Skip to main content
Tutorial

Who owns what? - Your guide on cut outs, meters, fuses and who's responsible

Who owns what? - Your guide on cut outs, meters, fuses and who's responsible
Show first post

55 replies

Tim_OVO
Community Manager
  • Community Manager
  • 1864 replies
  • July 19, 2020

Please keep us updated after we reach out to you and get things resolved. It would be great to hear from you about this, so there’s a conclusion to this topic. 


  • Carbon Cutter**
  • 19 replies
  • July 20, 2020

Hi @Tim_OVO ,  I didn’t get any call from you or Ovo generally as yet with any kind of solution. This leaves me with reporting this to the HSE tomorrow as previously advised.


  • Carbon Cutter**
  • 6 replies
  • July 21, 2020

Hi there,

I have just been canceled  by OVo the appointment with the engineer on 6th of August to upgrade my meter tails as I am looking to upgrade the main fuse from 60 to 100Amps with UK Power Network. 

Because of that I had to cancel their appointment too.

Very upsetting all this.

Anybody had recently any similar experience of upgrading meter tails with OVO or they are just pretending to do it but never actually getting it done?


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Author
  • Carbon Catcher***
  • 982 replies
  • July 22, 2020

Hi @Adiavel - we’ve just started this Topic to discuss these issues.

There are several parties responsible for different parts of your electricity supply. Customers find it tricky to work out who needs to do what and in what order.

In your case OVO are correct. The Service Fuse upgrade comes first. As you say, it’s the responsibility of your Distribution System Operator, UK Power Networks.

It’s possible that the DNO will also change/upgrade the meter tails at the same time. That depends on their engineer’s assessment whilst he’s on site. These decisions are made primarily on safety grounds. Even if you posted a photo here, I doubt that Forum Members could adequately evaluate the construction of the tails and their condition without handling them.

Please post again if you’d like to make further comment. That’s what the Forum is for!


  • Carbon Cutter**
  • 6 replies
  • July 22, 2020

Hi Transparent, thank you for your reply.

But I think you are very mistaken.

OVO MUST change the meter tails BEFORE the fuse is changed by UK Power Networks (DNO equivalent in my area). It is a common sense procedure. You can't let more power into the house by changing fuse when tails size might not cope with it. 

Also stating that DNO (or UK Power Networks in my case) might change the tails, it is again a HUGE untrue statement.

For DNO to change tails will need to break seals into the meter and the meter belongs to my Ovo energy supplier, so they will not do it.

Why are you providing false and misleading information?!

I was hoping on this forum I can find good answer.

My problem was related only to OVO handling very badly the meter tails upgrade appointment, blaming it on lack of engineers in my area. 

They booked me, they took my money  then a week later they cancelled my appointment.

Now they are playing the very hard to reach to try to book another appointment.

I just wanted to hear of similar experiences with other forum members.

 

 

 


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Author
  • Carbon Catcher***
  • 982 replies
  • July 22, 2020

Sorry to hear this @Adiavel

I have been present at three meter installations by OVO engineers when they broke the seal on the Service Fuse and changed the tails. They are permitted to do so under the MOCOPA Agreement.

I’ve also discussed the situation with my own DNO, with whom I enjoy good communications on technical issues. They said that they commonly change the tails to the meter when upgrading the Service Fuse… unless it’s obvious that the tails have recently been changed, as would be the case if a Smart Meter had been installed.

In either case, the tails themselves are simply regarded as the “side issue” to the change of meter or fuse. That makes sense, and errs on the side of safety.

This topic is primarily concerned with safety issues. If the DNO changes the Service Fuse for any of the 33 categories listed in the Faults and non-Compliances document then it also most likely that tails would be changed too.

You haven’t given a reason as to why you want the Service Fuse changed to 100A, so I don’t know if this is related to a “non-compliance”, or merely that you’d like more amps available.

I’m not in SE England, so I don’t often get to speak with UK Power Networks. Their policy may well be different. But it seems overly pedantic that they will not change the tails when they’re booked on-site to attend to their fuse.


  • Carbon Cutter**
  • 6 replies
  • July 22, 2020

Hi thank you for your reply.

Reason for fuse upgrade is that I need more Amps available for house as I will have a summerhouse CU installed soon, so more power demand overall.

Yes you are correct, the OVO engineers can change meter tails as Ovo owns the meter.

On UK Power Network it is clearly stated that the meter tails must be upgraded by the energy supplier BEFORE they can upgrade the fuse.

However because OVO it seems to be useless, I have contacted UK Power Network again and asked for a revised upgrade to 80 Amps only. This will be possible on the current meter tails size of 16mm hopefully. It is still a step forward for me.

Yes if the UK Power Network will decide that the whole fuse box needs to be changed because of visible damage or overheating, then probably they will break the seal on the top part of the fuse box where meters tails are fitted and be able to put new meter tails too at the same time with replacing the entire fuse box. It makes sense to me and hopefully this will be the case as I noticed some kind of black asphalt kind of leakeage along the fuse box, God knows from when, as the house electrics have been done in 1976 and I bought it as it is in 2012.

 

Thank you for your reply.

 

 

 

 

 


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Author
  • Carbon Catcher***
  • 982 replies
  • July 22, 2020

That bitumen leak might be the clinch argument, @Adiavel

Have a look at page 47 of the Faults and non-Compliances document. Category C-02 non-compliance is where bitumen has leaked but is not currently doing so. But there’s a particular note to say if the leak is still occurring, then the fault category gets raised to A-01 (the highest safety alert).

By all means post a photo here, but you’ll have to decide if you think the leak is happening now by seeing if the bitumen is soft/tacky. It’s indicative of the fuse getting too hot. There’s a good description on page 13, where A01 is described.


  • Carbon Cutter**
  • 6 replies
  • July 22, 2020

Thank you, Transparent.

The bitumen drippings looked solidified not liquid. So it happened some time in the past.

Thank you for this reply too. I will let them know so they can decide the apropiate action to be taken.

 


Bradley_OVO
Community Manager
  • Community Manager
  • 74 replies
  • July 22, 2020

Hi @Adiavel, I think @Transparent is correct when referring to this particular topic when discussing your query.

 

I’ve moved all of your comments over to this existing topic to keep everything in one easy to find place, which will mean other users will be able to get their hands (and eyes) on it.

 

Some great back and forth information here, and it would be extremely beneficial for us to hear more about your journey. Please continue to update this thread if and when you learn more about the process.

 

Have a great day,


Tim_OVO
Community Manager
  • Community Manager
  • 1864 replies
  • July 22, 2020

Yep some more really interesting questions about who should be doing what and when here. It’s clearly a grey area so I have a feeling this topic might be getting A LOT of action!

 

Thank you for sharing, @Adiavel - if you have any doubt as to what the next steps are from OVO’s side, we’re on FacebookTwitter and our Help centre has online chat! It would be really handy to hear back from you when you notify the DNO, so we know what next steps they’ve advised…?

 

Nice advice once again, @Transparent - you’re the most knowledgeable non-engineer we have as part of this community! 

 

 


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Author
  • Carbon Catcher***
  • 982 replies
  • July 22, 2020

Well I think @Adiavel ‘s idea of requesting an 80A fuse is a masterstroke. I doubt that the DNO holds many of those in the stores. So there’s a fair chance they’ll turn up with a standard 100A fuse anyway!

Just returning for a moment to the additional Consumer Unit you want to put into the summerhouse, I’m unsure how your local electrician might wish to link that to your existing Distribution Board. There are a number of alternatives, dependent on the type of cable (Steel Wire Armoured underground?) and what mechanical space there is in your existing CU.

When I started a house renovation about 5 years ago, I had the DNO relocate my meter into a new box built into the external wall. The existing arrangement was a mess of three CU’s, two with re-wireable fuses. So my friendly electrician placed a new 100A Switch Disconnector in a separate box screwed to the internal wall just behind the meter enclosure.

The DNO engineer arrived mid-morning, fitted the Service Fuse and meter, which had short tails running through the wall to the new Switch. He performed the required tests and left site.

My electrician called by a couple of hours later, made safe the loose cable-ends around the consumer units and ran an overly-long pair of new tails to the other side of the same 100A switch.

Each party had completed the work for which they had responsibility. But the arrangement allowed us several months to gradually run new cables through the house as the renovation work continued. Whenever we had a new circuit ready we could isolate everything without needing to call the DNO to pull their Service Fuse.

Anyone considering future changes to consumer units (perhaps for an EV charger) should ask their electrician for the same arrangement. It’s cheap, practical and safe.


  • Carbon Cutter**
  • 6 replies
  • July 22, 2020

He will split the meter tails and from the splitter he will feed both the house CU and the summerhouse CU. For summerhouse, a 16mm armoured SWA cable will leave the splitter, running on the ground along the garden fence towards the summerhouse to its CU.

Hopefully it is ok.

While the main fuse will be 100Amps and the meter tails need to be upgraded  to 25mm, I hope the 16mm Cable going to the summerhouse it is ok too, even if those kind of cables can carry maximum of 80amps, much more than the summerhouse will ever need at one time.

By my calculation both CU's added will never draw more than 80Amps at one time from the main cut out fuse. 

So if they got one and they agree to fit it than I will be very happy indeed.

But maybe they will see that my fuse box needs replacing so there is a chance to have actually the meter tails changed by them along with a 100Amp fuse, which will set the house ready for charging an EV vehicle in the future too.

They are UK Power Network, maybe different from DNO, hopefully everything will go as planned.

I will keep you updated.

Thank you for your reply, Transparent.

And finally, I received the appointment email from OVO for upgrading  the meter tails which now is 3 weeks later than the initial one...I lost faith they will do it, so I am trying to go ahead with the UK Power Network appointment if they will allow it.

Thank you again.

 


Amy_OVO
Retired Moderator
  • Retired Moderator
  • 115 replies
  • July 23, 2020

Hey @Adiavel, I’ve been in touch with our operations team to ensure the information I give is fully accurate.

It’s a shame to hear the appointment has been delayed, but the DNO won’t touch the meter tails at all, it will be in your best interest to wait for the appointment. It's best practice that we upgrade the tails before the fuse is changed. 

I'd also recommend having an isolation switch installed if you don't already have one, if you’re planning on having two consumer units.  It'll make it easier for the electrician to wire. We can do meter tail upgrade and isolation switch fitting in one job, no problem, please reach out to the team, you’ll find our contact details in the post earlier by @Tim_OVO

I hope this helps! 


  • Carbon Cutter**
  • 6 replies
  • July 23, 2020

Hi Amy, thank you for your reply. 

I will see what UK Power Network will do, maybe will cancel my appointment too or maybe they will be able to fit only a 80 Amps fuse on the current existing meter tails (16mm) which is still a great achievement for my property.

My electrician will install indeed 2 x  100Amp isolation switches, one for each CU, in order to allow trouble free maintenance in the future.

Thank you very much for your help.

Regards.

Adrian.


Amy_OVO
Retired Moderator
  • Retired Moderator
  • 115 replies
  • July 23, 2020

You’re welcome, @Adiavel, please keep us updated, the outcome of this may be very handy to other members.

There’s a post here that you and @Transparent might be able to shed some light on. 

:blush:

 


Transparent
Carbon Catcher***
Forum|alt.badge.img+2
  • Author
  • Carbon Catcher***
  • 982 replies
  • September 14, 2020

Any update on this please @Adiavel ?


  • New Member*
  • 1 reply
  • October 6, 2022

Just had my bill & there’s a £10 charge for Site Visit 2hr Time Slot I have no idea what this is & there’s no explanation on the bill. I have had to get in contact with Ovo over a missing payment which was THEIR ERROR so if this charge relates to that issue that is ridiculously unfair & needs cancelling. I am being so careful with my spending right now so for them to just add £10 on like it’ s nothing is disgusting. I am really worried about where I can go to ask for help with this, in case this #### company puts more charges on (I’m assuming/hoping coming on this page won’t cost me anything). Can anyone here help me?

  


Emmanuelle_OVO
Community Manager
  • Community Manager
  • 2572 replies
  • October 7, 2022

Hey @Egg,

 

Sorry for the issues you’ve had.

 

If you contact Support they can reverse this charge for you. I’d advise contacting them through web messenger. 

 

A ‘Site Visit’ might refer to a meter reader request, but if you haven’t booked anything of this nature it sounds like it’s been wrongly applied to your account. 

 

Keep us posted with how you get on.


  • New Member***
  • 1 reply
  • November 29, 2022

Living in council house, electricial (city contractor) went to change fuse fox, but there was no separator between the meter and fuse box, so he removed meter seal, installed separator then fuse box. Also told me that I don’t need to do anything about the broken seal, he will report it (somewhere), and some one will seal it in days. one week passed and no one came, no seal.

What I supposed to do about it?


Blastoise186
Plan Zero Hero
Forum|alt.badge.img+1
  • Plan Zero Hero
  • 7890 replies
  • November 29, 2022

Morning @JohnSmith ,

Strictly speaking, that electrician shouldn’t have snipped the seal without first getting permission from the supplier and DNO. Just something to know for next time.

If the meter seal is broken, have a chat with OVO’s Support Team and they should be able to get an engineer out to re-seal it. If it’s the Main Fuse, your DNO can help if you give them a call. Some DNO’s will also re-seal the meter too if you ask nicely.

This is a free service.


  • New Member*
  • 1 reply
  • January 19, 2025

I am all electric where I live and have economy 7 supply as well as normal peak supply, so 2 meter readings and 2 fuse boxes.  I am thinking of getting a smart meter installed.  I have 2 queries: firstly can the fuse boxes be relocated near the smart meter as part of the installation and is this straightforward (they are currently located in a quite restricted place in the spare bedroom) and secondly will a smart meter be appropriate with an economy 7 supply. Thank you.


BPLightlog
Plan Zero Hero
Forum|alt.badge.img+5
  • Plan Zero Hero
  • 2733 replies
  • January 19, 2025

Hi ​@sylviabrom , the fuse box (or consumer unit) is your own responsibility and so it can be moved but that would not be done by anyone fitting a new meter. You would need a qualified electrician to do that. There’s a guide here 


As for E7, yes, smart meters are designed to be able to work with a variety of tariffs


  • New Member*
  • 1 reply
  • February 4, 2025

I've been told by E.On that I need a new smart meter. I have an asbestos backboard The D.N.O says it's there responsibility to remove it at a cost of £600 they also said eon should fund this because its them that wants to put a smart meter in. eon says they don't fund this. Who is responsible .


Blastoise186
Plan Zero Hero
Forum|alt.badge.img+1
  • Plan Zero Hero
  • 7890 replies
  • February 4, 2025

Hi ​@Postoffice ,

Hate to say this, but in this situation E.On Next is NOT responsible for the meter backboard job, nor are they responsible for contributing anything towards it.

Under the rules of how this stuff works, the Customer (as in yourself) is considered the Owner of the Backboard, so it’s up to you to maintain it at your own cost - including paying for any replacements. You can pick up a new one pretty cheaply at a builders merchants, but replacing an asbestos backboard is a specialist job and as you’ve found out, a rather expensive one. Your DNO can help with doing that job itself, but they’ll expect you to pay in most cases.

Sorry that this wasn’t the answer you may have wanted.


Reply


Cookie policy

We use cookies to enhance and personalize your experience. If you accept you agree to our full cookie policy. Learn more about our cookies.

 
Cookie settings