Skip to main content
Solved

Storage Heater trying to charge outside offpeak time with change to Smart Meter


Hi

I had a smart meter installed recently and I am finding something strange with my Quantum Storage Heater.

Prior to the installation I was on a Economy 7 rate and my heater would come on at 12am and off at 7am to charge. I knew this due to the LED light on the switch turning on. This occured during my offpeak time, as also confirmed by meter usage.

Now, still on Economy 7, I am observing the heater isn’t coming on until 3am and the light stays lit up until 10am. I have confirmed my offpeak time on the smart hub is active at 12am onwards  (I can see the hourly rate changes over) but this isn’t activating or communicating with the heater. And between 7am and 10am, despite the LED light being lit up there is no usage so it isnt actually using my on peak time (again the hub confirms this from 7am onwards), which of course is good.

But it seems the heater has gone out of time. I have checked the settings on the heater and it shows the off peak tariff time is 12am to 7am. This leads me to understand the heater isn’t getting the opportunity to have its full period of charging, and after 7am its trying to keep charging but is getting no power.

So something seems to be confusing either the meter or the heater,

Could anyone shed some light on this, as it worked as expected for years until I had the smart meter installed.

 

Best answer by BPLightlog

Updated on 18/03/25 by Abby_OVO

 

Ok, so your new meter is a 5 terminal model (see the cable bottom right slightly forward of the others).

 

This type of device switches from peak to off peak by enabling the 5th terminal during off peak times which means that your heaters are supplied only when that feed is live. These devices do switch on and off at timings designed to prevent all local off peak switching at the same time. That means that it might not switch exactly on the hour but you should still get a full off peak period even if the switching means that it is off just after the hour. 


When you refer to your ‘smart hub’ I assume that you’re talking about your IHD (in home display) which is not a good indicator of when things switch. 


If the circuit does switch on during off peak - that’s a start .. we’ve seen several that don’t. 


The timings should be driven by your smart meter, nowhere else and so you should make sure that any off meter time switch doesn’t prevent power getting through. 

 

The following topics may also be helpful:

 

 

If you’ve still got questions about your own set up, feel free to leave a comment below or ask your own question here.

View original

15 replies

BPLightlog
Plan Zero Hero
Forum|alt.badge.img+5
  • Plan Zero Hero
  • 2765 replies
  • February 24, 2024

Hi @JamieTall , can you post a photo of your smart meter please. From that someone might be able to help


  • Author
  • Carbon Cutter****
  • 6 replies
  • February 24, 2024

Thanks for replying.


BPLightlog
Plan Zero Hero
Forum|alt.badge.img+5
  • Plan Zero Hero
  • 2765 replies
  • Answer
  • February 24, 2024

Updated on 18/03/25 by Abby_OVO

 

Ok, so your new meter is a 5 terminal model (see the cable bottom right slightly forward of the others).

 

This type of device switches from peak to off peak by enabling the 5th terminal during off peak times which means that your heaters are supplied only when that feed is live. These devices do switch on and off at timings designed to prevent all local off peak switching at the same time. That means that it might not switch exactly on the hour but you should still get a full off peak period even if the switching means that it is off just after the hour. 


When you refer to your ‘smart hub’ I assume that you’re talking about your IHD (in home display) which is not a good indicator of when things switch. 


If the circuit does switch on during off peak - that’s a start .. we’ve seen several that don’t. 


The timings should be driven by your smart meter, nowhere else and so you should make sure that any off meter time switch doesn’t prevent power getting through. 

 

The following topics may also be helpful:

 

 

If you’ve still got questions about your own set up, feel free to leave a comment below or ask your own question here.


  • Author
  • Carbon Cutter****
  • 6 replies
  • February 24, 2024

Thanks.

It’s good that it is working of course, but I’m concerned not as intended.

When you say it can change not exactly on the hour, a small change would be fine but this problem suggests I’m losing out on 3 hours charge.

The past 2 nights the LED attached to the Quantum heater indicating off peak is live and is charging hasn’t come until exactly 3am and then switched off at exactly 10am. Keeping an eye on the IHD, at 3am the IHD was already showing it was on offset peak time for 3 hours but the radiator only came on at 3am at which point my usage understandably jumped up. And then at 7am this morning the IHD showed the meter has switched back to the on peak rate and my usage dropped to almost zero but the LED on the radiator was still lit up for a further 3 hours until exactly 10am.

So the IHD is reporting the correct on and off peak times and rates. The radiator is set to match these times. But something is throwing this window out by 3 hours.


BPLightlog
Plan Zero Hero
Forum|alt.badge.img+5
  • Plan Zero Hero
  • 2765 replies
  • February 24, 2024

Hmm .. the offset on switchover should be just a few minutes at most, not several hours. 
From what you say, either the meter isn’t switching at the correct time (in which case it need a reset) or there’s another time switch somewhere in the circuit. 
 


  • Author
  • Carbon Cutter****
  • 6 replies
  • February 24, 2024

Thanks for your help, I appreciate you taking the time to look at it.

I was hoping a solution might be known but it looks like I’ll need to give OVO a call, which unfortunately never goes well. Thanks again.


Firedog
Plan Zero Hero
Forum|alt.badge.img
  • Plan Zero Hero
  • 2111 replies
  • February 24, 2024

It sounds as if the schedule for the Auxiliary Load Control Switch (ALCS) isn’t right, even though the meter is switching its counters from peak to offpeak and back again at the right times, which are given on your Plan page. The two should match. Yes, you’ll have to contact Support and get them to ask the smart team to send the ECAUL request to configure the ALCS. It might take a couple of tries to get the change to stick.


BPLightlog
Plan Zero Hero
Forum|alt.badge.img+5
  • Plan Zero Hero
  • 2765 replies
  • February 24, 2024
Firedog wrote:

It sounds as if the schedule for the Auxiliary Load Control Switch (ALCS) isn’t right, even though the meter is switching its counters from peak to offpeak and back again at the right times, which are given on your Plan page. The two should match. …

You are probably correct @Firedog although I can’t figure out why the indicator on the heaters should be ‘on’ between 3am and 10am? 
 

JamieTall wrote:

The past 2 nights the LED attached to the Quantum heater indicating off peak is live and is charging hasn’t come until exactly 3am and then switched off at exactly 10am. Keeping an eye on the IHD, at 3am the IHD was already showing it was on offset peak time for 3 hours but the radiator only came on at 3am at which point my usage understandably jumped up. And then at 7am this morning the IHD showed the meter has switched back to the on peak rate and my usage dropped to almost zero but the LED on the radiator was still lit up for a further 3 hours until exactly 10am.

..,

As the IHD doesn’t control the switch, what would be keeping the indicator live only between those times? Wouldn’t that be when the 5th terminal is live?


Firedog
Plan Zero Hero
Forum|alt.badge.img
  • Plan Zero Hero
  • 2111 replies
  • February 24, 2024

I’d guess that the LED just shows that the power supply is live, i.e. that the fifth terminal is live. It’s the heater’s internal clock that switches it* on at midnight and off at 07:00 (“I have checked the settings on the heater and it shows the off peak tariff time is 12am to 7am”). So it’s not charging between midnight and 03:00 because the ALCS is off, and not between 07:00 and 10:00 because the equipment’s heating elements are off even though the ALCS is on.

Every element of the timing puzzle has to be in alignment: the tariff (as shown on the Plan page), the tariff timings and rates as pushed to the meter (to manage its registers) and thence to the IHD, the ALCS to match the tariff timings and the time switches on the heaters themselves. This looks to be all in order except for the ALCS calendar, which is remotely controlled by the smart team at OVO. ECAUL should fix it.

 


*   ‘it’ being the heating element. There should be 24-hour power to the heater via a separate circuit to control its fans, so it discharges heat more quickly when asked. Quantum call this the ‘comfort’ setting, I think. The LED presumably only monitors the feed to the heating element. 

 


Abby_OVO
Community Manager
  • Community Manager
  • 1109 replies
  • March 6, 2024

Hey @JamieTall 

 

Did you get this sorted in the end, and are the heaters coming on and off at the right times now?

 

Let us know how you got on.🙂


  • Author
  • Carbon Cutter****
  • 6 replies
  • March 6, 2024

Hi

 

This unfortunately became the least of my concerns as OVO installed a pre payment smart meter that would not accept top ups. After 4 days of constant phone calls, extremely poor service and losing power an emergency engineer came. He replaced the smart meter back to an old style prepayment meter which I had before. He stated a smart meter should have never been installed and what was installed by the OVO engineer was done incorrectly. He theorised the storage heater was not being sent the right information because it couldn’t hold a signal.

 

Back to the old style meter and the storage heater is back working as it should. Now I’m facing a customer service wall of trying to get back my missing top ups, my previous meter balance, and all the compensation that was promised over and over. They refuse to transfer me and promised callbacks are never made. 
 

It has been a deeply stressful experience and continues to be so, but I’m persistent with daily emails to their complains department imploring them to take ownership to resolve this.

 

The alarming thing is the meter was originally changed due to a complaint about a faulty meter that was never dealt with that I had to contact the ombudsman about. I’m now back to square one with OVO owning me money and refusing to talk to me. It’s been one bit hellish circle to end up back to where I was in December.

 

 

 


Emmanuelle_OVO
Community Manager

I’m really sorry to hear this @JamieTall. Are you with OVO PAYG or Boost?

 

If you’re with OVO PAYG I’ll ask Forum_Support to reach out via private message to take a look into this for you. 

 

If you’re with Boost, you can find out more about their complaint procedure and contact channels on the website. 

 


  • Author
  • Carbon Cutter****
  • 6 replies
  • March 7, 2024

Hi

I’d appreciate that I’ve grown exhausted with their advance resolutions department and their lack of ownership.

I am with OVO PAYG. I have an account number, a complaint reference number, and an OVO ombudsman complaint number. I’ve also kept a full record of every time I’ve contacted OVO, what they’ve promised and what happened.

I’m now at a point where I’m sending an email every 48hours asking the same questions over and over and no one is replying. When I call up I am told my complaint is at ‘Tier 2’ and I can’t be transferred and I will be called back. These callbacks do not happen.

As it stands at the moment. OVO have not returned the balance that was on my previous meter that they told me would be transferred over. OVO are holding money that I topped up that never got credited to my meter. I was promised compensation for loss of earnings over two days as I had to sit in the house with no power waiting for callbacks and then for an engineer. This hasn’t been honoured. And finally the new meter has a standing charge over 3 times what I had before and no one will tell me why and each day I’m giving OVO more money that could be in error.

 


Emmanuelle_OVO
Community Manager

That sounds really stressful, I’m sorry to hear this, If your issue has been escalated to the Ombudsman, my advice would be to let them sort it out and contact OVO directly @JamieTall.

 

OVO will need to accept the resolution they provide. You can contact the Ombudsman on:

 

Here’s how to get in touch with them:

 


  • Author
  • Carbon Cutter****
  • 6 replies
  • March 8, 2024

The ombudsman have said since the original remedial actions have been completed (eventual installation of new working meter) any issues that have arisen from this would need to be a new case in which I have to wait 8 weeks before I can raise it.

 

So it’s 8 weeks of resending the same complaint and hoping someone eventually responds.


Reply


Cookie policy

We use cookies to enhance and personalize your experience. If you accept you agree to our full cookie policy. Learn more about our cookies.

 
Cookie settings