Solved

Does anyone have advice on why I need an additional consumer unit in meter box for EV charger?


Userlevel 2
  • Carbon Catcher*
  • 9 replies
Had an EV installer around today. Took a look around and decided it was too difficult to wire back to the existing consumer unit and the easiest option was to fit an additional CU in the meter box (the charger unit will be adjacent to it). He suggested that my supplier might be able to arrange it as the job would entail isolating the meter while the work was done.

Is this something Ovo do or could arrange and if so how do I go about it?

Chris
icon

Best answer by Transparent 19 April 2018, 10:21

Updated on 04/10/20: The info in this update was taken from this topic on ‘Who ones what’:

 

Electricity
 

Example of electricity meter setup


Distribution Network Operator (DNO) responsibilities

  • Meter tails before the cutout
  • Meter backboard
  • Cut-out (also known as 'service head'), which holds the main fuse - Its purpose is to absorb any energy surges which could damage the wiring and appliances within the property

 

You should contact the DNO in the event of:

  • Power cuts
  • Emergency relating to the cut-out
  • Exposed wiring between street and cut-out

DNO contact information can be found here.


OVO responsibilities

  • Meter - this records the electricity consumption of all electrical items in the property
  • Meter tails between cut-out to meter and between meter and isolation switch - they carry current between pieces of equipment
  • ​​​​​Time-switch (for older Eco-7 meters) - this dictates when each register on a meter records consumption

 

You will need to book an emergency appointment with OVO in the event of:

  • Meter sparking, smoking, overheated
  • Moisture in the meter
  • Meter off wall
  • Fault with meter tails
  • Exposed wiring meter tails
  • General fault with meter

 

Do this by calling us on: 0330 303 5063 between Monday to Friday 8am-6pm. Outside of these hours, dialing 105 is the next best action. See this topic for more info. 


Your responsibilities:

  • Consumer unit (also know as a fuse box)
  • All the wiring from the consumer unit into their property and appliances
  • Meter box

 

You should contact a NICEIC-qualified electrician in the event of:

  • Shocks from appliance
  • Appliance causing fuse to trip
  • Sparking, smoking, overheated appliance
  • After meter towards house

 

Here are details of electricians from the NICEIC website but we can’t recommend any specific electrician.

 

Hi @Gif,

I answered a similar question a few weeks back. Have a look at this thread first, and then post again here if you want more detail.

As you haven't yet filled out your Profile for this Forum, I can't tell you which Distributed Network Operator covers your area. But there's a PDF about New Connections which you can download from here and it has all their contact details in it.

You shouldn't really need to contact the DNO yourself because it's the qualified electrician they need to liaise with, but they're usually very helpful. There's no harm in calling them to ask for clarification if you need it.
 

View original

14 replies

Userlevel 7
Badge +2

Thanks @Bigstee, and for those readers seeking a translation….

MOCoPA = Meter Operation Code of Practice Agreement

 

I live a rural part of the Westcountry and have been party to telephone calls between local qualified electricians and our [color=#3070c0]DNO[/color] (Western Power) over the years. It is usually the case that WPD are indeed present when it is necessary to pull the fuse. But I have witnessed occasions where the response is “We can’t get to you for another half-hour yet; pull the fuse and continue your work in the meantime.”

Perhaps I am biassed in that such conversations have only occurred where it is a reputable local electrician, well known to the area [color=#3070c0]DNO Engineers[/color].

 

Just to clarify, an electrician is NOT allowed to cut seals and pull the main fuse, you have to work under a mocopa, to be able to do that, its illegal even tho they do ! 

Many thanks for your help, Transparent.  My consumer unit does have a 100A switch disconnector, so its seems that the engineer was recommending an additional one such as you describe.   I love the idea of doing this for £20-odd, but the Ovo person told me installation had to be done by their man (or woman), and I I imagine that most of the £158 would be for labour .

Userlevel 7
Badge +2

I think we could do with a bit more clarification please @Robin Fox.

Do you mean that your existing Consumer Unit doesn’t have a 100A Switch Disconnector within it?

Or is it that OVO require you to have another one between the [color=#A00080]Smart Meter[/color] and the Consumer Unit?

I have both… which means the Consumer Unit can be isolated without having to pull the 100A Service Fuse (and get the [color=#3070c0]Distribution Network Operator[/color] to reseal it). Here’s the separate box which just houses a disconnector:

 

If you don’t want to wait 9 weeks and pay £158 then you could surely just get a local electrician to install one similar to mine in the photo?

Although I bought a separate switch and enclosure, you can now get an all in one unit, designed for just such a scenario. Here’s one available from TLC-Direct at £13.45 +VAT.

 

Obviously you first need to confirm with OVO that such a unit would achieve what they’re after. Direct them to read this Forum post if it helps.

After I signed on to EV Everywhere, Charged EV gave me an appointment for installation about 5 weeks hence.  A engineer arrived on the appointed day, but said he had come just to do a survey. He hadn’t seen the information and photos I had sent ChargedEV.  After looking at my system he said a main isolation switch would have to be fitted before the charger could be installed.  On the phone, Ovo said this would cost me £158 and the earliest appointment they could offer was about 9 weeks away. 

    This is a gentle warning to others that the installation process may be neither fast or free.  A lot of time could have been saved if I had been asked, at the start, whether I had a main isolation switch.  ChargedEV are not great communicators.    

Userlevel 7
Badge +2
Those LEDs sound like a welcoming message for a would-be vandal @Gif.

What about covering them with a laminated sign:


WARNING - High Voltage:


Danger of death
Isolate at internal switch before disconnection



😛
Userlevel 2
They managed to use the existing CU after a bit of trial and error regarding access but the critical thing was, they came ready to install a new CU and to pull the main fuse and split the meter tails all on the day if plan A hadn't been possible.

The lockable units are not rocket science as it's only a simple turn key solution and not high security, more just a deterrent. You could of course use the CB in the CU to turn it off but CBs are not designed to be switches and would quickly become damaged.

That all said, on the front of the house, I cannot imagine anyone trying to freeload the charger anyway, it would be too obvious and at 7kw, they would have to be there too long to get any value out of it and they would then risk being found out. On a typical tariff, you would have to have a typical EV on the driveway for about 4 hours to fill it and even then you'd only steal about £4. Is it worth getting a criminal record for theft for that? Or even worse, the word "Freeloader!" emblazoned on the bonnet of your car in paint stripper?

The greater concern with these things in my opinion is vandalism or theft. I can see someone thinking that a charge point might be a useful thing to nick or even worse when they become commonplace, some idiot going down the street cutting all the tethered cables off to try to make £5 at the local scrappy. :@

I already have a charger installed in a garage which is good as the unit itself is out of harm's way and it is surprising how easy it is to disguise the tethered cable even when it is permanently mounted on an outside wall.

This latest charger is more of a challenge being mounted on the front of the house. I am however working on how to disguise it sufficiently such that some oik won't see it when driving past. The one thing I don't like is the fact that the manufacturers use LEDs (which can't be turned off) to signal functions to the user. This makes them very visible at night. 😞
Userlevel 7
Badge +2
That's good to hear, @Gif. Full marks to Chargemaster :)

Did you actually have a new/second Consumer Unit installed?

Or did Chargemaster find a way to connect the 32A feed via your existing consumer unit (or even directly off your Meter)?

Good comment about the charge-point itself being lockable. I had previously imagined it being necessary to have an isolator switch inside the house to prevent someone else "stealing" your electricity.
Userlevel 2
Well, I have to say that the guy chargemaster sent was a breath of fresh air. He couldn’t have been more helpful and the job is now sorted. Brand new 32amp lockable charge point installed and working. Full marks to them and if anyone is thinking of using them, I would highly recommend it.:D
Userlevel 7
Badge +2
Your comment raises a wider point of concern, @Gif.

There are several other Topics on this Forum where consumers have been complaining about the length of time they have had to wait for Smart Meters to be installed. There is a shortage of trained installers, with some geographical areas faring worse than others.

But the Smart Meters themselves are the forerunners of any number of smart devices which require installation by properly qualified engineers whose skill-set must be more extensive than that of an ordinary electrician or gas-fitter.

You've highlighted difficulties in getting a domestic EV Charging Point installed.

Next it will be Home Storage Batteries.

Then we'll need solar-panels rewired to directly feed those Storage Batteries instead of using their own inverters for Grid-connection...

... followed by Smart Washing Machines and Smart Freezers, using electricity only when it's below a defined cost-per-unit.

This new technology all requires installers who are trained in gas, mains electrics, wireless communications, software configuration and basic electronics diagnostics. That's quite a list, even though the depth of knowledge in each field may not be great.

I note that OVO are committed to having their own team of Meter Installers... which is wonderful.

But the need won't stop once we all have those Smart Meters.

It would be wonderful if we could just email OVO and get a site visit from a single engineer who can install "all things smart".

How much easier that would be than the problem you currently face, having to get three firms to coordinate their actions:
  • local electrician
  • Western Power (your DNO)
  • EV Charger-point installer

Let us know how your EV Charger installation goes. We may all have lessons to learn.
Userlevel 2
Thanks for that and understood. You wouldn't believe how hard it is to get someone to install a charge point for you if it's anything other than a quick simple job. I'm beginning to have an inkling that there may be an incentive with the government grant to only take on the simple ones to maximise profit and the others can go whistle!

Looking for a few more local people now who are on the list and may be slightly more customer focussed shall we say!

That said, before that I have Chargemaster coming on Tuesday next week so we'll have a laugh at what they say. I've told them until I am blue in the face that it might need some innovative thinking but I'm not confident they have been listening at all.

Who knows, they may surprise me and actually do something radical like help me.
Userlevel 7
Badge +2
Hi @Gif,

Yes, you can have two Consumer Units fed from the same separate isolator switch. That's the way I'd do it.

It's obviously slightly cheaper to omit the isolator switch altogether. The electrician would simply connect both CU's back to your meter. But every time an electrician needs to work on one of the CU's in future, he'd still need to snip the seal on the Master Fuse (100A) and call out an engineer from your DNO to check the installation and re-seal it.

Please ask for further clarification if you need it.
Userlevel 2
Sorry for the delay in getting back on this and thanks for the reply. Been up to other things and still no charger installed yet!

So I read the linked thread and fully understand why the isolator switch works. May be being thick here though but if an isolator switch is inserted in the meter box between the meter and my existing CU, how would a second CU be connected into the supply? It can’t come from the existing CU as that entails all the same access problems I have getting the supply to the charger location in the first place.

Effectively, the new CU needs to tap into the supply before the existing CU. Can more than one CU be fed from the isolator switch or would it mean tapping into the existing cables somehow?
Userlevel 7
Badge +2

Updated on 04/10/20: The info in this update was taken from this topic on ‘Who ones what’:

 

Electricity
 

Example of electricity meter setup


Distribution Network Operator (DNO) responsibilities

  • Meter tails before the cutout
  • Meter backboard
  • Cut-out (also known as 'service head'), which holds the main fuse - Its purpose is to absorb any energy surges which could damage the wiring and appliances within the property

 

You should contact the DNO in the event of:

  • Power cuts
  • Emergency relating to the cut-out
  • Exposed wiring between street and cut-out

DNO contact information can be found here.


OVO responsibilities

  • Meter - this records the electricity consumption of all electrical items in the property
  • Meter tails between cut-out to meter and between meter and isolation switch - they carry current between pieces of equipment
  • ​​​​​Time-switch (for older Eco-7 meters) - this dictates when each register on a meter records consumption

 

You will need to book an emergency appointment with OVO in the event of:

  • Meter sparking, smoking, overheated
  • Moisture in the meter
  • Meter off wall
  • Fault with meter tails
  • Exposed wiring meter tails
  • General fault with meter

 

Do this by calling us on: 0330 303 5063 between Monday to Friday 8am-6pm. Outside of these hours, dialing 105 is the next best action. See this topic for more info. 


Your responsibilities:

  • Consumer unit (also know as a fuse box)
  • All the wiring from the consumer unit into their property and appliances
  • Meter box

 

You should contact a NICEIC-qualified electrician in the event of:

  • Shocks from appliance
  • Appliance causing fuse to trip
  • Sparking, smoking, overheated appliance
  • After meter towards house

 

Here are details of electricians from the NICEIC website but we can’t recommend any specific electrician.

 

Hi @Gif,

I answered a similar question a few weeks back. Have a look at this thread first, and then post again here if you want more detail.

As you haven't yet filled out your Profile for this Forum, I can't tell you which Distributed Network Operator covers your area. But there's a PDF about New Connections which you can download from here and it has all their contact details in it.

You shouldn't really need to contact the DNO yourself because it's the qualified electrician they need to liaise with, but they're usually very helpful. There's no harm in calling them to ask for clarification if you need it.
 

Reply