Solved

Electric Vehicle (EV) charging and thunderstorms - Is it safe/recommended?

  • 10 August 2020
  • 51 replies
  • 4261 views

Userlevel 7
Badge +3

Given the upcoming weather, and the fact all my ev charge plugsĀ  and all public chargepoints all say "donnot use in thunderstorms" I was wondering:

A) Why

B) What is the real risk

C) Will anything prevent it actually charging

D) If you have a virtually flat battery in a storm, what should you do if you need to keep driving!

E) Is it (more?)dangerous with a v2g?

icon

Best answer by sylm_2000 10 August 2020, 20:41

View original

51 replies

Userlevel 7
Badge +2

I wasnā€™t aware that EV chargers advise not to be used in thunderstorms. I donā€™t see how the risks would be any different to using any other electrical device in the home during a thunderstorm. Moreover the car itself has better isolation due its rubber tyres.

Anyway, there are several other Topics here on the Forum where weā€™ve discussed lightning surge suppression and what is or isnā€™t present in the V2G Charger.

V2G Charger stopped working - No Power

OVO Smart charger stopped working

V2G charger tripping RCDs

Curiously Kaluza havenā€™t yet come back to us to confirm what surge protection is present in either of the Indra chargers they install. It would be interesting to hear fromĀ @Bobby_OVO about this.

Userlevel 7
Badge

Maybe its a way to cover themselves. But I have charged my Leaf in all kinds of weather conditions and itā€™s still driving beautifully with above 95+ SOH battery. Zapping it with a few rapid charges has helped balance the battery too! Not sure if you knew this @JequinlanĀ 

Userlevel 7

Some good questions here, and I think we have the community members here to answer them all!Ā 

Ā 

Forgive the spam tagging but Iā€™m going to mention all of our confirmed ā€˜EV volunteerā€™ badge earners for a bit of knowledge pooling:

Ā 

@IbrahimEVĀ @sylm_2000Ā @NeilGĀ @jp1Ā @AndrasĀ @D10hulĀ @DarrenGĀ @MikeyoungĀ @PeeteeĀ @aaronrĀ @PeterR1947Ā @DelboyĀ 

Ā 

Userlevel 7
Badge +2

My guess is that itā€™s to prevent a lightening strike on the house (very unlikely but not impossible) travelling through the mains to the charger through the cable into the car blowing all the electronics and possible the main battery?

Obviously, when unplugged, the car is a Faraday cage and therefore safe?

Userlevel 3
Badge

I am sorry but this is all a bit of an EV myth and totally incorrect.

  1. Charging a car whether at home or public charger in a thunderstorm is no less safe than actually you being out in that thunderstorm. Assuming you are physically outside then you are likely to be a preferred path to ground for lightning than the charger or the car.
  2. As above the real risk is that you are providing the prefered path to ground by being physically outside.Ā 
  3. There is nothing to prevent the charging from occuring during a thunderstorm. That said lightning can disrupt power from the sub station if it is ā€œtrippedā€ due to a strike. It may also be possible for network connections to be impairred that could impact a public charger.
  4. If I had a low battery during a thunderstorm I would probably pull over and wait in the car till the storm passes. Cars act as faraday cages so are safe places to stay. Getting out of the car, say to charge, puts you in harms way. As previously stated that has nothing to do with car or charger just the fact you are physically out in the open.Ā 
  5. V2G chargers have to pass the same stringent tests as anyother commercially available charger so should have the same level of safety.

They always say you should not drive a Golf in a thunderstorm as that is dangerous, or is that you should not play golf ā€¦ā€¦ā€¦.Ā  :-)

Userlevel 6
Badge +3

Agree with much said above.Ā  Electricity will find the least path of resistance, therefore, V2G chargers which I remember from my installation was tested for earthing.

I had an earth rod fitted at the time of installation of my first EV charger 5 years ago and it was the same earth which was used for V2G.

As part of the install, it is an essential safety check and that should put you at ease in using your charger during turbulent weather. Over the last five years I have used the EV charger come rain, snow or sunshine - no problems.

Humans on the other side are not ā€œgroundedā€Ā 

Userlevel 3
Badge +1

My thoughts are that charging is probably notĀ the problem, but the earth connection It provides probably will be. Actually disconnecting the car would probably be. The connection to earth will mean the car is no longer insulatedĀ and isolated. The issue will be that if the local grid or car get struck, a very large potential will be placed across the network and as a result current flow and energy will be releasedā€¦.Ā the sensitive electronics in both car and charger will be toast!Ā This is why pulling plugs from wall sockets is also advisable. A friend from work had a near miss strike few years backā€¦Ā a pole not far away was hit andĀ heĀ lost all the connected electronicĀ devices in the house! Phones, TV, radios, etc..

Ā 

Userlevel 5
Badge

Indra does not list surge protection as a safety feature of the charger itself, but perhaps a separate device was installed??Ā  From the specs:

Safety Features

  • Emergency stop button: Yes

  • Short-circuit protection: Yes

  • Over-current protection: Yes

  • Isolation system: Galvanic

  • AC earth leakage protection: Yes

  • DC earth leakage protection: Yes

Userlevel 7
Badge +2

I think youā€™re on the right tack thereĀ @AndrasĀ 

There was a response here on the Forum in 2019 stating that the Indra chargers both contained surge suppression.

I then did some further research and discovered that integral surge suppression is part of the standard for the CHAdeMO connection. Thatā€™s not the same as having anti-surge protection devices for the charger itself!

Ā 

The other puzzlement I still have is the ongoing debate about the need for chargers to have an earth connection ā€œfor safetyā€.

If your house is supplied with PME from the sub-station, then adding an earth is a no-no!

Howeverā€¦

ā€¦ if the charger had integral surge suppression, then this may indeed require a path to earth because itā€™s got to find somewhere to route those pesky electrons.

At the moment I think there is a confusion being caused in the debate as to whether the charger itself requires an additional earth (stake), or whether there is a need for an earth connected (solely) to a pair of internal transient suppressors.

The hypothesis Iā€™m putting forward is that perhaps an EV charger should have two separate earths. When being installed in a house that does legitimately have an earth stake, then those earths could be combined.

Userlevel 7
Badge +2

@TransparentĀ  Regulation 722.411.4.1 states that a PME earthing facility shall not be used as the means of earthing for the protective conductor contact of a charging point located outdoors or that might reasonably be expected to be used to charge a vehicle
located outdoors.Ā 

It then lists three methods, any one of which could be used.Ā  Fitting an earth rod is the most cost-effective and quickest way to comply with regulation 722.411.4.1.

Other methods include fitting a costly isolation transformer and incorporating special circuitry in the charger which monitors the incoming supply and disconnects the charger including the earth path if a fault condition is detected, the version 2 of my zappi charger has this functionality.

Userlevel 7
Badge +2

Thanks for thisĀ @PeterR1947 ā€¦.

So presumably the suggested installation of an earth rod is instead of using the earth provided by the PME isnā€™t it?

Userlevel 7
Badge +2

Thanks for thisĀ @PeterR1947 ā€¦.

So presumably the suggested installation of an earth rod is instead of using the earth provided by the PME isnā€™t it?


Hi @Transparent Iā€™m not really sure, when I have nothing better to do, Iā€™ll take of the front of my zappi and have a look!

Userlevel 7
Badge +2

ThanksĀ @PeterR1947Ā 

To help others understand what weā€™re discussing, hereā€™s the diagram which I pictured in my head when I suggested above that an EV charger could have two separate earths.

So Iā€™ve conjectured that the case/electronics has an earth stake, and that there are internal lightning/surge suppressors to quench whatever nasties arrive via the live & neutral. These too need a path to earth.

Iā€™m not saying this is how it should be. Iā€™m merely putting the hypothesis forward for discussion.

Userlevel 7
Badge +3

So, my install doesn't have sn earth rod, it has a "Matt:e" device inline, but my understanding from installers is it does a similar job. ThisĀ was done due to the fact the cable can in theory reach a public lamp post and (I quote the engineers here) "Some idiot could put the connector to the lamp post" so I believe it essentially is the same as the rod and i guess for similar sudden changes in potential and the reason i know my voltage was often over 253V (after kaluza confirmed thisĀ issue) and hence my substation had to be adjusted is the device kept triggering normally!Ā 

Userlevel 7
Badge +3

Also, just checked this morning at the relatively new polar charger in devon and no comments about thunderstorms on that one. I think it may be just to indeed protect the v2g more (or just being overcautious, like the do not immerse laptop in water type warnings.)

Userlevel 7
Badge +2

The Matt:E device is a different strategy. It has (relatively slow) over/under voltage detection. When such an event occurs, it disconnects the EV charger from the supply, including the earth.

I agree that this satisfies the requirements for connection in a property that has a PME supply (earth provided via the Neutral, which is connected to ground at the sub-station).

Using the O-PEN device, the isolation breaker must operate within 5secs. By that time, any self-respecting lightning strike will have long since done its damage and departed. :zap:

Thatā€™s why Iā€™ve drawn a pair of Varistors in the above diagram. These should be conducting within a microsecond, thus offering a path to earth by the time the peak lightning pulses arrive.

Ā 

Userlevel 2

Hi,

Ā 

I've had the unfortunate event of a large power surge causing damage to both my car and charging unit. I'm trying to recoup the costs incurred onto insurance and also get this issue raised with others as I believe the majority of EV owners are completely unaware that this could happen.

Ā 

If anyone has any avenues to suggest they would be most welcome.

Ā 

Ā 

Cheers

Userlevel 7

Oh no, sorry to hear this, @Mateus77Ā - can you share any more info this?

Ā 

@JequinlanĀ @sylm_2000Ā @PeterR1947Ā @NeilGĀ @AndrasĀ @MikeyoungĀ and a very recent new EV owner @TransparentĀ might have some advice, but Iā€™d suggest we need a bit more info first. For example what model of EV and what charger do you have?

Ā 

This is worth a read:

Ā 

There are several other Topics here on the Forum where weā€™ve discussed lightning surge suppression and what is or isnā€™t present in the V2G Charger.

V2G Charger stopped working - No Power

OVO Smart charger stopped working

V2G charger tripping RCDs

Ā 

and this:

Ā 

Indra does not list surge protection as a safety feature of the charger itself, but perhaps a separate device was installed??Ā  From the specs:

Safety Features

  • Emergency stop button: Yes

  • Short-circuit protection: Yes

  • Over-current protection: Yes

  • Isolation system: Galvanic

  • AC earth leakage protection: Yes

  • DC earth leakage protection: Yes

Ā 

Ā 

Userlevel 2

Hi,

The EV is an Audi A3 e-tron, so one of the earlier models launched.

The charger is a Rolec unit installed by one of their approved installers with an earth rod internal to the garage I have.

Ā 

The damage was caused by a power surge locally rather than a direct strike to my property or the car.

Ā 

The car was plugged in but not actively charging. At present the only avenue I have had to escalate these failings is to raise a case with TMO and see if they determine that the warnings and systems in place are deemed inadequate to protect consumers.

Ā 

Ā 

Thanks

Userlevel 7
Badge +2

HiĀ @Mateus77 and sorry to hear of your plight.

I have lots of information I can share with you, but Iā€™ll try not to swamp you.

The damage being caused by a surge in the locality makes perfect sense to me. If you had a direct lightning strike it effectively raises the voltage of everything in your house to n-thousand volts, and then it falls again. Thereā€™s no actual potential difference across any device.

But a nearby strike can cause more serious damage. The copper conductors carrying power and telephone into your home will propagate the surge-front at two-thirds the speed of light. But the ā€˜ground waveā€™ will be delayed by the resistance of the soil and rock.

Thus any device which is earthed will see thousands of volts across it.

Ā 

I too had a couple of nearby lightning strikes yesterday. Iā€™m on top of a hill near the southwest corner of Dartmoor!

The trip connecting mains power to my well pump was ā€˜taken outā€™ but everything else continued as normal. There are three reasons for this:

  • I have a pair quality surge protection devices on the mains incomer to the house
  • I have a properly installed (and tested) earth system, appropriate for the type of mains supply from myĀ substation transformer
  • My new EV (VW ID3) does not yet have a wall-mounted ā€˜chargerā€™. I use a 32A socket, described here in a separate topic.

The reason the well-pump always trips is because it has its own second path to earth via the column of water in the pipe!

Ā 

Have a look through that other topic first, and keep going until you reach the post where youā€™ll find this diagram

Ā 

Secondly, please complete your Forum Profile page. Thatā€™s where we look to get an idea of whereabouts you are in the country.

Lightning and earthing characteristics change across the regions, so these bits of background information are useful.

Ā 

Thirdly, post back here with more specific detail of your situation:

  • does your house have an earth-stake?
  • is the feed from your substation underground or overhead? What distance?
  • a photo of your Service Fuse and electricity meter would be useful
  • detail of what damage you believe has happened to the car and the charger, with photos if relevant
  • check any wired computer network you may have. Lightning has a tendency to make networked interfaces go intermittent. They sort of work, but slower.

Iā€™ll stand by to respond again once I know more.

Userlevel 6
Badge +3

So sorry about your incident, It is an expensive lesson learnt. I write this message with unprecedented lightening, thunderstorm and rain outside today. It seems the last discussion didnā€™t reach a conclusion.Ā 

As mentioned above, my V2G install took over the lightening rod installed previously by the Rolec engineer. I do not remember being advised not to use the charger in certain weather, unless there is a fine print I have missed to read.

Userlevel 2

The installation did add an internal earth stake specifically for the charger.

The power is all supplied underground.

The surge completely fried the charging unit and the charging interface of the car.

This made the car undriveable as needed to undo the handshake removal of the cable,Ā  so thought it was still plugged in! There was no visible damage.

Ā 

My biggest issue here is that users cannot be expected to know about all the surge protection needed and regardless should be expected to leave any EV plugged in overnightā€¦

Ā 

Ā 

Ā 

Ā 

Userlevel 7
Badge +2

ThanksĀ @PeterR1947Ā 

To help others understand what weā€™re discussing, hereā€™s the diagram which I pictured in my head when I suggested above that an EV charger could have two separate earths.

So Iā€™ve conjectured that the case/electronics has an earth stake, and that there are internal lightning/surge suppressors to quench whatever nasties arrive via the live & neutral. These too need a path to earth.

Iā€™m not saying this is how it should be. Iā€™m merely putting the hypothesis forward for discussion.

Just checked and confirmed that the charger uses the Earth stake connection exclusively; use of a PME earth alone for an EV charger isnā€™t allowed under the regs.

Userlevel 7
Badge +2

You are quite correctĀ @Mateus77Ā 

Ofgem has identified the lack of knowledge amongst us consumers as a serious issue holding back the advance of low-energy and renewable-energy devices. It is the responsibility of all of us to do something about thisā€¦ a good role for an open Forum! ā€¦ and also a great pub-discussion :wink:

Please tell any local friends & neighbours that weā€™re discussing your lightning-induced surges here - especially if they also have an EV.

Likewise if you know of any local electricians. They will have an understanding of the ground/earthing characteristics in your area which will be better than that from national/regional charger installers. Iā€™d like local electricians to become aware of the sort of anti-surge devices I use and where to install them to be most effective.

Userlevel 7
Badge +2

We donā€™t yet know if @Mateus77 has a PME feed to the house @PeterR1947 ā€¦ but youā€™re quite right of course. Iā€™m heading in that direction in this discussion!

And Mateus - Peter is a qualified electrician, OK?

Reply