful reply @Transparent.  I have been “thinking Chinese” now for several hours! The variety of interesting products on the AliExpress site is fascinating, but even though I have spent virtually all evening searching I still can’t find a suitable 6 pole isolator; not even the Yaming Electrical one you spotted “in less than a minute”. Infinite numbers of 4 pole and less, and some higher pole-number selectors, but 2 position isolators have eluded me. The “cam switch” description helps, but still not enough. I have registered with AliExpress, and left a query so await a reply. Although they seem to offer a bespoke service. in reality it is only for significant orders; I only want one!

This seems very lame, but I also need help in selecting the lightning suppression modules. You are absolutely right to say that they are very much more affordable on the FEEO site but it is very comprehensive and there is just so much choice. What parameters should I be applying in choosing surge protection? Or better still, if you were looking for 6 reasonably priced suppressors for my 6 incoming PV leads, which of the multitude available would you choose?

Meanwhile, thanks for your “thinking time” over the Pylontech data link and for all the other time you donate so generously to steer this project to an efficient outcome.

@dnshorto 

Userlevel 7
Badge +2

I wonder, @dnshorto if you’ve used the generic Alibaba Request-to-Quote system, rather than directly communicating with a particular supplier on AliExpress.

Here’s another 6-pole switch from Yaming. It has two-positions and centre-off, and is rated 32A, which is ample for your needs. Just check with them that it’s OK to use those contacts at DC 410v 10A (the open-circuit rating of the longer array).

All you’d be asking for is

a: all 6 switches to change-over between 2 contacts simultaneously. Ie you don’t want 3 connecting in switch position-1 and the other 3 in position-2  :thinking:

b: a change to the front-end. You’re seeking a yellow bezel and a red lever.

 

 

And if they ‘can’t do that’ I’d be very surprised.

If it were me, I’d probably buy this switch ‘as is’ and use my 3D printer to make myself a nice chunky red handle!

But it might be going a bit overboard for you to start ordering a 3D-printer just for this one job!

Userlevel 4
Badge +1

Once again @Transparent  you have found a relevant product which I have been unable to discover. I still don’t know how you do it! The Yaming Electric LW26-32/6 could be used although not ideal as it has 3 positions, and with shipping is up to nearly £18 with delivery by month end. Farnell’s standalone isolator at £45 with UK stock still might make sense.

I had a reply from FEEO on AliExpress messages.

Hi friend, we not have 6 pole isolator.”

So I asked another AliExpress messages question:

<<Yaming Electric have a cam switch LW26-32/6, 6 pole 3 position changeover. It does not feature on AliExpress list. I need it to isolate 6 PV solar feeds at max 410V DC at 10A. I need all 6 switches to changeover simultaneously, (not 3 on position 1, and 3 on position 2).>>

Response awaited.

I tried Yamin Electric’s own website but buying direct the minimum order is for 100 items, and the LW26-32/6 isn’t listed there either! Where did you uncover it?

Any further thoughts on the suitability of the inverter I proposed?

SKU: SOL-5K-RHI-48ES-DC Categories: Hybrid Inverter, Solis,

333mmx505mmx249mm. 17kg. £1200

 

3D printer eh! That’s worth remembering!

@dnshorto 

 

Userlevel 4
Badge +1

Quick question please @Transparent.

Yaming Electric have replied with the following message:

Please could you explain why 12 pairs of terminals (24) are required for 6 cables?

Thanks

@dnshorto 

Userlevel 7
Badge +2

I don’t think that switch diagram is correct @dnshorto 

The part we were looking at is a 3-position switch, but their diagram shows only 2-pos.

Here’s the diagram from their website for the switch we’re interested in and then adapting:

So this shows 6 stacked wafers. I’m a bit surprised they did it that way because a cam (moving contact) is surely able to connect either to one fixed contact or a different one as it turns. You don’t need two wafers to achieve the same result.

So the way I’d expect them to do it would look this this:

Even if they don’t have wafers which do this, they should at least understand that the diagram shows a change-over switch.

My diagram shows 6 wafers, each with three numbered terminals.

Terminal 2 connects to terminal-1 when the switch is in position-A;

and to terminal-3 when the switch is in position-B.

Userlevel 4
Badge +1

It’s a different switch. 2 position isolator. 

Userlevel 7
Badge +2

Now it’s my turn to be confused.

I thought you were looking for a switch which could connect a ‘source’ to one of two possible options.

There are two locations where one might be required to switch a ‘source’ either to the Growatt grid-connected inverter, or else to the proposed off-grid inverter:

  • PV Panels
  • Storage batteries

In any event, the device I’ve described in the table above has a centre-off position and will therefore act as an isolator as well.

Userlevel 4
Badge +1

Crossed wires @Transparent . If you check back, the switch I am at present trying to source is the 6 Pole isolator which you recommended where the 6 solar panel 4mm cables arrive. The changeover switch, which I will also need to source,  is to connect the battery either to the Growatt, or to the off-gris inverter, which doesn’t need to be 6 pole. If I understand the message from Yaming Electric correctly, as soon as they read that I am looking for an isolator, they realised that a 2 position switch was preferable. As you remarked in an earlier post, their customer service is amazing!

@dnshorto 

Reply