How quickly do your radiators get up to temperature with a heat pump (ASHP)?

  • 5 January 2022
  • 31 replies
  • 7823 views

Userlevel 3
Badge

Having recently enabled weather dependant mode and as the temps have dropped, my target LWT is 55° today.

After 2.5 hours of pump operation this morning (outside temp 1°), the LWT has reached 49°. Does everyone else’s system take this sort of time to get up to temp? Just want to check what the norm is before raising a query to Retrofit/Daikin.


31 replies

Userlevel 6
Badge +4

Hi @mrmojorisin04 

I think it’ll depend on the heat demand from the house. Heat pumps try to maintain a difference between the flow and return of 7-8C on our radiator based systems so if you are getting a bigger drop because lots of heat is being emitted in to the house it’ll take longer to get up to working temperature. 
55C is very warm for a heat pump, unless it’s the high temperature variety, but I think your pump is the same as mine. Today mines running around 40-42C, but I’ve changed my heating schedule to 20C between 6am -10pm, 18C overnight. House stay warms and the heat pump isn’t working so hard. COP has improved too. 
my weather curve is set to 48C at -3C and 25C at 18C. 

Userlevel 7
Badge +2

Agreed, my target LWT is 42 deg, it only heats to 54 deg when doing the DHW cycle. 

Userlevel 3
Badge

Thanks for the input @hydrosam 
My heating schedule is similar: 20.5° between 6am and 10:30pm and 18° overnight.

I’ve just switched weather dependancy on and am using the default. However, I was previously using 50° fixed LWT so it seemed to make sense that it would be higher on very cold days. The pump is capable of 55°, indeed that’s what the installers left it at.

My concern is the amount of time that it is running. At 7am this morning the room temp was 19.2°. 2.5 hours later it is 19.7°. That’s still pretty comfortable but at this rate the pump will be running constantly all morning and still only get to around 21° and the cost of that is pretty steep.

At the same time, my DHW, which is on reheat is stuck at 20°, presumably because it’s waiting for the house to get up to temp first.

I don't think the heat loss in the house is excessive. Generally with a target of 20.5°, on days where the outside temp is 5°+, the pump heats the house to 22° by around 9am and then it kicks in again when the room temp has dropped to 19°, which is normally early evening.

Userlevel 6
Badge +4

With weather dependency the idea is that the pump runs slow and steady. It probably took my house a day or two to get up to a nice 20-21c but now it’s just running on tick-over with a leaving water temperature currently at 39C. As we have similar sized houses (both 4 bed) it might be useful to compare the energy the heat pump used and produced, though insulation/heat loss levels do play a big part too. You might need your compensation curve a few degrees higher but not running at 50C.
I used 28kwh elec and the pump produced 86kwh of heat. On similar days back in November I used way more 40kwh+ but the house is more comfortable now. 
DHW takes priority over heating. Reheat only mode is not an appropriate setting for our systems despite what our installers may think.  A schedule will be much more efficient in terms of daily energy usage and not detriment space heating when you need it most. 

Userlevel 3
Badge

Thanks for the input @hydrosam 

The way you describe it, your system system starts and stops all the time to maintain a steady 20-21°. Mine doesn't do that, it runs for quite a while to get to 21-22° and then does nothing for a long time until it drops to 19° ( 16-17° overnight) at which point it starts again.

The issue I have had on the other thread does seem relevant - the engineer says that without the secondary cylinder to prevent frosting of the pump, it is using energy from the pump to defrost which means less efficient heating.

I've had to run on reheat up to now as my tank doesn't keep the water hot enough to run a schedule, but it seems like as well as the frost protection issue, my pressure valve is faulty and is letting hot water out for no good reason. Hopefully that’ll be the explanation for the loss of heat and I can look at running on a schedule when it is replaced.

Userlevel 3
Badge

Hi @hydrosam

Can I just check - does your heating come on pretty frequently during the day or is it once or twice like mine (i.e. only when the house temp has dropped by >3°, which takes quite a few hours normally)?

Userlevel 6
Badge +4

@mrmojorisin04 i have mine running permanently on a low and steady setting, it’s leaving water temperature today is around 29C. I found it used too much energy to heat the house back up from a cool temperature, because heat pumps can only heat up a house relatively slowly and they need to run hard to get there.  


It’s a different operating philosophy to traditional gas/oil boilers which is overheat, switch off, cool down, overheat again. 

Userlevel 3
Badge

@mrmojorisin04 i have mine running permanently on a low and steady setting, it’s leaving water temperature today is around 29C. I found it used too much energy to heat the house back up from a cool temperature, because heat pumps can only heat up a house relatively slowly and they need to run hard to get there.  


It’s a different operating philosophy to traditional gas/oil boilers which is overheat, switch off, cool down, overheat again. 

@hydrosam Many thanks, but I’m still not sure what that means in terms of how often your pump spins up to warm your rads and how long it then runs for to get the house back up to temp.

We have similar schedules/values for our room temperature (mine is 20.5° between 6am and 10:30pm and a little less overnight). On colder days, if I let it, then my pump would be apinning from 6am to midday to heat the house from 19° to 22°. One time when I did let it, the cost was £5 by midday. This was with the LWT set to 49°. I can imagine that if I had it lower, then it would basically be running all the time without ever reaching the desired temp and I can’t see that would be more efficient. Or maybe it would?

Once it's up to temp, there’s nothing that I deliberately do to stop it running. It's just the hysteresis that means it stops running for a while until the room temp drops enough for it to kick in again. This usually means that it spends 5/6 hours doing nothing (similar to a gas system).

I guess basically what I am asking is if your pump is constantly spinning and if so, do you find that your bills are reasonable when doing so (e.g. <£5 per day even on cold days). Or maybe you have set your hysteresis to less than 3° so that it starts and stops more frequently?

Userlevel 6
Badge +4

Hi @mrmojorisin04 I’ll try and explain a different way

I have set up my system so that its running as long as possible through the day by adjusting the weather dependant curve to thresholds that keep the house temperature just below that which would ‘trip’ the thermostat to turn off the pump.  So to answer your question of how many times a day does my pump spin up, it does this once at 6am and continues running through till 10pm, when it drops to a lower running temperature overnight but it is still running continuously through the night (at the moment whilst it’s cold). (There is a little bit more to the running continuously point because the pump cycles on/off a bit but that is another subject relating to defrost cycles, etc)

To do this you need to adjust the weather dependant curve and the schedule. It is a bit of trial and error before getting it right which will be why it’s much easier for an installer to follow the traditional approach of heating a house with just a thermostat and a hot water temperature flowing through the radiators. If you don’t have a technical background like me, or don’t have the time, or just aren’t interesting in adjusting the system settings, then it would require more intervention from the original installer. With the Mitsubishi systems (that I/we should have got:thinking:  and signed T&C’s for) these settings can be altered remotely by the installer but the functionality of the Daikin systems isn’t as good in this department.

Once I started adjusting the weather dependant curve it took my house a couple of days to settle up to a nice comfortable temperature because it needs the thermal mass in the house to catch up but once there the house remains comfortable and uses less energy to heat the house.

Savings weren’t huge for me because I’d already lowered the values in my weather dependant curve a bit but might be more significant for you if your system is running with a leaving water temperature of ~50C.

To compare my energy usage yesterday to a similar day last month.

2/12/21 (thermostat controlled) - Elec used by pump 23.3kwh, heat produced 61.6kwh, COP 2.64 Internal house temp failed to get to desired except late evening. On my tariff that’s £4.54 per day.

11/12/21 (weather dependant controlled) - Elec used by pump 19kwh, heat produced 596kwh, COP 3.14 Internal house temp 20C all day. On my tariff that’s £3.70 per day.

My worst elec usage before changes was:

28/11/21 - 42kwh used, 102kwh produced, COP 2.4

After changes:

08/01/22 - 38kwh used, 108 produced with COP 2.84.

I don’t have external temperature data to compare the two days but they were both close to 0C if I remember correctly for a lot of the day, during the second example the house was warm, back in November the house was cold for a lot of the day. 

If you want to start adjust the weather dependant settings I can try and help but I don’t know how that sits within the terms of our trial, and I’ve now owned up publicly to adjusting the weather dependant settings on my system which might get me… 

And remember I’m not a trained heating engineer just a layman who thinks he’s figured out how the big technologically advanced (but not as advanced as it should be) lump of kit installed in his house works.

 

 

Userlevel 3
Badge

That’s perfect, thanks @hydrosam 

It’s really interesting that you have got your system running almost continuously by effectively never reaching the thermostat setting. I wonder if reducing the hysterisis to say 0.5° (if that were possible) would achieve something similar?

I don't think our actual costs are that far apart as the figures that I quoted are for the whole house, not just the heating. My strategy so far has been to get the house warm during the warmest part of the day and limit the pump use during the colder periods. So I manually turn down the thermostat in the morning when it has got to around 20° rather than letting it run for hours to get to 22° and then during the afternoon I let it go to 22°, which generally keeps us warm enough during the night (supplemented with a log burner!).

I do still think/hope that once I have the additional cylinder installed that will take care of defrosting the pump, then it will run more efficiently during the cold snaps as it will utilise the energy in heating the water rather than defrosting the pump.

Userlevel 6
Badge +4

I think reducing the hysteresis will make things worse. It’ll cause the pump to stop more often. I had this issue with my Honeywell remote thermostat and just as the pump was getting to an operating temperature if would turn off and have to restart again. 
A better approach is to reduce the weather curve and allow the system to take longer to reach the thermostat temperature. 
What thermostat do you have controlling your pump?

Not related but your tag at the bottom describes your pump as using R32 refrigerant but the pump model number is the same as mine which uses the older R410a. I think one of those things is incorrect. 

Userlevel 3
Badge

I think reducing the hysteresis will make things worse. It’ll cause the pump to stop more often. I had this issue with my Honeywell remote thermostat and just as the pump was getting to an operating temperature if would turn off and have to restart again. 
A better approach is to reduce the weather curve and allow the system to take longer to reach the thermostat temperature. 

Fair enough, makes sense I think

What thermostat do you have controlling your pump?

Just the standard Daikin one

Not related but your tag at the bottom describes your pump as using R32 refrigerant but the pump model number is the same as mine which uses the older R410a. I think one of those things is incorrect. 

You caught me! Not sure why I did that, but it's gone now.

 

Userlevel 7

Hi heat pumpers,

 

@mrmojorisin04 @hydrosam please let me know if anyone objects to me moving this interesting thread into the public Smart Home category...

 

Have any of you noticed your fancy new heat pump badges? We thought this would help members to know who they’re speaking to and what sort of questions to ask based on their green tech.

 

@hydrosam you have allllll the badges thanks to your smart home!  

 

Userlevel 6
Badge +4

@Tim_OVO no problem with it being moved from here. I have seen a lot of issues on other forums of people trying to operate their heat pumps like boilers, for short periods at a high temperature. If this thread help informs someone it’s not the best approach then that will be a win. 

I’m afraid one of my badges has to be removed 😭. I don’t have an energy storage battery, I just want one. If OVO want to help fund a battery to make my heat pump use greener electricity then I’d be very happy to take that badge back 😁

Edit, just worked out thanks to @juliamc that the badge I thought was a battery was a smart meter so I keep all my badges. I still would like a battery to power my heat pump though… 

Userlevel 7

no problem with it being moved from here. I have seen a lot of issues on other forums of people trying to operate their heat pumps like boilers, for short periods at a high temperature. If this thread help informs someone it’s not the best approach then that will be a win. 

 

 

Completely agree, Hydrosam - I’m expecting this to be a popular search term over the next few years. 

Userlevel 3
Badge

@Tim_OVO no problem with it being moved from here. I have seen a lot of issues on other forums of people trying to operate their heat pumps like boilers, for short periods at a high temperature. If this thread help informs someone it’s not the best approach then that will be a win. 

I’m afraid one of my badges has to be removed 😭. I don’t have an energy storage battery, I just want one. If OVO want to help fund a battery to make my heat pump use greener electricity then I’d be very happy to take that badge back 😁

Edit, just worked out thanks to @juliamc that the badge I thought was a battery was a smart meter so I keep all my badges. I still would like a battery to power my heat pump though… 

@hydrosam 
The problem is, unless you go to the extremes of experimentation that you've had to go through, then the heat pump does end up working pretty much like a boiler. In my case, as I've described previously, it comes on two (maybe three) times a day with long periods in between where everything cools back down. The only real difference to. a boiler is that the radiators don't get anywhere near as hot, so it takes a lot longer.

Are you concerned at all that your approach may shorten the life of the pump with it being in pretty much constant operation?

Userlevel 7
Badge +2

But @mrmojorisin04 they’re designed to run continuously at a low temp.

Userlevel 6
Badge +4

Heat pumps are designed to run continuously as @juliamc says. The part the doesn’t do heat pumps good is multiple start/stops of the compressor, by this I mean multiple start/stops per hour which could be triggered by a poorly setup thermostat as mine was.
But you are quite right @mrmojorisin04 that I have been analysing my system more than most and installers simply don’t have the time to help owners optimise their setting, so if a thermostat can work then that’s the easy solution. The problem is most owners don’t know whether to, or how to, check whether the cycling is going on. And most installers won’t revisit to check  

I’m led to believe that on the continent this level of optimisation from the installer is common and systems are designed to operate with weather compensation mode enabled and run as efficiently as possible. (Caveat, this is anicdotal and something I’ve picked up from other forums) 

Userlevel 5
Badge +2

@hydrosam there is a great video just been posted by Heat Geek on YouTube which is aimed at users rather than installers, in short giving tips as to how to get the best out of your pump.

I have been experimenting with all day running, but the weather has been to warm of late to get much of a steer. One thing I have learned is to set the room thermostat up to a reasonably high temp, say 24°, and the curve down to the point that the radiator and room heat loss design run the show. A couple of weeks back I ran for two days at curve -2/40 to 25/25 but again the weather was good, and solar gain heated the house quite high (too high I would say).

we have a few cold days coming up so giving it another try.

Hoping to join you on March 2nd, but work keeps getting in the way. Doh!

Userlevel 1
Badge +2

Interesting, I’ve just set all my weather compensation numbers for eco Dan but cannot figure out how to set the room temp. When I go into schedule it’s blank and doesn’t let me add. I can only edit when it’s in room temp mode not compensation?any ideas anyone please. Cop is 3.5 currently but flow temp was 55 and only had heating on 4-9 pm at 18 degrees but costing £289 a month in winter. House not warm…. Maybe at 6 pm… but short lived.

Userlevel 6
Badge +4

@Jenp i don’t know Mitsubishi systems myself, @M.isterW might be able to help with specifics with the EcoDan. If running in pure weather compensation you may not be able to set indoor temperature, you tweak the weather compensation to achieve your desired indoor temperature.

55C is a really high flow temperature though. What figures did you use in the settings? Depends on house insulation and whether you have radiators or underfloor heating but I’d recommend a good upper end, around -2C outside to be 45C max for radiators and 35C max with underfloor. Mine is down at 40C at -5C outside. Set the low end of the weather compensation to 30C at 20C outside for rads, 20C at 20C for underfloor. 

But with lower flow, but more efficient, you will require a longer running time. I run my system for 20.5C from 06:00-21:30. It usually takes 2-3 hours to get up to 20.5C 

Userlevel 7
Badge +4

I think you need to spend some time learning about the best way to run a heat pump and how to operate the controls on the Ecodan control panel. Your posts are really confusing and you're talking about mutually exclusive settings - you can't have your flow temp set to 55 degrees and also be using weather compensation (unless the 55 degrees is for your DHW).

Userlevel 1
Badge +2

Thank you Sam that's very helpful. Misterw, not helpful, sam agrees that flow temp should be lower, not. High at 55.. I aplogise for ‘confusion’ in my post but this is my understanding and need help and advice. I have set wc up as per numerous blogs and heatgeek videos, flow temp according to them should be the lower the better for efficiency so I'm not sure why you are confused? I'm am grateful for help not sarcasm 

Userlevel 5
Badge +2

@Jenp i echo @hydrosam - it looks like you are getting there using weather comp but that setting only beneficial when running all day or for long periods.

 I used to run my system off the room stat but have since ditched that, opened all TRVs fully (other than main bedroom)and run the heating 0500-2100. Room stat is set at 22° but weather curve set to give me 19-20°, that way the heating cuts off only if gets above 22° and too uncomfortable for us. Max radiator water temp is set to 40° at -3.

you may well find that running like this your home will be toasty warm 24/7 AND your heating bill is lower. Now that’s magic!

Userlevel 1
Badge +2

Thanks Jason, Appreciate you taking the time to share this info… it takes a couple of hours generally.. it’s never really comfortably warm probably because of the way we’re using it. The water flow is only 16, I’ve read it should be minimum 19 so this could be why it takes 2 hours to get warm. I’ve set it to weather comp curve.. what I don’t understand is how do you run it 5_9pm. And I can longer see a room temp on the stat when it’s set to curve operation. I’ve set it at 40/0 and 25/15. I can only get room temp figure back if I run it from the room stat setting within the control panel. I maybe need to ask Mitsubishi. How do you know yours cuts off at 19? Do I need a separate room stat maybe, as this doesn’t show on eco Dan fc6 panel, hence my confusion. If yours goes off at 9 pm isn’t the ashp working overtime at 5am to get rooms warm again? I have cop of 3.5 but heat geek gets a massive 5.9 in an old cold uninsulated  office, how good is that! I have of Solar too so can use that to fund the cost during the day  when it’s cold but sunny.  Any one out there that can help with this set up of eco Dan fc6 - welcome, huge thanks Jason!

Reply