apparent massive surge of power on the Solis app


Forum|alt.badge.img

Can anyone please explain why suddenly a few days again the solis app started showing a massive surge of power from the grid, see below

 

Best answer by BPLightlog

Hi, I presume you’re looking at the spike in the top screenshot for 9/4.

At the level of 145kW, that wouldn’t be possible via a domestic supply and you can see the spike at the same level each side of zero. (Domestic supplies are limited to 80 or 100A for single phase which equates to approx 23kW)

I would guess this is a glitch rather than a true surge which could be caused by the CT or data cable picking up an external emf signal. You should be able to confirm by looking at your energy input via your meter and account.

View original

7 replies

BPLightlog
Plan Zero Hero
Forum|alt.badge.img+5
  • Plan Zero Hero
  • 2765 replies
  • Answer
  • April 9, 2025

Hi, I presume you’re looking at the spike in the top screenshot for 9/4.

At the level of 145kW, that wouldn’t be possible via a domestic supply and you can see the spike at the same level each side of zero. (Domestic supplies are limited to 80 or 100A for single phase which equates to approx 23kW)

I would guess this is a glitch rather than a true surge which could be caused by the CT or data cable picking up an external emf signal. You should be able to confirm by looking at your energy input via your meter and account.


Forum|alt.badge.img
  • Author
  • Carbon Cutter***
  • 5 replies
  • April 9, 2025

Thank you for the reply. I presumed it was some form of glitch or we would have gone up in smoke! Any idea how we stop it? Thank you very much


Peter E
Plan Zero Hero
Forum|alt.badge.img+1
  • Plan Zero Hero
  • 341 replies
  • April 9, 2025

As ​@BPLightlog said it has to be an instrumentation error either in the electronics or a processing error in the software. Suggest you contact the manufacturer to see if they have seen anything like this before. They might have a hardware fix or software update that can be applied.

 

If it occurs infrequently and radomly it is highly unlikely the manufacturer will have an explanation or a fix for it. Is there a forum where you can ask other users of the system?

 

Peter

 


BPLightlog
Plan Zero Hero
Forum|alt.badge.img+5
  • Plan Zero Hero
  • 2765 replies
  • April 9, 2025

If it happens very infrequently it’s safe to ignore .. you can just check the position of the CT and cabling just to ensure they haven’t slipped. Ours look like this 

You can see that the twin cable connecting to the CT doesn’t use twisted pair cable (twisted pair cable is often used in data connections to reduce external electrical noise). It is therefore susceptible to nearby pulses such as power tools or generators


Peter E
Plan Zero Hero
Forum|alt.badge.img+1
  • Plan Zero Hero
  • 341 replies
  • April 9, 2025

Just checked historic lightning records for this morning and there is nothing recorded in the UK but it doesn't record everything.

https://www.blitzortung.org/en/live_lightning_maps.php

 

You can select historic data data and time and watch it on a loop over a period of time.

 

Peter

 

 


Forum|alt.badge.img
  • Author
  • Carbon Cutter***
  • 5 replies
  • April 10, 2025

Thanks for all the replies. It appears, as of just now, do be back to normal. It must have been 4 days of a glitch in the display. Thanks again