The earlier parts dealt with the car and the benefits of installing an air-air heat pump (AAHP)  and this part deals with the immersion heater which I initially thought would not be viable but  you can either have a small cost benefit or trade that for a significant decrease in the gas usage.  

 

An immersion heater is just a heater. It has a COP of 1 which means that you only get out as  much heat as what you put in as electrical energy. We could use a heat pump with a COP of 3+  to heat the water in the hot water cylinder but I’m just exploring what the benefits are, if any,  of just using an immersion heater as they are relatively cheap to buy. We have a hot water tank  (in a system boiler) which is fed by a cistern in the loft and it’s a vented system. The tank  heating at the moment takes place with the gas boiler. This is because it is generally too  expensive to use electricity to heat water.

 

The electricity price per unit can be around 25p on the SVT or Fixed Price contract. Since gas at  the same time is about 6p / unit and the boiler efficiency is around 80% this means that heating  by gas - what I call the Gas Margin Price (GMP) - is around 6.8p / unit. This is very much lower  than the SVT and it isn’t economic to do that if that is the tariff you are on.  

 

** Normally this is 90% with heating but it’s lower with the higher temperature for the tank  and also pipe losses even though they are lagged.  

 

Where it gets more interesting is that if you have a ‘wholesale linked’ tariff then the unit price  varies throughout the day and can even go negative. This means there are times when electric  heating is more economic than gas. You just need to be selective when you use it.  

 

 

Above is the average Agile price for the first 12 hours of the day over a four month period for  2024 and there is a very persistent pattern. There is a dip in the price between 01:00 and 05:00  hrs where the average price is still above the GMP but not disastrously so. On some days it will  be above this and some days below. So it would seem possible that we can take advantage of  the lower prices with two simple controls in order to make direct heating viable. But, first, we  need to know how much heating we need to do on a daily basis. 

 

My hot water demand amounts to 3.7 kWh a day. With a 3kW heater we can add enough  energy to the tank with 3.7/3 = 1.2 hours of heating a day. If we had the timer set to 1.5 hours  starting somewhere between 02:00 and 05:00 then this would be more than enough. In  addition we can always switch it off on the days when the price is too high.  

The number of lowest-cost hits for each HH slot starting  
02:00 to 04:30 over a four month period. 
 
You can see which three slots are the cheapest to run the heater. On average  these are the slots starting 02:30, 03:00 and 03:30.  
Note: there are errors in the depiction of the best slots (four in a day) but it  doesn’t affect the results which are calculated differently.  
 

Calculating the total cost versus the maximum unit price 

 

I’ve defined the parameter Gas Margin Price Factor (GMPF) as a means of setting a threshold to  enable the tank heating.  

 

As you increase the value up from 0 to 1 the heating and the cost saving increases. With the  GMPF greater than 1, the electricity price goes above the GMP of 7.6p (6.1p / 80%), and you  start to eat into the savings you have made. With a GMPF above about 2.2 the heating is on  every day and you make a loss but you are no longer using gas to heat the water.  

 

The days when we select to have the immersion heater on  

 

So what we have here is not only the ability to save money but if we set the GMPF > 1 we can  trade saving money against saving gas. In the plots below the months are horizontal lines, Jan Apr 2004. A red square means the immersion heater needed to be on that day.  

 

GMPF = 1 (on/off threshold = 7.6p) . This maximises the saving at £18 a year. It also saves  250kWh of gas (out of 1800kWh). The negative is that you need to intervene on an almost daily  basis. The immersion heater thermostat would be set to the max of 80C as this would allow  heat to be carried over to the next day or two when the price might not be so favourable. The  savings could be a bit higher because of this. This is the money option.  

 

GMPF = 1.6 (on/off threshold = 12.2p). This is the breakeven value and saves 1000 kWh of gas a  year. Much less intervention is required but you still need to check every few days to see if the  immersion heater needs to be on or off. The heat battery effect is very much reduced here. It’s  a balance between money and green.  
 
GMPF > 2.5 – (on/off threshold = 19p) If we take the extreme option having it switched on all  the time then we have an annual loss is £22. The gas saving is now 1800 kWh a year. There is  no gas water heating. This is the green option.
At a glance this looks like the immersion heater is on all the time but the critical point is that it  is only powered at various HH slots between 02:00-05:00 every day, controlled by an  immersion heater time switch.  

 

At a glance this looks like the immersion heater is on all the time but the critical point is that it  is only powered at various HH slots between 02:00-05:00 every day, controlled by an  immersion heater time switch.  

 

Note: An immersion heater timer is used to handle the switching. A 3kW immersion heater  should never be wired to a plug as the current could overheat the plug / socket.  
 

Refining the selection of HH slots

 

When we identify the best slots there is a very persistent pattern.  
Note: I have no idea why the cheapest HH slots stay more or less the same but it  will have a lot to do with a repeating pattern of electricity usage. This could  change as more EV owners charge overnight but this will be an evolution rather  than a rapid change and EV charging is not the only factor as there is a lot of  night storage heating going on in the first four months of the year. I will update  the blog with any changes in usage. I could also look to see if this pattern  changes in the 2023 data. 
 

Reducing the intervention required  

 

If you change the variable to fixed slots there is a barely perceptible change in the plot. In fact,  it is such a small change I’ve had to put both plots next to each other. Some of you might have  spotted that the savings plot doesn’t start at zero. This is because there ae negative values in  the Agile pricing so rather than complicate the graph with negative values I chose to show the  plot starting at a non-zero saving. It’s about £6 and a 100kWh of gas.  

 

The maximum loss increases from £22 to £25 which seems a fair swap for not having to change  the slots every day.  
 

A summary so far  

 

At first sight would seem to be completely uneconomic to use electricity to heat all the hot  water we use. For 1800 kWh it would cost £432 on the SVT and £270 on an average Agile price  of 15p. This is compared to a gas price of about £110. However, if we use a time switch that  comes on every day for the selected minimum-cost times then it works out only about £25  more expensive than gas. There is no regular intervention required but an occasional check can  be carried out to ensure the best time slots are still being used. If you want to you can  selectively turn the power off on the most expensive days which will save some money as in  the previous section. 

 

Saved Gas vs Electricity cost. The GMPF value with the ‘best’ trade-off?

 

As you opt to save more gas by having the immersion 
heater on at higher prices you can see this with the blue  
line. The dotted grey line shows the slope of the gas  
saving so you could say that the optimum trade-off  
between higher electricity costs and saving more gas  
could be where the gas slope is the steepest. A GMPF of  
about 1.6.  
 

This seems to correspond to the point where the whole project is just about cost neutral in  running costs which is tempting. You also save about 1000 kWh of gas.  

  

What this means in operating a gas boiler  

 

If we have the AAHP running (as in my other blog) then this could take the full heating load  from at least May to October. In addition the immersion heater looks to be able to provide hot  water in the tank the whole year round for an extra £25. I can’t see any reason why the gas  boiler actually needs to be on for six months of the year except for odd occasions. It’s going to  last a long time and the bigger issue is probably going to be spares over the extended lifetime.  

 

An Alternative Strategy – Full Control / Least Cost (possibly) 

 

For the sake of completeness there is another possible strategy that could be employed if you  are willing to set up a full control system (with associated costs) to take advantage of the Least  Cost HH periods that are available on Agile. If you sum all of the Least Cost HH periods and put  them into a plot it would look like this. This is the sum of all Least Cost Agile HHs x The number  of each value. Note: the lowest cost HH slots are negative.  

 

 

For the first 200 hours (400 HH periods) the total value is -150. If 1kW of power is taken during  those particular periods then you would have earned £1.50. Continuing on, after 400 hours the  cost would be neutral. The sum of the positive prices past the 200 hour point being equal to the  sum of the negatively priced hours up to that point.  

 

For the immersion heater we need a minimum of 1.2 x 365 = 438 hours of heating. Reading off  the plot above, 438 hours is just about cost neutral which is some kind of a coincidence. Each  unit is very nearly free. This is obviously well under our GMP of 7.6p unit so we will fulfil our  entire power demand (well, maybe not as we will see later), displace all the gas used for water  heating for practically no cost.  

 

Sounds too good to be true. Is this real?  

 

We are saving 1800 kWh at 7.6p per unit so this amounts to about £110 a year (the original  cost of gas) so that isn’t a bad start. We have to pay for the more complex control equipment  which will probably be an IoT device connected to the WiFi and some lines of code so it can  read the day ahead prices from Agile to switch on the immersion heater. If you want to be  fancy you could get it to read the changing gas tariff as well to calculate the GMP instead of  having it hard coded. If you know the three lowest priced HH periods in the next 24 hours you  can switch the immersion heater on for those slots. You also enter the value of GMPF  depending upon how you want to operate. Maximum profit (set to 1) , neutral cost (1.6) or  maximum gas saving >2.2).  

 

Assumptions and limitations  

 

However, it’s always the small print that gets you in the end. You may know the lowest HH  periods in the next 24 hours but the problem is that HH periods are like buses. You don’t get  them spaced out evenly, they tend to arrive in bunches. After a number of low cost HH slots  you will have raised the temperature in the tank to a maximum of 80C and you can’t use the  rest. It’s as frustrating as charging the car up one night with low rates only to find you could  have done the same charge the next night with negative rates and got paid for it as well.  

 

Damn! I would need to write (yet) another simulation to take care of the bunching. I’ve got an  awful feeling that the bunching problem more or less takes us back to the fixed time scenario  we had above and that only has a very simple control mechanism. It isn’t the lack of qualifying HH slots it the lack of suitably spaced qualifying HH slots. If I find the time I’ll explore this option  (along the lines of you can’t have more than three heating HH slots in a day) and see if it comes  out as being cost effective. It may be that the best solution is a combination of both methods.  I.e. an intelligent control system looking for the cheapest slots but it’s actually spends most of  its time in ‘damage limitation’ mode.  

 

Conclusion  

 

The timer plus switch solution above is simple and cost effective if you are on the Agile tariff.  There is a trade-off between Green and Saving Money and the user can decide what is more  important but you need to take account of future wholesale prices and it is worth reading the last section on the volatility of these. I decided to look at this because I bought a cheap fan  heater and used it when Agile prices were near zero and it practically paid for itself in two  weeks.  

 

This is an exercise to see if running an immersion heater is at all practical and relates to the  simulation. When the new boiler is fitted I’m going to run the immersion heater at different  levels of GMPF (0.5, 1.0, 1.5 and 2.2) and see how the gas water heating changes in response to  that. We have gas cooking as well so I’ll probably program the gas water heating outside of the  times we normally use the gas hob so I can separate out the gas usage. I should be able to  separate out the immersion heater usage from charging the car so I can keep a track of those  costs.  

 

Relating to tariffs, going green and costs 

 

Keeping specifically to the issue of the viability of running immersion heaters (and any other  direct heating method with a COP of 1) it is quite obvious that doing this only makes sense  when using a ‘wholesale related’ tariff. You can’t save money or affordably go green (save gas)  using an SVT or Fixed Price tariff. However, there are issues with wholesale related tariffs. What  I’ve done here is to run the immersion heater model against the Agile tariffs for 2019 to 2023  as a comparison using the appropriate SVT prices for gas at the same time.  

 

The ability to economically save gas (with direct heating) is dependent upon the relationship  between the gas price and the Agile price. This was thoroughly disrupted by the energy crisis  being triggered by Covid and the invasion of Ukraine. However, 2024’s results look more stable  and are tending to go back towards the 2019 situation. The steady, long term trend in the fall of  Agile prices continues. It would be far preferable to use heat pump water heating but the cost,  compared with a simple immersion heater and timer, makes it an expensive option. As a rough  calculation a heat pump water heater would cost £1,400 and it would save about £100 a year in  running costs. Over 10 years that would be about £40 year. It is comparable in price but you  may have problems integrating this with a gas boiler. 

 

An immersion heater would cost £50 plus £20 for a timer but could cost £25 a year at the  current rate. A total cost of £320 over 10 years and that would be £32 a year. In the worst case  if Agile prices led to bigger yearly losses then you could take the option of not using the heater.  

 

Next steps  

 

Mid May - The immersion heater timer due to arrive and will be wired in waiting for the new  tank.  

 

28/29th May - The new Vaillant boiler / tank / immersion heater is due to be fitted. I’ll provide  updates on how the immersion heating goes. Good or bad.  

 

Breaking news …  

 

12th May - Having looked again when we’ve had minimum prices I’ve noticed there are lower  values in the late afternoon. I’m going to have to tweak the minimum HH slots finder now to  include the afternoon and evening so an update on that later. Early indications are that there is  a better trade off point and lower losses so looking promising.  

Watch this space … 

 

I think you are being a little generous with your 80% efficiency for gas heating of hot water. I have attached 4 temperature sensors to our tank and from these I can estimate the stored energy in the tank.

I operate the tank at a nominal 50 °C with a boiler temperature of 67 °C. Even when the tank is “cold” (no useful hot water as the tank is below 43°C) it still has a significant volume of warm water, so re-heating our (160 l) tank only requires 2 to 3 kWh.

I measured efficiencies in the range 55% to 65% based on the temperatures in the tank and measured gas consumption.


@BeePee Thanks for the feedback. I chose 80% because I didn’t think it would be above that. If it’s below, and you make a good case that it is, then it makes the immersion heater with selective heating times and days even more viable.

 

I started off this journey thinking that there would be one solution to do everything. I.e. a ASHP would do everything. Well it can but it’s a bit like a smart phone that can be a GPS and a camera as well. Well, I’ve got a smart phone but I have a Garmin GPS that does a better job at 5% of the power consumption and a rugged, programmable Pentax camera with better resolution, colour balance, zoom ability and much less power hungry.

 

Likewise, the ASHP is good for medium heat output (lower COP on the coldest days) but my new Air Air HP is 3kW and less than one tenth of the price. The immersion heater saves gas and produces as high a temperature that I want (80C) without suffering from a loss in COP. My new Vaillant gas boiler will easily heat the house on the coldest of days with complete ease for a third of the price of an ASHP. With these working together I will probably only be using the gas boiler for heating on the very coldest days and I’ll be down to about 15% of the typical gas use for a four bedroom detached house. This is my understanding of Net Zero. You only use gas where you can’t reasonably use anything else. This amount can be offset.

 

Peter

 

 

 

 

 

 


Two further points made me look for an alternative way as well. An ASHP is quite a complex piece of equipment. At the moment we probably don’t know how reliable they are going to be in the long term. I’m also concerned about the price of spare parts and the cost of labour (high tech equipment) to fix it as well. My old Potterton 60e lasted 24 years (a bit noisy now) and cost me £160 for a new control board, fitted, about 10 years ago.

Secondly, the water in the radiators that goes out to the heat pump unit outside doesn’t have glycol in it as it makes the water too viscous and reduces the COP. If I’m away on holiday in the winter and the RCD trips (as has happened before) and there is a significant freeze then that is going to kill the heat pump. In five years time will we have an ASHP mis-selling scandal doing the rounds? Just because the government are pushing this for all they are worth it doesn’t mean it’s a good idea.

 


More thoughts on Water Heating Losses

Hi @Peter E 

Following on from my comment about gas boiler hot water efficiency I have used the last 3 weeks data to get a better estimate of just how efficient my hot water set-up is.

Although my 160 litre hot water tank is quite old I have lagged it with an extra 75 mm of loft insulation (the stuff made from recycled plastic bottles). I have fitted it with four temperature sensors ⅛, ⅜, ⅝, and ⅞ down the tank. To estimate the stored energy in the tank I draw a straight line between the four temperatures and extrapolate up to the top and down to the bottom. The stored energy is then effectively the area under the curve (times the volume and specific heat capacity). I also measure boiler flow in and out of the tank and the cold inlet temperature.

I set the (condensing) boiler set-point to 67°C, and aim for a water temperature of around 50°C (actually my home-built controller aims for around 160 l of hot water when mixed down to 43°C)

Below is a typical heating cycle. The yellow line is the temperature ⅜ of the way down, and the blue line at the bottom, ⅞ down. The two red lines are the boiler flow and return showing a maximum flow temperature of 65°C and return of 58°C.

So for the past few weeks I have monitored the gas consumed and the energy increase to the tank during the afternoon heating cycle (the morning cycle is more difficult to assess because our water usage is more random in the mornings as well as gas usage for breakfast – it depends when we get up!).

Using the evening heat-up cycle allows me to correlate the heat entering the tank against the gas used.

The best-fit line shows an efficiency of just 57%! The intercept suggests that during each heating cycle around 0.3 kWh is lost.

I have tried to scale this up for our typical day.

I have looked at so many websites trying to get ACTUAL, real world data but didn’t find anything of real use, although there was a suggestion that a typical household uses around 40 l of hot water per person per day. Ours is probably slightly higher than this.

So based on two showers and three sets of washing up per day I ended up with:

  1. Boiler Losses: 0.7 kWh, 10%
    • Assume a boiler efficiency of 90%
  2. Retained in Pipe-work (Boiler to tank): 0.6 kWh, 8%
    • Estimated from the graph of gas input to tank heating.
    • IF the system has pump over-run and the heat is returned to the tank then this loss is related to the water tank temperature.
    • If the system does not utilise pump over-run then the loss relates to the boiler temperature
  3. Pipe loss (Boiler to tank & Radiators): 1.88 kWh, 26%
    • The pipe-work between boiler and tank will continuously lose heat during the heating cycle.
    • We have two towel rail radiators which heat whenever the pump is running. These contribute the majority (1.5 kWh) of the loss.
    • Lagging the pipe-work can reduce this although not always possible.
    • The loss is proportional to the boiler temperature.
  4. Tank Standing losses: 0.82 kWh, 12%
    • Our system is set to heat water just before any major use, and is left “cold” overnight.
    • Losses are proportional to the tank temperature.
  5. Trapped between Tank & tap: 0.23 kWh, 3%
    • We must run off around 2 l of water in the kitchen before the water runs hot. This means that 2 l of hot water is left in the pipes cooling between each run-off.
    • When washing up this is around 20% of the water used. Hand washing is probably even more inefficient, showers using around 30 l, more efficient, and baths most efficient (least economic).
  6. Available to use: 2.8 kWh, 39%
    • A little worrying that only 40% of the energy used actually end up in the sink or shower!

A neighbour asked if it would be better to boil the kettle when washing up? Given the price differential between peak electricity and gas, probably not, quite. Of course if you don’t use the hot water from the tank it is still cooling down.


Hi @BeePee That is EPIC with regards to data collection and nothing I've said so far is worth anything without data to show that it works or underpins the assumptions made in the first place. I'll get back a little later with some more detailed comments but what you have posted is greatly appreciated.


@BeePee 

I’m not quite sure I understand the differential between the upper and lower tank temperatures unless, of course, after the tank was heated some hot water was drawn off just before 17:30.

 

I understand that the blue line drops on starting the boiler because the pump drives colder water into the coil before the boiler heats it up and the temperature rises rapidly. I can understand the higher rate of rise of the boiler flow as it’s a more modern boiler and it is running at a high rate, realises the temperature is rising quickly and turns down the gas for a lower rate of rise until the return temperature exceeds the cut off value and the boiler switches off.

 

There is certainly a good correlation between water tank output and the gas used but puzzled as to why the slope is only 57%. A good thought about the intercept being the start up losses (cold water in the pipe beforehand and hot water afterwards) which dissipates into the house rather than the tank.

 

Certainly there are a lot of little losses everywhere that add up to quite a substantial loss overall. If you have an efficiency of only 40% overall you can apply my Gas Margin Price (GMP) calculation to get the equivalent electric price. 6p/0.4 = 15p. Not practical when the SVT is 24p but this is slightly less than the non-peak Agile average so theoretically doable. However (there is always the however) you need an electric water heater at every point where you need hot water as storing / transporting the water is part of the losses that you are trying to avoid. You also need multiple installations around the house with wiring etc etc.

 

It sort of gets you either way.  Appalling efficiency of a central gas system or the marginal cost benefit / installation costs of multiple electric.

 

However, if Green is a priority then you might want to sacrifice the beer tokens to the God of Green and do the multiple electric hot water points. There may even be a halfway house (haha - just seen that) where you use gas to warm the water (less losses) and raise the temperature locally. With a hot water bill of £110 a year for me (I have an electric shower) it seems a lot of work anyway to go down that path. Is does niggle me that you have to run a lot of cold water out to get to the hot water. And then the hot water just sits in the pipe getting colder.

 

The other issue is that the pipe / tank losses are somewhat reduced in the winter as they contribute to heating the house in an uncontrolled way. Although if you have TRVs on all radiators then heating will be correspondingly reduced. It’s all horribly messy and no real winners.

 

My philosophy is keep it as simple as possible and go for the big wins to start with. There may be an answer but it’s not obvious but it does get you thinking about what you might do about that.

 

Peter

 

 


Hi @Peter E 

If I put all 8 temperatures on the graph gets very messy!

The reason for choosing the two tank temperatures.

Blue is 1/8 up from the bottom so is very sensitive to any draw-off. The yellow is 3/8 the way down the tank and above the top of the heating coil. The reason I chose it is that my controller keeps the pump running until the boiler flow/return temperatures are just above the “yellow” temperature.

At 16:05 (ish) I did the washing up, hence the big fall on the blue, and small on the yellow, The boiler turns on at 16:15 and does transfer some heat from the upper tank to the lower until the boiler catches up. You are correct that the initial steep rise in boiler temperatures is because the boiler runs at its high rate, the little dip occurs when the boiler modulates down. I have (just) managed to match the low boiler output to the heat exchanger so for small top-up I don’t get the boiler cycling. You can also see when the pump turns off (when the two boiler curves touch, just as they cross (fall below) the yellow curve.

We always heat the water just before usage, hence the two showers at 17:15 and 17:30. You can also see that although the bottom of the tank (blue) is now cold, the upper yellow temperature has changed very little.

I had looked at an electric point of use water heater for the kitchen but whilst gas is so much cheaper than electric it doesn’t seem worth while (yet). Also if I need a hot water tank for showers and baths then the hot water is there anyway.

I estimate that my hot water contributes around 2300 kWh (£140) to my total usage, and as you say in the winter months all the losses just help to heat the house.

Thanks

Barry


Some very interesting points in all this coupled with all the data collected - fab!

A couple of things .. I track water usage (and target savings) via my water meter. This shows average daily usage as well as being active in reducing usage 

Our heating system also tracks hot water usage separately to heating and so I have data for those values also. 

A steady reduction has continued from earlier years. 

One thing on agile price variations @Peter E , you need an automated trigger as it appears that cost is not as predictable as might be expected. I use a system called ‘Home Assistant’ which gathers all my data from various sensors alongside pricing each day when prices are published (I use gas tracker as well as agile). This can calculate and enable switching based on your required trigger calculations .. and it’s also a fun system to explore


@BPLightlog  Yes. You do need to automate for maximum saving or at least reduce the losses if saving gas is more of a priority. As in my blog there are persistent patterns of lower prices that work almost as well as actively looking for low half hour slots on a daily basis. I've just had my new boiler / tank / immersion heater fitted and I'm now in the process of exploring how best to predict / schedule the HH slot heating for lowest cost and I'll update here and in the blog as to what I've found.

 

An initial finding is that you probably can't use consecutive HH slots as the water gets heated up locally and the immersion heater switches off earlier and earlier with each slot. I may need to separate the HH slots with a gap of one or two slots to allow time for the heat to diffuse outwards and write that into my excel simulation and see how close I can get with that.

 

Thanks for reminding me about Home Assistant. I must have a look at that.


I’m sure you’ve seen https://energy-stats.uk/octopus-agile-south-eastern-england/amp/ a terrific website for the data enthusiast. I’ve just found this graph on it which shows how Agile’s price alters throughout the day - averaged over the year. 

 


It shows that you can beat the SVT / Fixed Price contracts by a wide margin for most of the day. Prices are a bit higher atm (mid April to early July) but you can get very low or even negative prices at times. My average cost per unit is about half the current SVT of 24p.


Hi @Peter E 

The latest graphs from my system.

First my plot of actual gas usage Vs the estimated increase in cylinder stored energy (now over 5 weeks). Not much difference really; still around 57% efficient with slightly higher 0.4 kWh standing loss.

 

At the risk of confusing matters the following is a plot of the tank and boiler temperatures during an evening heat phase (actually the 4.98/2.7 kWh point).

The blue lines are the tank temperatures, the red the boiler flow and return, and the green is my estimate of the stored heat energy (based on measured cold water inlet - right hand scale).

Boiler turns on at 16:15, and requires two heat cycles to achieve temperature.

The usage comprises two baths (17:30 and around 18:00) and a little later hair washing.

 


In a message I sent to @BeePee I've just measured the energy input to my new hot water tank (immersion heater) to bring the temperature up to its normal level and it takes 3kWh. From previous measurements it takes 5kWh of gas to do the same thing. Efficiency is 3/5 = 60%. In good agreement but it shows you how lossy the tank water heating process is for the detailed reasons that BeePee gave earlier. I've switched my gas hot water heating off now. That will save 1800kWh of gas a year. I never expected that to be such a decisive result.


Reply