Solved

Low gas pressure going into boiler - how to check if pressure coming into the gas meter is adequate?

  • 8 February 2020
  • 4 replies
  • 85 views

Had a boiler service yesterday and to cut a long story short the engineer said that that gas pressure coming into the boiler was below the minimum required. 

He said itn should be 13mb but it's 11mb from what I can gather. He advised to get a thicker gas pipe installed.

However is there any way to check if the gas pressure coming into the meter is adequate, who do I contact?

 

icon

Best answer by PeterR1947 11 February 2020, 12:45

All I can say is that the gas pipe feeding your boiler should be 15mm.

Depends where you live, but worth giving Cadent a call on 0800 0745 788 and asking if they can check your gas pressure for you, your gas meter has a regulator on it (sealed) but they should be able to increase the pressure assuming there is no other problem.

 

Peter

View original

4 replies

Userlevel 7
Badge +2

Hi @Gurpster 

 

Good question this, and I can understand you wanting an answer. 

 

We have a few engineers knocking about who are best placed to answer here. Our MVP engineer adviser is @PeterR1947 - what do you reckon? Any checks anyone other then a GSE can do for gas input pressure?

 

Userlevel 6
Badge +1

All I can say is that the gas pipe feeding your boiler should be 15mm.

Depends where you live, but worth giving Cadent a call on 0800 0745 788 and asking if they can check your gas pressure for you, your gas meter has a regulator on it (sealed) but they should be able to increase the pressure assuming there is no other problem.

 

Peter

Userlevel 5
Badge

Did the engineer check the pressure at your meter? It should be 21mbar +/- 2mbar.  The allowed pressure drop when an appliance is on is 1mbar  in the  gas pipe feeding the appliance. 13mbar  is itself way too low, its not supposed to be below 18mbar. The test port inside the appliance may be further downstream and thus have an additional loss but 7mbar inside the appliance seems excessive.

The engineer may have carried out a pressure check with gas not flowing in the pipe supplying the appliance, in which case it ought to read the same value as at the meter.

As PeterR1947 says the pipe should be quite substantial. Can you post a picture of the gas pipework feeding your boiler along with a ruler for scale?

There isn’t an easy check that customers can carry out. You could look at flame height when other appliances are turned on assuming you have other gas appliances.  Flame height is related to pressure.

;TLDR contact the engineer for more details or have a second engineer check. 

All I can say is that the gas pipe feeding your boiler should be 15mm.

Depends where you live, but worth giving Cadent a call on 0800 0745 788 and asking if they can check your gas pressure for you, your gas meter has a regulator on it (sealed) but they should be able to increase the pressure assuming there is no other problem.

 

Peter

Just gave cadent a call and an engineer will be with me shortly due to low pressure being treated as an emergency.

 

Update to follow.