Boiler new Aug 2022. Ideal Logic+ Combi C
Thermostat / programmer fitted May 2023. Ideal Halo RF, not wifi connected.
August 2025 weather compensation fitted. Ideal OS2.
Straight forward to install the sensor and two core cable connected and run into the house for connection to the boiler. Cable run approximately 5m. Terminal on the sensor are not marked and the boiler weather compensation terminals likewise not marked. All connections made as per the Ideal instructions sheet.
Boiler switched on and nothing untoward. The instructions state that the house temperature is now controlled using the boiler flow temperature dial. Turn it clockwise to raise the house temp and anticlockwise to lower the house temp. The screen should indicate a range of 5℃ minimum and 30℃ maximum.
When I move the dial it performs as it always did and shows a temperature of the water flow. Minimum 30℃ and maximum set by myself of 64℃. Previously the minimum flow temperature was 40°C.
Checked my connections and all OK. However there was a link between the opentherm terminals. I believe this was fitted by the manufacturers. I removed this link.
Time to trail the system but first I set the weather compensation curve to 15. These seem to be arbitary numbers between 0 and 40. It was 18.
The stat was reading 21℃ and the set point increased to fire the boiler. The flow was set at 45℃ and the pump speed was switched to 100%. As the water temp increased it stabilised at 34℃ and sat there. The boiler had modulated down. The one thing I should have checked was the fan speed giving me an idea of the fire rate.
Previous experience was when trying to run the boiler at a flow of 40℃ the flame/fan speed would not reduce less than 25% and the flow would reach the set point and shut off the flame. On this occasion the flow and return would sit there at 34/25℃. No doubt if I let it run longer it would have shut down.
It looks to me that the boiler is being controlled by the weather sensor by modulating down more than I would normally see. What I normally see is the opentherm modulating down to a fan speed of 25% and the pump speed slow to 70% and the stat shut down the boiler at about 0.3℃ above the set point.
The house is a three bed Edwardian Terrace. The loft is well insulated and the windows double glazed sash type. These are pretty airtight. I’ve always tolerated a few draughts to allow the house to breathe.
My question is has anyone come across this before? The situation is the boiler is working fine but not as described in the instructions that came with the sensor or what I’ve read on line. As said above I removed the Opentherm link but there’s no mention of this in the instructions. Everything I’ve read says that the sensor will control the boiler but the thermostat still has control.