Can I go from two electricity meters to a single Economy 7 meter?


Badge

I’m currently with SSE but hope I can get an answer here as they have been taken over by OVO. I have two separate electricity meters, one for standard rate, and one for storage heater and hot water, the latter being controlled by a clock which gives two separate charging periods.  We don’t use the heater except for background (low rate is about 45% total usage) and I think Economy 7 would be cheaper.  Is this possible to move to a single E7 meter (smart if poss) and would there be a charge?  The whole system dates from the 1960s and so far as I know the only change has been two new meters a few years ago.  Picture of distribution board attached.

 

icon

Best answer by Transparent 29 May 2020, 13:44

Hey @johnlbrooks - that’s an “interesting” historical electricity fuse-board!

Your initial question is reasonably straightforward, although there are some alternatives to consider.

But the photo raises some other factors which are worthwhile considering… particularly around the area of safety.

 

1: Let’s deal with the split tariff and dual meter question first:

Yes, the two meters and clock could be replaced with a single Smart Meter. Most domestic Energy Suppliers would probably fit a “5-terminal” meter. It has two “live” outputs which can be energised at different times according to the tariff-rules you opt for.

OVO are currently evaluating/testing a 5-terminal meter, which should be available for installation soon. See comments from @Nancy_OVO here.

 

There is an alternative option using a standard 4-terminal Smart Meter and some “smart” Dimplex Quantum storage radiators controlled by the Kaluza Platform.

I described this scenario to another customer here just a few days ago.

Since your immersion heater is a similar device, this could also be used with the same control method to make use of cheapest-rate electricity. I’d need to do a bit more research to check how this could work.

 

2: Safety of the existing installation:

a; The larger silver isolator switch at top centre looks like the mains incomer. We wouldn’t fit that now. Your local Distributed Network Operator (DNO) needs to be asked if they could change this to the usual 100A Service Fuse.

If you don’t know who is your DNO, fill out your Forum Profile and I’ll work it out for you.

 

b; The green earthing wires are too small. They need replacing with 10mm² green/yellow wire and your earth connection (copper stake?) checked for compliancy. This requires a local electrician. I’m unsure if OVO would be prepared to change you to a Smart Meter unless you had adequate earthing.

 

c; Your only safety (earth-leakage) trip appears to be on the input to the fusebox feeding the storage radiators. There’s no RCD that I can see on your lighting/power circuits. As the house wiring is old, there’s an higher chance of faulty wiring which could cause damage, but fail to blow the fuse. Not good!

Personally I’d be asking a local electrician to quote for a new “split load” Consumer Unit. These come ready-built with two RCD (safety) trips and a range of MCB trips which replace the present set of fuses.

 

The Consumer Unit here has ten MCB trips of a mix of different Amp ratings. There is a wide range to choose from. This one I found on the website of the electrical wholesalers, TLC Direct.

View original

17 replies

Userlevel 4
Badge

Hey @johnlbrooks, welcome to the forum!

 

We’ve got a whole bunch of great experts on this forum that would be able to help you with any questions you have.

 

@Transparent is a very knowledgable ninja, and is currently on here fairly often - Transparent, would you care to give your 2 cents on this one?

 

Thanks!

Userlevel 7
Badge +3

Hey @johnlbrooks - that’s an “interesting” historical electricity fuse-board!

Your initial question is reasonably straightforward, although there are some alternatives to consider.

But the photo raises some other factors which are worthwhile considering… particularly around the area of safety.

 

1: Let’s deal with the split tariff and dual meter question first:

Yes, the two meters and clock could be replaced with a single Smart Meter. Most domestic Energy Suppliers would probably fit a “5-terminal” meter. It has two “live” outputs which can be energised at different times according to the tariff-rules you opt for.

OVO are currently evaluating/testing a 5-terminal meter, which should be available for installation soon. See comments from @Nancy_OVO here.

 

There is an alternative option using a standard 4-terminal Smart Meter and some “smart” Dimplex Quantum storage radiators controlled by the Kaluza Platform.

I described this scenario to another customer here just a few days ago.

Since your immersion heater is a similar device, this could also be used with the same control method to make use of cheapest-rate electricity. I’d need to do a bit more research to check how this could work.

 

2: Safety of the existing installation:

a; The larger silver isolator switch at top centre looks like the mains incomer. We wouldn’t fit that now. Your local Distributed Network Operator (DNO) needs to be asked if they could change this to the usual 100A Service Fuse.

If you don’t know who is your DNO, fill out your Forum Profile and I’ll work it out for you.

 

b; The green earthing wires are too small. They need replacing with 10mm² green/yellow wire and your earth connection (copper stake?) checked for compliancy. This requires a local electrician. I’m unsure if OVO would be prepared to change you to a Smart Meter unless you had adequate earthing.

 

c; Your only safety (earth-leakage) trip appears to be on the input to the fusebox feeding the storage radiators. There’s no RCD that I can see on your lighting/power circuits. As the house wiring is old, there’s an higher chance of faulty wiring which could cause damage, but fail to blow the fuse. Not good!

Personally I’d be asking a local electrician to quote for a new “split load” Consumer Unit. These come ready-built with two RCD (safety) trips and a range of MCB trips which replace the present set of fuses.

 

The Consumer Unit here has ten MCB trips of a mix of different Amp ratings. There is a wide range to choose from. This one I found on the website of the electrical wholesalers, TLC Direct.

Badge

Dear @Transparent 

Many thanks for your answer and I note your safety suggestions.  Unfortunately, I have realised that I left out a couple of facts from my original question.

I’ve marked up my photo with the wiring layout that was previously hidden.  The biggest omission is that (I have been told) we have 3-phase power that enters the board at the numbers 1, 2 & 3 in the picture.  Those are hefty copper coated wires. The grey and black boxes they enter are 100 amp fuses. To my uneducated eye it looks like phase 3 supplies the off peak system.  The heating is fan driven hot air through underfloor ducts from a single large storage block in the centre of the house.  The grey box under the smaller fuse box is, I think, a RCD for the lighting/power.

Does any of this alter your views.  Many thanks for your patience

Userlevel 7
Badge +3

Thanks for the clarifications @johnlbrooks and I’m pleased to find someone else who draws on top of photos like I do!

You having 3-phase would account for the size of the isolator box for the house incomer at top-centre. I’m still unsure what is the function of the smaller silver isolator at top-left, but it doesn’t matter for this discussion, so let’s press on.

I’d left out a space in my earlier reply, which meant you couldn’t click on a link taking you to the Topic where @Nancy_OVO mentioned 5-terminal meters. I’ve now re-edited it above, but I want to repeat it again here because it just happens to be within a recent discussion about a house with 3-phase electricity!

For the sake of others reading this at a later date, in John’s photo above, his labels 2 & 3 are the two phases, each entering the top of a 100A Service Fuse. Label 1 is the neutral connection which eventually goes to the larger consumer unit (bottom-right) supplying the main house circuits.

Your ducted hot-air heating sounds wonderful. This is obviously not going to be replaced by few Dimplex Quantum storage radiators! So scrub that suggestion.

The “correct” way to do all this would be to have two separate 45A ALCS devices connecting your heat-storage block and your hot-water immersion heater respectively. Each could then be driven by the Kaluza Platform I mentioned earlier.

Those devices don’t yet exist. But the electronics could readily be derived from the existing V2G charger, currently being trialed in 400 homes in GB.

There are other relevant Topics to read here, such as this one about Load Shedding and ALCS, and ALCS control from SMETS2 meters.

What we really need is a new Topic here on the Forum where we can run such concepts past a senior manager at Kaluza.

At this point I tag @Tim_OVO and say: “the ball is in your court. please do what you can to arrange this!”.

 

And John, I’d like a bit more information from you please:

  • Fill out your Forum Profile so we have your basic background information
  • Do you have gas (grid-connected or in bottles/tank)?
  • Do you have any renewable energy sources such as solar panels?

Thanks.

Badge

Thanks.  Profile updated, have mains gas used for cooking, no renewable source.

Userlevel 7
Badge +3

Sorry, I forgot to respond to the comment about the RCD for the main fusebox.

This may do what’s required of it… assuming it’s rated to trip at 30mA of current imbalance.

However, using a single device like this for the whole house isn’t a great way of providing a protection system which is “friendly”. As it’s presently wired, as soon as a faulty device gets plugged into a socket, the trip operates and plunges the entire household into darkness! :scream:

That’s why I was suggesting a split-load consumer unit as a basic minimum.

Userlevel 7
Badge +3

Ah… we both responded simultaneously.

Thanks for the Profile information. I had (incorrectly) guessed that you were in Scotland based on the type of electricity supply and ducted hot-air heating!

I’ll have a think about the implications of you having gas, but no renewable sources (yet). The best strategy for future energy needs is to spread your usage across multiple devices/sources. I have a hot water cylinder with three different energy inputs for example.

Badge

Payback period is quite important at my age!  The main reason for wanting E7 is so I can switch supplier freely.  Having 2 meters means, as I expect you are aware, that I am stuck with SSE because no other supplier will accept a switch.

Userlevel 7
Badge +3

OK @johnlbrooks so I’ll try to avoid suggesting strategies with a 20-year payback time! :wink:

Do you happen to know the current or power-rating for that central heat-storage block?

I’m wondering if it’s essential to retain two phases, or if it’s possible to run everything from a single-phase meter.

 

Secondly, you may not now be as “stuck with SSE” as you suppose. As a result of the acquisition, all SSE’s problematic sites have now become OVO’s responsibility!

If one of your existing meters or the time-clock were to fail, they would have to be replaced anyway.

Even if OVO used existing technology and installed one their approved 5-terminal SMETS1 meters, they are scheduled to be upgraded to SMETS2 functionality and migrated across to the National Smart Meter Network as of 28th June.

Badge

Thanks @Transparent, The heater is a Creda Comfortaire.  I’m slightly confused because according to the rating plate on the heater it is 5 kw off peak, 250 w on peak (which I guess is for the fan), but the service leaflet I inherited from the previous owner says that the minimum model Comfortaire heater is 6 kw!  I suppose we go with the rating plate.

I’m not sure exactly what you mean as to not being “stuck”.  I understand that OVO have taken over, but surely unless I get a single meter as opposed to two I am now stuck with OVO instead of SSE?

Thanks again for your interest.

 

Userlevel 7
Badge +3

That’s interesting @johnlbrooks - so the Comfortaire has two separate electrical feeds; one for the heater element which is controlled by the off-peak time-clock, and another for the fan, which must remain “live”.

I’d be surprised if it took as much as 250w to run the fan and any associated electronics/sensors. I have a twin-fan MVHR (mechanical ventilation with heat recovery) unit, and that only draws 80w peak.

However, 5kW is pretty small for a whole-house hot-air system. I can understand why it’s fed from a timeclock to enable you to benefit from cheaper-rate electricity. But I have no idea why this would need to be on a separate phase!

To put this in context, most electric shower units would be rated around 10kW and we don’t insist those houses use 3-phase.

Creda is also now a division of Dimplex, who have licensed OVO’s control system for their Quantum Storage Radiators. I wonder if the controller could be made available as a retro-fit to your Comfortaire? You could try emailing them to enquire.

So my current assessment (pun intended!) is that you could ditch one of the phases and have an ordinary single-phase SMETS2  Smart Meter with an Economy-7 tariff.

Just be aware that it is common practice for customers with E7-tariffs to pay a higher-rate per kWh for their standard electricity. So E7 isn’t always viable.

And that’s why I think you might wish to avail yourself of a smart-tariff “layer” over the top of an ordinary tariff. You’d then be fed much cheaper electricity by the Kaluza Platform whenever it bought-in low-priced energy on the wholesale market. And as it’s got weather-forecast input, you’d only be fed enough electricity for the predicted demand over the next 24 hours.

I hope I’m making sense.

Just in case I’ve missed anything, I’m going to tag @PeterR1947 to use his engineering experience on the above recommendations, and correct me as required.

Userlevel 7
Badge +2

Some great technical support here from @Transparent - @PeterR1947 will be about at some point this week as well. I’m sure he’ll have a look and see if we’ve missed anything. 

 

Those devices don’t yet exist. But the electronics could readily be derived from the existing V2G charger, currently being trialed in 400 homes in GB.

What we really need is a new Topic here on the Forum where we can run such concepts past a senior manager at Kaluza.

At this point I tag @Tim_OVO and say: “the ball is in your court. please do what you can to arrange this!”.

 

Sounds like a great idea for a topic - get this posted and I’ll make it into an article and share with my colleagues at Kaluza. Plans are in place for this already, an ‘Ask me anything’ with a Kaluza product manager. So @johnlbrooks get this suggestion in when that’s posted later this week hopefully!

Badge

Thanks @Transparent 

My system was installed in 1965 so I doubt whether any modern control system could be retrofitted.  But I could be wrong!

Very interested in your suggestion to ditch a phase and go E7 on just one.  From what you’ve said earlier I guess I’d have to pay for an ordinary E7 meter as the smart meters are not yet available.  Changing the supply to just one phase would cost even more I guess.

Userlevel 6
Badge +1

@Tim_OVO@Transparent@johnlbrooks All, the suggestions are sensible, the distribution board is a typical 1960s nightmare!  As a first, I would suggest getting a local electrician to install a split load Consumer unit as @Transparent suggested; the earth wires should be updated at the same time.  You should expect to pay between £250 and £500 for this. At least, once that is done you can feel safe and deal with the meter problem afterwards.

I wonder now you get on with the warm air heating?  The reason I ask is that in 1965 I rented a house which had that sort of heating and it was fine until the thermostat clicked off when the house rapidly went cool!  In fact, the landlord had gas fired CH installed and the warm air system deactivated.  I’m not suggesting you replace the system, Just curious as to how you find it.

Badge

Hi @PeterR1947 

Thanks for your comments.  I’ll look into making the improvements.

We don’t use the comfortaire for main heating - that comes from a large log stove in the sitting room -  the thermostat is in that room and as we leave it set at 60 degrees (F) the fan (rather noisy) only comes on occasionally, usually in the morning before I’ve made up the stove.  We also use electric convectors and fan heaters according to which room we are in.

It’s on from Oct to May and provides some background warmth to the house and particularly  the kitchen/diner where the block is located.  I’ve actually never tried to use it to provide the main heat - the previous owner said it was inadequate so since we bought the house (1983!) we’ve used the stove for main heat.  Also, the ducts don’t go to two of the bedrooms or the bathroom. 

Total on and off peak consumption is about 12500 kwh/pa of which about 45% is off peak (includes hot water).

That’s probably much more info than you wanted!

 

Userlevel 7
Badge +3

It looks like we’re all heading in the same direction at the moment, which is gratifying!

Let’s deal with a few of the easier issues quickly.

 

1: Although not ideal, it is possible to have an E7 tariff from OVO and use a standard 4-terminal Smart Meter. It takes the entire house onto the cheaper tariff for those 7 hours. That’s one reason why the standard daytime costs are higher than otherwise.

I’d prefer it to use a 5-terminal Smart Meter because that would lower the unit costs in daytime. But since OVO don’t yet offer such a tariff, we have little idea whether this is financially beneficial in your case.

And my best-of-all option would be to have a 4-terminal Smart Meter but with extra in-line Smart Switches controlled by the Kaluza Platform to run the immersion heater and the Comfortaire. That doesn’t tie you to any particular hours to have electricity fed to those devices.

 

2: Don’t worry that there are bits of the puzzle which don’t yet exist as a “final product”. The technology is already within the V2G charger and is also successfully running hundreds of those Dimplex Quantum Radiators across the UK.

We need to start that separate Topic and persuade Kaluza to put it in a stand-alone box. If they won’t do it, then there’s plenty of Far-East rivals who’ll be reading what I’ve posted here, and will be only to pleased to take Kaluza’s market from them!

 

3: It’s likely that the Comfortaire lacks the levels of insulation which we would now use to surround the ducts. That could be remedied piecemeal, depending on accessibility, and thus improve efficiency.

You now know I’ve got a working (self-installed) MVHR unit to which I still have further ducts to be added. I’ve installed a secondary heat-source in this, using a small (150mm square) radiator in the flow-pipe which is fed from the same water at 45ºC that gets sent to my underfloor heating (UFH) pipes.

I also have a vacuum-tube solar hot-water system. So if we get a cold but sunny day in mid-winter, my UFH and ducted warm-air are supplemented from the solar input.

If I’d bought a house with a Comfortaire like yours, that’s exactly the sort of strategy I’d use. Keep the ducts and add another heat source!

 

4: I suggest you email hello@ovoenergy.com and make an initial enquiry as to having a Smart Meter and an Economy-7 Tariff.

Give the URL of this Topic so that they can read what we’re discussing.

Mark the email “For attention of SMETS Engineering Team” so you don’t end up with some terribly polite reply from an ordinary member of Customer Services who hasn’t a clue what 3-phase and 5th-terminal actually mean!

I think the costs will be much less than you think.

The Smart Meter is free. The Installer will have the 100A Service Fuses open anyway, and will simply  remove the wire which feeds one of them.

You could also have your local electrician there at the same time so they fit the new tails into a new split-load Consumer Unit.

I’m struggling to think why this should cost anything more.

Badge

Thanks @Transparent 

What a lot to think about!  The ducts are mostly under the solid floor so inaccessible.

Option 4 looks the immediate way forward and i’ll also contact an electrician.

Very many thanks.

Reply